Three-Phase Heaters (2kW Each) - Star Connection: Neutral Conductor Required? 25.4 Ohm Resistances

s.alex5 9930 15
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 16167450
    s.alex5
    Level 8  
    Hello.
    I have a problem because I have three heaters made of resistance wire. The power of each supposedly 2kw.
    And I don't know if I need to connect a neutral conductor with a star connection.
    Will with zero without it will work the same as with zero.
    Each heater has 25.4Ohm
    Thanks for the reply. Regards.
  • ADVERTISEMENT
  • #2 16167490
    JaroPC
    Level 16  
    As the heaters are identical, they are connected in a star and constitute a symmetrical receiver. No current will flow through the neutral conductor (except in the case of voltage unbalance), so in principle it is not necessary to connect it.
  • ADVERTISEMENT
  • #3 16167525
    zbich70
    Level 43  
    s.alex5 wrote:
    And I don't know if I need to connect a neutral conductor with a star connection.

    And the protective conductor are you going to connect?
  • ADVERTISEMENT
  • #4 16167576
    s.alex5
    Level 8  
    Damn but I have now measured these heaters and one has 25ohm the other 25.2ohm and the third 26.5ohm.
    So with this configuration you need zero?


    Protective conductor only on the furnace casing?
  • ADVERTISEMENT
  • #5 16167608
    zbich70
    Level 43  
    s.alex5 wrote:
    Damn, but now I have measured these heaters and one has ....

    Measure IPZ again
  • #6 16167615
    s.alex5
    Level 8  
    What is IPZ?

    PS.
    They are resistance wire heaters wound in spring on request from a company producing heaters
  • #7 16167622
    zbich70
    Level 43  
    s.alex5 wrote:
    What is IPZ?

    Short circuit loop impedance.
  • #8 16167625
    s.alex5
    Level 8  
    Or?
    You know I'm a beginner I would be grateful if you would describe more or less how to measure it.
  • Helpful post
    #10 16167643
    Hajna
    Level 24  
    Three-Phase Heaters (2kW Each) - Star Connection: Neutral Conductor Required? 25.4 Ohm Resistances The question is what type of network and heater you have, what is the voltage and what is the device.
  • #11 16167673
    s.alex5
    Level 8  
    It is to be a ceramic oven. I think 230v, but I don't know completely.
    When ordering, I told the seller what they are about to be three heaters of 2kw and gave the temperature to which they are to heat.
    Everything is controlled by a thermostat and contactless contactors.
  • Helpful post
    #12 16167680
    Hajna
    Level 24  
    This is a wrong wiring diagram, but the author will probably say where he lives and based on its location zbich70 we will guess.
  • #13 16167692
    s.alex5
    Level 8  
    What is going on???
  • Helpful post
    #14 16167707
    Hajna
    Level 24  
    Tel. 600 97 44 03 call the author of the topic
  • #15 16167712
    zbich70
    Level 43  
    s.alex5 wrote:
    What is going on???

    The point is that this furnace (or anything else) should be joined by an individual who has the knowledge and skills ... documented .
    Otherwise, the insurer will cry out, but the prosecutor will start rummaging.
  • #16 16167724
    s.alex5
    Level 8  
    Thank you for your help.
    greetings

Topic summary

The discussion revolves around the connection of three identical 2kW resistance wire heaters configured in a star connection. The main query is whether a neutral conductor is necessary, given that the heaters have resistances of approximately 25.4 Ohms each. Responses indicate that in a symmetrical load configuration, a neutral conductor is not required unless there is a voltage imbalance. The author later questions the need for a neutral conductor after measuring slight variations in resistance among the heaters. Additional inquiries about protective conductors and the specifics of the heating system, which is intended for a ceramic oven, are also made. The importance of proper installation by a qualified individual is emphasized to avoid safety and legal issues.