GSW Bus Connection: Understanding PE Rail, WLZ Wires, PEN Separation, and Grounding Earth Electrode

ROSOMAK7 37959 27
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 11985782
    ROSOMAK7
    Level 15  
    Hello, I know that the topic has been discussed many times, but somehow it does not appeal to me.
    Namely, what should the GSW bus connection look like? Let's assume that we have a four-wire WLZ led to the RG, where the separation (on the PE bus) PEN to PE and N is connected to the PE bus, sockets are connected to the PE rail, and then we pull the (thick) wire from the PE bus to the GSW located e.g. in the basement to which we connect metal pipes, taps, bathtubs, boiler ... and the GSW itself is connected to the hoop iron which is screwed to the foundation earth electrode. I understand it well? Should it look like the picture shows? GSW Bus Connection: Understanding PE Rail, WLZ Wires, PEN Separation, and Grounding Earth Electrode
  • ADVERTISEMENT
  • Helpful post
    #2 11986145
    .Jack
    Electrician specialist
    ROSOMAK7 wrote:
    Should it look like the picture shows?

    Actually, the idea is like the picture shows.
    You should only strive for the equalizing rail to be as close as possible to the conductive media introduced into the building, which are preferably close to each other in one place.
  • #3 11986415
    gogi20
    Level 24  
    ROSOMAK7 wrote:
    then, from the PE rail, pull the (thick) cable to the GSW located e.g. in the basement to which we connect metal pipes, taps, bathtubs, boiler .......

    If, for example, metal taps are not on metal pipes, but the installation is made of plastic, we do not ground such taps. The same goes for other metal sanitary "fixtures". I do not know if you know about it, but I wrote it so as not to miss it.
  • #4 11986455
    ROSOMAK7
    Level 15  
    Yes, I know that taps on plastic pipes are not grounded, acrylic bathtubs ... sometimes in such a small single-family house, there is nothing to ground? What exactly is a foundation earth electrode? is the slab reinforcement? if so, we attach a rope to it and that's it? because reinforcement is not connected to the ground. So the hoop also has to go into the ground?

    The sentence starts with a capital letter. [retrofood]

    Added after 2 [minutes]:

    Or maybe thick wire driven into the ground is used for this and connected to the reinforcement and then concreted?
  • #6 11986494
    kkas12
    Level 43  
    Buddy, recommended (obligatory?) Reading.
    Firstly Link
    Later PN HD 60364 5-54.

    Without familiarizing yourself with these materials, you will not know what to do and why.
  • #7 11986515
    ROSOMAK7
    Level 15  
    Ok, if the house has several floors, then you have to connect to each "slab" or only to the lowest one?
  • ADVERTISEMENT
  • #8 11986523
    kkas12
    Level 43  
    Read, read, read.
    The number of storeys does not affect the foundation earth electrode.
  • #9 11986544
    ROSOMAK7
    Level 15  
    kkas12 wrote:
    Buddy, recommended (obligatory?) Reading.
    Firstly Link
    Later PN HD 60364 5-54.

    Without familiarizing yourself with these materials, you will not know what to do and why.

    Ok, so far I'm not going to do anything, at most I'm trying to get SEP qualifications but first I'd like to know a little bit.

    Added after 4 [minutes]:

    Suppose it is 10m from GSW to, for example, a boiler and a stove, but these two devices are 2 meters apart. So is it enough to connect the stove to the boiler and then pull the cable to GSW? do both devices have to be connected separately?
    The question may be a little pointless.
  • Helpful post
    #10 11986620
    kkas12
    Level 43  
    However, you are probably lazy.

    What you are asking Dr. Musial explained in an accessible way.
    So is the norm.
    GSW Bus Connection: Understanding PE Rail, WLZ Wires, PEN Separation, and Grounding Earth Electrode
  • #11 11986788
    ROSOMAK7
    Level 15  
    Thanks for your help, I'll start reading as soon as I have time.
  • #12 11988328
    stomat
    Level 38  
    gogi20 wrote:

    If, for example, metal taps are not on metal pipes, but the installation is made of plastic, we do not ground such taps. The same goes for other metal sanitary "fixtures". I do not know if you know about it, but I wrote it so as not to miss it.

    I would like to add that we do not ground taps on metal pipes, we "ground" the pipes themselves.
  • #13 11988478
    janek1815
    Level 38  
    I read this and I have a confusion, since the house is only supplied with water through the PE pipe and the sewage system, what are we grounding? Metal bathtub only?
  • ADVERTISEMENT
  • #14 11988509
    .Jack
    Electrician specialist
    janek1815 wrote:
    what are we grounding?

    Even if there is nothing to ground, which I doubt, the first thing to do is grounding the PE busbar to which the green and yellow protective conductors of the receiving circuits are connected.
    It is supposed to be an equalization of potentials or a more difficult word like equipotentialization. This is what the circus is for.
  • ADVERTISEMENT
  • #15 11988517
    kkas12
    Level 43  
    Nothing but GSW is grounding buddy john1815 , but we include with equipotential bonding.
    And what should be included in these connections is presented by the standard and Dr. Musiał in the link I provided earlier.
  • #16 12002612
    Anonymous
    Anonymous  
  • #17 12003437
    kkas12
    Level 43  
    And when the equipotential bonding does not fulfill its role?
  • Helpful post
    #18 12003456
    .Jack
    Electrician specialist
    cKKqa wrote:
    Unfortunately, the use of these connections is obligatory in Poland.

    And what else is better than equipotential bonding?
    kkas12 wrote:
    And when the equipotential bonding does not fulfill its role?

    When there is no continuity between accessible and foreign conductive parts within reach and they hang in the air.
    Equalizing connections are designed to prevent long-term maintenance of dangerous voltage within the reach of the hands and are the most reliable method of protection against electric shock. How can their effectiveness be denied?
  • #19 12004093
    kkas12
    Level 43  
    If there is no connection between the accessible and non-accessible parts, then there is no potential equalization.
    So there is no equipotential bonding in this case.
  • #20 12004244
    Anonymous
    Anonymous  
  • #21 12004280
    kkas12
    Level 43  
    Either you write about equipotential bonding, which, unfortunately, should be performed obligatorily, or you write about equipotentialization of ground rooms with the use of a foundation earth electrode.
    These are two separate issues that must be distinguished.
    And if you think equipotentialization is lame, then the foundation earth electrode serves no purpose.

    And don't write crap about the paddling pool and first understand the correct definition of an alien part.
  • #22 12004444
    Anonymous
    Anonymous  
  • #23 12004501
    kkas12
    Level 43  
    Buddy, by the old habit, you introduce multithreading of the topic.
    You don't explain anything, but you use well-known slogans without any problems, confusing the topic more and more.
    Therefore, I propose to return to the statement about the misfortune introduced by the obligatory use of equipotential bonding.

    And once again, I appeal for a "rational" familiarization with the term foreign conductive part, because if our colleague had no problem with this, we would not read the above nonsense based on the paddling pool canvas.
  • #24 12004653
    ROSOMAK7
    Level 15  
    Observing your polemic, I think that the topic will probably be closed in a moment, so I would like to ask one more question before it happens. If a five-wire WLZ is connected to the RG, then should the GSU be connected to the earth? and maybe not use this fifth conductor (PE) at all?
    GSW Bus Connection: Understanding PE Rail, WLZ Wires, PEN Separation, and Grounding Earth Electrode
  • #25 12004683
    kkas12
    Level 43  
    Better not "judge" if they don't judge you.

    And why such a question, since both the doctor and the standard 5-54 do not make the performance of the grounded GSW dependent on whether PEN or PE is introduced into the switchgear (facility).
  • #26 12004757
    ROSOMAK7
    Level 15  
    Because if in this case it is grounded by the GSW (hoop iron) and in the cable joint, where the PEN split took place, PE has been grounded, then we have two groundings and it can't be so?
  • #27 12004783
    Miniax
    Electrician specialist
    cKKqa wrote:

    I have no problem with the definition of the foreign part, moderator. Maybe the paddling pool can introduce "positive" and "negative" potential, but if the paddling pool is not connected, how can it introduce anything?


    What potential is added, what is negative? What are you writing about?

    Besides, a shower tray which is not "structurally" earthed (eg through a sewage system) is not a foreign conductive part and should not be covered by equalizing connections.

    Another of your statements, which proves that you do not understand the definition of the foreign conductive part.
  • #28 12004817
    kkas12
    Level 43  
    Where did such a conclusion come from
    Quote:
    ... in the cable joint, where the PEN was split, PE has been earthed, we have two earthing points, and it can't be so?
    my friend ROSOMAK7? You are still not reading the indicated materials.
    You prefer to "educate" on the forum.
    But for God's sake, you must have some foundations.

    Grounding the PEN in the connector should not be of any concern to you. You shouldn't even ask if it was done.
    This is up to the energy supplier and nothing to do with you.

Topic summary

The discussion revolves around the proper configuration of the GSW bus connection in relation to grounding and equipotential bonding in electrical installations. Key points include the necessity of connecting the PE bus to the foundation earth electrode, the importance of grounding metal fixtures, and the distinction between equipotential bonding and grounding. Participants emphasize the need for compliance with standards such as PN HD 60364 5-54 and the significance of ensuring that all conductive parts are properly bonded to prevent dangerous voltage levels. The conversation also touches on the grounding of devices in multi-story buildings and the implications of using a five-wire WLZ system.