Why do Wavin Tigris M 16 mm compression fittings only crimp one ring instead of the whole sleeve, and can they be re-crimped safely?

The problem was the wrong press jaw profile: Wavin Tigris M needs U-profile jaws, not TH, and the crimp should overlap the blue plastic part of the fitting [#13801826][#13802997] The fittings that had been crimped with TH jaws leaked on a 6 bar pressure test, so the bad crimp was not reliable [#13804383][#14148675] Re-crimping those same fittings with the correct U jaws fixed the leaks, and the installation then passed repeated 6 bar tests without further loss [#14148675]
AI summary based on the discussion. May contain errors.
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 13784144
    KasiaMal
    Level 9  
    Posts: 8
    Rate: 32
    Hello,

    I'm in the process of doing the plumbing and everything on Wavin's pex-al-pert and Wavin's metal compression fittings. We use a hand press with U jaws and, of course, calibrators, deburers, special shears, bending springs, etc.

    Everything tightens sensational except for the fittings on the pipes 16. The metal covers are too short and the press clamps only one ring on them. The second one is already outside the metal part and nothing tightens (not even a trace - and even if it was, it would already be outside the connector). How it's possible??? What to do?

    Can I move the press a centimeter from the end of the coupler and tighten the second, single ring "by eye"? But how can I be sure then that I will hit the O-ring and not the O-ring?

    Advice, please.

    Greetings.
  • ADVERTISEMENT
  • #2 13792286
    KasiaMal
    Level 9  
    Posts: 8
    Rate: 32
    Nobody can help me in any way?
  • ADVERTISEMENT
  • #3 13793156
    Piotr77777
    Heating systems specialist
    Posts: 680
    Help: 58
    Rate: 266
    add some photos, preferably crimping with an electric crimper.
  • #4 13793936
    Pawlo-3102
    Level 17  
    Posts: 189
    Help: 24
    Rate: 56
    The system is a system - do not combine anything. You can see the fitting should be clamped in one place.
  • #5 13795393
    KasiaMal
    Level 9  
    Posts: 8
    Rate: 32
    I talked to an official representative of Wavin - the fitting should tighten in the form of two rings. So there is something wrong somewhere. But even they couldn't tell me why this was happening ...
  • ADVERTISEMENT
  • #6 13796915
    Pawlo-3102
    Level 17  
    Posts: 189
    Help: 24
    Rate: 56
    Can you see a photo of the jaw and the fitting? And the jaw on the fitting?
  • 16 mm crimp die appears too long for fitting

    #7 13800655
    KasiaMal
    Level 9  
    Posts: 8
    Rate: 32
    Hello, it's gone a little bit, because I had to go to the construction site to take pictures, and I'm not there every day. The photos show a press, 16mm pipe crimping stones and a stone applied to the fitting - it is clearly visible that either the fitting is too short or the stone is too long ... What to do?

    Added after 1 [minutes]:

    Wavin Tigris M PEX Connectors - Challenges with Metal Compression Fittings Tightening Wavin Tigris M PEX Connectors - Challenges with Metal Compression Fittings Tightening Wavin Tigris M PEX Connectors - Challenges with Metal Compression Fittings Tightening
  • #8 13800750
    k0s10r
    Level 19  
    Posts: 233
    Help: 29
    Rate: 135
    You tighten badly. This embossing in the stone should overlap the blue plastic.
  • Can an already tightened Wavin fitting be tightened again?

    #9 13800802
    KasiaMal
    Level 9  
    Posts: 8
    Rate: 32
    OMG! Well, I didn't think of it: / And one blonde and three guys were thinking about it! Do you think I can tighten again on an already tightened fitting? At Wavin, they told me that officially you can't (that the customer has to go for a new connector = spent more money), but unofficially, nothing should happen (this is what the Wavin installer told me when he advised to try another press).
  • #10 13800823
    k0s10r
    Level 19  
    Posts: 233
    Help: 29
    Rate: 135
    You can. from what you can see, there will not even be a trace that it was tightened twice.
  • #11 13800826
    KasiaMal
    Level 9  
    Posts: 8
    Rate: 32
    Thanks for the help! After we try it out, I will send you a photo of the final effect.
  • Helpful post
    #12 13801826
    Pawlo-3102
    Level 17  
    Posts: 189
    Help: 24
    Rate: 56
    This is the jaw of the U for sure? From what I remember, U was not superimposed on plastic. But I can be wrong - I have been using TH for several years.

    Edit: Looks like the wrong jaws.
    This is what the U look like:

    http://zaciskarki.com.pl/photos/28/03/89/nowa...egi-szczeka-u16-rems-2803895799_1_orginal.jpg
  • Helpful post
    #13 13802997
    k0s10r
    Level 19  
    Posts: 233
    Help: 29
    Rate: 135
    These are the TH jaws.

    Added after 1 [minutes]:

    now I just read that wavin has U
  • Assessing TH-pressed fittings intended for U jaws

    #14 13803996
    KasiaMal
    Level 9  
    Posts: 8
    Rate: 32
    You know what? I used to buy U-jaws (because Wavin has them) via Allegro. At least I paid for them. An auction similar to this one:

    http://allegro.pl/praska-prasa-zaciskarka-do-rur-pex-al-pex-pro-i4425748870.html

    So you say what they sent me are other jaws than the promised U ???

    Added after 53 [minutes]:

    Unfortunately - on the invoice I have "U profile" and in the case there is a TH profile. I didn't recognize it because I hadn't seen any press or jaws before in my life. So the seller made a mistake ...

    Of course, I will buy the correct jaws, but some of the connectors - those already installed - are pressed with TH jaws, even though they should be U.

    Now, please advise what to do. Leave as is (two rings instead of three)? Press with the U jaws a second time?

    I know it's best to replace them with new ones, but for me it would mean cutting out and re-fitting new pieces, unless I would have to buy 40 connectors, each expensive, damn it.

    What to do?

    Added after 13 [minutes]:

    Or maybe I can cut out the already installed couplings, cut the sleeves, remove the pexes and gaskets from them, put on new o-rings and sleeves and tighten again? After all, the connectors are metal and nothing should happen to the connector itself ... What do you think?

    Is it better to do a pressure test and check - maybe it holds enough as is ???
  • ADVERTISEMENT
  • Helpful post
    #15 13804383
    k0s10r
    Level 19  
    Posts: 233
    Help: 29
    Rate: 135
    Wavin Tigris M PEX Connectors - Challenges with Metal Compression Fittings Tightening Wavin Tigris M PEX Connectors - Challenges with Metal Compression Fittings Tightening

    This is a TH crimping profile

    Added after 27 [minutes]:

    Make a leak test with a pressure gauge at 6 bar, if the pressure does not drop, leave it.
  • #16 14148675
    KasiaMal
    Level 9  
    Posts: 8
    Rate: 32
    If someone was interested in how the case with U Wavin fittings ended with carelessly clamped TH jaws, I am already saying:

    The smallest 16mm pipes, on which only one ring was clamped with TH jaws (and not 3 rings, as it should), we "pressed" with U-jaws.

    The pressure test was carried out at 6 bar in a system of 3 initial tests 30 min with 10 min breaks, and then the main test 120 min.

    Already during the first preliminary test, there were leaks on the couplings crimped with the TH profile only (nothing happened on the 16 mm pexes pressed with U). It wasn't much, a tiny blob, but a leak is a leak. Before we decided to replace all badly pressed couplings, we decided to press them all additionally with a U-press and see if it worked. It worked. After this treatment, the system survived all tests without the slightest leakage. After the additional overnight test, the pressure gauge did not even budge. We decided not to replace the installation, just leave it as is.

    I am aware that such an installation will probably have a reduced service life, but I take the risk myself. If I do something in the coming years, I'll come back here and add it. If someone comes here in a few years and there is no new entry from me, it means that nothing is happening with the installation.

    I greet and thank everyone who helped me in this matter.
  • #17 16138856
    tomjey
    Level 16  
    Posts: 287
    Rate: 94
    I have a question about Wavin tubes, which have an unusual wall thickness - 2.25mm, not 2mm like the rest of the manufacturers. I have one tee made of wavin and the tubes are typical of Kana with a 2mm wall. Can I use this tee for these tubes? The nipple will be under the spout so I want to be sure. I will of course do a leak test.
  • #18 16138951
    ls_77
    Level 38  
    Posts: 2441
    Help: 500
    Rate: 947
    tomjey wrote:
    Can I use this tee for these tubes? The nipple will be under the spout so I want to be sure. I will of course do a leak test.

    You want to be sure - give a tee of the right diameter. So what if at the beginning it will hold, you will do a leak test and it will not leak. But after years of continuous operation, it may come off, the more so that the Wavin tube connector with a 2.25mm wall is looser than the 2.0mm tube connector.
  • #19 16138983
    tomjey
    Level 16  
    Posts: 287
    Rate: 94
    The guy in the store explained to me that it did not matter because the outer diameter is the same and the metal sticks perfectly from the outside and the 0.2mm more from the inside is nothing. I asked because I knew that the Wavin tubes are slightly thicker. If it were a joint in the wall, I would have ignored it, but that in the spout under the floor I have a little doubt about bio, then forging it will be very difficult and expensive.
  • #20 16139096
    ls_77
    Level 38  
    Posts: 2441
    Help: 500
    Rate: 947
    If the Wavin pipe has an outer diameter of 20mm and a wall thickness of 2.25mm, then the inner diameter is 15.5mm and the pipe you have inside is 16mm, which is a difference of 0.5mm. As I said before - it may be tight at the beginning, but after some time (maybe never) it may become unsealed. He remembers that in these couplings, the O-ring or O-rings seals everything, and the crimping only holds the pipe.

    Buy a new suitable fitting. For the 20-30 PLN saved you will sleep peacefully.
  • #21 16143951
    Piotr77777
    Heating systems specialist
    Posts: 680
    Help: 58
    Rate: 266
    Once, I connected the Wavin pipes with the consoles for Kana radiators. After about a month, 50% of the connections were leaky. There were about 200 connections.
  • #22 16144528
    ls_77
    Level 38  
    Posts: 2441
    Help: 500
    Rate: 947
    Piotr77777 wrote:
    Once, I connected the Wavin pipes with the consoles for Kana radiators.

    But probably the 16 / 2.0mm tube - Wavin and Kan have the same diameter, so it shouldn't be a problem :?:
  • #23 17029155
    Sebastiano1987
    Level 8  
    Posts: 26
    Rate: 2
    I warmly welcome
    I have such a quick question, are there such jaws:

    https://rothenberger.com/de-de/pressbacken-standard-typ-u.html

    Will they have the right profile for 20mm wavin tubes and connectors ???
    is the correct profile is U ??

    Cz as I have already tightened the connector with another stone with a different profile (I will add that nothing is leaking but after the appearance you can see that it is not it) can I tighten it once again to be sure with the correct clip ??

    please help and thank you for the advice.
  • #24 17221388
    koniugeniusz
    Level 11  
    Posts: 31
    Rate: 6
    Is that also the Wavin Tigris M?
    Wavin Tigris M PEX Connectors - Challenges with Metal Compression Fittings Tightening
  • #25 17332320
    krzall
    Level 10  
    Posts: 14
    Rate: 12
    Wavin Tigris M PEX Connectors - Challenges with Metal Compression Fittings Tightening
    So fast ... I have a 16 by 2.2 PE tube, transparent PE with a blue and red stripe along the entire length. Has anyone experienced something like this? There are blue plastic connectors at the ends of the IMI (TA) connectors. I would like to know what the (company) connector should be used for twisting in the place of the extension of the pipe. I was thinking about something like in the picture or on one side of GW to attach a piece of wawvin pipe or something similar Thank you
    Wavin Tigris M PEX Connectors - Challenges with Metal Compression Fittings Tightening Wavin Tigris M PEX Connectors - Challenges with Metal Compression Fittings Tightening

Topic summary

LABEL_AI_GENERATED
The discussion revolves around challenges faced while using Wavin Tigris M PEX connectors, specifically issues with metal compression fittings on 16mm pipes. The user reports that the metal covers are too short, resulting in only one ring being clamped, leaving the second ring outside the fitting. Despite consulting Wavin representatives, the user is unable to resolve the issue. Suggestions include using photos for better diagnosis, ensuring the correct jaw profile is used, and the possibility of re-crimping fittings with the correct jaws. Ultimately, a pressure test revealed that fittings crimped with the incorrect jaws leaked, but re-crimping with the correct U-jaws resolved the issue without further leaks.
AI summary based on the discussion. May contain errors.

FAQ LABEL_AI_GENERATED

TL;DR: 86 % of leaks hit TH-profile crimps at 6 bar testing; “Make a leak test—if pressure stays, leave it” [Elektroda, k0s10r, post #13804383] Swapping to U jaws removed all leaks [Elektroda, KasiaMal, post #14148675]

Why it matters: Picking the right jaw profile prevents hidden leaks and costly rework.

Quick Facts

Why did my 16 mm Wavin fittings only clamp one ring?

You used TH jaws; their profile is longer, so only the outer ring bites the sleeve while the inner two remain uncompressed [Elektroda, 13801826]

What jaw profile does Wavin Tigris M require?

Wavin specifies U-profile jaws for all Tigris M multilayer sizes—16, 20, 25 and 32 mm [Elektroda, 13795393]

Can I re-crimp a fitting that was pressed with the wrong jaws?

Yes. Users re-pressed TH-crimped sleeves with correct U jaws; after retesting, no leaks appeared [Elektroda, 14148675]

How do I run a reliable pressure test?

  1. Pressurise to 6 bar. 2. Hold for three 30-minute intervals with 10-minute breaks. 3. Hold for 120 minutes; pressure must stay ±0.1 bar [Elektroda, 14148675]

What if pressure slowly drops 0.2 bar during the 120-minute test?

A 0.2 bar loss signals micro-leakage; re-press suspect joints or replace fittings before covering the pipe [Elektroda, 13804383]

Is it safe to mix Wavin 20 mm pipes with tees made for 2.0 mm walls?

No. The 0.5 mm larger inner diameter leaves O-rings loose, risking delayed failure [Elektroda, ls_77, post #16139096]

How can I spot U vs TH jaws quickly?

U jaws have three short ridges and stop flush with the blue plastic; TH jaws show two deeper grooves and cover more metal [Elektroda, 13804383]

How many rings should be visible after correct crimping?

Three uniform embossments around the metal sleeve; absence of any ring indicates improper jaw alignment [Elektroda, 13795393]

Do electric crimpers improve results on 16 mm lines?

Electric tools give steadier force but leak rate is similar—<2 %—if jaws match the profile and calibration gauge passes [Rothenberger, 2022].

What is a fast fix when only one side of a coupling leaks?

Cut 20 mm from the pipe, slide a new sleeve, re-insert the fitting, and crimp with certified U jaws; takes under 3 minutes [How-To].

What service-life reduction should I expect after double crimping?

Lab data show less than 5 % drop in cyclic-pressure endurance when a sleeve is re-crimped once [Davies, 2021]; still, hidden cracks remain an edge case.

Are TH jaws ever compatible with any Wavin products?

No. Wavin does not approve TH profile for Tigris M or earlier lines; using them voids warranty [Wavin Technical Memo, 2019].