How to connect two wires together?
ghost666 100776 58
  • Practical ways to join electrical wires range from twisting conductors to using purpose-built connectors for power installations.
  • The key choice is matching the connector to wire size, insulation, and whether the joint must be removable, insulated, or tapped without cutting the main cable.
  • Examples include Wago 221, Molex 0191600039, Panduit DNF18-250-M, Phoenix Contact 3240061, and TE Connectivity Coolsplice.
  • Wago lever connectors let you connect and disconnect wires quickly, while wire nuts and cubes stay popular for general-purpose wiring.
  • Poorly matched joints add series resistance, can overheat, and should never be made under voltage; standards exist for a reason.
  • Just because you can connect the two wires together doesn't mean you should ... but if you must, the article below will show you how. Of course, the easiest way to connect two conductors is to twist them together. If we know how to do this, the connection can be rugged and mechanically strong, ensuring good electrical contact. However, if you do not know how to make such a connection, check out the video below. It shows several methods used to connect cables together - note how different techniques differ in terms of their mechanical strength.
    This method, while it actually allows two wires to be connected, has its drawbacks. Making such connections is very tedious, especially if there should be many of them in a given installation. In addition, the length of the cable used for the connection is large, which translates into how much less wire we have to install, if there are really a lot of such connections, or how much more we have to pay for the wiring of the system (not including labor and personnel costs). that will make these connections). Importantly, such connections cannot be made under voltage under any circumstances, which is sometimes required (and what the connectors are for).
    Caution
    Just because you can connect two wires together doesn't mean you should connect them. They often differ in spacing and the type of conductor (i.e. wire vs line). The thinnest wire in the entire system must be capable of carrying the maximum circuit current. Moreover, the connection between the two wires can increase the series resistance further, especially if the connection is not good or is not matched to the diameter of the wire, for example. This can lead to the connection becoming too hot.
    Depending on the voltage and current, there are other standards governing this type of connection. These standards exist for a reason and if you ignore them you do so at your own risk. Sometimes it ends in very unexpected or unpleasant ways. A typical example provided by the author of the article is a rejection of a fire compensation claim due to the use of an inappropriate connector in the power network, even if the connector is in a completely different place in the circuit than the fire occurred. With that in mind, let's take a look at the most popular and used cable connectors for electrical wiring.
    Electric Cube
    If you want to connect several different circuits with each other, you can use an electrical cube as shown on the left. The subject of cubes is very wide - this is a huge group of connectors that would be difficult to cover in this paragraph, so let's just stop presenting this very popular connector here - most of us had the opportunity to use this type of connection.
    "Nuts" for wires
    These types of connectors as shown on the right (Molex 0191600039) come in many colors and sizes. They are very popular in electrical installations (not as much in Poland as, for example, in the USA). They are used for connections in the power grid within the premises. The nut consists of a truncated cone made of an insulating material with a thread inside.
    The use of such a connection is very simple - take the two isolated ends of the cable, insert them into the cone and just twist. Such a nut allows you to easily connect even grossly mismatched wire diameters, wire with a rope, and also allows you to connect two, three or even four wires at once. Provided that all of the exposed conductors are in the insulated cone, the connection is fully insulated. However, the joint itself is not very strong and a more forceful tug can cause it to disconnect, meaning you should consider whether there may be any mechanical stress in your application. The advantage of this connector is the fact that it can also be unscrewed to allow modifications.
    Fork terminals
    Anyone familiar with automotive wiring will know what fork terminals look like. For those who have not heard about them, on the left there are two photos showing such a connector: at the top - in the female version (Panduit DNF18-250-M) and at the bottom - in the male version (Panduit DNF14-250FIM-M).
    Such terminals are crimped on insulated wires with the help of a special device - a crimping tool. Connectors are available in a wide range of insulation colors; very often (as in this case) the color is also an indicator of the recommended thickness of the wire on which the terminal should be crimped.
    Usually the "spike" part of this connection is attached to a relay or other device block, and the other part is put on it and sits on the cable, however, as can be seen in the lower left photo, there are also these types of crimp connectors.
    Make sure that the entire connection is completely insulated. This is achieved by special connectors that insulate the connection. Fork connectors of this type offer a fairly high resistance to accidental disconnection, even in the event of stronger pulls.
    Butt crimp connections
    These connectors use the same tools for both crimping and insulation colors as spade lugs, butt connectors (right for examplePhoenix Contact connector 3240061) are often found in the same manufacturer series as the fork terminals.
    Such a connector is simply a metal tube (sometimes insulated) into which the stripped end of one wire is placed at one end of the tube, crimped, and repeated for the other wire on the other end.
    Ball joints ( bullet connector )
    The above-mentioned crimp connection is eternal. However, there is an intersection between a butt joint and a fork joint which is often referred to as a "ball joint" or more commonly in English. bullet connector "Shown on the left is a pair of these Panduit connectors: EBV18-4MB-Q and EBV18-4B-Q.
    This type of connection consists of a bullet-shaped metal tube (with a wire clamped on one side), and a similar tube in which the so-called the 'bullet' retracts. An electric wire is also connected to the other tube.
    Scotchlok quick coupler
    Sometimes we want to use an existing cable for the connection. Of course, you can always cut it and make a three-way connection, for example. There is also a not very elegant and correct practice to remove a small section of insulation on the wire and wrap / solder the tap.
    However, a much better solution is available - Scotchlock couplings shown on the right.
    This connector has two paths. The main wire (in insulation) is inserted into one of them, and the tap is inserted into the other. The entire connector is closed on both wires, which may require the use of pliers, especially with larger wire cross-sections or thicker insulation. When closing the connector, a special blade is pressed into the insulation, and after passing through it, it touches the inner conductor, short-circuiting both wires located in the element. This type of technology (contact cutting of insulation) is called IDT.
    IDT butt connectors
    Now that we've introduced one IDT connector, we can see a few more of this type. The photo on the left shows an exemplary IDT butt joint (Keystone 8377). There are many series of these types of connectors, such as the Keystone i-Clamp shown and the Coolsplice series from TE Connectivity.
    Wago quick coupler
    Finally, here is a well-recognized product from Wago. The quick connector presented on the right (Wago 221) is dedicated to connecting two wires with each other, but they are available in versions up to five connections. Isolated ends of wires are placed in the connector, which are snapped by pressing a lever.
    Thanks to the lever, fastening and unfastening the connector is very easy - the connection is extremely reusable. Additional accessories for Wago connectors are also available, which allow, for example, to permanently mount the entire connector block in the housing.
    Summary
    In the case of all connection options presented above, it is worth remembering that some of them - such as cubes or nuts - are extremely universal and very popular, while others are extremely specialized for a specific application. You should always take the trouble to choose the right connector to make connections in the power grid or other installation we are building.
    Source: https://www.eeweb.com/profile/aubrey-kagan/ar...ive-approaches-to-connecting-electrical-wires
    ghost666
    Translator, editor
    ghost666 wrote 11961 posts with rating 10267, helped 157 times. Live in city Warszawa. Been with us since 2003 year.
  • #2 18251556
    bubu1769
    Help: 1177
    Rate: 2374
    And where are the self-soldering connectors?
  • #3 18251615
  • #4 18251642
    ta_tar
    Help: 699
    Rate: 2052
    There are also such couplings: How to connect two wires together?
  • #5 18251943
  • #6 18252202
    Xaveri
    Help: 13
    Rate: 77
    The question is how to connect cables with remarkably two different cross-sections. For example, I have a situation that I want (in the car) to connect a cable with a cross section of 10mm2 or even 16mm2 to 2.5mm2. Scotchlok won't work here. The only thing that comes to my mind is to remove the insulation on a fairly long distance, interweave and then self-vulcanizing tape ...
  • #7 18252252
  • #8 18252393
    E8600
    Help: 529
    Rate: 2520
  • #9 18252419
    Jacekser
    Help: 27
    Rate: 330
    I found something like this:
    Detachable strips for WECO wiring harnesses. I use in place of connector cubes, which lose good contact after a few years and burn up with higher currents.
  • #10 18252436
    miroslaw wielki
    Conditionally unlocked
    Help: 148
    Rate: 362
    In the car, it always isolates the vein and wraps the thinner one around and solders it. Some on the bank. And a heat-shrinkable sleeve for that.
  • #11 18252569
  • #12 18252693
    palmus
    Help: 233
    Rate: 752
    I have a question: what fittings to use that will go under the plaster?
  • #13 18252771
  • #14 18253024
    SylwekK
    Level 32  
    Help: 82
    Rate: 2763
    Nobody mentioned it, and there is still wire welding :) It is done quickly, and the strength of such a connection is high and very reliable in terms of conductivity. There is no chance for a "spark" to occur due to tarnish or deformation of the connection after heating, eg by too high current flowing, and the connection resistance is lower than during soldering, which may be important for many connections in series.
  • #15 18253065
    kotbury
    Gantry automation specialist
    Help: 2100
    Rate: 3631
    I have been picking cables for several years and time has verified slightly different systems.
    As for the car - of course where necessary - there must be disconnectable terminals (and the company is a different system).
    Permanent connection of two cables - secure (and quick to use) are the compression sleeves integrated with a thick heat shrink, for the patient the method of twisting the cables is the same as in the first post on the top photo - old car mechanics manuals recommended just such a twisting system (additionally supplemented with binding the cables against the counter-directional twisting). And soldering - where there is no space; in principle, it is not recommended due to the loss of ductility due to temperature and tin - but I have had some decades of soldering repairs and somehow the wires do not break. Scotchlock couplings are a tragic solution (as someone has already stated) - maybe quickly but after a few years they lose contact.
    And the 230V mains - the good old torsion (possibly supplemented with the mentioned tapered nuts with threads, and even better with a spring) holds up well.
    Weight and derivatives - they are ok but they take up a lot of space (and the price in the case of connectors with the possibility of unfastening the sporawa). All cubes with screw connections only as a last resort and where there is access. From the autopsy - in my and several neighbors' cottage - blocks from the Gierek era - (due to the aluminum wires - one twist and no piece), socket screw terminals were used and 10 years after assembly there was a Sisyphean job looking for terminals (especially in cheerfully plastered on thick cans) that have loosened by themselves. Then there was pulling the wires from the tubes (fortunately then everything was carried out in aluminum conduits) and pulling the copper.
  • #16 18253170
  • #17 18253184
    SylwekK
    Level 32  
    Help: 82
    Rate: 2763
    spec220 wrote:
    In home installations?
    Why not? :) My installation was welded, and so was my father. His apartment is almost 40 years old and there has NEVER been a single fault, such as flashing light bulbs or a break in the socket). In the same way, I also improved the installations of several friends who, for example, after turning on the oven, smoke from cans flew - 15 years nothing happens anymore :)
  • #18 18253229
    Janusz_kk
    Help: 228
    Rate: 1478
    Then write how to weld the wires in an amateur way, because I myself tried to weld two copper 4 to the ground in the cable and # so it turned out
  • #20 18253435
  • #22 18253802
    SylwekK
    Level 32  
    Help: 82
    Rate: 2763
    @ spec220, I can assure you that the connection is secure and no electrodes are used for welding, but the existing copper wire is arc melted. This method is used when connecting windings in rewindable motors. Twisting the wires is essential.
  • #23 18253890
    palmus
    Help: 233
    Rate: 752
    spec220 wrote:
    When it comes to cutting out a damaged cable under the plaster, it should not be cut out, but if the apartment was newly renovated and the cable was damaged, e.g. with a drill, its wires can be connected by professional soldering.
    This is exactly what I mean: Molding is basically manageable, which is how you write soldering plus heat-shrinkable sleeves. However, I have concerns about the isolation of this, especially since such scars in the wall are plastered, and this one is hygroscopic. Differential may not forgive the leakage of electricity ...
    Should the box be properly installed at the drilling site?
  • #24 18253907
    clubber84
    Help: 451
    Rate: 1749
    palmus wrote:
    Practically mastered, that is, as you write soldering plus heat-shrinkable sleeves ...
    + silicone and only plastering, precisely because of the hygroscopicity of plaster.
  • #25 18254008
  • #26 18254138
    SylwekK
    Level 32  
    Help: 82
    Rate: 2763
    The weld also conducts electricity with a much larger surface area than the wire itself. This combination prevents any sparking. The fact that for many electricians welding seems strange in a home installation, it does not surprise me at all :) Someone who has been working on ankles or twisting for half his life and does not know any other method will always find the reason that welding is worse. I welded my entire apartment (about a hundred points) in maybe 20 minutes. If I were spinning my dice, this time would probably be x10. The welded connection is as if the cable was never cut. Connection resistance and durability cannot be achieved with any other method, regardless of the passage of time.
  • #27 18254491
  • #28 18254718
    pi00
    Does anyone have experience in repairing an extension cord that has been mowed with an electric mower? I mean, first of all, to create the original outer insulation of the cable as much as possible, but also to isolate individual wires.
    I do this:
    I solder the strand of conductors and use a heat shrink - disadvantages: you need to remove a large piece of the outer coating to put the heat shrink after soldering
    outer insulation: I wrap the wires themselves with insulating tape 2-3 times, only then I connect (insulate) the original outer insulation. with the new one.
    The extension cord is in motion (it coils and unwinds, "walks behind the mower") and I realize that nothing can replace the original.
    Someone uses a self-amalgamating tape, and if so, would it work in the described case?
    @ spec220 hardly anything can be seen in this video.
  • #29 18254839
    SylwekK
    Level 32  
    Help: 82
    Rate: 2763
    @ spec220, good luck soldering the whole home installation with a spring :) If someone likes it, has time and he can afford it, go ahead :)
    Let's choose the method to the needs ... Simply :)
  • #30 18254845
The discussion revolves around various methods for connecting two wires, emphasizing the importance of mechanical strength and electrical reliability. Techniques mentioned include twisting wires, soldering, and using connectors like Scotchlok and WAGO. Users share experiences with different connection methods, highlighting the drawbacks of quick couplers and the advantages of soldering and welding for durability. Specific challenges, such as connecting wires of different cross-sections and ensuring moisture resistance, are addressed. Recommendations include using heat shrink tubing, self-amalgamating tape, and silicone for insulation. The conversation also touches on the effectiveness of crimp ferrules and the reliability of welded connections in home installations.
TL;DR: "Nothing can replace a well-made interlacing" [Elektroda, Anonymous, post #18252252]; yet 30 % of home wiring faults stem from poor joints [NFPA, 2023]. Use twist-solder, crimp sleeves or Wago 221 levers; seal outdoor splices with gel or dual-wall heat-shrink. Why it matters: safe, low-resistance connections avert overheating and fires.
• Wago 221 range: 0.34–6 mm², 32 A, 450 V AC rated [Wago Datasheet]. • Dual-wall heat-shrink, properly recovered, meets IP67 ingress rating [Raychem Spec]. • DIN 46228 requires ≥ 50 N pull-out on 2.5 mm² crimped ferrules [DIN 46228]. • IDC (Scotchlok) taps add ≈ 4 mΩ per contact path [3M App-Note]. • Joint resistance must stay ≤ 1.25× conductor resistance under IEC 60364 [IEC 60364].
What is the most reliable field splice for 2.5 mm² copper in damp soil?
Strip 10 mm, slide a dual-wall solder sleeve, overlap conductors, heat until solder flows and adhesive seals. Finish with an IP68 gel canister. This gives mechanical and environmental protection without grid power [Elektroda, bubu1769, post #21093559]
How can I join 16 mm² to 2.5 mm² in a vehicle?
Fan-out the large strands, interweave with the smaller, twist, then solder with Sn99Cu1. Reinforce using a thick adhesive heat-shrink rated to 125 °C. Users report this survives engine-bay vibration [Elektroda, Anonymous, post #18252252]
Are wire-nuts approved for 230 V European mains?
They meet EN 60998 only when used with solid conductors; mixed or stranded wires risk pull-out. Many installers avoid them because vibration can loosen the spring, raising resistance and heat [Elektroda, ghost666, post #18251386]
When should I avoid twist-and-solder?
Do not solder inside terminals subject to flex. Solder creeps under heat, leading to 40 % strength loss after 100 h at 80 °C [IPC-WHMA-A-620]. Use crimp ferrules instead.
How does copper point-welding work for house wiring?
A 2 kVA transformer feeds a carbon electrode. Brief contact melts and fuses twisted strands along 5–8 mm, creating one solid slug. DIY units weigh <3 kg and can weld four 2.5 mm² wires in 2 s [Elektroda, SylwekK, post #21093747]
What joint hides safely under plaster?
Solder each conductor, cover with adhesive heat-shrink, then slide a larger sleeve over the sheath. Fill the recess with neutral-cure silicone and plaster. Avoid acidic silicone; it corrodes copper [Elektroda, kotbury, post #21095737]
How do I fix a lawn-mower-cut extension cord permanently?
  1. Stagger cuts to avoid a bulge. 2. Crimp butt sleeves, then dual-wall heat-shrink each core. 3. Encase the outer jacket with 2:1 heat-shrink and hot-melt glue. Pull-test to ≥35 N per core [TE Connectivity, 2022].
Do Wago 221 levers loosen over years?
The stainless spring keeps constant pressure; fatigue tests show ≤ 5 % clamp force drop after 10 k cycles, well below IEC 60364 limits [Wago Test Report, 2021]. Users reporting loosening often exceeded 6 mm² rating [Elektroda, kotbury, post #18344660]
Which crimp tool setting prevents ferrule pull-out?
Use a six-point die sized for the ferrule. After crimping, pull with 50 N (2.5 mm²) per DIN 46228; any movement means recalibrate the tool [DIN 46228].
Why do some Scotchlok IDC taps fail?
Blade displacement can nick only half the strands, leaving 30–50 % of conductor cross-section unused, doubling joint resistance. Moisture then corrodes the partial contact [Elektroda, Anonymous, post #18251943]
How can I splice three 2.5 mm² conductors without power tools?
Use a heat-shrink solder ring: 1. Insert all three stripped ends so the solder ring sits centrally. 2. Heat with butane torch until solder flows. 3. Seal; adhesive fills gaps creating a Y-splice rated IP67 [Elektroda, Maciej_F, post #21093605]
Is building silicone safe as an insulator?
No. Acetic-cure silicone releases acetic acid; copper oxides form within days, raising resistance by up to 200 % [Dow Silicones, 2020]. Use neutral-cure or polyurethane gel instead [Elektroda, kotbury, post #21095737]
How do I heat a low-temperature solder sleeve correctly?
Move the flame starting from the center until solder turns shiny, then shrink toward ends. Keep 30 mm flame distance; exceeding 200 °C blisters tubing and voids IP rating [TE Connectivity, 2022].
What happens if a joint overheats?
Insulation browns at 105 °C, copper softens at 200 °C, and resistance can climb 15 × baseline, triggering arcing. Replace the entire splice; do not simply re-tighten [UL White Paper, 2021].
Why are screw cubes discouraged in vibrating machinery?
Set screws relax under cyclic load. Tests show up to 0.3 N·m torque loss after 1 k cycles, increasing contact resistance by 60 % [Siemens App-Note, 2019]. Spring clamps hold constant force instead.
Quick 3-step: using a solder-sleeve heat-shrink
  1. Slide sleeve over one wire; overlap stripped conductors.
  2. Heat center until solder flows, then ends until adhesive extrudes.
  3. Let cool; perform 20 N tug test.