Don't be afraid of technical advisers - that's what they are for. Any designer, even acting on your behalf, will do exactly the same - he will contact technical advisors asking for help in selecting devices.
lodzik1990 wrote: You need an inverter with two power measurement points.
In the morning, five panels reach their maximum power, and in the afternoon, the inverter switches to the second string of 18 panels.
I do not remember the minimum voltage for the inverter to start.
The minimum voltage for the inverter to start depends on the specific model. The inverter selection algorithm would be as follows:
1.selection of the model of PV panels - determination of their power, open circuit voltage and closed circuit current (for STC and NOCT conditions).
2. determination of the maximum power of the PV installation - most simply Ppv = nx Pmax
3.defining whether the inverter is to operate on a 1- or 3-phase installation.
4. determination of the maximum string voltage and its current (to remind: panels connected in series - open circuit voltages add up, current equal to the current of a single panel). In your case, respectively
DC voltage: String 1 - Voc1 = 5x Voc; String 2- Voc2 = 18x Voc (possibly Woc2 = 9x Voc if you connect two strings of 9 panels in parallel).
DC currents: String 1 - Isc1 = Isc; String 2 - Isc2 = Isc (or Isc2 = 2x Isc if you connect two strings of 9 panels in parallel). However, it is worth using longer chains, because even with less sunlight they will create more tension.
5. preliminary selection of the inverter based on the AC power and voltage and the number of MPP trackers
6. checking the voltages and currents of the DC side. If they fall within the limits specified by the manufacturer, then OK. At the same time, it is worth ensuring that the lower DC voltage value of the inverter is sufficiently low so that the inverters work even in conditions of lower sunlight
7.configuration of the system if something does not meet the boundary conditions (e.g. too low / high DC voltage of a single chain)
It is difficult to talk about specific solutions without knowing the exact situation and location / orientation of your installation, but I will present the above using the example of the first devices from the edge.
PV panel: Sharp 256 Wp / Mono: NQR256A
inverter: DELTA RPI H5A Flex 1ph (5kVA, 2MPP, DC IN: Vdc = 30 ... 600V, Idc = 11A / MPP)
Your configuration would look like this:
MPP1 = String1: Voc1max = 5x 32.5V = 162.5V; Isc1max = 9.95A; P1max = 1280W
MPP2 = String2: Voc2max = 18x 32.5V = 585.0V; Isc1max = 9.95A; P2max = 4608W
The input power of the second DC input has been exceeded, i.e. the inverter may not fully use the potential of the panels (of course, with good insolation parameters, but for NOCT conditions, the power is not exceeded).
This configuration will only work if both chains will produce energy simultaneously (i.e. the slopes are arranged in such a way that both are illuminated at the same time). Inverters have such a parameter as the permissible input unbalance, in this case it is the ratio of 4% / 96%.
Otherwise, consider using two inverters - one for a 5-panel string (DC inputs connected in parallel). The second is for connecting a chain of 18 panels (DC inputs connected in parallel).
For other panels and inverters, the optimal configuration may be different.