Nie, dziękuję Przekieruj mnie tamsoprano1085 wrote:so do you think that this scheme from "castorama" was developed by someone not competent ??
I was just following him and I was convinced that no one was doing this scheme
So what do you think? that the four-track FR is redundant and the C20 is also redundant ?? and if so, why ??
Please correct your spelling. [kkas12]
kkas12 wrote:Hello!
The four-track FR is not only redundant, but also introduces the risk of damaging the receivers. Apart from the groundlessness of interrupting the N track in simple installations that do not require it, the four-line FR is completely unsuitable as the main switch of the switchboard from which single-phase circuits are derived.
The reason is that the N line is not marked. So this switch will not disconnect a specific (marked) contact as the last one and will not close it as the first one. And what happens in the event of a break in this path (N) needs no explanation.
It is the manufacturer, not the seller, that decides whether the surge arrester is backed up.
Each manufacturer specifies the upper value of the protection preceding the switch disconnector, above which back-up is required.
This is also the case with LEGRAND.
http://serwis-klienta-legrand.pl/download/a95e029c/ochronniki_paniemprzepieciowe.pdf
PS
I suggest experimentally how the FR contacts close.
All you need is any voltage source (preferably Ul), four controls and the appropriate connection system.
Plumpi wrote:Interestingly, they will be disconnected and if someone does not look into the switchgear for several months, he will be unaware that they will never work. It would be appropriate to at least bring out the switchgear light informing about open "back-up" but rather nobody does it at home?As for the C20, it is not superfluous, on the contrary it is very much needed. This is called backing up protectors. It works in such a way that when an overvoltage occurs in the arrester, a short-circuit occurs and the excess charge is brought to the ground through the PE protective circuit (i.e. the PE strip, the PE conductor connecting to the GSW, the ground conductor and the earth electrode).
The protectors can absorb a certain amount of energy and give it back to the environment in the form of heat. Part of the overvoltage energy is also released as heat in PE conductors.
However, at the time of discharge, an ionized channel is formed in the arrester through which, apart from the surge current, the short-circuit current of the network also begins to flow. If there was no such protection of the arresters, this short-circuit current could cause complete damage to the arrester in which the discharge occurred before the circuit breaker in the terminal disconnects the entire supply circuit. The additional protection disconnects the circuit of the arresters, limiting the amount of energy released in the arrestor as a result of the short-circuit current flow, and thus protects quite expensive arresters against their complete damage.
kkas12 wrote:
I propose to empirically check how the FR contacts close.
All you need is any voltage source (preferably Ul), four controls and the appropriate connection system. [/ I]
Quote:The results of many years of recordings show that during the year, overvoltages with the following amplitude distribution appear at any point in the low-voltage electrical installation:
300 to 500 V - several hundred cases,
500 to 1000 V - several dozen cases,
1000 to 5000 V - several cases,
over 5000 V - a few cases.
elpapiotr wrote:Buddy Bronek - first reading , then a statement.
bronek 22 wrote:Dr. Musiał writes about topics. Even giving the characteristics.It's a different topic, it's just a short piece of resistance wire. L = 0.
zdzisiek1979 wrote:in which - when you look at them - is full of errors (sometimes deliberately placed - because only sales counts).Go here and there are two brochures on overvoltages and read up on the installation of arresters. http://moeller.pl/DesktopDefault.aspx?PageID=800
Plumpi wrote:
As for the C20, it is not superfluous, on the contrary it is very much needed. This is called backing up protectors. (...)
elpapiotr wrote:you can find out more about SPD coverage.