Nie, dziękuję Przekieruj mnie tamalienone wrote:It is natural, when the water is heated, its volume increases, and since there is no outlet, the pressure increases.which indicates 6 Bar while the water is being heated.
alienone wrote:There can only be one correction: between the valve on the cold water inlet to the boiler and the tee for the safety group, a check valve should be installed so that the water does not flow back from the boiler to the entire domestic installation, but only discharges its excess in the aforementioned safety group.I do not have an expansion vessel, so I am asking if it can be installed this way?
ls_77 wrote:DHW expansion vessels are factory filled with ~ 3.5-4bar.
Those with a filling pressure of ~ 1.5 bar are most often for CO and are not suitable for DHW!
Look for hot water vessels.
If you have ~ 4 bar at the input from the mains, then as much as at the input I would set in the vessel.
TL;DR: A 50 °C temperature rise expands water by ~2 %, which can push 4 bar mains up to 6 bar without a correctly-sized DHW expansion vessel. “Install the check valve before the tee” [Elektroda, stanislaw1954, post #17767530]
Why it matters: Correct placement and pressure settings stop nuisance valve dripping, save water and reduce Legionella risk.
• Typical DHW safety valve setting: 6 bar (EN 1487:2007). • Expansion vessel pre-charge = mains pressure − 0.2 bar (e.g., 3.8 bar for 4 bar supply) [Elektroda, emigrant, post #17768846] • Sizing rule: 0.1 L vessel per 1 L boiler at 4 bar; 80 L boiler → ≥ 8 L vessel [REFLEX Datasheet]. • Minimum connection pipe: ½" (15 mm) [Elektroda, stanislaw1954, post #17767910] • Flow-through models (Refix DD, Airfix D/A) meet potable-water hygiene codes [Flamco Manual, 2023].