I have 2kW off-grid installations for water heating, I will describe from my own practice how it works.
12 monocrystalline PWR-180Wp panels, 2160Wp in total
Connected in two rows, they give a voltage of 212V
MPP regulator with a power of 2500W, giving alternating current (rectangle)
The structure is made of 40x40mm H-shaped aluminum profiles.
The rest of the bolts, connectors, aluminum or stainless steel.
Strings protected with 10A MC4 diodes and 6A 10x38 fuses.
Cable for the 10mm2 regulator (I had one) 8.5m.
On the roof, cables from panels to 6mm2 boxes are UV resistant.
Protection, two-pole DC circuit breaker.
The structure is earthed with a separate conductor.
100L horizontal boiler.
Standard heater 3x1500W 230V, 3kW connected to the regulator, 1.5kW for a separate thermostat as additional heating from the network.
On the side of the DC panels I gave a voltmeter and an ammeter, the regulator at the AC output is equipped with a voltmeter.
Panels set to the south at an angle of 18 °, from the east and west sides of the tree, in the morning the shadow descends around 8.00 am and reappears around 4.00 pm, of course in summer.
The installation has been in operation for the third year, flawlessly. I bought used panels, I don't know which year they are from, half of them are older, the cables are 2008 and they have older type of connectors. The rest comes from a demonstration installation, according to the seller, the newer ones were not connected, you can actually see the differences, in the older ones the foil is yellowed, but the current is the same.
From March to September the hot water comes from the sun, except on very cloudy, rainy days, even then, in summer, hot water remains in the boiler all day, sometimes it rises by a few degrees. Generally in summer, on a sunny day in the late afternoon, the water reaches 85 ° C. In spring and autumn the temperature rises by about 40 ° C. In winter, with temperatures of a few degrees plus plus, we smoke at home in the afternoon, e.g. in December, when there were sunny days, the temperature would rise by about 30 ° C. He writes approximately here, every day is different, same as the water temperature in the boiler in the morning, it is rarely below 30 ° C, hot water is also used during the day.
I noticed that in summer, when it is hot 25-30 ° C with full sun, the panels heat the water slightly better than in bright clouds. They are definitely sensitive to high temperature, at 35 ° C I measured the temperature of the panel by applying a thermometer to the frame, it was 65 ° C, the silicon plate closed between the glass and the foil probably warmed up to a higher temperature. From what I read a small tilt angle (as for me ) makes better use of diffused light, this would be confirmed by practice.
The Vmpp voltage should be 212W, but at about 200V, the panels heat the best, the regulator corrects them from 185 to 205V.
At the beginning, the installation was connected as a cascade, the 250/500 / 1000W 230V heater was switched on manually, but it worked so-so, switching between the heaters resulted in large voltage spikes. That's why I bought a regulator, the installation started to heat much better. At the beginning I left the heater from the cascade, only connected in a series of 1750W, but with strong sunlight it could not cope. When it was cool to 20 ° C, the voltage reached 230V, which is well beyond Vmpp, now it is 3kW. With moderate or weak sunlight, it heats the same way, while in strong sunlight, when it is cooler at 200V, the intensity exceeds 11A, i.e. several-year-old panels give over 100%. Of course, the measurements are made with cheap instruments.
The situation with the maximum no-load voltage, Voc, is interesting, it is higher in the morning when it is cool, but the sun is lower than at noon, but then the panel will give the most current.
I wrote a little, maybe it will be useful to others.
As for the advantages of on-grid, I absolutely agree and that will be the next stage. However, I'm going to leave 2-3kW off-grid for water heating anyway, and in order not to waste energy, you can connect the panels through a relay, which, after disconnecting the heating, will supply electricity to the inverter to a separate MPPT output. Nothing will be wasted and electricity will flow to the grid when it is needed most, in the afternoon.
My proposal for a 1kW installation with the possibility of expansion to 2.5kW in the amount of up to PLN 2,500. Prices taken from a well-known auction site.
195Wp monocrystalline panels at PLN 298 x 5 = PLN 1490.
MPPT regulator PLN 590
5 panels will give 975W at 186V, if you add one more 1170W and 226V
6mm2 cable, DC switch, the rest in the description above.
You can buy cheaper panels, e.g. amorphous ones, only they work with a higher voltage, they take up more space. You need more connectors, cable, profile, and that also costs money.