Replacing Aluminum with Copper Wiring: Feasibility of Installation Above Suspended Ceiling?

Emiliano 33187 9
Best answers LABEL_AI_GENERATED

Can I route a new copper electrical installation above a suspended ceiling and then drop cables vertically to the sockets, and can I use 3x1.5 mm² instead of 3x2.5 mm² for the TV room sockets?

Yes, you can run the installation above the suspended ceiling, but the cables should be mechanically protected there, for example in conduit or PVC trays, and the connections should remain accessible in boxes under the fittings rather than hidden above the ceiling [#8687229][#8688067][#8687991] A canless solution is recommended in that ceiling space, because hidden boxes above the suspended ceiling would be inaccessible later [#8687229][#8687192] If you do use conduits, they should be laid so they can be removed or serviced if needed [#8687229] For socket circuits, use 3x2.5 mm²; 3x1.5 mm² is not the recommended choice for sockets [#8687192] It is also advised to size the conduits generously enough to allow later cable replacement or adding new cables without reopening the walls [#8688067]
AI summary based on the discussion. May contain errors.
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 8686705
    Emiliano
    Level 12  
    Posts: 92
    Help: 1
    Rate: 6
    Hello,
    During the renovation of the house, I decided to replace the old aluminum electrical installation with a new copper one. There will be a suspended ceiling in each room. I wanted to ask experienced electricians if there are any contraindications to place it above the suspended ceiling instead of boxes and cable routing in the plaster and to lead the cables vertically from above to the sockets in the plaster? In addition, I wanted to know if in the room where the TV will be located, I could use 3x1.5 mm cables instead of 3x2.5 mm?

    greetings
    Emil
  • ADVERTISEMENT
  • #2 8687192
    grzesdc
    Level 16  
    Posts: 238
    Help: 5
    Rate: 50
    cable in a conduit, cans and so will be above the ceiling - inaccessible. 2.5mm is used for socket circuits.
  • #3 8687229
    Miniax
    Electrician specialist
    Posts: 1438
    Help: 173
    Rate: 290
    As my colleague wrote above, the cable should have some protection against mechanical damage (e.g. conduit). As for the cans, in this case the most practical solution will be a canless installation. It will take up more wire, but in the event of a breakdown you won't have to smash the ceilings.
    Of course, if you already use conduits, it's best to install them so that they are removable :)
  • ADVERTISEMENT
  • #4 8687265
    grzesdc
    Level 16  
    Posts: 238
    Help: 5
    Rate: 50
    with a conduit it's hard to do
  • #5 8687349
    Emiliano
    Level 12  
    Posts: 92
    Help: 1
    Rate: 6
    Thanks for the answers. I am aware that I could get to the cables only after breaking the ceiling. Instead of cans, I just wanted to twist the cables and put them on this suspended ceiling, but I do not know if it does not differ from the standards governing the installation of electrical installations.
  • #6 8687514
    grzesdc
    Level 16  
    Posts: 238
    Help: 5
    Rate: 50
    to turn? Are you kidding me?

    Maybe leave this installation replacement to someone who has the authority and knowledge.
  • ADVERTISEMENT
  • #7 8687681
    Emiliano
    Level 12  
    Posts: 92
    Help: 1
    Rate: 6
    I think the cables need to be connected somehow. On other forums I read that twisted pair is a sure connection point. And what do you suggest instead of a twisted pair?
  • ADVERTISEMENT
  • #8 8687707
    miler80
    Level 34  
    Posts: 2143
    Help: 272
    Rate: 1395
    Make a good twist and break the twisted pair, insulate it, put it in a sealed airtight box. In practice, most electricians do this, and that's fine.
  • #9 8687991
    robert_sz
    Level 16  
    Posts: 105
    Help: 15
    Rate: 23
    I had a similar case to the thread described by the author.

    Our solution was like this:
    We hung PVC trays (upside down) on the ceiling, and arrange the cables to the rooms in the trays. When laying the cables, pieces of 2-4 cm covers were helpful, with which we blocked the cable so that it would not fall onto the floor.
    If there were more sockets on the same wall in the room, we made one furrow vertically and the rest horizontally.
    It was a great album and the difficulties it involved. We had to do some of the installation with a flat DYT cable.
    All canned joints so as not to demolish the ceiling.

    We decided to use lockable trays, because during the works, additional customer requests were on the agenda.
  • #10 8688067
    kkas12
    Level 43  
    Posts: 17400
    Help: 1076
    Rate: 4312
    Hello!

    Peszel in such installations is a pointless excess of form over content.
    One of my colleagues presented the use of a PVC trough. And this is approximately how it should be done. In addition, pipes should be placed in the walls between the fixtures and the space between the suspended ceiling and the ceiling, and of course no boxes in this space. Pipes, of course, of the right diameter and in such a number that the possible replacement or addition of new cables does not force the walls to be forged again.
    All connections should be made in boxes under the fittings.

    Nowhere in the world is g / k disc treated with such exaggerated care as some colleagues recommend here.
    Cutting out any mounting holes and their re-patching is a cost of several dozen zlotys. So it's time to end this exaggerated concern, no matter what.

Topic summary

LABEL_AI_GENERATED
The discussion revolves around the feasibility of installing copper wiring above suspended ceilings during a home renovation, replacing old aluminum wiring. Key points include the necessity of protecting cables from mechanical damage, preferably using conduits or PVC trays for organization. Participants emphasize the importance of adhering to electrical standards and suggest avoiding inaccessible installations that would require ceiling demolition for repairs. The use of 3x1.5 mm cables instead of 3x2.5 mm for TV locations is questioned, with recommendations leaning towards using appropriate gauge cables for socket circuits. Overall, the consensus is to ensure proper installation techniques to facilitate future access and modifications.
AI summary based on the discussion. May contain errors.