Hey, the fast mode in the above-mentioned fan did not give me, a new one is the cost of about 700 zł so of course I would prefer to repair.
The fan works in such a way that the slow mode is permanently on, while the fast mode is activated by a separate switch. The slow gear works, while the fast gear does not, but it seems to want to turn on.
Well, I found a defective mkp2 2.2uF 400 VAC Class B capacitor from F&T. The capacitor has barely half the capacity.
Well, unfortunately I can't find it anywhere. In fact, I have not even been able to determine a similar mkp.
There is a circuit board, powered from the mains - a circuit that is designed to shift the phase and probably its task is to start fast rotation.
The motor is 1 phase, unfortunately I don't know much about its paramaters. There are basically 3 condensers, w oprniki and 1 varistor. I will post the schematic later, if it would be useful to deduce a possible replacement.
Does anyone perhaps know where to look for such a contraption? And anyway, what is the difference between MKP and MKP2? The only thing I have determined is that the mkp2 has a lower intrinsic resistance and performs better in high-frequency circuits. And here's the question, this type of circuit rather works only at 50Hz. So is it necessary to use MKP2? I guess it could be MKP with identical capacitance and go.
The only other question is what kills the MKP? Well, and if this capacitor is killed, did the varistor survive?
Well, and the question is still about the varistor (s14 k320), could you advise me how to test such a contraption outside the circuit?
Could it perform a role other than protection? It is mounted on the ground, at the very input of the network.
Thanks in advance for any help.
The fan works in such a way that the slow mode is permanently on, while the fast mode is activated by a separate switch. The slow gear works, while the fast gear does not, but it seems to want to turn on.
Well, I found a defective mkp2 2.2uF 400 VAC Class B capacitor from F&T. The capacitor has barely half the capacity.
Well, unfortunately I can't find it anywhere. In fact, I have not even been able to determine a similar mkp.
There is a circuit board, powered from the mains - a circuit that is designed to shift the phase and probably its task is to start fast rotation.
The motor is 1 phase, unfortunately I don't know much about its paramaters. There are basically 3 condensers, w oprniki and 1 varistor. I will post the schematic later, if it would be useful to deduce a possible replacement.
Does anyone perhaps know where to look for such a contraption? And anyway, what is the difference between MKP and MKP2? The only thing I have determined is that the mkp2 has a lower intrinsic resistance and performs better in high-frequency circuits. And here's the question, this type of circuit rather works only at 50Hz. So is it necessary to use MKP2? I guess it could be MKP with identical capacitance and go.
The only other question is what kills the MKP? Well, and if this capacitor is killed, did the varistor survive?
Well, and the question is still about the varistor (s14 k320), could you advise me how to test such a contraption outside the circuit?
Could it perform a role other than protection? It is mounted on the ground, at the very input of the network.
Thanks in advance for any help.