Soldering vs. Traditional Connections in Electrical Installations: Pros, Cons & Regulations
invx 30879 14
Can soldering be used instead of terminal blocks or other traditional wire connectors in an electrical installation, and is twisting the wires then insulating them with tape acceptable?
Yes, soldering is allowed for wire connections in low-voltage electrical installations, and well-made twisting is also used; however, a soldered wire should not be clamped directly under a screw terminal because tin is brittle and such joints burn out easily [#1483236][#1488759][#1484564] The cited regulations say conductors may be joined by welding, pressing, soldering, or suitable accessories, and that solid copper conductors up to 10 mm² and cables up to 6 mm² may be connected without terminals as long as the ends are soldered [#1483236] For copper conductors above 10 mm², terminals are required, while aluminum should use spring-loaded screw connections [#1483236] In practice, twisting plus soldering can be a very reliable joint because well-twisted conductors create several copper-to-copper contact points that solder then mechanically stiffens and seals [#1488759] The downside is that soldered connections are harder to repair or modify later, so they are less convenient in installations that may need future changes [#1482075][#1483114]
  • #1 1481834
    invx
    Help: 17
    Rate: 102
    are soldering in the electrical installation allowed instead of traditional connections with cubes or terminals ???? what about twisting the wires and then isolating it with tape?
  • #2 1481858
    bestler
    Help: 254
    Rate: 894
    I do not know how it is theoretically, i.e. from the regulations, but I know that soldering has better parameters than any twisting or using cubes. The solder is a permanent galvanic connection, then there is no sparking - and thus the system is more reliable.
  • #3 1482075
    KMY
    Help: 25
    Rate: 97
    I agree with the bestler. Electrical installations at home, for example, are not soldered for one reason only. Difficulty in getting to all points with a soldering iron, and with possible future repairs, it is easier to unscrew the wire from the strip than to desolder it. And for such voltages and currents as in an electrical installation, a twist is enough, only well-made.
    And if you need to extend a short wire, you can easily solder it, even if you can't twist it properly.
  • #4 1482184
    invx
    Help: 17
    Rate: 102
    that is, that the torsion is correct ?? because it seems to me not, after all, when you push such a twist into a can, not too deep, the twist may break, so you will never twist it so carefully that it does not sparkle later
  • #5 1482257
    Raaf
    Help: 37
    Rate: 77
    twisting + soldering later or insulation and it's great for years.
    problems only when disconnecting (in the case of renovation, modification, checking). but there is a guarantee of good connection and no sparking (copper in these places will not oxidize. Good in conditions where there are corrosive fumes (pigsties, battery rooms, etc.), or humidity)
    in the case of extending the cables, twisted connections are recommended (solder increases the resistance at this point and, consequently, heats the cable)
  • #6 1482331
    invx
    Help: 17
    Rate: 102
    so it should not solder ??
  • #7 1482553
    bestler
    Help: 254
    Rate: 894
    My friend Raaf, maybe solder has more resistance than copper itself, but I'm sure that if, for example, you connect the cable in a deep well, at a depth of 70 m, it is worth twisting, soldering and protecting it against moisture. In a home installation, however, there are no special indications to solder the wires, unless, for example, we notice sparks in a box, flashing lights, etc.
    Coming back to overheating of the solder, it never happened to me that the soldered wire would desolder itself, that I was aware of too much heat emitted on the connector (I mean home installations all the time), but I have already seen a lot of burnt cans, sockets, circuit breakers where "something" did not connect ;)
    Regards :)
  • #8 1483114
    balt
    Level 19  
    Help: 12
    Rate: 19
    Unfortunately, my colleague Raaf is right, the solder connection has more resistance for two reasons:
    1.A combination of at least two different metals (wire and solder material),
    2. fabrication of a metal alloy surface
    However, the losses are not so big that it will desolder right away. I personally made a twisted pair installation and soldered is still without reservations today. I soldered it so that I turned on the current, heating the 250W soldering iron (like for gutters), then turned off the voltage and a few solders and heating again, etc. Such installation excludes the possibility of later modifications, at least it is difficult. Currently, I recommend a twisted pair for "caps". I don't know what Polish ones are, but I use American ones and they are great, no connection problems.
  • #9 1483236
    bullo
    Rate: 10
    as for the legal basis, I mean the SEP regulations, it is so ....
    "The wires can be joined together by welding, pressing, soldering and using accessories designed for this purpose."
    "Copper conductors with solid conductors up to 10 mm2 and cables up to 6 mm2 may be connected without terminations, except that the ends should be soldered. Copper conductors above 10 mm2 should have terminals, and for aluminum, use spring-loaded screw connections.
    this is all that can be found in the regulations on the method of connections in electrical installations up to 1KV
  • #10 1483394
    balt
    Level 19  
    Help: 12
    Rate: 19
    Personally, I do not recommend soldering the end of the cable to the screw terminal, they burn or melt very nicely. Like a stranded wire and a clamp, the screw is either a suitable terminal or nothing.
  • #11 1484564
    thalex
    Help: 7
    Rate: 42
    bullo wrote:
    as for the legal basis, I mean SEP regulations, it is so ....
    "The conductors of the cables can be joined together by welding, pressing, soldering and using accessories designed for this purpose."
    "copper cables with solid conductors with a cross section of up to 10 mm2 and cables up to 6 mm2 it is allowed to connect without the ends, except that the ends should be soldered . copper conductors above 10 mm2 should have terminals, and for aluminum, spring-loaded screw connections should be used.
    The soldered wire must not be screwed on with a screw !!!
    Because tin is brittle, it will not show any spring properties, such a connection is very susceptible to burnout.
    If you do not believe it, take a look at the extensions after some time of their use, where someone soldered the ends of the wires to screw them with a screw
    I understood the quote so that you can twist the screw after soldering: oh well, unless I misunderstood :(
  • #12 1485012
    bullo
    Rate: 10
    buddy thalex I know that this may raise doubts ... I have mixed feelings about this ... but I only cite the entry from the SEP regulations ....
    ... they explain the rationale for such conduct by "protecting against the possibility of individual wires separating in the lines" by soldering or by using endings or sleeves ...
  • #13 1485061
    thalex
    Help: 7
    Rate: 42
    I know it from practice.
    The soldered line and the bolted in the clamp will burn out, of course, with a significant value of the flowing current.
    Not to be confused with ring terminals, which are intended for soldering and then for twisting with a screw.
  • #14 1485186
    bestler
    Help: 254
    Rate: 894
    Well, as you can see, everything depends on what and for what purpose it is supposed to be used. I think that the author of this post has a total confusion in my mind :P
  • #15 1488759
    grzegorz_r
    Help: 9
    Rate: 10
    1. Twisting wires in electrical installations is used. I even met covers for twisted wires (fixed with one screw).
    The advantage of a twisted connection: direct copper-copper contact, not copper-other metal as in the case of cubes.
    2. Soldering twisted wires (only applies to wire)
    I checked 2.5mm2 on the cable. I spun it, soldered it, and disassembled it. Twist length 2.5 cm. With well-twisted conductors, several points of contact between copper and copper are created, which the tin cannot access. In this case, brazing the twisted wires acts as a mechanical stiffening and encapsulates these points. All in all, a very reliable connection.
The discussion centers on the use of soldering versus traditional connections (twisting, cubes, terminals) in electrical installations. Participants highlight that while soldering provides a permanent galvanic connection with better reliability and no sparking, it poses challenges for future repairs and can increase resistance, leading to overheating. Twisting wires is deemed sufficient for most home installations, provided it is done correctly. Regulations permit soldering, but caution against soldering wires to screw terminals due to the brittleness of solder. The consensus suggests that twisting is preferable for ease of maintenance, while soldering may be used in specific scenarios, such as in corrosive environments or for extending wires. The SEP regulations outline acceptable methods for wire connections, emphasizing the importance of proper techniques to prevent failures.