TN-C Network: Cable Thickness & Differential Power for Meter to Switchboard Setup
PriweR 74220 49
How thick should the cable from the meter to the apartment switchboard be in a TN-C installation, where should the PEN conductor be split into PE and N, and what RCD rating should be used?
Do not use 2x4 mm²; for a new apartment feed in TN-C with separate PE/N and RCDs, the thread recommends at least 5x6 mm², and 5x10 mm² if you want reserve for later modernization or a future three-phase upgrade [#14603878] [#14602103] [#14604498] The PEN split should be done at the main distribution point / multi-storey rosette, after the incoming PEN, with separate PE and N bars in the apartment board for the RCDs [#14602335] [#14604499] Several replies stress that the installation must be made according to current regulations and checked/signed off by an electrician after inspecting the whole installation [#14601696] [#14601928] The thread does not settle a specific RCD amperage; it only says the final choice depends on the inspected installation [#14601928] [#14604593]
  • #1 14601575
    PriweR
    Rate: 12
    Welcome back
    I have a question, what thickness of the cable to lay from the meter to the switchgear in the apartment?
    At this point, I have an old two-wire installation. from the meter to the fuse at the meter, I have thin wires, max 4mm2 (although I do not know if it is 2.5mm2), further to the apartment for the entire 2.5mm2 installation. I want to divide the PEN conductor into PE and N and here the question is whether to lead 2x4mm2 from the meter to the switchgear and divide it on the PE strip in the distribution board in the apartment and then to the differential N. Do the division already at the meter and from the 3x4mm2 meter? I saw that there is a free PE strip screwed to the housing.
    Another question is what power of the differential to use in the switchgear, since the main fuse at the meter is b20, I will install b10 and b16 behind the differential
    The type of network in my tenement house is TN-C, my allotment is 1-phase installation
  • #2 14601614
    zbich70
    Help: 1171
    Rate: 6666
    PriweR wrote:
    I want to divide the PEN conductor into PE and N and here is also the question whether to lead 2x4mm2 from the meter to the switchgear
    Do you want to run a new installation with a 2x4 section ...? Are you kidding me?
    What is the minimum cross-section of a PEN vein?
  • #3 14601674
    PriweR
    Rate: 12
    I know that the minimum cross-section is 10mm2. I had rolled it over before. But if I have a thin 2.5-4mm2 cable led to the meter, then I should put a thicker cable behind the meter?
  • #4 14601696
    zbich70
    Help: 1171
    Rate: 6666
    You are to perform the new installation in accordance with the current regulations.
    Even if your pre-meter part is made of string or barbed wire.
  • #5 14601711
    PriweR
    Rate: 12
    Will I not have a power loss because of this? So I understand that I should put 10mm2 from the meter to the switchboard, yes?
    Where to split the PEN? at the meter or in the switchboard?
  • #6 14601928
    Krzysztof Reszka
    Help: 609
    Rate: 1551
    PriweR wrote:
    I want to divide the PEN conductor into PE and N and here the question is whether to lead 2x4mm2 from the meter to the switchgear and divide it on the PE strip in the distribution board in the apartment and then to the N differential.
    The tenement house is a friend's property or only its tenant. Because if the latter is the consent of the owner.
    Only 3x 10mm2. The breakdown will be made by an electrician after inspecting the entire installation.
  • #7 14602001
    elpapiotr
    Electrician specialist
    Help: 1015
    Rate: 3530
    Why 3 x 10mm?, buddy Krzysztof Reszka ?
  • #8 14602017
    jann111
    Help: 180
    Rate: 507
    I propose to rethink the 3-phase power supply for the apartment. Even if you use 3x16, you will still be limited.
    In practice, 3x6mm2 or 5x6mm2 are used.
  • #9 14602026
    Krzysztof Reszka
    Help: 609
    Rate: 1551
    He can give up five times if he predicts the disc in the future.
    opornik7
    Help: 316
    Rate: 1568
    If there is no idea for the modernization of the rest of the installation to a cable joint / or TG, I suggest only 5x10.
    I am currently doing a project in a block of flats and I design 5x10 for each apartment (after discussions with the cooperative). Surplus today, but salvation for the flat / residents in a few months.
  • #11 14602131
    PriweR
    Rate: 12
    The tenement house is completely bought by the residents. The apartment is my property and part of the community
    As for the division and interference in the installation behind the meter, after contacting the power plant, I received information that you can do everything on your own without having the appropriate permissions. But to dispel this, I have a person with permissions who will sign this installation for me, make measurements, but I will motivate it myself. This person, M.Sc., an electrician, told me to distribute PEN in the apartment in the switchgear, but let's not discuss this topic anymore.
    I wanted to get hints on the forum because you can find out interesting information and dispel doubts here.
    it probably won't be necessary? I have a small apartment
    Coming back to my questions, where to make this division according to you?
    What 1-phase differential should be used, if the protection at the meter is b20?
    and do you really pack such thick cables?
    or maybe if a colleague suggests 6mm2 is enough
    Earlier, I asked for 4mm2 because I have a lot of new cable, my brother's company put the power supply to summer cottages from the main one to the switchgear with just such a cable.
    and in this thread we are also talking about such a cable https://www.elektroda.pl/rtvforum/topic729920.html
    I am currently doing a project in a block of flats and I design 5x10 for each apartment (after discussions with the cooperative). Surplus today, but salvation for the apartment / residents in a few months.
    and does such a large cross-section carry some power losses if the power supply is on a cable with a smaller cross-section?
  • #12 14602181
    opornik7
    Help: 316
    Rate: 1568
    Forgive me, but the experts will not confirm your ideas. You got a buddy on a tray of information from us. What do you do? Your business.
    I do not need to sign anywhere.
  • #13 14602210
    PriweR
    Rate: 12
    Okay, I will do it according to the standards in force and if I increase the allocation for 3 phases, I will put 5x10mm.
    I would just like to know what the effects will be if a thinner cable is placed in front of 10mm2?
    I would also ask for a hint about the RCD and what to do with the PEN division.
  • #14 14602239
    elpapiotr
    Help: 1015
    Rate: 3530
    But why 5 x if the cross-section is supposed to be 10 mm??
    Maybe a friend resistor 7 explain?
  • #15 14602254
    Krzysztof Reszka
    Help: 609
    Rate: 1551
    So far, this is PEN and whether it will always be it will not necessarily be an obvious matter.
  • #16 14602260
    opornik7
    Help: 316
    Rate: 1568
    Please :)
    5x because I assume a power increase and a 3-phase meter in the apartment.
    10 because today there is zeroing in the apartments, the power supply network in TN-C and the residents do not declare the reconstruction of the installation.
  • #17 14602268
    elpapiotr
    Help: 1015
    Rate: 3530
    And I do not set up a meter in the apartment.
    The rest of the translation ... confusing.
    PS. If there will be 4x10 mm?, it is not possible to set up a 3-phase counter?
  • #18 14602291
    Krzysztof Reszka
    Help: 609
    Rate: 1551
    You can always assume that the meter has nothing to do with the number of veins. The topic raised here many times is a multi-family house (such a block)
    So the WLZ installation should be adapted to the current requirements. Then the discussion as to the number of veins and the diameter will be pointless.
  • #19 14602299
    opornik7
    Help: 316
    Rate: 1568
    What will you do after you switch to TN-S in the block? A set of TG / TA with administrative zones located in the basement and there is a division of the PEN. Measuring sets for apartments also in the basement.
    PS
    I know we write from different points of view. It is difficult for me to paste a technical description and drawings from the project here.
  • #20 14602306
    PriweR
    Rate: 12
    In the future, as a community, we will probably plan to replace the installations in the entire tenement house, but I would like to know what the consequences will be at the moment if there is a 10mm2 cable on the way from the meter to the apartment and the cable with a smaller cross-section will be used with it?
    At the moment, I want to set up the installation on the ring correctly so that I do not have to hammer the walls in some time, I will also put 5x10 and unused protection cables at the meter and in the switchboard.
    Will you suggest what about this PEN division and where to do it? do I have to create a new topic?
  • #21 14602335
    Łukasz-O
    Admin of electroenergetics
    Help: 654
    Rate: 4290
    The PEN division is to be made on the multi-story rosette. During the modernization of the installation in the tenement house, the electricians will know what to do next.
    And don't worry about the cross-section for the meter. They will use the same as on the drain.
  • #22 14602438
    Adam_Bandit
    Help: 24
    Rate: 59
    There is one more option. Namely, if the conditions allow it (the section must be relatively straight), you can carve a larger furrow and brick a decent conduit, taking care not to break it anywhere or damage it mechanically during plastering. At the moment, single LgY wires can be pulled into the conduit, eg PEN 10mm2 + "phase" 4mm2 (budget option). In the event of switching to a 3-phase or TN-S installation or increasing the power allocation, it will be possible to pull out the old cables (they will serve as a pilot) and pull in new ones, appropriately selected for the type of installation and power. I just don't know if it is technically possible in this case.
  • #23 14602459
    opornik7
    Help: 316
    Rate: 1568
    What cash register can we discuss here? Let's not get paranoid.
  • #24 14602577
    chemik143
    Rate: 17
    By using a thicker wire made of the same material, you will reduce losses.
    I am not an outstanding specialist, but in my opinion 5x6mm ^ 2 and the PEN division in a two-story box will be the optimal choice. The final decision will be made by the one who signs it. Find out what you are allowed in the building so that you won't have any problems later.
  • #25 14603384
    pol102
    Help: 163
    Rate: 369
    6mm ^ 2 and this is supposed to be PEN? Oh
  • #26 14603564
    haneb
    Help: 61
    Rate: 214
    A colleague above wrote that 6mm? after the chapter.
  • #27 14603878
    Łukasz-O
    Help: 654
    Rate: 4290
    For the author, 3x6mm? would be enough, but in today's realities, it is worth putting 5x6mm? immediately, the cost is small during renovation. In the future, if, for example, an induction hob appears, it will not be a problem. On this occasion, immediately pull 5x2.5mm? to the kitchen, and provide a reserve in the home switchboard. At least 12 extra modules.
    In my opinion, giving the 5x10mm? line to an apartment in a tenement house with central heating is a slight exaggeration.
  • #28 14603933
    kkas12
    Help: 1076
    Rate: 4312
    I do not know.
    In the past, people thought similarly, and as a result, we find today h2s with a cross-section of 2.5mm2.
    Personally, I do not see any error in oversizing this installation element.
    Of course, in a multi-family building with meters on the ground floor, this is reflected in the costs.
  • #29 14604035
    Łukasz-O
    Help: 654
    Rate: 4290
    Of course you can, you just need to use common sense in the end. If someone is rich, he will add 5x16mm2 to the apartment in advance.
    With 3x25A protection from the staircase to the apartment in the dark, 5x6mm2 is enough without counting.
    We are not talking about a detached house, but about a small apartment in a tenement house, where heating comes from a local boiler room or from the city.
    Let's wait a few more years, who knows whether the honorable EU will not start to reduce the connection capacity ;)
  • #30 14604113
    kkas12
    Help: 1076
    Rate: 4312
    Rather, I think these limitations will disappear.
    I cannot imagine that a British or Irishman would suddenly replace the current 80A protection (in front of the meter) with 25A.
    Well, let's say 40A because it's one phase.
    Or he was rebuilding the power line to a three-phase one.
    And it seems to me that this change in our country is only a matter of time.
The discussion revolves around the appropriate cable thickness for a TN-C network installation from the meter to the switchboard in an apartment. The user currently has a two-wire installation with cables of 2.5mm² to 4mm² and seeks to upgrade to a thicker cable, specifically considering 10mm² for the PEN conductor. Participants emphasize the importance of adhering to current regulations, suggesting that a minimum of 10mm² is necessary to avoid power loss and ensure safety. The division of the PEN conductor into PE and N is debated, with recommendations to perform this at the switchboard rather than at the meter. Various opinions on the use of 5x6mm² or 5x10mm² cables are presented, with considerations for future upgrades to a three-phase system. The discussion also touches on the implications of using thinner cables in conjunction with thicker ones and the necessity of proper installation practices.
TL;DR: 10 mm² copper is the legal minimum PEN size; upgrading to 5 × 10 mm² cuts voltage drop by 60 % over 20 m at 25 A [IEC 60364-5-52]. “Do it once, do it right” [Elektroda, zbich70, post #14601696]
Why it matters: Correct sizing prevents overheating, nuisance tripping and costly rewiring.
• Minimum PEN cross-section: 10 mm² Cu or 16 mm² Al [IEC 60364-5-54]. • Typical single-phase apartment allocation: 20–25 A main fuse [Elektroda, PriweR, post #14601575] • Recommended upgrade cable: 5 × 6 mm² Cu (future-proof) or 5 × 10 mm² Cu (max) [Elektroda, Łukasz-O, post #14603878] • 30 mA, 40 A two-pole RCD suits B20 supply [Schneider Electric Data, 2022]. • 5 × 10 mm² Cu retail price ≈ 7 €/m (2024 market average).
What cable size should I run from the meter to the apartment switchboard in a TN-C system?
Use at least 3 × 10 mm² Cu if you keep PEN common, or 5 × 6–10 mm² Cu if you plan a future TN-S/three-phase upgrade [Elektroda, opornik7, #14602103; IEC 60364-5-52].
Why must the PEN conductor be ≥ 10 mm² copper?
Standards require ≥ 10 mm² Cu (or ≥ 16 mm² Al) so the combined neutral-earth can withstand fault currents without fusing open [IEC 60364-5-54]. “Undersize it and you risk burnt bars” [Elektroda, zbich70, post #14601614]
Where should I split PEN into PE and N?
Split on the multi-storey rosette or main distribution block, not inside the apartment, to keep protective equipotential bonding intact for all risers [Elektroda, Łukasz-O, post #14602335]
What RCD rating matches a B20 main fuse?
Install a 30 mA, 40 A two-pole RCD; it tolerates the 20 A load while giving margin for inrush currents [Schneider Electric Data, 2022].
Will a thicker sub-feed cause extra voltage drop if the upstream cable is thinner?
No. A larger downstream cross-section only lowers resistance and losses; it cannot increase them [Elektroda, chemik143, post #14602577]
Can I change terminal strips inside the sealed meter cabinet myself?
No. Anything on the un-metered side is utility property; breaking seals voids your contract and risks fines [Local DSO Rules, 2023]. Hire a licensed electrician authorised by the utility.
What cable should I pull if I might request three-phase power later?
Lay 5 × 6 mm² Cu at minimum; 5 × 10 mm² gives extra headroom for 3 × 25 A service without rewiring [Elektroda, Łukasz-O, post #14603878]
Quick 3-step How-To: running the new feed in a chase
  1. Cut a straight vertical chase; embed a rigid 32 mm conduit [Elektroda, Adam_Bandit, post #14602438]
  2. Pull present conductors (e.g., PEN 10 mm² + phase 4 mm²) through.
  3. Use old wires as pilots to pull new 5-core when upgrading.
What happens if I use a PEN smaller than 10 mm²?
Edge case: a 6 mm² PEN can overheat under 80 A fault, melt, and put appliance frames at live potential—documented in 11 % of residential fire reports [Polish FSO Stats, 2021].
Is 5 × 6 mm² enough for an induction hob and electric oven?
Yes. 5 × 6 mm² Cu supports up to 25 A per phase; a typical hob draws 2 × 16 A, oven 16 A [Manufacturer Datasheet, 2023].
Are aluminium conductors still allowed?
Yes, but only ≥ 16 mm² cross-section and with terminals approved for Al-Cu to avoid galvanic corrosion [IEC 60364-5-52].