zybie wrote: check if the pump is really spinning, because it may be blocked
canon314 wrote: The pump works, when the radiators are deaerated, I run out of dirty water with rust.
Actually, you should check it out more closely. It may turn out that the pump actually does not pump. The fact that you are spraying water with rust from your radiators is not enough, because in the system after "tapping" the water you have a pressure higher than the atmospheric pressure and hence it is obvious that the water will leak through the radiator.
The pump, on the other hand, can work but not forcing, e.g. the impeller is twisted. The motor may spin, but the rotor will stop. I do not know this pump, but since you have 25-40 in the designation, the Grundfos equivalent has a lifting height of 4 meters, so water in the installation up to 4m should "flicker".
The fact that eventually "something will move" is normal even in a system without a circulation pump.
Added after 2 [minutes]: The stove is on the same level as the installation? Is it in the basement? The flat where? Maybe the level difference is more than 4 meters?