Transitioning from Oil to Gas Furnace: Ideal Gas Boiler for 170m2 House with Old Insulation
sartyx 35199 20
What gas boiler power should I choose for a 170 m2 poorly insulated house with high-temperature radiators, and is a condensing boiler worth buying?
For heating alone, a boiler up to 16 kW should be enough and may even be oversized, but if you want instantaneous domestic hot water, around 20 kW is typically needed unless you use a storage tank [#13619607][#13621728] A condensing boiler is still worthwhile even with high-temperature radiators, because condensation depends on the return temperature, not the supply temperature [#13619607] In practice, if the return stays around 30–35°C most of the season, a condensing boiler will condense and be more economical than a regular boiler [#13619607] Even with radiator systems designed for 75/60°C, the boiler can still be around 100% efficient at about -10°C outside and up to 109% at +10°C, so it can save fuel despite not always running at ideal low temperatures [#13619607] If you add a hot-water tank, the lower-power boiler can handle heating well, and the tank covers domestic hot water demand [#13623204]
  • #1 13618687
    sartyx
    Rate: 12
    I'm in the process of changing from oil to gas furnace after 14 years of using an oiler.
    Home insulated according to the old technology from 14 years ago so max. outside 10 cm, poorly insulated usable attic (but as we have radiators there already a few years have worked maybe a few times - heat goes from below in addition we have bedrooms there so we do not need and do not want to have super warm), floor tiles about 2x 30 m2 only downstairs in bathrooms and kitchens, otherwise everywhere carolyfery + fireplace. Thanks to saving money over the years, the stove only on really cold days worked more than 3-4h/day + reheating with the fireplace - we burned oil first about 2000l/year and for the last few years only 1200l/year, which together with the fireplace heating came out to about 500 PLN/month considering the whole year. Due to the fact that oil has become very expensive since we moved into the house, thus the costs went up significantly, and also because they finally connected us to gas, we decided to switch to this fuel.
    Unfortunately, I have trouble with the selection of the boiler.
    I don't have too many floorboards, and radiators are high temperature so I don't know if it's worth it to be interested in condensate. On the other hand, the cost of purchase is a difference of 1000 PLN, but the question is whether the condensate at temperatures higher than these optimal 30-50 degrees will not wear out faster, will it be more economical than a regular single-function boiler ?
    Second question what power should the boiler have ?? Up to 16 KW or up to 20 KW ?
  • #2 13619607
    Zbigniew Rusek
    Help: 394
    Rate: 1542
    For heating you certainly do not need more than 16kW, maybe even too much, but what about hot water for the bathroom. Heating water requires more power (the comfort of flow-heated hot water is about 20kW, unless there is a storage tank, but it takes up space). As for the condensing boiler, this temp up to 50 degrees refers to the temperature on the return and not on the supply (condensation depends on the return temperature), and the temperature on the supply is always higher than on the return (50 degrees on the return is usually about 70 degrees on the supply, similarly, 40 degrees on the return will be 60 degrees on the supply, and t. d.). That is, condensation would also occur if the radiators were supplied with 70-degree water (i.e., there would be 50 on the return) and such radiator temperatures are needed only for a few, top a dozen days in winter, i.e., for most of the season the parameters would not exceed 50 degrees supply/30-35 return). Frosts of 15-20 degrees happen occasionally (sometimes there is a heating season when such conditions will not occur at all). A condensing boiler is more economical than a regular one, but more expensive. On the Viessmann website it is stated that even when the installation is designed for 75/60 degree parameters (supply 75 degrees, return 60 degrees, that is, radiators really very hot), even at an outdoor temperature close to minus 10 degrees the efficiency of the boiler will be about 100% at +10 outside will be up to 109%) - there is a chart there.
  • #3 13619701
    sartyx
    Rate: 12
    water tank is 120 l vailant - in my opinion and many others sufficient, when it comes to comfort - it is known - at the moment I do not have hot water, only as I set myself on the stove, so it suits us and probably by this we also save a lot of money,, the question is when these 20KW is really used ? only to heat water ?
  • #4 13621728
    Zbigniew Rusek
    Help: 394
    Rate: 1542
    Yes, for heating water. After all, a typical bathroom stove - the so-called Junkers has a power of about 20 kW or even a little more (Junkers generally come in versions of 19.2kW or 23.6kW, Vaillant similarly - with the advantage of the smaller power). A 192kW stove provides a flow rate of 11 liters per minute of water heated by 25 degrees (or 5.5 liters per minute heated by 50 degrees); 2306kW provides 14 liters per minute heated by 25 sotpni (7 liters per minute heated by 50 degrees). I emphasize, it is about the increase in the temperature of water relative to the temperature of cold water, not the specific temperature of water. Conclusion - hot water requires about 20kW of power.
  • #5 13621795
    sartyx
    Rate: 12
    then what are 14 and 16 KW boilers for then ????
  • #6 13623204
    Zbigniew Rusek
    Help: 394
    Rate: 1542
    sartyx wrote:
    then why are there 14 and 16 KW boilers ???
    If there is a storage tank, then you do not need as much power to heat water, as in the case of instantaneous water heating (as in Junkers) and such a boiler will successfully suffice. Only that the storage tank takes up space and has a certain capacity. There are advantages and disadvantages of each method of heating water. Note: a boiler that provides instantaneous hot water heating in addition to central heating is a dual-function boiler (a single-function one can also provide hot water, but when connected to a storage tank).
  • #7 13624407
    sartyx
    Rate: 12
    is it true that if I buy a boiler from an online store I may have a problem with the first startup service for free by the service center ????
  • #8 13639723
    piotr_boncza
    Help: 135
    Rate: 338
    No, the first start-up, bought in Poland, is always included in the price of the boiler. More often, you have to pay for the service to get there.
  • #9 13640241
    Piotr77777
    Heating systems specialist
    Help: 58
    Rate: 266
    Not all boilers have free of charge first start-up. Secondly, not every authorized service technician wants to fire up boilers bought on the Internet, and thirdly, I have seen boilers bought in Poland on the Internet intended for the market of another country outside the EU, and therefore the warranty was not valid in Poland.
  • #10 13660500
    kabee84
    Help: 39
    Rate: 164
    piotr_boncza wrote:
    No, the first start-up, bought in Poland, is always included in the price of the boiler. Increasingly, you have to pay for the arrival of the service.
    Immergas Nike/Eolo - first start-up paid 100% by the customer, unless the seller (Installer) in the sales contract offers to cover this cost.
    Otherwise, often boilers of higher power are also started up for a fee by the user.
    These are the examples that come to mind. So that you always need to read the terms of the warranty....
    Added after 11 [minutes]:
    Piotr77777 wrote:
    Secondly, not every authorized service technician wants to fire up boilers bought over the Internet, thirdly, I have already happened boilers bought in Poland over the Internet intended for the market of another country outside the union and thus the warranty was not valid in Poland.
    Secondly, it is related to the third.
    If the boiler does not come from an authorized Polish distributor, who would pay for commissioning of the service technician? That's why (very rightly) service technicians do not want to run equipment from an uncertain source (online store).
    The warranty as a manufacturer's warranty does not apply, but there is such a thing as seller's liability - and we automatically have a 2-year warranty in the case of a consumer sale (the buyer bought it privately, not as a company - the Law on Special Terms of Consumer Sales...). or one year warranty in case of sale to a business entity (Warranty Act).
    By the way.... I guess it's only in Poland that a customer, based on knowledge taken from the Internet, without any schooling or practice in the field, can choose a heating appliance for himself, build an electrical/hydraulic system, assess the efficiency of chimney systems, build himself a domestic sewage treatment plant - and for all this he will get approval, papers, etc.... And then fires, flooding, failure to meet environmental standards, etc. etc.... Massacre. And further reading on forums, buying on the Internet.... And on and on Maciej.... Poles...
    FEMAX Łazienki. Ogrzewanie. Instalacje.
    Szczęśliwa 25, Gdańsk, 83-110 | Tel.: 664 XXX XXX (Show) | Company Website: femax.pl
  • #11 13663308
    lemonr
    Rate: 19
    And I guess it is only in Poland that a house project is conquered by many "mgr inż" among others the one on heating and selects a 24kW gas boiler and in reality 8kW is enough. So graduated school in this area does not prove anything ( in many cases). Thanks to the knowledge of the Internet, it is more difficult for "experts" to perform magic.
  • #12 13678754
    haneb
    Help: 61
    Rate: 214
    Exactly. At my place, the professional who did the whole installation installed 17kW and now after replacing the boiler itself, 10kW is enough.
  • #13 13678914
    piotr_boncza
    Help: 135
    Rate: 338
    It's me who apparently has an outdated manual:
    Preliminary commissioning
    After completion of all installation work
    (including filling the system), call
    Authorized Immergas Service.
    The service technician will perform the first commissioning
    free of charge,
    at the same time instructing the user on the
    use of the boiler.
    Note: The first commissioning performed by
    Authorized Service is a prerequisite
    for the warranty. The initial inspection ensures
    maintaining boiler features such as reliability,
    efficiency and economy.
    kabee84 wrote:
    Incidentally.... I guess it's only in Poland that a customer, based on knowledge taken from the Internet, without any schooling or practice in the field, can choose a heating appliance for himself, build an electrical/hydraulic system, assess the efficiency of chimney systems, build himself a domestic sewage treatment plant - and for all this he will get approval, papers, etc.... And then fires, flooding, failure to meet environmental standards, etc. etc.... Massacre. And further reading on forums, buying on the Internet.... And on and on Maciej.... Polaczki...
    There you are undeniably right, although when I see someone write Polaczki, I get a knife in my pocket....
    Added after 45 [minutes]:
    lemonr wrote:
    And I guess it's only in Poland that a house project is conquered by many "mgr inż" among others the one from heating and selects a 24kW gas boiler and in reality 8kW is enough. So graduated school in this area does not prove anything ( in many cases). Thanks to the knowledge of the Internet "experts" are more difficult to perform hocus-pocus.
    He selects a boiler with a capacity of 24kW, because that is what is needed to flow sufficient water for washing.
    The fact that most often less is needed for heating is obvious ;) .
  • #14 13680478
    lemonr
    Rate: 19
    piotr_boncza wrote:
    It takes a 24kW boiler, because that's what it takes to flow enough water for washing.
    It is not! I am writing about a boiler with a storage tank! And if it were not for the knowledge taken from the Internet, which you so negate I would probably buy one.
  • #15 13680515
    mauri_b
    Help: 109
    Rate: 529
    Initial start-up
    After all installation work is completed
    (including filling the system), an
    Authorized Immergas service technician must be called.
    free of charge,
    the use of the boiler.
    for the warranty. Initial inspection ensures
    From last year, there are other provisions in the warranty card, saying that there is a charge for the first commissioning of a non-condensing boiler. Condensing boilers still have free commissioning with reimbursement of travel costs.
    Similarly in Vaillant, except that there is no obligation for the first commissioning by the service of traditional boilers, while in Immergaz there is an obligation - to have a warranty.
  • #16 13681269
    kabee84
    Help: 39
    Rate: 164
    mauri_b wrote:
    From last year, there are other provisions in the warranty card, saying that there is a fee for the first start-up of a non-condensing boiler. Condensing boilers still have free commissioning with reimbursement of travel costs.
    Exactly.
    http://pl.immergas.com/materialy/warunki_gwarancji/kotly_tradycyjne.htm
    As for MA and projects.... Let's not hide - the designs of heating systems in the general designs of single-family houses are on a "copy-paste" basis, universal, matching most houses. And so - a house of 110m2 and 240m2 have the same boiler rooms.... Decent installation companies are there to customize the heating system for a given building taking into account all the guidelines (also how many people will use the house, what the temperatures should be, etc., etc.)
    For the rest - a 24kW boiler (even if it is not a 2-function version but with a hot water exchanger) for a 170m2 house is not some glaring mistake.
  • #17 13681364
    lemonr
    Rate: 19
    kabee84 wrote:
    A 24kW boiler (even if it is not a 2-function version but with a hot water exchanger) for a 170m2 house is not some glaring mistake.
    Well, let me add that this is a design for an energy-efficient house (186m2 of which 150 heated area), is it still not a glaring error?
  • #18 13683393
    kabee84
    Help: 39
    Rate: 164
    lemonr wrote:
    kabee84 wrote:
    kabee84 wrote:
    A 24kW boiler (even if it's not a 2-function version but with a hot water exchanger) for a 170m2 house is not some glaring mistake.
    Well, let me add that this is an energy-efficient house project (186m2 of which 150 heated area), is it still not a glaring error?
    I think not. Better to oversize than undersize. Such a boiler would work - it would just "rest" more often. Worse, if there was designed a device far too small for example 3kW (although such probably do not exist)....
    You cling to these poor designers.
    You are looking too blindly at building-wide projects.
    I will repeat - that's what industry specialists are for, to design systems for a specific object. Just who uses the services of such companies? Nobody! Because reading on the Internet comes out cheaper.....
  • #19 13683525
    lemonr
    Rate: 19
    I have been to two such specialists both on the letter V. And what, they did a cost estimate based on the provided design with a 24kW boiler. Which industry specialist has the time to spend more than 30 minutes with a client?
  • #20 16312029
    lukaszon
    And what do you think about such a boiler http://kotlarstwo.co/pl/kwm-sgr/ with a capacity of 25 Kw ?
    The price of such a boiler from the manufacturer is about 5300 PLN + free transport http://allegro....
    Will be enough for 150 m2 ?
    Moderated By mirrzo:
    I have removed the link to the auction
    3.1.18. Do not send links that will become inactive after some time. This will make the discussion lose any sense.
  • #21 16313677
    Arbiter
    Rate: 101
    25kw is probably for a 700m2 house (contemporarily insulated)
The discussion revolves around transitioning from an oil furnace to a gas boiler for a 170m2 house with outdated insulation. Users debate the appropriate boiler capacity, with suggestions ranging from 14kW to 25kW, emphasizing that heating water requires higher power (around 20kW). The importance of considering both heating and hot water needs is highlighted, with distinctions made between instantaneous and storage tank systems. Concerns about the commissioning of boilers purchased online are raised, noting that not all brands offer free initial startup services. The conversation also critiques the common practice of oversizing boilers in heating system designs, advocating for tailored solutions based on specific household needs.