The structure of the panels on the roof without lightning rod and on the roof with lightning rod and separation spacing should be connected with each other by equalizing connections. Then it should be connected to the grounded GSU / GSW. It is not a mistake to conduct this grounding inside the building, as someone wrote earlier, because whether the lightning current flows through it depends on many other factors. This wire should be kept at a distance from others.
If there is a lightning rod on the roof and the gaps are not kept, then apart from the above connection to the GSU, the structure must be additionally connected to the lightning rod. The panels, of course, in the LPZ0B zone.
As for PE, there is no need for PE on the roof and there is no such conductor. :)
Added after 6 [minutes]: comer3 wrote: Hello,
Following this thread regarding PV in the TNC installation, I did not find an answer to one question. Namely, assuming that the DC side of the installation will be made in accordance with the figure from post # 6 (DC protectors and the inverter housing connected to the GSU), whether the AC side of the inverter connected to the TNC network (L1, L2, L3, PEN) should be mounted with a surge arrester ? Does (looks at) ZE (Tauron) require this when reporting an installation? If required, which arrester is better to put on - one dedicated to the TNC (unfortunately it costs not little), can you use the grounding you have made and connect the PE terminal of a typical arrestor (B + C) to the GSU and the PEN conductor at the output of the inverter to the N connector ( here I do not know if I will not do more damage to the receiving installation in the event of a discharge by such a connection than if I did not put a protector on the AC side at all)?
Such a protector is available only if the distance along the cable to the T2 protector of the home installation exceeds 10m. If you do not have this protector, do it there first, not at the inverter. It should be the same as the network topology. That is, four-pole 3 + 1 to TT, any four-pole to TN-CS and any three or (if there is one) four-pole to TN-C.
The typical B + C earpieces are a scam. At 90%, you need T2 (old C) and connect it to ground and / or PE.
My installation has been> 5 years without any SPD except the deceived Moeller "B + C" in the main switchboard. Soon I will change to new ones.