How do I determine the optimal number of PV panels in one string for an inverter with a 210–480 V MPPT range and 360 V nominal PV voltage?

Choose the string length so the panels’ operating voltage under load is close to the inverter’s suggested/nominal PV voltage, but never let the string’s open-circuit voltage exceed the inverter’s maximum DC input voltage, especially in cold weather [#16278841] MPPT will track the best power point within its range, so you do not need to hit exactly 360 V, but you should keep the string in the MPPT window and near the inverter’s preferred working point for best efficiency [#16278841][#16279548] The voltage you calculate from Voc alone is not the full answer: use the panel voltage under load for the string size, then check that the total current of all parallel strings stays below the inverter’s max DC input current [#16278841][#16278519] As a practical rule, the thread advises leaving a few percent margin below the maximum voltage because a sunny, frosty day can push panel Voc above the nominal value [#16278841] The number of parallel strings is then limited by the inverter’s input current, and the total PV power should generally stay within about 115–120% of inverter power [#16278841]
Generated by the language model.
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 16278067
    Anonymous
    Level 1  
  • ADVERTISEMENT
  • #2 16278397
    franekmigas
    Level 12  
    By the parameters, I can see that they are monocrystalline panels, could you please send me the name and type of the inverter and panels?
  • #3 16278434
    Anonymous
    Level 1  
  • #4 16278519
    franekmigas
    Level 12  
    You should pay attention, first of all:
    Panels - voltage and maximum current
    Inverter - DC voltage and maximum current
    and then you choose the number of panels in a string and how many strings you can connect with each other
  • Helpful post
    #5 16278841
    putas
    Renewable energy sources specialist
    If it is possible, we connect them in series so that the total operating voltage of the panels under load is close to the suggested operating voltage of the inverter.
    Besides, there are three parameters that we do not exceed
    - max inverter input voltage - i.e. one string without load cannot exceed this voltage, we even leave a few% slack, on a frosty and sunny day the panels can output a voltage slightly above the norm
    - max input current of the inverter - that is the total max current of all strings
    - the total power of all panels does not exceed 115-120% of the inverter power
  • ADVERTISEMENT
  • #6 16278865
    Anonymous
    Level 1  
  • #7 16278895
    franekmigas
    Level 12  
    You still need to know the maximum DC input current of the inverter
  • #8 16278981
    Anonymous
    Level 1  
  • ADVERTISEMENT
  • #9 16279126
    krzysiek_krm
    Level 40  
    Hello,
    Without analyzing the documentation, or asking the manufacturer what he meant, it is difficult to say anything meaningful.
    It is possible that the nominal voltage was given just like that, but it is possible that it is actually optimal, for example the inverter achieves the highest possible efficiency at this voltage, which is quite advantageous, because then the maximum power of the device can be obtained.

    greetings
  • ADVERTISEMENT
  • #10 16279164
    franekmigas
    Level 12  
    2 examples from my installation. Optimal PV Panel String Connection: Inverter & Panel Parameters for 210-480V MPPT Voltage Range Optimal PV Panel String Connection: Inverter & Panel Parameters for 210-480V MPPT Voltage Range
  • #11 16279295
    Anonymous
    Level 1  
  • #12 16279385
    franekmigas
    Level 12  
    I have 2 installations.
    1: Mastervolt XS3200 + 40 panels GS-50 (4 strings * 10 panels) max voltage 580V
    2: Mastervolt XS2000 + 4 panels Q.Cell Q.PRO - G4.1 265W (1 string), maximum voltage 140V
  • #13 16279452
    3301
    Level 34  
    And don't you think that in the case of 2 installations you have a little too low voltage, in this MPP inverter the range is from 145V and you have 140 and maybe that is why the efficiency of the 2nd installation. is lower by approx. 1% than the installation. 1.
    Tomorrow I have to receive such an inverter only XS 6500, I will start testing it.
  • #14 16279470
    franekmigas
    Level 12  
    Very good 2 MPPT inverter, so the possibilities are very large
  • #15 16279485
    3301
    Level 34  
    Probably a better solution would be two of them after 2000, but there was a bigger one and the price was much lower than two
  • Helpful post
    #16 16279505
    prose
    Level 36  
    Here is a simple diagram that MPPT will not do everything on the example of the Fronius IG 60 HV inverter, giving the DC input max voltage is lost on production. Optimal PV Panel String Connection: Inverter & Panel Parameters for 210-480V MPPT Voltage Range

    Here is the inverter data.
    Optimal PV Panel String Connection: Inverter & Panel Parameters for 210-480V MPPT Voltage Range
  • #17 16279507
    franekmigas
    Level 12  
    this 6500 is really 2x3200 in electronics and 2000 is a pile worth nothing
  • #18 16279523
    3301
    Level 34  
    It made me feel good, although I was not aware of it
  • #19 16279538
    franekmigas
    Level 12  
    those that have the inscription on the right side of the plate work the longest
    MADE IN PRC
  • Helpful post
    #20 16279548
    prose
    Level 36  
    I tried on high, low and medium and 280V as in the chart I got the best results, each inverter has its best working point at MPPT point.
    Attachments:
    • Optimal PV Panel String Connection: Inverter & Panel Parameters for 210-480V MPPT Voltage Range 7948961500_1386614549.png (65.33 KB) You must be logged in to download this attachment.
  • #21 16279712
    Anonymous
    Level 1  

Topic summary

✨ The discussion centers on optimizing the connection of photovoltaic (PV) panels to an inverter with a specified MPPT voltage range of 210-480V. The main inquiry involves determining the optimal number of panels to connect in a string, considering the inverter's nominal voltage of 360V and maximum current specifications. Participants emphasize the importance of matching the total operating voltage of the panels to the inverter's optimal voltage for efficiency, while also adhering to the inverter's maximum input voltage and current limits. The consensus suggests that while the MPPT can adjust to varying voltages, connecting panels closer to the optimal voltage can enhance performance. Examples of installations and inverter models are shared, highlighting the practical implications of these calculations.