How should a surge arrester, residual current device, and overcurrent circuit breaker be connected in building switchgear, and is the order surge arrester -> RCD -> overcurrent breaker correct?
No, that order is not correct; the surge arrester should be placed behind the disconnector/FR, not before it, and it is not intended for TN-C networks where PEN is separated in the device [#17120766][#17129472] Ground the arrester to the PEN bus; an N bus is not required in that arrangement [#17129472] An RCD is still necessary [#17129472] The arrester should also protect the installation even when the FR/disconnector is switched off [#17131205]
  • #1 17120752
    piomar93
    Rate: 14
    Hello gentlemen!
    I have a question about connecting a surge arrester with a residual current device. Is the given scheme correct? I mean the switchgear itself in the building: surge arrestor -> residual current circuit breaker -> overcurrent circuit breaker -> receiver.
    Regards Correct Connection: Surge Arrester -> Residual Current Device -> Overcurrent Circuit Breaker
  • #2 17120766
    mawerix123
    Help: 482
    Rate: 951
    It is not correct, there is no disconnector and the PEN must not be separated on the apparatus. For this, this protector is not intended for TN-C networks
  • #3 17129449
    piomar93
    Rate: 14
    So this connection will be correct?
  • #4 17129472
    mawerix123
    Help: 482
    Rate: 951
    Protector behind the disconnector and grounding to the PEN bus, N bus not required.
    By the way, RCD is necessary :?:
  • #5 17130404
    pol102
    Help: 163
    Rate: 369
    Let a friend take it so logically. How to replace the insert in the limiter when the voltage cannot be removed effectively? As a reminder, the switch disconnector did not take the name from the "pins".
  • #6 17130793
    Brivido
    Help: 226
    Rate: 430
    And some counter, pre-meter security? I think they are ;)
  • #7 17131205
    Łukasz-O
    Admin of electroenergetics
    Help: 654
    Rate: 4292
    Nonsense, this is a disconnector to disconnect the entire switchgear and not selected circuits.
    In addition, the arrester is to protect installations even if FR is switched off.
  • #8 17131379
    kortyleski
    Help: 957
    Rate: 3860
    mawerix123 wrote:
    , N rail not required.
    Note that a colleague writes about the receiver and paints the engine. The motor rather protector does not need a different receiver, however, may need an N bus. As usual, residual information and a request for help.
  • #9 17131392
    piomar93
    Rate: 14
    Is the engine not a receiver? In addition, I drew briefly, I mainly meant the limiter itself and the RCD. I will not draw all the socket and lighting circuits. Gentlemen, I mean the idea!
  • #10 17132553
    pol102
    Help: 163
    Rate: 369
    Well, you have everything written. Working behind an RCD turned off or a circuit breaker is an unnecessary risk and stress. A colleague has never heard of glued contacts?
  • Clarifying surge arrester placement after meter and limiter
    #11 20161899
    PIOTREL
    Help: 41
    Rate: 172
    I read this topic because I face a similar dilemma myself.
    If there are BM protections in the sequence in front of the meter, then a power limiter, a meter, you can put a surge arrester after it, then a switch disconnector and all the rest? There are different schools. What do colleagues think about this?
    I am asking because I want to split it into two circuits, each one on a different level, behind the limiter. Each floor, circuit would start with a switch disconnector.
  • #12 20161909
    Łukasz-O
    Help: 654
    Rate: 4292
    There is only one school. The limiter is to be behind FR.
  • #13 20161923
    PIOTREL
    Help: 41
    Rate: 172
    So in my case, I would have to install two surge arresters for each floor.
The discussion revolves around the correct connection sequence of a surge arrester, residual current device (RCD), and overcurrent circuit breaker in electrical installations. Initial responses indicate that the proposed connection lacks a disconnector and improperly separates the PEN conductor, which is not suitable for TN-C networks. Subsequent replies emphasize the necessity of placing the surge arrester after a disconnector and grounding it to the PEN bus. The importance of RCDs is highlighted, with concerns about operational risks when devices are not properly isolated. The conversation also touches on the need for multiple surge arresters when splitting circuits across different levels in a building.
TL;DR: Use a Type 1+2 SPD near the origin; coordinate with FR and RCDs. 30 mA RCDs protect sockets. "Install SPDs as close as possible to the origin." For electricians and advanced DIYers aligning TN wiring and device order. [Schneider Electric, 2022]
Why it matters: The right SPD–FR–RCD order avoids nuisance trips, preserves protection, and simplifies safe maintenance in TN systems.
  • Residual current protection: 30 mA for additional protection; consider 100–300 mA upstream for fire protection, where permitted. [Schneider Electric, 2022]
  • In TN‑C, bond the SPD to the PEN bar; do not split PEN, and skip the N bar if unused. [Elektroda, mawerix123, post #17129472]
  • One stated practice: place the SPD behind the main disconnector (FR), then feed RCD/MCBs. [Elektroda, Łukasz-O, post #20161909]
  • If the feeder from the entry SPD to a sub-board exceeds ~10 m, add a downstream SPD stage. [Phoenix Contact, 2020]
  • Keep total SPD lead length (phase/neutral to PE) as short as possible, typically ≤0.5–1 m. [DEHN, 2014]
Is SPD -> RCD -> MCB -> load the correct order?
Not without a main disconnector (FR) and proper PEN handling. Place the SPD behind the disconnector and bond it to the PEN bar. Skip the N bus when the load does not need neutral. Then feed the RCD and MCBs as required. [Elektroda, mawerix123, post #17129472]
Where should the SPD go relative to the main disconnector (FR)?
Follow the stated practice: “There is only one school. The limiter is to be behind FR.” That puts the SPD on the load side of the disconnector. It then protects the board and downstream circuits while FR is on. [Elektroda, Łukasz-O, post #20161909]
Can the SPD still protect when the FR is switched off?
One expert noted, “the arrester is to protect installations even if FR is switched off.” To keep protection with FR open, installers place the SPD upstream of FR. Confirm utility rules for any device before the meter, and ensure safe isolation procedures. [Elektroda, Łukasz-O, post #17131205]
Do I need an RCD on a motor circuit?
Use 30 mA RCDs for socket-outlet circuits for additional protection. Fit RCDs on motor circuits when required by standards, environment, or risk assessment. Use selective or high-immunity types if leakage or drives cause trips. Coordinate RCDs with the SPD for reliable operation. [Schneider Electric, 2022]
How should I connect an SPD in a TN‑C system?
Do not separate the PEN conductor inside devices. Use an SPD model suitable for TN‑C and bond it directly to the PEN bar. As warned: “PEN must not be separated on the apparatus.” Some SPDs are not intended for TN‑C networks. [Elektroda, mawerix123, post #17120766]
How do I replace an SPD module safely?
Use a safe isolation routine. 1) Open the main disconnector (FR) to de-energize the switchgear. 2) Verify absence of voltage with an approved tester. 3) Withdraw the SPD cartridge and fit the replacement, then restore power. Do not rely on upstream fuses alone for isolation. [Elektroda, pol102, post #17130404]
Are there risks when working behind a switched-off RCD or breaker?
Yes. Contacts can weld (“glued contacts”), leaving parts live even when switched off. Always test for absence of voltage before contact. Lock out the supply if possible. Use devices certified for isolation when you need safe disconnection. [Elektroda, pol102, post #17132553]
How do I prevent nuisance RCD trips caused by SPDs?
Place SPDs upstream of RCDs so surge currents bypass the RCD, or use selective/time-delayed RCDs. Keep leads short and bonding direct to reduce residual surge currents. This coordination minimizes unwanted RCD tripping during surge events. [Phoenix Contact, 2020]
Do I need one SPD per floor or sub-board?
Add SPDs in downstream boards when the feeder exceeds about 10 m or each board has its own disconnector. Cascaded stages limit energy at each level. For two floors with separate main switches, fit SPDs in both boards. [Phoenix Contact, 2020]
Where do I bond the SPD in a TN‑C‑S board?
Bond the SPD to the PEN/PE bar in the main distribution board. Keep connections short and straight to minimize voltage rise. Do not route through the N bar unless needed for the SPD type. [Elektroda, mawerix123, post #17129472]
Is an N bus required if I only feed a three‑phase motor?
No. If the motor does not need a neutral, omit the N bus. Connect the SPD to the PEN bar and supply the motor through appropriate overcurrent protection and control gear. [Elektroda, mawerix123, post #17129472]
Is my SPD compatible with TN‑C networks?
Not all SPDs fit TN‑C. An SPD meant for TN‑S/TN‑C‑S may be unsuitable in TN‑C. Select a model specifically rated for TN‑C, and never split PEN inside the device. [Elektroda, mawerix123, post #17120766]
Which SPD class and rating should I use at the service entry?
Use a Type 1 or Type 1+2 SPD at the origin. Choose lightning current capability to match the installation; 12.5 kA Iimp per pole is common. Match backup overcurrent protection to the SPD’s datasheet. [Phoenix Contact, 2020]