Correct Connection: Surge Arrester -> Residual Current Device -> Overcurrent Circuit Breaker

piomar93 40404 12
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 17120752
    piomar93
    Level 5  
    Hello gentlemen!
    I have a question about connecting a surge arrester with a residual current device. Is the given scheme correct? I mean the switchgear itself in the building: surge arrestor -> residual current circuit breaker -> overcurrent circuit breaker -> receiver.

    Regards Correct Connection: Surge Arrester -> Residual Current Device -> Overcurrent Circuit Breaker
  • ADVERTISEMENT
  • #2 17120766
    mawerix123
    Level 39  
    It is not correct, there is no disconnector and the PEN must not be separated on the apparatus. For this, this protector is not intended for TN-C networks
  • #3 17129449
    piomar93
    Level 5  
    So this connection will be correct?
    Correct Connection: Surge Arrester -> Residual Current Device -> Overcurrent Circuit Breaker
  • ADVERTISEMENT
  • #4 17129472
    mawerix123
    Level 39  
    Protector behind the disconnector and grounding to the PEN bus, N bus not required.
    By the way, RCD is necessary :?:
  • #5 17130404
    pol102
    VIP Meritorious for electroda.pl
    piomar93 wrote:
    So this connection will be correct?
    Correct Connection: Surge Arrester -> Residual Current Device -> Overcurrent Circuit Breaker

    Let a friend take it so logically. How to replace the insert in the limiter when the voltage cannot be removed effectively? As a reminder, the switch disconnector did not take the name from the "pins".
  • ADVERTISEMENT
  • #6 17130793
    Brivido

    Level 34  
    pol102 wrote:
    piomar93 wrote:
    So this connection will be correct?
    Correct Connection: Surge Arrester -> Residual Current Device -> Overcurrent Circuit Breaker

    Let a friend take it so logically. How to replace the insert in the limiter when the voltage cannot be removed effectively? As a reminder, the switch disconnector did not take the name from the "pins".

    And some counter, pre-meter security? I think they are ;)
  • ADVERTISEMENT
  • #7 17131205
    Łukasz-O
    Admin of electroenergetics
    Brivido wrote:

    And some counter, pre-meter security? I think they are ;)


    Nonsense, this is a disconnector to disconnect the entire switchgear and not selected circuits.
    In addition, the arrester is to protect installations even if FR is switched off.
  • #8 17131379
    kortyleski
    Level 43  
    mawerix123 wrote:
    , N rail not required.

    Note that a colleague writes about the receiver and paints the engine. The motor rather protector does not need a different receiver, however, may need an N bus. As usual, residual information and a request for help.
  • #9 17131392
    piomar93
    Level 5  
    Is the engine not a receiver? In addition, I drew briefly, I mainly meant the limiter itself and the RCD. I will not draw all the socket and lighting circuits. Gentlemen, I mean the idea!
  • #10 17132553
    pol102
    VIP Meritorious for electroda.pl
    Well, you have everything written. Working behind an RCD turned off or a circuit breaker is an unnecessary risk and stress. A colleague has never heard of glued contacts?
  • #11 20161899
    PIOTREL
    Level 26  
    Hello
    I read this topic because I face a similar dilemma myself.
    If there are BM protections in the sequence in front of the meter, then a power limiter, a meter, you can put a surge arrester after it, then a switch disconnector and all the rest? There are different schools. What do colleagues think about this?
    I am asking because I want to split it into two circuits, each one on a different level, behind the limiter. Each floor, circuit would start with a switch disconnector.
  • #12 20161909
    Łukasz-O
    Admin of electroenergetics
    There is only one school. The limiter is to be behind FR.
  • #13 20161923
    PIOTREL
    Level 26  
    So in my case, I would have to install two surge arresters for each floor.

Topic summary

The discussion revolves around the correct connection sequence of a surge arrester, residual current device (RCD), and overcurrent circuit breaker in electrical installations. Initial responses indicate that the proposed connection lacks a disconnector and improperly separates the PEN conductor, which is not suitable for TN-C networks. Subsequent replies emphasize the necessity of placing the surge arrester after a disconnector and grounding it to the PEN bus. The importance of RCDs is highlighted, with concerns about operational risks when devices are not properly isolated. The conversation also touches on the need for multiple surge arresters when splitting circuits across different levels in a building.