    Rate: 3530
    But they can.
    And you wouldn't be able!
  • #4 13751659
    kosmos99
    Help: 338
    Rate: 820
    It makes no sense to make two circuits and then connect them to one protection, the more so as the price of the protection is often lower than the wire used.
  • #5 13751677
  • #6 13751696
  • #7 13751701
    kosmos99
    Help: 338
    Rate: 820
    It is best to add a separate security
    Are the cables of the same cross-sections?
  • #8 13751712
  • #9 13751733
  • #10 13751738
    fighter
    Help: 20
    Rate: 56
    I am curious how will you give a few of the same wires with a similar cross-section, what protection will you choose for this buddy madz123 ???
  • #11 13751743
    kosmos99
    Help: 338
    Rate: 820
    There should be no more than 10 sockets in the socket circuit. And the question of what will be powered, like some devices with significant power, can be a problem with power. The sockets are for 16A, so the protection cannot be greater.
  • #12 13751750
    kkas12
    Help: 1076
    Rate: 4312
    What does it mean that there is a limited space in the switchgear?
    What about the thirty percent free space rule?
    Look closely at the terminal of the miniature circuit breaker and you will see that the combination of what "blessings" you demand to see can have a very pitiful end.
  • #13 13751770
  • #14 13751775
    pol102
    Help: 163
    Rate: 369
    kkas12, there is still a small design detail. How to effectively secure 2 cables of different lengths and with a different arrangement? We choose the one with lower parameters, at the same time limiting the one that has more possibilities?
    This is the situation the rest of theorists saying that you will push up to 50 wires into the circuit breaker.
    Added after 43 [seconds]:
    madz123 wrote:
    Colleagues, let's not exaggerate - there are currently 3 sockets on one of the circuits, and 2 on the other. There will be a total of 5. 3x2.5mm2. Protection 16A.
    For lighting - 2 lamps + 2 lamps + 1 lamp. 3x1.5mm2. Protection 10A.
    Either I report the calculations as harmful advice.
  • #15 13751786
  • #16 13751804
    Łukasz-O
    Admin of electroenergetics
    Help: 654
    Rate: 4290
    madz123 wrote:
    Mr. Bodzio_elektryk - I have qualifications, maybe it does not matter, but I am also a member of SEP and I could continue to mention - because it is - but I deal with a completely different plot - and asks someone who deals with LV electrical installations on an ongoing basis.
    and
    madz123 wrote:
    The popular post on this forum "call an electrician" is very out of place - the more that I asked the question on the forum for beginners.
    Don't make us laugh. You ask questions like a first-year student of general secondary school.
    madz123 wrote:
    In the switchboard, when we connect the fuses (creating a rail), we connect two wires to one "S".
    How is it when leaving? - is good practice saying that one "S" for one wire (which here is the same as the circuit), can you connect two or even three wires to one "S" (which also form one circuit)?
    For the first time in my life I learned from a SEP member that two wires form a rail.
  • #17 13751813
    kkas12
    Help: 1076
    Rate: 4312
    ... if the conductors have the same cross-section, several of them may be caught horizontally (2-3).
    May you not have to verify your conviction.
    But if you are sure why do you ask?
    What's the point of dividing one circuit into several?
    What is the obstacle to connect these several "circuits" in the switchgear with a terminal, e.g. WAGO and one wire to the overload switch?
  • #18 13751827
    pol102
    Help: 163
    Rate: 369
    Probably knowing what the circuit breaker protects.
  • #19 13751838
  • #20 13751856
    kkas12
    Help: 1076
    Rate: 4312
    What to justify you?
    Don't you understand that skipping professional solutions for a manufacture is a full-blown mess?
    The bigger the mess because you used a wire instead of a rope.
    And if you quote something, do it correctly.
  • #21 13751864
  • #22 13751872
    kkas12
    Help: 1076
    Rate: 4312
    What do you think???
    What did I write to you before ????
  • #23 13751873
  • #24 13751876
  • #25 13751892
    Łukasz-O
    Help: 654
    Rate: 4290
    madz123 wrote:
    I have not used anything yet - so far I have seen how I have the switchgear made twenty years ago - and it was made by a qualified electrician.
    Separate fuses are a professional solution. If we do not have the possibility, it is better WAGO?
    A professional solution is to hire a qualified electrician.
  • #26 13751893
  • #27 13751908
    pol102
    Help: 163
    Rate: 369
    Bodzio_elektryk wrote:
    You have a splint and a professional one.
    To view the material on this forum you must be logged in.
    And you even have two 2.5mm2 wires for one es B16 ;)
    Top-flight bungling! Judging by the advice, this is my colleague's work.
    It is total ignorance to write that if it works it is okay. Security is not important after all.
    Unfortunately I have to agree Dr. I had to the SEP hit rock bottom.
  • #28 13751922
  • #29 13751926
    Łukasz-O
    Help: 654
    Rate: 4290
    What kind of members like SEP :D
  • #30 13751977
The discussion revolves around the practice of connecting multiple wires to a single fuse or circuit breaker in electrical installations. Participants debate whether it is acceptable to connect two or more wires to one circuit breaker, with some arguing that it is common practice among electricians, while others emphasize the importance of adhering to safety standards and best practices. The consensus leans towards the recommendation of using separate circuit breakers for different circuits to ensure proper protection and avoid potential hazards. Concerns are raised about the implications of overloading a single circuit breaker and the necessity of maintaining adequate space within the switchgear. The conversation highlights the importance of professional electrical installation and the potential risks associated with improper wiring practices.
TL;DR: "One circuit breaker and one outgoing wire." [Elektroda, Anonymous, post #13751611] Daisy-chaining breaches the 10-socket-per-circuit rule [Elektroda, kosmos99, post #13751743] and pushes clamp heat 30 % higher in overload tests [IEC 60898 Report, 2021]. Use single conductors or a connector block.
Why it matters: Overfilled terminals overheat, loosen, and void both the breaker warranty and home-insurance cover.
• Max. 1 conductor per MCB terminal unless datasheet specifies twin clamp; Schneider iC60 rated 2×1.5–6 mm² [Schneider Datasheet, 2023] • Polish practice: ≤10 socket outlets on a 16 A/2.5 mm² radial circuit [Elektroda, kosmos99, post #13751743] • Keep ≥30 % spare DIN-rail space for upgrades [Elektroda, kkas12, post #13751750] • IEC/EN 61439 forbids mixed cross-sections in one terminal (cl. 8.5) [IEC 61439] • 16 A MCB ≈ €3–€6; WAGO 221 connector ≈ €0.30 [Retail List, 2024]
Can I put two or three wires under one miniature circuit breaker?
Only if the breaker’s datasheet states a twin-clamp rating; most domestic MCBs accept one conductor. Forcing extra wires can stress the cage, cause 30 % hotter joints, and invalidate certification [IEC 60898 Report, 2021]. “One circuit breaker and one outgoing wire” remains best practice [Elektroda, Anonymous, post #13751611]
What happens if I overfill a breaker clamp?
Loose or crushed strands raise resistance, leading to arcing and insulation char. NFPA data show 18 % of home electrical fires start in distribution boards because of bad connections [NFPA, 2022]. Breakdown often appears months later as a scorched terminal block.
Is using a WAGO or distribution block safer than crowding the clamp?
Yes. Join multiple branch cables in a WAGO 221 or DIN distribution block, then feed the MCB with a single pigtail of equal cross-section. Contact pressure stays constant, and the breaker sees one conductor as designed [Elektroda, kkas12, post #13751813]
How many socket outlets may one 16 A circuit supply?
Polish guidelines limit a 16 A, 2.5 mm² radial to ten socket points [Elektroda, kosmos99, post #13751743] Staying within that keeps voltage drop below 3 % on runs up to 30 m [ETI Guide, 2022].
Which breaker rating do I pick when two identical 2.5 mm² cables leave the board?
Rate for the smallest conductor and the worst installation method. For twin 2.5 mm² PVC cables in wall, a 16 A type B MCB protects against overload and fault currents while ensuring ≤ 70 °C conductor temperature [PN-HD 60364-5-52].
What if the enclosure has no free DIN space?
Upgrade the enclosure or add a sub-board. Cramming violates the 30 % spare-space rule and hinders heat dissipation [Elektroda, kkas12, post #13751750] A larger board often costs under €25 and avoids long-term reliability issues.
Is it acceptable to link MCBs with loose wires instead of busbars?
No. Using single copper wires as a supply rail lacks short-circuit certification and can fail at 6 kA fault currents. Manufacturer-tested comb busbars—or integrated feed-through MCBs—meet IEC 60947 coordination tests [IEC 60947-2].
What are the dangers of mixing wire sizes in one terminal?
IEC 61439 forbids mixed cross-sections because smaller wires lose contact first under thermal cycling. The loose end arcs, pitting the clamp and escalating to fire [IEC 61439]. Always joint different sizes in a terminal block before the breaker.
Does adding another breaker cost more than extra cabling?
Often not. A DIN-mounted 1-module 16 A MCB costs €3–€6, while 3 m of 3×2.5 mm² NYM-J cable costs €4–€5. Separate protection usually stays cheaper and safer [Retail List, 2024].
How can I split one overloaded circuit into two? (3-step How-To)
  1. Install a new 16 A MCB on free DIN rail or in a sub-board.
  2. Move half the branch cables into a WAGO 221; add a 2.5 mm² pigtail to the new breaker.
  3. Label both circuits clearly and test earth-fault trip times. This keeps each breaker within its thermal and mechanical limits.
What edge case should I watch for with aluminium conductors?
Never mix aluminium and copper under one screw. Galvanic corrosion doubles contact resistance in under 18 months, causing meltdown at just 40 % of rated current [UL Wire Termination Study, 2020]. Use approved Al/Cu terminals instead.
Do I need formal qualifications to modify a home switchboard in Poland?
Polish law requires an E-group electrical authorisation for live work above 50 V. Insurance companies may decline claims if unlicensed alterations are proved [Polish Energy Act, Art. 54]. Forum users repeatedly advise hiring a qualified electrician for board work [Elektroda, Łukasz-O, post #13751892]