Integra 128 & ETHM-1 Connection: Remote Access Blocked via DloadX, Satellite RJ/pin5 Cable

pawel448 28605 19
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 12403111
    pawel448
    Level 9  
    Hello,
    I have a 128 integrated connected to the ETHM-1 via a Satellite RJ/pin5 cable, and connected to the local network.
    Connection via www works without any problems, the problem occurs when you try to connect via DloadX, the following message appears: "Remote access to the control panel is blocked. Further communication is impossible."
    Downloading is disabled and all keys match.
    Configuration:
    Integra 128 & ETHM-1 Connection: Remote Access Blocked via DloadX, Satellite RJ/pin5 Cable Integra 128 & ETHM-1 Connection: Remote Access Blocked via DloadX, Satellite RJ/pin5 Cable
    Please help,
    Regards.

    ..................................................... ..........................
    Announcement

    Also read:
    ETHM 1 Plus/Integra Control. Selected Issues

    We invite you to familiarize yourself with other guides, highlighted topics, articles in the field of security systems such as intercoms, automatic gates and barriers, alarm systems, cameras, access control:
    Security systems guides


    If you do not find the answer to your question in the above-mentioned topics, please visit the forum:
    Security systems


    We also encourage you to visit the General Guides section, where you will find materials from other sections of the forum, including those for people starting their adventure with electronics:
    General Guides
  • ADVERTISEMENT
  • #2 12403316
    Stan-Mar

    Level 27  
    When choosing a connection, you connect through 1 or 2:
    1. TCPIP: Dloadx ->ETHM,
    2. TCPIP: Dloadx
  • #3 12403324
    pawel448
    Level 9  
    Connects via 1.
  • #4 12403382
    Stan-Mar

    Level 27  
    Approx. okay.
    What version of the control panel, ETHM, and dloadx
  • #5 12403427
    pawel448
    Level 9  
    dloadx - 1.11.005,
    ETHM-1 - v1.06,
    centrala - v1.11
  • ADVERTISEMENT
  • #6 12403452
    Stan-Mar

    Level 27  
    In this configuration you should have ETHM/GSM answering selected instead of ISDN/GSM/ETHM modem
  • ADVERTISEMENT
  • #7 12403828
    pawel448
    Level 9  
    Integra 128 & ETHM-1 Connection: Remote Access Blocked via DloadX, Satellite RJ/pin5 Cable

    And so all the time ... receives data ...
  • #8 12403843
    Stan-Mar

    Level 27  
    PM me the settings
    check also the options - service - block downloadingu
  • #9 12493508
    andpak
    Level 13  
    Hello!
    I have the same problem, can you tell me what was the solution.
  • #10 12495699
    dariusz.bembenek
    Stationary Alarms specialist
    pawel448 wrote:
    And so all the time ... receives data ...

    andpak wrote:
    I have the same problem, can you tell me what was the solution.


    What's the problem? Because if with the fact that he "receives data all the time" - this is not a problem. So it has to be. It is such an indicator that "there is communication all the time".
  • #11 12497516
    andpak
    Level 13  
    Hello!
    Thank you for your answer. Headquarters gives me messages like this all the time.
    What should I do or do I need to select something in the settings?

    I connect to the server:
    Connected.
    Module: ETHM-1 V1.05
    Receives data.....
    The control panel is monitoring, wait....
  • #12 13077623
    PAWLOO1989
    Level 19  
    How to solve the above problem from the connection popup I keep waiting..

    connection with the PBX was not established after an attempt to download data and in the connection window it is still waiting for data
  • ADVERTISEMENT
  • #13 13079026
    andpak
    Level 13  
    Hello!
    In the options select:
    - modem answering,
    - external modem,
    - ISDN/GSM/ETHM modem
  • #14 13146681
    drFeelGood
    Level 10  
    I fought on different computers for several hours, when I exhausted all methods, I restored the factory settings of the control panel, programmed it from the beginning and it went right the first time :-)
  • #15 13156422
    piotr_be
    Level 11  
    Looks like an installation problem ETHM-1 at Integra Satel is not a rare case and the service manual itself is not always helpful, because there is no step-by-step implementation described there.
    Considering that the posts of my colleagues helped me a lot when installing this module, I will try to gather my experience and describe the whole procedure step by step.

    After connecting the modules to the control panel Integra 64 it remains to connect the card with a cable used to connect the RS-232 ports of the ETHM-1 module and the INTEGRA control panel with the RJ type socket. (Cable diagram in the manual "TCP/IP ETHM-1 communication module - page 4)

    There is no need for an RS-232 cable to program other parameters, because everything can be done from the keypad.

    From the manipulator:
    1) ([SERVICE CODE][*][9] ) -> options -> options.phone
    a) External modem - set "Y"
    b) Answer modem - set "Y"
    c) ISDN/GSM modem - set "Y"
    (set "T" with the "8" key, remove the marker with the "6" key)
    2) Structure ->Hardware->Keypads->Settings->ETHM-1->DloadX key
    (set there any string of characters and then enter the same in DloadX)
    a) write back DloadX Port - by default 7090
    c) check if Z DloadX is "T"
    3) Status->IP/MAC ETHM-1 - check if an IP address is assigned

    After these activities, ping ETHM-1 if it responds - which still does not mean that everything is OK if it responds to pings.

    Now let's move on to the program DloadX . In the menu Communication->Passwords, phone numbers and verify that everything is entered as needed.

    TCP/IP connection
    - LAN/WAN
    - Server address: (enter the address assigned to the ETHM-1 card here)
    - Port: (if not changed then 7090)
    - DloadX key: enter the one that has been set

    After that enter the menu Connection and choose: TCP/IP: DloadX->ETHM

    Attention! Do not turn on Download on the keypad!

    If, after initiating the connection, a screen appears with the following information:
    Integra 128 & ETHM-1 Connection: Remote Access Blocked via DloadX, Satellite RJ/pin5 Cable

    That means it works :-)

    Attention!
    If, despite correct settings, a message appears during connection via TCP/IP: DloadX->ETHM "Remote access to the control panel is blocked. No further communication possible" it will most likely only help to reset the control panel from the pins. The post above shows that my case was not isolated, so it can be concluded that there are such flowers in Integra control panels. Interestingly, from what I remember, in the fields DloadX server and GuardX server there were some "bushes" of several characters. After the control panel reset, these fields are empty. And most importantly - it works :-) .
  • #16 13271892
    piotr_be
    Level 11  
    Quite an unusual situation with the problem of the ETHM-1 card with Integra-64, so I will describe it. to 7090 via DloadX - even though the card responded to pings.
    Only a hard reset from the pins helped, then it worked until the power was turned off.
    Then the same again.
    After a two-day struggle, I left the control panel switched on for the night, and in the morning ... I saw that the manipulator was dead :(
    I gave it for service, it was fixed, after two weeks it arrived to me.
    I connected to the hub. I reconfigured the whole thing again, exactly as before.
    After turning off the control panel and turning it on again, I was surprised to see that everything works fine!
    Everything indicates that the cause of problems with the operation of ETHM-1 was a malfunctioning manipulator, which fortunately "burned out".
    After all, they work on the same bus anyway.
  • #17 13585801
    JarekPrzybyl
    Level 15  
    I've been working on a newly purchased set since yesterday and it seems I'm having similar problems.

    Briefly summarizing: I follow the above step by step, when I try to connect I get:

    20:38:53: Connecting to server: 10.1.1.77:7090
    20:38:53: Connected.
    20:38:53: Panel not ready, disconnected.

    What am I doing wrong?
    I tried the pins (by the way - what do the pins give? I expected a factory reset, and the whole configuration stayed with me), ethm-1 ping, I am able to connect to the control panel directly via RS and via www.
    Such a curiosity, less important to me at the moment: the GuardX program does not connect to me either. It asks for a password, then regardless of what I enter (I tried the same password as for DloadX, service, random numbers) the password entry window turns gray and stays like that until I close it manually.

    Below the options window, the "ethm-1 monitoring" option is also enabled as a result of the combination, I also tried without it.

    Integra 128 & ETHM-1 Connection: Remote Access Blocked via DloadX, Satellite RJ/pin5 Cable
  • #18 13586021
    Stan-Mar

    Level 27  
    Disable ETHM monitoring - it is used only for monitoring to stations via LAN network. I hope you connected the RS ETHM to the RS of the motherboard with the PIN5-RJ wire (not the one from the programming cable). Finished downloading?
  • #19 13586043
    JarekPrzybyl
    Level 15  
    I'm replying to myself, because the problem partially resolved itself, thus moving on to the next stage.
    The reason for the above-described inability to connect was probably not closing the DWNL-RS session. I am now connecting. And the "connecting" state is all I get. Now the connection attempt looks like this:

    I am connecting to the server: 10.1.1.77:7090
    Connected
    ETHM-1 V1.07 module
    Receives data

    And with this state the program hangs, the "TCP/IP connection" window remains with the "not responding" status, the only thing I can do is kill the entire program, to do this I also have to kill the process, because it does not respond to a simple click on the cross .
    I suspect that the same problem prevents me from connecting with GuardX, only there I can close the window at least, not here. And I can connect via www without any problem, I remind you...

    [Update]

    I'm replying to myself because I partially located the cause of the problem. From another computer, with the good old XP on board, I just couldn't connect (message "headquarters not ready"), but after turning off the windows firewall everything started working. At that point, on that computer, it was enough to add the DloadX application to the trusted list and add port 7090 to the exceptions list, and everything started to run wild.

    Unfortunately, I still can't deal with the laptop I use every day, with Windows 7 on board and the system firewall intercepted by the corporate antivirus Symantec Endpoint Protection. And here it is for the devil, disabling this antivirus does nothing either...

    @stan-mar - sorry, I just noticed that you wrote back in the meantime :) Yes, the reason was not disabled downloading, and now I'm struggling with a probably blocked port somewhere on my laptop...
  • #20 13756138
    foxx102
    Level 11  
    Did you manage to solve this problem? I have the same but I'm afraid it's not a firewall issue but the new dload X. Everything was fine on the old one but unfortunately I can't find version

Topic summary

The discussion revolves around issues connecting the Integra 128 control panel to the ETHM-1 module via a Satellite RJ/pin5 cable, specifically regarding remote access problems encountered when using DloadX software. Users report receiving a "Remote access to the control panel is blocked" message despite successful local network connections. Various troubleshooting steps are suggested, including ensuring correct settings for modem answering, checking firmware versions, and verifying cable connections. Some users resolved issues by restoring factory settings or adjusting configuration options. The conversation highlights the importance of proper setup and configuration for successful communication between the control panel and the ETHM-1 module.
Summary generated by the language model.