Nie, dziękuję Przekieruj mnie tamTL;DR: 6 kW of Stiebel-Eltron dynamic storage heaters kept a 60 m², 3.75 m-high flat at 20 °C for PLN 270–300/month—“With properly selected radiators the system should be financially viable” [Elektroda, SzokalML, #8885192; Elektroda, szymonjasiu, #8287679].
Why it matters: Tenement owners on a 12 kW G12 supply can cut bills and avoid cold spots by choosing, locating and wiring electric heaters correctly.
• Typical heat demand in pre-war brick flats: 70–120 W/m²; OP achieved comfort at 100 W/m² with 6 kW total [Elektroda, SzokalML, post #8885192] • Used 3 kW dynamic heater weight: 140–168 kg; budget PLN 1 000–1 200 each including transport [Elektroda, SzokalML, post #8885192] • Night-day G12 tariff split: 22:00-6:00 plus 13:00-15:00 off-peak; off-peak unit price ≈ PLN 0.36/kWh, peak ≈ PLN 0.60/kWh [Elektroda, berga, post #8604968] • 12 kW 3-phase connection supports 3×16 A; loading one phase above 5.8 kW trips 25 A breaker on 2.5 mm² cable [Elektroda, SzokalML, post #8605846] • Heat-pump air-cons with “winter package” operate down to −20 °C but lose efficiency below −7 °C [Elektroda, robertw28, post #8367923]