After this venting, has the head been opened (at least to a temperature that is higher than the current temperature in the room where the radiator is located)? If so (the best way to check this is to open the heating head to maximum), then there is a problem with the flow through the radiator. It's worth checking how the so called presetting is set (it acts as an orifice) and this can be checked by removing the thermostatic head (it looks like a Danfoss to me on the photo, so it should be quite simple). If it's a Danfoss (which it looks like it is), when you remove the head there will be a metal ring with numbers from 0 to 7 and then an N on it. The higher the number, the higher the flow of the heating medium through the radiator (N is the maximum flow - as if without an orifice and this setting is generally only used to flush the valve). On the brass body (on the screw side) there is a dot - a reference point - whichever number is opposite the dot indicates the setting. To change the setting, you have to pull the metal ring a little towards you and turn it (if it is not stained, you can do it with your fingers, if it is dirty, you may need to use e.g. a pair of pliers). In any case, if venting does not help (all indications are that there is no air), the cause is a lack of heating medium flow or a very weak flow. If the setting was on a low value and, in addition, the head was in the closed position all the time, the valve may have become silted up. If this is in Krakow (especially near the Ugorek housing estate) - I could come.