- Selecting a Gas Boiler for a 70m2 Two-Level Apartment with One Bathroom: Roca Sara 24/24F Issues
electronic_buff 32109 25
How can I choose a gas boiler for a 70 m² two-level apartment with one bathroom to ensure comfortable domestic hot-water supply, especially during the heating season?
Choose a low-minimum-power condensing boiler, ideally a single-function unit with a built-in hot-water tank (or a combi with an integrated tank), because that setup gives better domestic hot-water comfort than an oversized plain combi [#16237013][#16239639] Aim for a boiler that starts from about 2–3 kW; several replies warn that 24–26 kW combis tend to cycle too much in a small apartment and are less economical [#16236475][#16237013][#16239639] One concrete suggestion was the Termet Ecocondens Integra II 25 kW with a 45 l tank, minimum power 2.8 kW and up to 7 years warranty, with service availability treated as essential [#16237013] Other tank-equipped examples mentioned were Vaillant VCI 296/5-5, Saunier Duval IsofastCondens/IsotwinCondens, De Dietrich MCA 25/28 BIC, and later the smaller Termet Ecocondens Gold Plus was praised as quiet and trouble-free [#16239085][#16382890][#17150472] Before buying, check whether your chimney can accept a condensing-boiler flue and make sure there is good local service, since that matters more than brand alone [#16824901][#16244226]
  • #1 16235860
    electronic_buff
    Rate: 8
    Ladies and Gentlemen!
    The matter is not easy, because you have to choose a boiler for the apartment (70m2, two-level apartment, one bathroom at a distance of about 10m from the boiler). At the moment, we are using Roca, Sara 24 / 24F (dual-function). There are several things that bother me, namely:
    1) Has big problems with domestic water heating, especially during the heating season. By the way, the recommended pressure in this furnace is 1.5 Bar - I noticed that during the heating season this pressure drops quite drastically when the furnace does not heat up (by approx. 0.5 Bar). I can't increase this pressure either, because it rises dramatically when the stove turns on and starts heating up again.
    2) Has big problems with turning on (again utility water). It is often related to 1) (pressure drop), but I observed the same problem before the heating season (then the set pressure was at the said 1.5 Bar). Can anything be done about it?
    Returning to the merits - 1) and 2) make me replace the boiler. And here the first question arises: a double or single-function boiler? Generally my priority is to make the boiler very well coped with domestic water heating , also (or maybe most of all!) during the heating season. After exploring the topic (I am not an expert in this field, and for sure I will not become an expert), it comes out that to ensure the necessary condition, which I mentioned, a single-function boiler with a reservoir would be better. Is this my conclusion true or is it possible to find a good combi boiler that will provide high comfort of use in the case of domestic water heating ?
    At the moment I am keeping an eye on the following boilers:
    1) Viessmann Vitodens 100-W with 6.5-26 kW - B1KC026 (dual function),
    2) Viessmann Vitodens 100-W 6.5-19 kW with Vitocell 100-W type CUG (single function),
    3) JUNKERS CERAPUR MIDI ZWB 24-1 RE (dual-purpose)
    4) JUNKERS CERAPUR MIDI ZWB 24-1AR (single-function + "some" heater)
    5) VAILLANT VUW PRO 240 / 5-3 ERP (dual-purpose)
    6) IMMERGAS NIKE STAR 24 4 ERP (dual-purpose)
    7) VAILLANT ECOTEC PLUS VCW 296 / 3-5 (dual function)
    Yes, I know that the cross-section is quite large ... Opinions on the Internet regarding the above boilers are positive. How to choose the best one?
    In conclusion, I would like a new boiler:
    1) Allows for comfortable use of domestic water (trouble-free and quick heating, also during the heating season).
    2) It was failure-free
    3) He was quiet
    I know the requirements are strong, but I think it's better to pay (a little?) More now and end up with a good stove than to pay less and end up feeling nervous ...
    I kindly ask honorable forum members for help. Each tip is worth its weight in gold! :)
  • #2 16236475
    GETomek
    Help: 7
    Rate: 123
    Make a list again with boilers that start working from 3kW, then you will be satisfied with this size. Then look for a site in your area, because we don't know where you live.
  • #3 16236695
    electronic_buff
    Rate: 8
    Do you think about the minimum nominal heat output? I am from Silesia.
    Oh, in the previous post I forgot to mention the De Dietrich boilers. We are also thinking about this company ...
  • Recommend Termet Integra II with 2.8 kW minimum output
    #4 16237013
    serwo66
    Help: 61
    Rate: 292
    De Dietrich has the most expensive parts I advise against. As a colleague wrote, take into account boilers with a minimum capacity of 2-3 kW because these are from 6-7 kW and this is as much as you need to heat the whole apartment in frost -25 degrees C. The boiler will clock all the time, so it will not be economical. I recommend a combi boiler with a built-in hot water tank 45 lt Termet Ecocondens Integra II 25 kW with a minimum power of 2.8 kW and a warranty of up to 7 years. The basis is see the service.
  • #5 16238332
    electronic_buff
    Rate: 8
    The Ecocondens Integra II 25 kW termet looks really good, but ... it's too big :( I have just measured what I need and it comes out that: the boiler can be high (here Termet could easily do it), width (I give the maximum dimensions): 56 cm, depth: 50-55 cm. I really like the idea of the built-in tray. Can you recommend any other boilers with such a tray?
  • #6 16239085
    ls_77
    Help: 500
    Rate: 947
    You need to provide even more details:
    70m2 apartment on which floor and how many of them are there in the block?
    is it possible to insert a combustion pipe into a condensing boiler - you need to find out in the "cooperative"?
    Only condensing boilers will have a low minimum power, so all boilers with an open combustion chamber fall off. The condensate, unfortunately, requires inserting a ~ 80mm diameter flue pipe into the existing chimney. From boilers with a built-in storage tank, you also have:
    Vaillant VCI 296 / 5-5 (it is a 2-function boiler VCW 296 / 5-5 + "backpack" with two small containers - one is hung on the other)
    SaunierDuval IsofastCondens (1x21 l.) 25kW
    SaunierDuval IsotwinCondens (2x21 l.) 30kW and 35kW
    DeDietrich MCA 25/28 BIC (40 y.)
  • #7 16239327
    wsjoanna222
    Rate: 14
    If you don't have a floor heating, don't listen to this nonsense about condensing boilers
    these boilers are suitable for underfloor heating
    you will pay much more than for a turbo and the point is that the boiler should heat up the apartment quickly
    unless you have oversized radiators
    I would buy [Gas boiler Vaillant Turbo Tec combi boiler
  • #8 16239423
    palala
    Help: 59
    Rate: 105
    I am one of those people who, at their own request, let themselves be stretched out on a condenser.
    I will say this - I do not have an underfloor heating system, some of the radiators are still cast iron and this heating season I have not yet exceeded 50 on the boiler. As for the cost of heating, it is comparable or cheaper than before on ground / pea in previous seasons. Thermal comfort and time saved ...... The boiler works almost 24/24, almost does not clock - the exception is that it will turn off after a frosty night when the sun is strong (windows from the east and south), most of the time it works at minimum power.
    Best regards and I wish you correct zakuopów.
  • #9 16239459
    wsjoanna222
    Rate: 14
    remember that cast iron is not a sheet, as is usually the case, think why there are cast iron radiators in the blocks and find out what the price is today.
    condensation for panel heaters at the parameters of 80/60 ° C and the condensate has the highest efficiency at 50/30 ° C and what such a customer does as
    is he cold?
  • #10 16239489
    palala
    Help: 59
    Rate: 105
    It does not deal with heating installations - first of all. Secondly, my father-in-law has a turbo, 2x smaller apartment, for me strange settings of the room controller, minimum power for him about 7 kW - a boiler for power - consumption like my own (although it has a better insulated building than me) and a vestibule. I do not go into why there is cast iron in the blocks (heat allocators ;) ). In the spring I will have the rest of the radiators replaced with aluminum.
    You can look for my posts - when there is little heat demand, the room controller lowers the power and the supply temperature. Most of the time it works at a minimum or a little over. For the author of the thread, I propose to do an experiment - to put 6 kW electric heaters in the house and wait for the results ..... Maybe I'm wrong, but it may result from the fact that I have a comparison.
    Regards
  • #11 16239538
    electronic_buff
    Rate: 8
    The apartment is on the 2nd and 3rd floors (there are 3 floors). We do not have underfloor heating. Could I ask for more information on condensing boilers? Why are the owners of such stoves "dissatisfied"? Is it about their wastefulness?
    Regarding the Vaillant Turbo Tec boiler - reviews here: http://www.ceneo.pl/25185159 do not encourage ...
  • #12 16239639
    jack63
    Help: 851
    Rate: 2822
    palala wrote:
    For the author of the thread, he proposes to do an experiment - to install 6 kW electric heaters in the house and wait for the results.
    The only effect will be ... the fuses will "blow" after a short time.
    Advice pointless, even harmful.
    Don't listen to nonsense. Each condensing boiler (almost) installed in accordance with the art and not oversized will be more economical than a turbo-generator. The floor does not have much to do with it, because 90% of the heating period will still work at a low flow temperature. Well, unless someone "saved" on radiators and gave them tiny ones, requiring 90/70 oC.
    As colleagues wrote, look for a boiler with the lowest minimum power possible.
    The most optimal is to use a low-power boiler, and therefore min. together with the DHW tank.
    In new blocks, developers install boilers, min. 24 kW for the convenience of DHW, which are a disaster for central heating. The boilers cycle and burn more gas, working in conditions that are not optimal for them. However, the developers are banging it. They will not pay for gas and the tenants have the illusory feeling that "everyone pays for their heating", which is nonsense in the block of flats.
  • #13 16239648
    wsjoanna222
    Rate: 14
    Since cast iron radiators accumulate heat
    Compact heat exchangers are located in the blocks
    what kind of heaters do you have
    are they twice as powerful
    if so, you can install the condensate with the tank
    heater power such as eg Purmo CV22 600/600 at temperatures
    75/65/20 c = 1025
    55/45 / 20c = 514
    as you can see, the power of these radiators is halved
    the condensing boiler has the highest efficiency at 55/45 / 20c
    I do not understand what is the matter with this water that you cannot heat up
  • #14 16239811
    ls_77
    Help: 500
    Rate: 947
    I'm curious where!
    These boilers have not been offered for 1.5 years, because the European Union has banned them from being placed on the market. And the boiler manufacturers knew about it earlier and had already finished production earlier. If they are still in stores, they may be "storage loungers". As for performance, the condensates are more efficient than the turbo and much quieter.
  • DeDietrich rejected for width; SaunierDuval reliability questioned
    #15 16243573
    electronic_buff
    Rate: 8
    Thanks for the list! DeDietrich rather falls out of it, due to its dimensions (it is too wide). SaunierDuval looks good - does any of you have experience with this company? (And it's perfect with this boiler)? Interesting - I can't find reviews about this boiler on the web ...
    Regarding Vaillant, I found these reviews: http://www.opineo.pl/opinie-721080-vaillant-ecotec-plus-vcw-296.html, which are quite unpleasant ...
  • #16 16244226
    ls_77
    Help: 500
    Rate: 947
    I would not be influenced by these opinions.
    Unfortunately - with every condensing boiler it is so, if anyone cares, so does it.
    The condensate is very easy to "blow" and then it can cause problems. But systematic service avoids this. This is the case with all brands, not only with Vaillant :D
  • #17 16246014
    electronic_buff
    Rate: 8
    I agree that everything can be taken for granted, but comments like there are stressful ... :)
    How about these Saunier Duvals? Is it worth taking a look at them?
  • #18 16381996
    electronic_buff
    Rate: 8
    In the spring, I come back to the topic of boiler replacement, afraid to carry out this action in the winter (what if something went wrong!). The following boilers were left on the battlefield:
    - Junkers Cerapur Compact with a container 120l ST 120-5 Z,
    - Vaillant VC 146 with the same hopper.
    Any suggestions? Thank you in advance!
  • #19 16382890
    serwo66
    Help: 61
    Rate: 292
    Termet gold plus with a tray of 100 lt
  • #20 16383715
    Zbigniew Rusek
    Help: 394
    Rate: 1542
    is he cold?
    Not necessarily. For condensate, it is important that the RETURN temperature does not exceed 50 degrees and the supply temperature does not affect condensation, so it can be successfully on the supply, e.g. 70 degrees (on the return 50) and there will be condensation.
  • #21 16625527
    badboyszn
    Hello everyone!
    I am faced with the challenge of buying a gas boiler (apartment 100m2). I only know that it is supposed to be a condensing boiler with two functions. It is difficult for me to decide on a specific model. Thanks in advance for your help. Pawn!
  • #22 16823434
    Gary K
    Hello. I will join the question. My apartment is approx. 100 m on the 1st and 2nd floor (two-level). Block from 1936. Energy-saving windows, former German block. I don't have a floor heating. I am currently using a Termet minimax dynamic turbo boiler. It seems to me that more and more starts to consume about 200m of gas per month, now. 21/19 degrees Celsius settings. I am wondering about the replacement and now the question is whether condensing dual-function or similar with a closed combustion chamber and what company. Please help.
  • #23 16824901
    ls_77
    Help: 500
    Rate: 947
    Gary K wrote:
    I am thinking about replacing and now the question is whether condensing dual-function or similar with a closed combustion chamber and what company
    Combination systems with a closed combustion chamber are no longer available on the market. The ban on production and import came into force in September 2015. From that moment on, boilers already manufactured or already imported could be sold. For a long time I have not even seen anywhere in stock in any warehouse. If you buy somewhere, think about it - it may be a storage "deck chair".
    Rather, you will be left with a choice between condensing boilers. You just need to check what chimney you have currently installed for your boiler. Not all chimneys for "turbo" boilers are suitable for condensation!
    The choice of the brand is up to you - it must depend on access to a good service in your area.
  • #24 16860239
    Filip49
    DeDietrich MCA 25/28 BIC (40) - I would take this one. De Dietrich did not let us down and we have been using it for several years.
  • #25 17150472
    KamilWysoki
    I have a Termet Ecocondens Gold Plus condensing boiler (it is smaller than Ecocondens Integra II). It belongs to the "A" energy class in terms of both central heating and domestic hot water. I have no problem waiting a long time for hot water, it is quiet and so far there has been no breakdown.
  • #26 17734603
    specol
    The most optimal is to use a low-power boiler max, and therefore min. together with the DHW tank.
    In new blocks, developers install boilers, min. 24 kW for the convenience of DHW, which are a disaster for central heating. The boilers clock and burn more gas while operating in conditions that are not optimal for them. However, the developers are banging it. They will not pay for gas and the tenants have the illusory feeling that "everyone pays for their heating", which is nonsense in the block of flats.
    I can confirm that I feel it during the first heating season. I have a boiler with a minimum capacity of 8.5 kW. This is where minus 9 is on the outside, it ticks every now and then ... Well, first apartment, no knowledge. Price etc etc idt.
The discussion revolves around selecting a suitable gas boiler for a 70m2 two-level apartment with one bathroom, currently using a Roca Sara 24/24F model, which has issues with domestic water heating and pressure drops during the heating season. Participants suggest considering boilers with a minimum output of 2-3 kW to ensure efficiency, particularly during colder months. Recommendations include condensing boilers like the Termet Ecocondens Integra II 25 kW, Vaillant VCI 296/5-5, and SaunierDuval models, emphasizing the importance of low minimum power for optimal performance. Concerns about the size of the boilers and the need for built-in hot water tanks are also discussed. Users share experiences with various brands, highlighting the need for good service availability and the impact of radiator types on heating efficiency.
TL;DR: A 70 m² duplex usually needs only 3–6 kW heat output, so “look for a boiler with the lowest minimum power possible” [Elektroda, jack63, post #16239639] Correct sizing cuts cycling and boosts hot-water comfort. Why it matters: Oversized units cost up to 15 % more gas every year.
• Recommended minimum output for 70 m² flat: 2–3 kW [Elektroda, serwo66, post #16237013] • Condensing models give 6–11 % higher seasonal efficiency than non-condensing units [EST, 2023] • EU ErP banned open-flue combi sales from Sept 2015 [European Commission, 2015] • Typical 100 L integrated tank adds ~45 kg and 52 cm depth [Vaillant VCI datasheet, 2024] • Annual service costs in Poland: €80–120 [Heat24 Market Report, 2024]
Why does system pressure drop 0.5 bar when heating stops?
The expansion vessel may be under-charged or failed. When water cools, pressure falls; if the vessel cannot absorb volume change the swing grows [Vaillant Service Guide, 2024]. Re-pressurise vessel to 0.2 bar below cold system pressure and replace if diaphragm torn.
What minimum boiler power should I target?
Look for models that modulate down to 2–3 kW. This matches the peak 6–7 kW load during −25 °C frost quoted in the thread [Elektroda, serwo66, post #16237013] and prevents rapid cycling.
Are condensing boilers efficient with panel or cast-iron radiators?
Yes. Condensation depends on return temperature below 50 °C, not emitter type [Elektroda, Zbigniew Rusek, post #16383715] Oversize or double-panel radiators let you run 55/45 °C flow/return and gain 6–11 % extra efficiency [EST, 2023].
Do I need to upgrade the flue?
Condensers require a 60/100 mm concentric or an 80 mm liner. Check if the building allows inserting this in the existing shaft [Elektroda, ls_77, post #16239085] Without consent, replacement may be impossible.
Which compact combis with an internal tank fit 56 cm width, 55 cm depth?
  1. Vaillant VCI 296/5-5: 47 cm W, 59 cm D [Vaillant datasheet, 2024].
  2. Saunier Duval Isofast Condens 25: 47 cm W, 54 cm D [SD brochure, 2024].
  3. Termet Ecocondens Integra II 25: 44 cm W, 55 cm D [Termet sheet, 2024].
How often should a condensing boiler be serviced?
Annually. Neglected units fill with acidic condensate slime, leading to sensor failure and blocked siphons within 2 years [Elektroda, ls_77, post #16244226]
What is boiler cycling and why avoid it?
Cycling is rapid on/off operation when output exceeds demand. Every 1000 extra cycles can raise gas use by 3 % and shorten fan life [Carbon Trust, 2022]. A low minimum power and weather compensation stop cycling.
Edge case: what if the condensate pipe freezes?
The boiler locks out with an “EA” or flame-loss code. Lag 22 mm pipes and add a 3 W trace heater. In emergencies, pour warm (not boiling) water over the outside pipe [Gas Safe Register, 2023].
How large a cylinder do I need for one shower and kitchen sink?
A 40–50 L internal tank supplies a 7-minute 9 L/min shower plus wash-up without temperature dip. Larger 100 L cylinders add redundancy but extend reheat time [Viessmann Sizing Chart, 2024].
How can I improve hot-water comfort without space for a tank?
Install a small plate heat-exchanger combi with 3 kW minimum and add a 15 m secondary recirculation loop. Keep loop at 50 °C to limit losses [BS EN 12831-3, 2017].
3-step: how to verify a boiler’s minimum output before purchase?
  1. Open the technical datasheet and locate “Nominal heat output min. (80/60 °C)”.
  2. Ensure the value ≤3 kW for your 70 m² flat.
  3. Confirm the same figure under “DHW standby” to avoid oversized DHW stage.