Refix DE – what initial pressure for DHW diaphragm vessel on 120L heater?

robert45 64716 14
Best answers

What precharge pressure should a diaphragm expansion vessel for a 120 L domestic hot water heater be set to when the water system pressure varies from 1.5 to 3.7 bar?

Set the vessel precharge before connecting it to the system, with the installation depressurised, and adjust it to the lowest water pressure in the system rather than leaving the factory 4 bar setting [#12530647][#12527300] The vessel is not meant to raise pressure or replace a hydrophore; its main job is to limit pressure rise from water heating [#12530647] If you also want hydraulic knock suppression, the precharge should be slightly below the operating pressure, about 0.25 bar below the maximum network pressure, but not so low that the vessel fills completely with water at higher pressure [#12526910][#12527009] In a variable hydrophore installation, that means the precharge must be chosen with the minimum and maximum system pressures in mind, and 4 bar is too high if it is above the actual water pressure in use [#12527300][#12526926] The original poster later reported that reducing the vessel pressure fixed the water hammer and the installation worked properly [#12841868]
Generated by the language model.
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 12526891
    robert45
    Level 22  
    Posts: 644
    Help: 44
    Rate: 89
    What initial pressure should be set in the diaphragm vessel for a 120l gas water heater.
    The hydrophore system works in the range of 1.5 - 3.7 bar.
    The installer left the factory set pressure Refix DE - 4 bar
  • ADVERTISEMENT
  • #2 12526898
    W0jtek92
    Level 39  
    Posts: 3852
    Help: 469
    Rate: 1254
    Why change your pressure?
  • #3 12526909
    Skwantowany
    Level 20  
    Posts: 311
    Help: 28
    Rate: 14
    And what is the diaphragm vessel for in hot water?
    The diaphragm vessel is installed in closed central heating systems, where water circulates in a closed circuit.
  • ADVERTISEMENT
  • #4 12526910
    saskia
    Level 39  
    Posts: 5756
    Help: 174
    Rate: 1086
    It can be, but it would be better if the pre-pressure was at least a quarter of a bar below the max. network pressure.
    One main reason is the damping of hydraulic clatter when the valves close.
    If the diaphragm does not have pressure pressure over its larger surface, then its operation takes place with a delay, ie it only partially eliminates hydraulic knocks, and the compensatory operation is also slow and only with a significant increase in pressure.
    such a vessel should work similarly to a CO vessel and be about 1/4-1/3 filled with water.
  • #5 12526926
    Skwantowany
    Level 20  
    Posts: 311
    Help: 28
    Rate: 14
    saskia wrote:
    One main reason is the damping of hydraulic clatter when the valves close.

    OK, but if the pressure is variable in the network, as stated by the author of the post, even twice, then the vessel may have a pressure value greater than the pressure in the network at the moment and thus does not fulfill its role. if it was possible to maintain the pressure in the system at a certain level, then the vessel would do its job.
  • #6 12526949
    saskia
    Level 39  
    Posts: 5756
    Help: 174
    Rate: 1086
    Consider the fact that at low pressures (lower pressure range) hydraulic knocking is unlikely to occur.
  • #7 12526961
    Skwantowany
    Level 20  
    Posts: 311
    Help: 28
    Rate: 14
    saskia wrote:
    It can be, but it would be better if the pre-pressure was at least a quarter of a bar below the max. network pressure.

    saskia wrote:
    Consider the fact that hydraulic knocking is unlikely to occur at low pressures.

    This is a quarter of a bar (+ a little) below the pressure of the vessel, this vessel will not work.
    In that case, you would need to specify a min. the pressure at which knocks occur and the vessel should only work from this pressure.
  • #8 12527009
    saskia
    Level 39  
    Posts: 5756
    Help: 174
    Rate: 1086
    This would be the best solution, but here we are limited by the capacity of the vessel.
    If we reduce the initial pressure in the vessel too much, then with large pressure fluctuations in the network, it may happen that the vessel has too low initial pressure and with increased pressure in the network is completely filled with water, which will not meet the basic protection as an expansion vessel protecting against pressure increase, e.g. in the boiler, and then the safety valve will have to work, and this should rather be avoided, because that's what the expansion tank is for :-)

    This quarter of a bar lower initial pressure, it only gives additional use of the vessel to eliminate hydraulic knocks, while maintaining the basic tasks of the vessel, but it will not eliminate them in the entire pressure range.
  • #9 12527300
    robert45
    Level 22  
    Posts: 644
    Help: 44
    Rate: 89
    As I wrote, the pressure is variable, because it is a hydrophore installation (own water intake).
    The measurement of the pressure in the vessel after filling the installation with water showed 4.5 bar, regardless of the pressure and temperature of the water. I lowered it to 3.5 bar. I probably did it incorrectly, because without draining the water from the vessel. I assumed (I do not know if right) that if the vessel pressure was higher than the water pressure in the system (max. 3.7 bar), then the vessel does not fulfill its function.
    Reflex recommends setting the pre-pressure in this vessel to the lowest water pressure in the system.
    I thought that the purpose of the diaphragm vessel, apart from water hammers, is the comfort of using several water intake points without loss of pressure.
    This was the case before the vessel was installed. Simultaneous drawing of hot water caused a significant drop in pressure, and thus the comfort of use (e.g. from the shower) was unsatisfactory.
  • ADVERTISEMENT
  • #10 12530647
    saskia
    Level 39  
    Posts: 5756
    Help: 174
    Rate: 1086
    The diaphragm vessel is not a hydrophore and will not supplement pressure drops, but it can only prevent too much pressure increase after changing the temperature of the water in the boiler.
    By setting the pre-pressure slightly below the system pressure, it can also eliminate heavy hydraulic clatter by absorbing (smoothing) abrupt changes in pressure and flow.

    The initial pressure is set before connecting the tank to the system, i.e. when there is no pressure in the system (pressure = 0). The pressure measurement of the network should be made at the same level of the system where the diaphragm (compensation) tank is installed.
  • #11 12530670
    William Bonawentura
    Level 34  
    Posts: 2419
    Help: 187
    Rate: 612
    Skwantowany wrote:
    And what is the diaphragm vessel for in hot water?
    The diaphragm vessel is installed in closed central heating systems, where water circulates in a closed circuit.


    A complete tank protection system includes:
    pressure reducer or pressure switch on the cold water supply,
    check valve,
    diaphragm vessel approved for contact with drinking water (white)
    safety valve at the outlet of the storage tank.
  • ADVERTISEMENT
  • #12 12841868
    robert45
    Level 22  
    Posts: 644
    Help: 44
    Rate: 89
    robert45 wrote:
    As I wrote, the pressure is variable, because it is a hydrophore installation (own water intake).
    The measurement of the pressure in the vessel after filling the installation with water showed 4.5 bar, regardless of the pressure and temperature of the water. I lowered it to 3.5 bar. I probably did it incorrectly, because without draining the water from the vessel. I assumed (I do not know if right) that if the vessel pressure was higher than the water pressure in the system (max. 3.7 bar), then the vessel does not fulfill its function.
    Reflex recommends setting the pre-pressure in this vessel to the lowest water pressure in the system.
    I thought that the purpose of the diaphragm vessel, apart from water hammers, is the comfort of using several water intake points without loss of pressure.
    This was the case before the vessel was installed. Simultaneous drawing of hot water caused a significant drop in pressure, and thus the comfort of use (e.g. from the shower) was unsatisfactory.

    After changing the pressure in the vessel, the installation works without water hammer.
  • #13 12841900
    serwisant73
    VIP Meritorious for electroda.pl
    Posts: 3158
    Help: 188
    Rate: 1259
    Skwantowany wrote:
    And what is the diaphragm vessel for in hot water?

    Weird question....
  • #14 12842669
    pan_kotek
    Level 20  
    Posts: 561
    Help: 12
    Rate: 115
    I will join the topic.
    What is the difference in the location of the safety valve:
    1) at the cold water inlet to the hot water tank
    2) at the outlet of hot water from the tank

    I understand that the difference is in the temperature of what will flow out.
  • #15 13130077
    robert45
    Level 22  
    Posts: 644
    Help: 44
    Rate: 89
    The installation is working properly. The change in the initial pressure in the vessel did not adversely affect the operation of the system. Thank you for your comments. Topic to be closed.

Topic summary

✨ The discussion centers on determining the appropriate initial pressure for a diaphragm vessel in a 120L gas water heater system, specifically within a hydrophore installation operating between 1.5 and 3.7 bar. The factory setting of 4 bar was deemed too high, as it could prevent the vessel from functioning effectively under variable network pressures. Participants emphasized the importance of setting the pre-pressure slightly below the maximum network pressure to mitigate hydraulic clatter and ensure the vessel's protective role against pressure increases. The consensus suggests an initial pressure of approximately 3.5 bar, with considerations for maintaining comfort during simultaneous water usage and preventing water hammer. The diaphragm vessel's role is clarified as not supplementing pressure drops but rather smoothing pressure fluctuations.