  • #1 12902761
    masiej2
    Level 10  
    Hello
    I have a problem, or rather a query, I have valves on the return shown in the photo:
    Heater Return Valves: Hexagon Socket Adjustment, Unscrew Valve, Improve Radiator Flow
    To the point, I marked the thread on which the cover cap comes in green, the key can be put on red, and the hexagon socket in blue and turned to the right or left. My question is, if I put the key on what I have marked in red, can I completely unscrew the inside of this valve and plug it with a screw-on plug (marked in green)?
    I have the impression that the flow is poor, the radiators' pits are cold, the Allen adjustment probably does not work, I don't really have the patience for it anymore ... I just want to improve the flow. I messed up a bit with what I wrote, but I hope it is understandable.
    Thanks in advance for any answers. Sorry if I posted my question in the wrong section. greetings
  • ADVERTISEMENT
  • #2 12902827
    W0jtek92
    Level 38  
    Hello, since the return valve is open to full and there is still poor circulation, maybe it is to blame for the supply valve, or some dirt clogged the supply valve and you have poor circulation. What is the installation? What is the source of heat?
  • #3 12902833
    tompotter
    Level 18  
    You can do that
  • #4 12902835
    Piotr77777
    Heating systems specialist
    Open the return valve to the max. I suspect that the limited flow is influenced by the installation made of PP, not the return valve.
  • #5 12902846
    masiej2
    Level 10  
    bake for everything :D 14KW. circulation pump 25/40 1 speed Installation of the PP pipe.
    Maybe it is to blame for covering, or also for dust, although I'm only interested in whether I can wring out this interior, blind it and whether it will work. I already have enough of these valves, I would like to change all of them to ball valves because you can get crazy. By the way, at what point is the return valve open to full?

    (as I burn in the stove, i.e. I start, I have, for example, 60 C at the exit, and the return may be 25 ... so something wrong with these returns, and after 15 minutes the return gets warm, but the supply temperature drops to 40 ... So it heats up quickly, flows worse, and cools down. And I would like a sensible circulation, on the furnace 60 return 50. Therefore, to my empty peasant mind, if I blow these inserts in the sense of the content of this return valve, the flow should be higher ????. The closed circuit installation (previously there was gas heating) worked well and the open circuit has problems.
  • #6 12902911
    Duduś74
    Moderator of HydePark
    masiej2 wrote:


    (as I burn in the stove, i.e. I start, I have, for example, 60 C at the exit, and the return may be 25 ... so something wrong with these returns, and after 15 minutes the return gets warm, but the supply temperature drops to 40 ... So it heats up quickly, flows less well, and cools down.


    The temperature drops because the pump is turned on, and since it does not heat up (there is a large heat consumption), the stove is too weak.
    Enter the heating surface of the building, number and size (power) of radiators.
  • #7 12902923
    masiej2
    Level 10  
    the pump is running all the time. It is not the fault of a poor stove or heaters.
    I mean the flow itself. It takes too long, it is too weak, and I just want to increase it. Not to raise the pump to 2nd or 3rd gear, but to stay in 1st gear, but to increase the flow.
  • ADVERTISEMENT
  • #8 12902965
    Duduś74
    Moderator of HydePark
    Higher flow means that your stove will cool down even faster. But if you insist so, then since unscrewing the flanges at full does not give you anything, then, as the previous speakers wrote, you have clogged somewhere or too small diameter of the pipes, or too weak a pump.
    So:
    Duduś74 wrote:

    Enter the heating surface of the building, number and size (power) of radiators.
  • #9 12903020
    masiej2
    Level 10  
    heating area about 95 m2. 3 heaters 120cm v22, 3 heaters 180cm v22, and 2 small ladders in the bathrooms.
  • #10 12903103
    Zbigniew Rusek
    Level 38  
    14kW of boiler power is the "excess" power for this living area. Surely the cause of bad heating is poor flow. What are the radiator supply valves? If it is modern (with a thermostatic head), you can change the setting after removing the head. It may also be that the closure is OK, but the thermostatic head choked the flow because it sensed that the room has reached the set temperature (reducing the flow causes the radiator to become cool at the bottom, although generally more heat is needed from the legs than from the back) ). This may be the case sometimes, especially with oversized radiators. You need to check whether turning the thermostatic head to a higher temperature in the room will result in better heating at the bottom. If not, it is to blame (the thermostatic valve could also get fouled up) or too small cross-sections of the pipes.
  • #11 12903110
    MarudaP
    Level 21  
    Check the supply and return on all radiators to see if there are any big differences and how this will change when you turn the pump on at higher speed.
  • #12 12903135
    masiej2
    Level 10  
    My radiators are mainly set to N or 7 (this is on the radiator supply) and on the return this "super" valve I do not know how to set, left or right? (hence the idea to twist the entire cartridge out, if anything is possible, in my opinion yes). The pump is on the return.
    If you set the pump to 2nd or 3rd speed, the highest radiator, i.e. the ladder in the bathroom, stops heating, while the pipe that goes to the vessel starts to heat less in the middle.
    so the supply heaters are warming up nicely, although the returns are cold. So, I repeat my "hello" question, can I unscrew the inside of these return valves and plug them? will this increase my expected flow so that the returns are also warm ??
  • ADVERTISEMENT
  • #13 12903175
    MarudaP
    Level 21  
    Probably like all valves, by turning it to the left - we open, and right - we close. If it is a ball it is possible to make a turn by 90 *, if it is a regular one it is possible to make a few turns. The inside of the valve can be removed and plugged with a plug, but for this operation you need to drain the water from the system.
  • #14 12903180
    masiej2
    Level 10  
    Thank you very much for the answer regarding the removal of the inside of the valve.
    Now the question is, will removing it and blinding it increase the flow ??
  • #15 12903332
    MarudaP
    Level 21  
    Probably not much. Rather, I suppose some muck is blocking the drain somewhere and a rinsing could be done. And by the way, don't you hear "trickling" somewhere?
  • #16 12903353
    Duduś74
    Moderator of HydePark
    You can unscrew the middle from the valve and screw the cap (of course with the gasket) and the flow may increase a bit. But the rule is, if the stove is "boiling," and the radiators do not heat up or heat up poorly, you have problems with heat reception, i.e. radiators too small, pipes diameter too small, choked radiators, pipes, etc.
    And if you can't reach the temperature on the stove, it means that the stove power is low.
    If it is an all-purpose stove, take into account that the power and efficiency of the stove are given for a specific type of fuel. For the most part (I omit wood gasification boilers) power and efficiency are given for hard coal. What does this mean in practice, while burning everyone, the power of such a furnace drops from the alleged 80 percent to about 50%, and later comes as a surprise: the furnace is OK, and it heats poorly.
  • #17 12903377
    masiej2
    Level 10  
    I don't hear any strange noises. What is better to leave or wring out?
    I don't know anymore ...
  • #18 12903391
    MarudaP
    Level 21  
    The drain valve is for when it is necessary to dismantle the radiator, close both valves, put the cuvette under the radiator and take it off. We go with him outside the house and rinse.
  • #19 12903689
    marcin273
    Level 17  
    Take a picture of this pump in the boiler room as it is installed. Check the filter is clean. If you can (you have shut-off valves), unscrew the 4 Allen screws and check that the impeller is not killed, something or melted and that it turns when the pump is turned on. Check the differential valve if the ball has not hung up after turning on the pump you should hear the ball hit.
  • ADVERTISEMENT
  • #20 12903739
    Anonymous
    Anonymous  
  • #21 12903792
    das160
    Level 15  
    Hello
    1 The return radiator valve is correct and absolutely should not be replaced
    ball valve - ball valve, designed for installation, e.g. hot utility water,
    2 Return radiator valve, by unscrewing the hexagonal socket to the left, we open the max
    100% nut - do not remove the insert
    3 Poor flow on all radiators could indicate clogged filter in front
    pump co
    4 if the boiler does not reach the temperature, - too low boiler power, low calorific value
    fuel.
    5
    Quote:
    To the point, I marked the thread on which the cover cap comes in green, you can put the key on in red, and the hex key on the blue and turn it to the right or left

    Who do you expect advice from - a person whom you need to explain what the return valve looks like?

    Now my advice:
    Open all return valves and check the filter in front of the CH pump, watch the temperature on all radiators.
    Take a photo or draw a central heating pump connection diagram, write whether the system is old or new, write how many square meters you heat, and what is the thermal insulation of the building.
    You write that increasing the pump speed limits the flow - this must be some error in the installation.

    Heater Return Valves: Hexagon Socket Adjustment, Unscrew Valve, Improve Radiator Flow
  • #22 12904067
    dareksin
    Level 16  
    das160 wrote:
    Now my advice:
    Open all return valves and check the filter in front of the CH pump, watch the temperature on all radiators.
    Take a photo or draw a central heating pump connection diagram, write whether the system is old or new, write how many square meters you heat, and what is the thermal insulation of the building.
    You write that increasing the pump speed limits the flow - this must be some error in the installation.


    Also check if you have a check valve in front of the pump?

    If you have this check valve to transfer behind the pump.
  • #23 12904817
    masiej2
    Level 10  
    I cleaned the filter, it's okay. The case looks like this, I am burning in the stove, I have 60 degrees on it. return around 25st. After 15 minutes, the return is around 45-50, but the temperature in the furnace also drops to 45-50.
    My point is to make the flow better ...
  • #24 12905422
    MarudaP
    Level 21  
    Correct reaction. The conclusion is, the water must have a closed circuit somewhere in front of the radiators. There is no need to do without a drawing of the installation.
  • #25 12905448
    dareksin
    Level 16  
    Exactly. Draw us.

    If the supply and return temperatures are similar and the radiators are only slightly warm, does most of the water return in a shorter way?
  • #26 12905764
    das160
    Level 15  
    Hello
    Quote:
    The case looks like this, I am burning in the stove, I have 60 degrees on it. return around 25st. After 15 minutes, the return is around 45-50, but the temperature in the furnace also drops to 45-50.
    My point is to make the flow better ...


    1 A greater flow takes energy from the boiler to the radiators, where the energy is transferred to the room, and cold water returns - most often it is a difference of about 20 oC, e.g. 70/50
    2 In your case, the boiler has too low power, since the temperature drops from 60 to 45 after the radiators are energized - and no greater flow will do anything here, because the temperature has dropped on the boiler, where to get the energy to power the radiators if there is no heat in the boiler?
    3 You have some mistake, but without photos or a detailed sketch, I will not help you,
    4 Write whether the system is old or new, write how many square meters you heat, and what is the thermal insulation of the building, how many radiators you have - these are important data
    5 If you have automatic head radiator valves, unscrew the heads and check that the needle is not seized and that it returns to the open position.
    6 If you had a problem with the flow, the temperature in the boiler would increase - no energy consumption,
    7 Your problem is elsewhere, so please describe your installation.

    Heater Return Valves: Hexagon Socket Adjustment, Unscrew Valve, Improve Radiator Flow

    Heater Return Valves: Hexagon Socket Adjustment, Unscrew Valve, Improve Radiator Flow
  • #27 12905932
    masiej2
    Level 10  
    Unfortunately, I will not do the drawing, because the installation is 10 years old, I have no idea how the pipes go, etc. There is no sense in digging that far.
    So what, set all of them to the highest flow, i.e. N, the lower valves on the hex key to the maximum left, and this will be the highest flow. I just mean that the radiators should be all warm, top and bottom.
  • #28 12906182
    das160
    Level 15  
    Quote:
    So what, set all of them to the highest flow, i.e. N, the lower valves on the hex key to the maximum left, and this will be the highest flow. I just mean that the radiators should be all warm, top and bottom.


    This will be the greatest flow, assuming the control valves are operational, of course.
    However, as you wrote yourself, the temperature in the boiler drops to 45oC, where will you get the energy to heat the radiators?
    The flow distributes the energy to all radiators, but it has to take it from the boiler and the boiler is cold for you.
  • #29 12906770
    masiej2
    Level 10  
    Hmm, I will throw something more than 1 piece of wood into the cauldron :D ?
    well, what if they are not operational? so if I unscrew the interior from the return valves, the flow should improve, right ??
  • #30 12906883
    FOSGEN1
    Level 27  
    You have denied this increase in flow. The boiler, as colleagues write, has an allowance that the temperature drops for a while, it is probably normal, because the boiler returns cold from the system. Aren't you trying to smoke all day with that one piece of wood? Do you have any knowledge of how this boiler heated in previous seasons?

Topic summary

The discussion revolves around issues with heater return valves, specifically regarding their adjustment and the impact on radiator flow. The user inquires about the possibility of unscrewing the interior of the return valve to improve flow, as they are experiencing poor circulation and cold spots in their radiators. Responses suggest that the problem may not solely lie with the return valve but could also involve the supply valve, dirt in the system, or inadequate pump power. Several participants recommend checking the entire heating system, including the pump, filters, and radiator settings, to identify blockages or inefficiencies. The consensus is that while unscrewing the valve may provide some improvement, it is essential to ensure that all components of the heating system are functioning correctly to achieve optimal flow and heating efficiency.