DEFENCE wrote: Well, I don't have that option. I import panels on my own from parts of Poland where I get a good price. And this is known shipping costs, so it's best to get the target number of panels. In general, I bet on the 1f inverter all the time. Or maybe someone from the forum has a 1f inverter and will tell you how it raises the voltage, if only on one phase.
Such calculation of the voltage increase requires the power of the installation P, the impedance of the short-circuit loop Z and the voltage in the network U, and if users with PV installations are connected to this network, the voltage measurement should be done on a sunny day.
?U = P x Z / 253
by transforming the above formula, we can also calculate the power of a single-phase installation that can be connected to the network so that the voltage does not increase above 253V
P= (253- U) x 253 / Z
Added after 1 [minutes]: DEFENCE wrote: Well, from what I associate are in the very large vicinity of 250, and so much can be. So what would a single-phase boost on one phase with 5 V? And three phase on each how many V?
3 times less