Residual current device in the TN-C photovoltaic installation

eclipse99 35868 35
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 14485986
    eclipse99
    Level 11  
    Hello,

    I came across several installation diagrams of photovoltaic power plants, each with a 4P 40A / 300mA Type B residual current circuit breaker (for example from the HAGER brand).

    The only strange thing is that the selected diagrams worked in the TN-C system, which made it practically impossible to use a differential ...

    The question is where did they get there? This is a design error?

    Link to the switch - >> http://www.hager.pl/katalog-produktow/rozdzia...zniki-roznicowopradowe-typ-b/cfb440d/4965.htm
  • ADVERTISEMENT
  • #2 14486002
    zbich70
    Level 43  
    List these diagrams, especially their sources.
  • ADVERTISEMENT
  • #3 14486016
    Anonymous
    Anonymous  
  • #4 14486188
    eclipse99
    Level 11  
    Schemat:

    Residual current device in the TN-C photovoltaic installation
  • #5 14486306
    Anonymous
    Anonymous  
  • ADVERTISEMENT
  • #6 14486309
    BILGO
    Level 38  
    eclipse99 wrote:
    The only strange thing is that the selected schemes worked in the TN-C system

    Why do you think so ?
  • #7 14486367
    masonry
    Level 30  
    eclipse99 wrote:

    The only strange thing is that the selected diagrams worked in the TN-C system, which made it practically impossible to use a differential ...


    Why do you say it's TN-C?
    After all, the RCD is inserted on the DC side.
  • #8 14486784
    eclipse99
    Level 11  
    I was simply at the site of a potential investment and I noticed that PE + N are connected together in the main switchboard ..... hence my supposition that the designer did not read the documentation :-)

    I was also wondering why these differentials are so expensive ... even 3,000 PLN!
  • ADVERTISEMENT
  • #9 14486860
    jacur
    Level 32  
    masonry wrote:
    After all, the RCD is inserted on the DC side.


    Rather between the inverter and the "produced energy" meter

    And this RCD protects the inverter anyway?
  • #10 14487159
    BILGO
    Level 38  
    Certainly, these RCDs do not protect the Inverters. PV inverters have enough built-in safeguards ...
    I wonder why they cost 3,000 ;) Could you please provide a model?
  • #11 14487191
    eclipse99
    Level 11  
    Such differences are located between the inverter and the meter of produced energy.

    I gave the link to the RCD earlier.
  • #12 14487238
    Anonymous
    Anonymous  
  • #13 14487299
    Anonymous
    Anonymous  
  • #14 14487352
    jacur
    Level 32  
    WojcikW wrote:
    It is a special residual current device designed for circuits powered by inverters (or other power electronic converters).


    Then there should be an RCD of type B behind each inverter?
    It is probably the opposite. RCD type B It is used to protect the power supply circuits of inverters.

    There is something about that in this pdf page 22:

    http://www.el-team.com.pl/pliki/dfs4b/DFS_4B_DRCA_2013_czięćc.pdf
  • #15 14487466
    Anonymous
    Anonymous  
  • #16 14487644
    jacur
    Level 32  
    Mostly, this type of RCD was installed on the power supply of inverters. But maybe because of the price it is not very popular and you need to increase sales just as you might imagine.

    but I like "just in case" p.23

    - technical instructions VdS 3145 - "Photovoltaic installations" - recommended ("for all
    accident" ;) according to 4.4.4.3 the use of circuit breakers for protection against fire
    RCD;
  • #17 14487696
    BILGO
    Level 38  
    In my opinion, the use of RCD type B for PV inverter type inverters does not make sense. Of course, RCD can be used, but AC type is sufficient.
  • #18 14488513
    Anonymous
    Anonymous  
  • #19 14491157
    arelektroda
    Level 23  
    Can someone explain the difference in the diagram in post # 4 and in the descriptions. E.g.
    eclipse99 wrote:
    Residual current circuit breaker 4P 40A / 300mA, Type B
    My point is to clarify whether the rated differential current should be 30 or 300 mA because it is "such a small" difference.
  • #20 14491378
    Anonymous
    Anonymous  
  • #21 14491479
    BILGO
    Level 38  
    At the beginning of the argument, gentlemen, decide which inverter is concerned, whether it is an inverter - a PV inverter, or an inverter - a frequency converter.
    From what I understood my friend Jacur wrote about an inverter - a frequency converter ;)
  • #22 14491555
    Anonymous
    Anonymous  
  • #23 14491949
    Wirnick
    Level 30  
    I want to note that the RCD is at the installation site 3x230V 50Hz. It does not matter what is the front or before (it checks itself - whether there is current asymmetry) - it checks the condition of the installation in both directions - in the current receiving phase or in the voltage generation phase. The type of RCD depends on the harmonics of the current.
  • #24 14492139
    Anonymous
    Anonymous  
  • #25 14492365
    Wirnick
    Level 30  
    Bronek22 wrote:

    The 30mA RCD is designed to protect people - not devices.
    It is to prevent people from being "killed" in the event of an electric shock.


    Looking at the figure below, those using renewable and traditional energy are deprived of the protection of second-lieutenants. despite the use of an RCD in the inverter.
    Residual current device in the TN-C photovoltaic installation
  • #26 14492633
    Anonymous
    Anonymous  
  • #27 14492890
    Wirnick
    Level 30  
    Bronek22 wrote:

    RG pictorial drawing, without details.

    Mr. Bronek, I will present a very detailed drawing now.
    Represents 100% basic protection of the user - only the inscription is available.
    Residual current device in the TN-C photovoltaic installation
    Still, the RCD is not allowed to function properly.
  • #28 14492985
    Anonymous
    Anonymous  
  • #29 14493134
    Anonymous
    Anonymous  
  • #30 14493650
    Anonymous
    Anonymous  

Topic summary

The discussion revolves around the use of a 4P 40A / 300mA Type B residual current device (RCD) in a TN-C photovoltaic installation. Participants express concerns about the appropriateness of using RCDs in TN-C systems, highlighting a ban on their use in such configurations. The original poster questions whether the installation diagrams represent a design error, given that PE and N are connected in the main switchboard. Various responses clarify the role of RCDs, with some suggesting that RCDs are not necessary for inverter protection, while others debate the correct placement of RCDs in relation to inverters. The conversation also touches on the cost of RCDs and the need for precise definitions of protection requirements in photovoltaic systems.