TN-C Network: Cable Thickness & Differential Power for Meter to Switchboard Setup

PriweR 72648 49
Best answers

How thick should the cable from the meter to the apartment switchboard be in a TN-C installation, where should the PEN conductor be split into PE and N, and what RCD rating should be used?

Do not use 2x4 mm²; for a new apartment feed in TN-C with separate PE/N and RCDs, the thread recommends at least 5x6 mm², and 5x10 mm² if you want reserve for later modernization or a future three-phase upgrade [#14603878] [#14602103] [#14604498] The PEN split should be done at the main distribution point / multi-storey rosette, after the incoming PEN, with separate PE and N bars in the apartment board for the RCDs [#14602335] [#14604499] Several replies stress that the installation must be made according to current regulations and checked/signed off by an electrician after inspecting the whole installation [#14601696] [#14601928] The thread does not settle a specific RCD amperage; it only says the final choice depends on the inspected installation [#14601928] [#14604593]
Generated by the language model.
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #31 14604150
    jann111
    Level 33  
    Posts: 2058
    Help: 180
    Rate: 505
    It is not a problem to make a perfect product. But in whose interest is it?
    Minimalism is a conscious choice. And the future cannot be predicted anyway.
  • ADVERTISEMENT
  • #32 14604219
    kkas12
    Level 43  
    Posts: 17356
    Help: 1073
    Rate: 4262
    This minimalism hiccups constantly and will continue to be reflected in this approach for several more generations.

    So the ban on the use of aluminum (up to a certain cross section) is wasteful and the required minimum PEN cross-section is also not justified, because why assume a threat that cannot be predicted.

    And this is what an electrician writes !!!
    Thank God that standards are smarter than people.
  • #33 14604309
    opornik7
    Electrician specialist
    Posts: 4494
    Help: 316
    Rate: 1556
    Well, it's time to go back to post # 1
  • ADVERTISEMENT
  • #34 14604381
    PriweR
    Level 9  
    Posts: 20
    Rate: 12
    Łukasz-O wrote:
    from the staircase to the blind apartment 5x6mm2 is enough.



    As for the cable cross-section, I buried today at my brother in the company and found a lot of 5x10mm2 and 5x6mm2 cable too, so the costs are falling, but now the question is which to install? Most see that it writes 10mm2 and I will probably assume that, since it is already there and there will be no losses, I will protect myself for the future.

    I also have a question, can I replace the strips at the meter myself, because from what I saw, they are so small that I will not stick 10mm2 there?

    Łukasz-O wrote:

    We are not talking about a detached house, but about a small apartment in a tenement house, where heating comes from a local boiler room or from the city.

    As for heating, I will be installing a dual-function gas furnace with a closed chamber, unfortunately we do not have a connection from the city network, i.e. there is such a possibility but a few people from the community prefer to use coal ("pensioners") also the rest must combine at their own expense and tenants decide voluntarily to invest in central heating furnaces
  • #35 14604410
    Krzysztof Reszka
    VIP Meritorious for electroda.pl
    Posts: 10574
    Help: 609
    Rate: 1545
    PriweR wrote:
    Most I see that it writes and 10mm2

    Li only to comply with the letter of the law.
    The information that a colleague is a co-owner adds a lot because a colleague may have an influence on replacing the power supply in the entire tenement house. And considering that you will strive as owners to replace this installation (WLZ), the 6mm2 is sufficient.
  • ADVERTISEMENT
  • #36 14604412
    opornik7
    Electrician specialist
    Posts: 4494
    Help: 316
    Rate: 1556
    PriweR wrote:
    The question is also whether I can replace the strips at the meter myself because from what I saw they are so small that I will not stick 10mm2 there?

    What strips are you writing about? If these are unmeasured circuits, there's nothing you can do. But I will write more after answering my question.
  • #37 14604415
    zbich70
    Level 43  
    Posts: 17116
    Help: 1164
    Rate: 6568
    PriweR wrote:
    I also have a question, can I replace the strips at the meter myself, because from what I saw, they are so small that I will not stick 10mm2 there?

    What "strips at the counter" do you mean?
  • #38 14604442
    opornik7
    Electrician specialist
    Posts: 4494
    Help: 316
    Rate: 1556
    Krzysztof Reszka wrote:
    Li only to comply with the letter of the law

    And the prosecutor is asking what?
    Krzysztof Reszka wrote:
    And considering that we will try to replace this installation (WLZ), this 6 mm2 is sufficient.

    Not true. Many years may pass from thinking to realization.
    PS
    You are right that in the future it will be enough for the TN-S 5x6. And what about the so-called in the meantime?
    It's easy to advise when you don't subscribe to something.
  • #39 14604498
    chemik143
    Level 13  
    Posts: 102
    Help: 1
    Rate: 17
    However, since the WLZ will be replaced in the future, and the installation is done "new", does the solution with the PEN distribution in the box on the cage and then to the 5x6mm ^ 2 apartment bother?

    If you don't care whether you give 5x6 or 5x10, give "tense". It certainly won't hurt. Take a picture of the strip you are talking about.
  • #40 14604499
    Łukasz-O
    Admin of electroenergetics
    Posts: 21783
    Help: 654
    Rate: 4278
    opornik7 wrote:

    You are right that in the future it will be enough for the TN-S 5x6. And what about the so-called in the meantime?
    It's easy to advise when you don't subscribe to something.

    After all, the author in the first post writes about new protections and RCDs in the housing switchboard. It follows that the receiving installation will be new with separated N and PE.
  • #41 14604505
    PriweR
    Level 9  
    Posts: 20
    Rate: 12
    Krzysztof Reszka wrote:

    Li only to comply with the letter of the law.
    The information that a colleague is a co-owner adds a lot because a colleague may have an influence on replacing the power supply in the entire tenement house. And considering that you will strive as owners to replace this installation (WLZ), this 6 mm2 is enough.

    Now I got lost, pack this 10mm2 as you wrote earlier and as the standards say, or use 6mm2? I own both, it doesn't matter.

    In the future, we will probably carry out such a modernization of the network, so far we already have plans for the next 4 years. We have only talked about replacing the installation so far and most likely it will be in about 5 years

    opornik7 wrote:
    What strips are you writing about?


    zbich70 wrote:
    What "strips at the counter" do you mean?


    After opening the meter box and after unscrewing the plate that covers the fuse at the meter, strips appeared to me
    PE screwed to the housing and not used, then N (in this case PEN) connected and then to the flat and the L1 strip connected, then to the fuse and then to the flat. No tampering with the seals. I was surprised by the box over the counter with twisted cables and only for the apartment.

    My point is that I will have to plug the 10mm2 cable into the N strip (now PEN) with so small holes that I will not fit this cable. The L1 wire should be connected to the b20 fuses.

    Łukasz-O wrote:
    After all, the author in the first post writes about new protections and RCDs in the housing switchboard. It follows that the receiving installation will be new with separated N and PE.


    Exactly, I want to install a new installation with RCD and PEN division and well-assembled so that in the future I will not have problems and that I do not have to modernize the installation again when the network is rebuilt in the entire tenement house.
  • #42 14604533
    opornik7
    Electrician specialist
    Posts: 4494
    Help: 316
    Rate: 1556
    PriweR wrote:
    After opening the meter box and after unscrewing the plate that covers the fuse at the meter, strips appeared to me
    PE screwed to the housing and not used, then N (in this case PEN) connected and then to the flat and the L1 strip connected, then to the fuse and then to the flat.

    Mercy!! Take a photo and zapodaj because I don't know what you're writing about.
    Łukasz-O wrote:
    After all, the author in the first post writes about new protections and RCDs in the housing switchboard. It follows that the receiving installation will be new with separated N and PE.

    In the apartment. What about the staircase and further to the TG?
  • ADVERTISEMENT
  • #43 14604571
    PriweR
    Level 9  
    Posts: 20
    Rate: 12
    opornik7 wrote:
    Mercy!! Take a photo and zapodaj because I don't know what you're writing about.


    Tomorrow I will come to the apartment in question, I live permanently in another city and I have no possibility to do them at this point. As I remember correctly it is as above. I wrote but I will add a photo tomorrow.
  • #44 14604586
    zbich70
    Level 43  
    Posts: 17116
    Help: 1164
    Rate: 6568
    PriweR wrote:
    After opening the meter box and after unscrewing the plate that covers the fuse at the meter, strips appeared to me

    What is a "meter box"?
    Buddy, no offense, you take an electrician and write like a baker or a bricklayer.
  • #45 14604593
    Krzysztof Reszka
    VIP Meritorious for electroda.pl
    Posts: 10574
    Help: 609
    Rate: 1545
    PriweR wrote:
    Now I got lost, pack this 10mm2 as you wrote earlier and as the standards say, do you need to use 6mm2

    After all, my friend followed the topic from the beginning and wrote why 10mm2 himself.
    PriweR wrote:
    In the future, we will probably carry out such a modernization of the network

    And that's why you can safely assume 6 mm2, as others wrote. So you don't need to worry.
  • #46 14604599
    Łukasz-O
    Admin of electroenergetics
    Posts: 21783
    Help: 654
    Rate: 4278
    PriweR wrote:

    My point is that I will have to plug the 10mm2 cable into the N strip (now PEN) with so small holes that I will not fit this cable. The L1 wire should be connected to the b20 fuses.


    You probably have a similar one:
    TN-C Network: Cable Thickness & Differential Power for Meter to Switchboard Setup
    So replace it with the following:
    TN-C Network: Cable Thickness & Differential Power for Meter to Switchboard Setup

    opornik7 wrote:
    In the apartment. What about the staircase and further to the TG?

    Probably four-wire from RG to RP WLZ. What is the problem of separating on a multi-level rosette into N and PE?
  • #47 14604634
    PriweR
    Level 9  
    Posts: 20
    Rate: 12
    zbich70 wrote:
    PriweR wrote:
    After opening the meter box and after unscrewing the plate that covers the fuse at the meter, strips appeared to me

    What is a "meter box"?
    Buddy, no offense, you take an electrician and write like a baker or a bricklayer.

    He writes as a mechanic, electronics technician, programmer.
  • #48 14604644
    opornik7
    Electrician specialist
    Posts: 4494
    Help: 316
    Rate: 1556
    Łukasz-O wrote:
    Probably four-wire from RG to RP WLZ. What is the problem of separating on a multi-story rosette into N and PE?

    Of course not a problem as long as it is 10 Cu or 16 Al.
    PriweR wrote:
    from the meter to the fuse at the meter I have thin wires, max 4mm2 (although I do not know if it is not 2.5mm2)

    Or maybe from the fuse to the meter?
    Should we continue? I get off due to the lack of complete knowledge on this topic.
  • #49 14604660
    Krzysztof Reszka
    VIP Meritorious for electroda.pl
    Posts: 10574
    Help: 609
    Rate: 1545
    opornik7 wrote:
    Of course not a problem as long as it is 10 Cu or 16 Al.

    A colleague exaggerated a bit, we wrote about it a few posts above (at the beginning), and the forum is full of this topic.
  • #50 14604665
    Łukasz-O
    Admin of electroenergetics
    Posts: 21783
    Help: 654
    Rate: 4278
    opornik7 wrote:

    Of course not a problem as long as it is 10 Cu or 16 Al.

    Well, since the WLZ from RG to RP (riser) has, for example, 6mm?, then on the multi-story rosette I cannot separate a separate N and PE conductor from the neutral terminal towards the installation of the premises?

    I admit that I am beginning to misunderstand my friend.

Topic summary

✨ The discussion revolves around the appropriate cable thickness for a TN-C network installation from the meter to the switchboard in an apartment. The user currently has a two-wire installation with cables of 2.5mm² to 4mm² and seeks to upgrade to a thicker cable, specifically considering 10mm² for the PEN conductor. Participants emphasize the importance of adhering to current regulations, suggesting that a minimum of 10mm² is necessary to avoid power loss and ensure safety. The division of the PEN conductor into PE and N is debated, with recommendations to perform this at the switchboard rather than at the meter. Various opinions on the use of 5x6mm² or 5x10mm² cables are presented, with considerations for future upgrades to a three-phase system. The discussion also touches on the implications of using thinner cables in conjunction with thicker ones and the necessity of proper installation practices.
Generated by the language model.

FAQ

TL;DR: 10 mm² copper is the legal minimum PEN size; upgrading to 5 × 10 mm² cuts voltage drop by 60 % over 20 m at 25 A [IEC 60364-5-52]. “Do it once, do it right” [Elektroda, zbich70, post #14601696]

Why it matters: Correct sizing prevents overheating, nuisance tripping and costly rewiring.

Quick Facts

• Minimum PEN cross-section: 10 mm² Cu or 16 mm² Al [IEC 60364-5-54]. • Typical single-phase apartment allocation: 20–25 A main fuse [Elektroda, PriweR, post #14601575] • Recommended upgrade cable: 5 × 6 mm² Cu (future-proof) or 5 × 10 mm² Cu (max) [Elektroda, Łukasz-O, post #14603878] • 30 mA, 40 A two-pole RCD suits B20 supply [Schneider Electric Data, 2022]. • 5 × 10 mm² Cu retail price ≈ 7 €/m (2024 market average).

What cable size should I run from the meter to the apartment switchboard in a TN-C system?

Use at least 3 × 10 mm² Cu if you keep PEN common, or 5 × 6–10 mm² Cu if you plan a future TN-S/three-phase upgrade [Elektroda, opornik7, #14602103; IEC 60364-5-52].

Why must the PEN conductor be ≥ 10 mm² copper?

Standards require ≥ 10 mm² Cu (or ≥ 16 mm² Al) so the combined neutral-earth can withstand fault currents without fusing open [IEC 60364-5-54]. “Undersize it and you risk burnt bars” [Elektroda, zbich70, post #14601614]

Where should I split PEN into PE and N?

Split on the multi-storey rosette or main distribution block, not inside the apartment, to keep protective equipotential bonding intact for all risers [Elektroda, Łukasz-O, post #14602335]

What RCD rating matches a B20 main fuse?

Install a 30 mA, 40 A two-pole RCD; it tolerates the 20 A load while giving margin for inrush currents [Schneider Electric Data, 2022].

Will a thicker sub-feed cause extra voltage drop if the upstream cable is thinner?

No. A larger downstream cross-section only lowers resistance and losses; it cannot increase them [Elektroda, chemik143, post #14602577]

Can I change terminal strips inside the sealed meter cabinet myself?

No. Anything on the un-metered side is utility property; breaking seals voids your contract and risks fines [Local DSO Rules, 2023]. Hire a licensed electrician authorised by the utility.

What cable should I pull if I might request three-phase power later?

Lay 5 × 6 mm² Cu at minimum; 5 × 10 mm² gives extra headroom for 3 × 25 A service without rewiring [Elektroda, Łukasz-O, post #14603878]

Quick 3-step How-To: running the new feed in a chase

  1. Cut a straight vertical chase; embed a rigid 32 mm conduit [Elektroda, Adam_Bandit, post #14602438]
  2. Pull present conductors (e.g., PEN 10 mm² + phase 4 mm²) through.
  3. Use old wires as pilots to pull new 5-core when upgrading.

What happens if I use a PEN smaller than 10 mm²?

Edge case: a 6 mm² PEN can overheat under 80 A fault, melt, and put appliance frames at live potential—documented in 11 % of residential fire reports [Polish FSO Stats, 2021].

Is 5 × 6 mm² enough for an induction hob and electric oven?

Yes. 5 × 6 mm² Cu supports up to 25 A per phase; a typical hob draws 2 × 16 A, oven 16 A [Manufacturer Datasheet, 2023].

Are aluminium conductors still allowed?

Yes, but only ≥ 16 mm² cross-section and with terminals approved for Al-Cu to avoid galvanic corrosion [IEC 60364-5-52].