ktasior wrote: To sum up:
In conclusion, let the electrician take what he wears and give the money back. What he carved cries out to heaven for vengeance. I don't even ask why he didn't apply the RCD to other circuits.
In fact, most installations have to be made from scratch, use another larger switchgear, which will be equipped with appropriate overcurrent circuit breakers, RCD, main switch. Voltage signaling is also a good solution.
As for the circuits:
1. Lighting 3 and 4x1,5mm2 eg RCBO - B10;
2. Working sockets in the kitchen 3x2.5mm? - B16;
3. dishwasher socket 3x2.5mm? - B16;
4. oven socket 3x2.5mm? - B16;
5. Circuit of the induction hob 5x2.5mm? (on the side) - B16;
6. Washing machine socket 3x2.5mm? - B16;
7. bathroom socket (if the washing machine is located in a different room) 3x2.5mm? - B16;
8. Sockets in rooms (max 10 sockets per circuit) 3x2.5mm? - B16.
It is worth to separate the circuits of general sockets into rooms, e.g. living room and bedroom separately.
I also remind you that the socket circuits must also be protected by an RCD. Lighting in the bathroom also with RCD or RCBO.
Here is an example of an apartment switchboard:
ktasior wrote: This is just one more question: Is there any provision that 2.5 mm cables should be led to the sockets?
There is no, but on the condition that the circuit is secured to max B13, which in practice means little functionality. A stupid start-up of the vacuum cleaner may trigger the security, and yet other devices will be connected in the circuit.