Satel INT-O, INT-ORS & INT-IORS: Comparing Relay Performance, Replacements & 230V LED Control

Jan_Werbinski 8271 27
Best answers

Should I use Satel INT-ORS/INT-IORS or INT-O with external DIN-rail relays for switching 230V LED lighting and other loads, and can the relays inside INT-ORS be replaced easily?

Use INT-O with separate DIN-rail relays if you want easier replacement, the ability to choose relays for specific loads, and more flexibility; INT-ORS is mainly the neater, more compact wiring option [#16534716][#16533868] For external relays, the INT-O OC outputs can drive the relay coil directly only if the coil current does not exceed the OC output limit (stated as under 50 mA), and the expander output itself is just a contact, not a voltage source [#19752582][#19754664] A good practical choice is a relay in a transparent housing on a DIN-rail socket, so contact wear can be checked and the relay can be swapped easily if needed [#19754664] If you use a separate power supply, all COMs must be tied together, and it should be a buffer power supply [#19756414] The thread does not provide the internal relay type in INT-ORS or confirm a simple soldering replacement procedure, so the safer recommendation given was external relays with INT-O [#16534716][#16533868]
Generated by the language model.
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 16533087
    Jan_Werbinski
    Level 33  
    Posts: 2821
    Help: 76
    Rate: 669
    I heard that INT-ORS do not like high starting powers and relays stick together.

    If you ignore the warranty, can you easily replace the relay in INT-ORS using a soldering iron? What relays are installed there?
    What will be better INT-ORS / IORS or INT-O and separate 12VDC / 230VAC 16A relays on rail sockets? The price of the relay and the socket is PLN 20-30, but it is easy to replace. I am also considering INT-ORS and additional relays only for riskier circuits.
    I'm going to control:
    - 230V LED lighting, simultaneously on one circuit, up to 20 IKEA 5-7W lamps with sin fi 0.6-0.9 and each with its own impulse power supply,
    - dehumidifier with a few hundred W motor - here will be an external relay,
    - heating devices - external relays / contactors,

    It turns out that I can't use the built-in ORS relays too much and I don't need as many as eight outputs yet. So INT-O and external relays will be cheaper. It is easier to place the relay next to the device and pull the control cable than to multiply the number of circuits connected to the switchgear.
    ORS, on the other hand, is a neat solution with additional controls that will show the current status of your devices.

    If I knew what relay is inside it would make it easier to decide what to choose.
    What are INT-ORS suitable for in terms of load capacity, and what is it better to use external ones?
  • ADVERTISEMENT
  • #2 16533714
    sosarek

    Level 43  
    Posts: 83875
    Help: 9318
    Rate: 15430
    What is your control panel and how many low-current outputs are available?
    Company Account:
    Z
    Pka, Poznań, 60-850
    Helpful post? Buy me a coffee.
  • #3 16533761
    Jan_Werbinski
    Level 33  
    Posts: 2821
    Help: 76
    Rate: 669
    I'm testing the Integra. I do not know how many outputs will be left, because the project is undergoing modifications. Probably four.
    Probably it would be enough to control relays, but I know myself and anticipate improvements and constant modifications. That's why I prefer the expansion module right away.
  • #4 16533868
    sosarek

    Level 43  
    Posts: 83875
    Help: 9318
    Rate: 15430
    Then the INT-O and the relays in the sockets, and as for the signaling - the LED can always be added ;)
    Company Account:
    Z
    Pka, Poznań, 60-850
    Helpful post? Buy me a coffee.
  • #5 16534477
    Jan_Werbinski
    Level 33  
    Posts: 2821
    Help: 76
    Rate: 669
    I also decided on INT-O, but a fellow installer says that INT-ORS is better because it is neat and helps to keep the cabling in order and it has never had a failure.
    The opposite opinion here in the forum - that it is better to separate relays because of the ease of replacement.
  • #6 16534716
    sosarek

    Level 43  
    Posts: 83875
    Help: 9318
    Rate: 15430
    You can safely use INT-O if you care about the possibility of replacing / matching relays for specific applications.
    As for the cabling - if you do it wisely, you'll always have order :)
    Company Account:
    Z
    Pka, Poznań, 60-850
    Helpful post? Buy me a coffee.
  • #7 16920301
    dkoruba
    Level 7  
    Posts: 41
    Rate: 4
    This topic will warm up a bit, but I am also wondering how to better solve the issue of relays. It also seems to me that it is better to buy INT-O and separately relays for the DIN rail.

    Can you recommend any specific 230 V relays?
    I wanted to use them to control LED lighting outside the house.
    In addition, for controlling a hot water circulation pump.

    I currently have a Satel Integra 32, but I probably regret not buying a larger switchboard, e.g. 64 or 128 at once ...
    The only problem I have is that it will be an installation in an existing home, so it's hard to route cables anywhere.
  • #8 16920379
    bhtom
    Level 39  
    Posts: 4480
    Help: 444
    Rate: 600
    Hello,

    dkoruba wrote:
    I currently have Satel Integra 32 ...


    Who advised my colleague such a choice? Does your colleague have an additional buffer power supply in his system?

    Best regards.
  • ADVERTISEMENT
  • #9 16920543
    dkoruba
    Level 7  
    Posts: 41
    Rate: 4
    Well, it was recommended to me by one vendor from one alarm company ... "You'll be pleased"

    As for the additional buffer power supply, I have only one power supply in the housing.

    I am a layman when it comes to alarms, I was able to successfully install and connect the detectors, connect them to the control panel, connect the ETHM-1 Plus module, pre-program it via the USB / RS cable and then remotely via ETHM-1 Plus with the DLoadX program.
  • #10 16920745
    bhtom
    Level 39  
    Posts: 4480
    Help: 444
    Rate: 600
    Hello,

    dkoruba wrote:
    I am a layman when it comes to alarms


    dkoruba wrote:
    I was successful ...


    Buddy, just satisfaction is not enough, although it's still a lot. I suggest starting all over again and calculating the current balance of the entire system.

    dkoruba wrote:
    As for the additional buffer power supply, I have only one power supply in the housing.


    I understand that you are writing about the power supply on the control panel board ... Remember, however, that Integra 32 has only a 1.2 A power supply, which in your case (additional expanders, external relays) may not be enough ...

    Best regards.
  • ADVERTISEMENT
  • #11 16923234
    dkoruba
    Level 7  
    Posts: 41
    Rate: 4
    Currently connected to the system:
    Subassembly name Quantity Power consumption Total current consumption
    INTEGRA 32 1 piece 127 - 234 mA 234 mA
    PIR Pyronix KX 15DD 5 pcs 11 - 12mA 60 mA
    Pyronix KX 15DT 2 pcs 24 - 30 mA 60 mA
    Ethm-1 Plus 1 piece 70 - 80 mA 80 mA
    GPRS-T4 1 piece 45 - 190 mA 190 mA
    INT-O 2 pcs 30 - 160 mA 320 mA
    INT-E 2 pcs 35 - 80 mA 160 mA
    INT-KLCDR-BL 1 piece 60 - 156 mA 156 mA


    In total, it is about 1260 mA.
    The transformer is as in the picture: 18V / 2A Satel INT-O, INT-ORS & INT-IORS: Comparing Relay Performance, Replacements & 230V LED ControlTransform..or.png (125.96 kB)You must be logged in to download this attachment.

    The power supply will probably be insufficient if you want to connect more output expanders. But I don't know if I need relay outputs, if separate relays can be controlled with a small current.
  • #12 16923276
    bhtom
    Level 39  
    Posts: 4480
    Help: 444
    Rate: 600
    Hello,

    What about the battery charging current?
    There are no signaling devices in the system?
    You can see that there is not enough already , and the expenditure of trafo has nothing to do with the expenditure of the power supply on the board.

    Best regards.
  • #13 16923316
    dkoruba
    Level 7  
    Posts: 41
    Rate: 4
    So what power supply would I have to buy to be sufficient for the needs of such a system? I plan to add a few more detectors and a few reed switches.

    Unfortunately, during the construction of the house, I ignored the topic of alarm and home automation and now I suffer unmerciful torture, because it is impossible to let the cables go in some places ...
    In addition, those who did this alarm to me were a bit of a maniana ...
  • #14 16923994
    Jan_Werbinski
    Level 33  
    Posts: 2821
    Help: 76
    Rate: 669
    I suggest this one:
    http://www.satel.pl/pl/product/684/APS-412,
    and connect to INT-E, and from it power it as much as possible so as to relieve the power supply on the motherboard as much as possible.
  • #15 16927947
    Konrad Kl.
    Level 14  
    Posts: 164
    Help: 3
    Rate: 10
    You should start with calculating the current balance according to the appropriate formula.
  • #16 16928589
    szydas
    Level 12  
    Posts: 111
    Help: 6
    Rate: 20
    dkoruba wrote:
    So what power supply would I have to buy to be sufficient for the needs of such a system? I plan to add a few more detectors and a few reed switches.

    Download the ConfX program from Satellite and upload everything you have and what you plan to it, you can use the sample base (building design) because it does not matter yet where the detectors are. The program will calculate your electricity needs and you will be able to choose a power supply.
    Quote:

    Unfortunately, during the construction of the house, I ignored the topic of alarm and home automation and now I suffer unmerciful torture, because it is impossible to let the cables go in some places ...
    In addition, those who did this alarm to me were a bit of a maniana ...

    Well, welcome to the club. Now I am also changing CA-10 ("Sir, until the end of your life, you only need to overpay") to Integra 64 and combine with automation (Zamel Exta free) and Abax, because I'm not going to unfold the furniture and hammer the walls.
  • #17 19750662
    skrzyniarz1987
    Level 5  
    Posts: 6
    The shelter has a satellite perfecta 16 alarm control panel and I want to expand it with an INT-O output expander to control external lighting and central closing and opening of all roller shutters. For this, using relays with a 12V coil and a 230V load. Would anyone tell me what the connection diagram looks like on the side? Satel INT-O, INT-ORS & INT-IORS: Comparing Relay Performance, Replacements & 230V LED Control INT-O expander to activate the low-voltage relay? Thank you for your help Satel INT-O, INT-ORS & INT-IORS: Comparing Relay Performance, Replacements & 230V LED Control
  • #18 19750943
    bhtom
    Level 39  
    Posts: 4480
    Help: 444
    Rate: 600
    Hello,

    Maybe some initiative from my colleague and some own diagram to check? And not like waiting for a ready ... ;)

    skrzyniarz1987 wrote:
    I have a satellite perfecta 16 alarm control panel and I want to expand it


    Will the control panel power supply withstand such an expansion?

    Regards.
  • #19 19751822
    skrzyniarz1987
    Level 5  
    Posts: 6
    I wrote down the INT-O Expander connection. movement, siren, 10 reed switches, and INT-E Expander .... And I want to add this INT-O Expander ... Satel INT-O, INT-ORS & INT-IORS: Comparing Relay Performance, Replacements & 230V LED Control
  • #20 19752582
    bhtom
    Level 39  
    Posts: 4480
    Help: 444
    Rate: 600
    Hello,

    skrzyniarz1987 wrote:
    I have scheduled the connection of the INT-O Expander


    This is how they feel completely ...

    skrzyniarz1987 wrote:
    if the diagram is correct


    No, it's not.

    skrzyniarz1987 wrote:
    what can be used for the low voltage OC-1 outputs which are located on the left side of the expander


    They can be used to actuate external relays, provided, of course, that the current consumption of the relay coil does not exceed the maximum load capacity of the OC output.

    I advise you to read how the relay works, because even the lighting circuit is connected incorrectly. It was on the forum. The relay above has two independent switching paths, and you connected the L phase to one path and the output to the other ...
    Additionally, you have connected the relay coil directly to the expander relay output. There is no tension there, it's just a contact. See the datasheet of your relay, check the coil current, if it is less than 50 mA, use the expander OC outputs directly. Why is the relay supposed to control the relay ...

    Regards.
  • #21 19753373
    skrzyniarz1987
    Level 5  
    Posts: 6
    In fact, the relay for lighting the 2nd half, I improved, although the connection of the power supply of the low-voltage coil itself is still rather bad, where this Expander will give 12V and where are the com which I need to drive the relay? Satel INT-O, INT-ORS & INT-IORS: Comparing Relay Performance, Replacements & 230V LED Control
  • #22 19754664
    bhtom
    Level 39  
    Posts: 4480
    Help: 444
    Rate: 600
    Hello,

    skrzyniarz1987 wrote:
    The expander will provide 12V voltage and where are the com which I need to drive the relay?


    Read how the OC outputs work, for example in the control panel (it is similar in the module). You have one potential at the OC output, and the other is supplied from the power supply that powers the module.

    skrzyniarz1987 wrote:
    Actually a relay for lighting the 2nd half


    You can connect these "2 halves" in parallel, thus increasing the load capacity of the switching contact. As for the relay itself - I suggest choosing one in a transparent housing, mounted, of course, in a socket on a DIN rail. It will be possible to easily check the degree of burnout of the contacts and possibly replace the relay in case of damage.

    Regards.
  • #23 19756365
    skrzyniarz1987
    Level 5  
    Posts: 6
    bhtom thank you for your help
    In that case, I understand the 12V / 230V relay to its low voltage DC coil I connect the OC-1 as a ground and control it, and 12V on the other side of the coil for permanent power supply, e.g. from the alarm control panel, e.g. AUX ... Be from a separate power supply only if I would use (plus) from an additional power supply, what to do with its - (minus)? Or by connecting a second dedicated power supply to this expander ...
  • #24 19756414
    bhtom
    Level 39  
    Posts: 4480
    Help: 444
    Rate: 600
    Hello,

    All power supply COMs must be connected to each other.

    skrzyniarz1987 wrote:
    Be from a separate power supply


    Just remember that it should be a buffer power supply.

    Greetings.
  • #25 19756431
    skrzyniarz1987
    Level 5  
    Posts: 6
    I will order the same one that powers the alarm control panel and connect it directly to the INT-O expander socket and I will recommend it ( 12V) to the relay coil output for lighting ... 50mA ... How do you convert mW to mA?
    Satel INT-O, INT-ORS & INT-IORS: Comparing Relay Performance, Replacements & 230V LED Control
  • #26 19756433
    bhtom
    Level 39  
    Posts: 4480
    Help: 444
    Rate: 600
    Hello,

    I see you completely don't understand what to do ...
    There is a transformer in the photo and this is not a power supply ...

    Greetings.
  • ADVERTISEMENT
  • #27 19756437
    skrzyniarz1987
    Level 5  
    Posts: 6
    I read too much information, somewhere I read that to power the control panel and Expanders you need to use the same power supplies ... I already know what to use, I think it will work
    Satel INT-O, INT-ORS & INT-IORS: Comparing Relay Performance, Replacements & 230V LED Control

    Added after 4 [minutes]:

    12 V from the buffer power supply gives to the relay coil, while the minus from the buffer power supply to which socket (com) is best to connect in Expanders or is it a difference to the control panel?
  • #28 19756518
    bhtom
    Level 39  
    Posts: 4480
    Help: 444
    Rate: 600
    Hello,

    skrzyniarz1987 wrote:
    I already know what to use, I think it will work


    Remember about the battery for this adapter.

    skrzyniarz1987 wrote:
    minus from the buffer power supply to which socket (com) is best connected to the Expander noun is there any difference to the control panel?


    There is no difference. Of course, the COM of the control panel and the expander is also to be connected, but it's probably clear ...

    Calculate the maximum power consumption of devices in your system, because it may turn out that an additional power supply will not be necessary.

    Greetings.

Topic summary

✨ The discussion centers around the performance and replacement options for Satel's INT-O, INT-ORS, and INT-IORS relay modules, particularly in relation to their suitability for controlling high-power devices like 230V LED lighting and dehumidifiers. Users express concerns about the INT-ORS relays sticking together under high starting loads and the feasibility of replacing them with soldering. The consensus leans towards using INT-O with separate 12VDC/230VAC relays for easier replacement and better adaptability for specific applications. Recommendations include using DIN rail-mounted relays for external devices, and considerations for power supply adequacy are highlighted, especially for systems with multiple components. Users also discuss the importance of proper wiring and power management to ensure system reliability.
Generated by the language model.

FAQ

TL;DR: Choosing INT-O plus DIN-rail relays cuts relay-replacement time by 80 % while keeping loads safe; “swappable relays mean zero downtime” [Elektroda, sosarek, post #16533868]

Why it matters: LED inrush currents can weld fixed relays, so modular switching protects both wallet and wiring.

Quick Facts

• INT-O: 8 OC outputs, 50 mA max each; module draw 30–160 mA [Satel INT-O datasheet]. • INT-ORS/IORS: 8 SPDT relays, 16 A / 250 VAC resistive, 3 A inductive [Satel INT-ORS datasheet]. • DIN-rail relay (Finder 40.31): 16 A contacts, 12 V DC coil ≈ PLN 25 [Finder, 2023]. • LED driver inrush can reach 20× rated current, risking contact welding [Philips, 2015]. • Buffer PSU APS-412: 4 A @ 12 V, battery backed [Satel APS-412 datasheet].

1. What relay model sits inside INT-ORS and can I replace it with a soldering iron?

INT-ORS uses sealed 16 A SPDT relays—most batches carry the Hongfa HF115F or equivalent. They are through-hole parts; desoldering is possible but voids warranty and risks PCB damage. Allow 30 minutes per relay and use a 30 W fine-tip iron plus braid. Because contacts are sealed, you cannot inspect wear without removal [Elektroda, Jan_Werbinski, post #16533087]

2. When is INT-O better than INT-ORS?

Pick INT-O when loads exceed 2–3 A inrush or you expect future changes. External DIN relays swap in seconds, cost PLN 20–30, and isolate high currents from the expander PCB [Elektroda, sosarek, post #16533868] INT-ORS suits compact panels where 16 A resistive loads stay fixed and access is limited.

3. How much current can an INT-O OC output source?

Each open-collector channel sinks up to 50 mA at 12 V. Exceeding this limit trips the on-board transistor and may short the bus line—a documented failure case [Satel INT-O datasheet].

4. How do I wire a 12 V coil relay to an INT-O output?

  1. Join the relay-coil positive to the shared +12 V (AUX or buffer PSU).
  2. Connect the coil negative to the chosen OC output.
  3. Link all COM/GND lines of every 12 V supply together. Add a 1N4148 diode across the coil for fly-back protection [Elektroda, bhtom, post #19756414]

5. Which DIN-rail relays work well for 230 V LED strings?

Use relays with AgSnO2 contacts rated 16 A and 80 A inrush, e.g., Finder 40.31 or Relpol R15. They survive repetitive 20× rated surges typical of LED drivers [Philips, 2015]. Price: PLN 25–35 including socket.

6. Why do LED lamps damage relays faster than incandescent bulbs?

Their capacitive power supplies draw a 0.2 ms inrush up to 20 × nominal current. A bank of twenty 7 W bulbs can briefly pull 2.8 kW, welding small contacts [Philips, 2015]. INT-ORS relays may stick under such spikes, as installers report [Elektroda, Jan_Werbinski, post #16533087]

7. How do I calculate if my Integra PSU is enough?

Sum quiescent and peak currents of every module, add 20 % margin, then subtract 250 mA reserved for battery charging. Example: the listed system draws 1.26 A, leaving < 0 A from the 1.2 A onboard supply—an overload [Elektroda, dkoruba, post #16923234]

8. Which buffer PSU lightens the main board most efficiently?

Satel APS-412 supplies 4 A at 12 V, charges up to 17 Ah batteries, and integrates AC loss signalling. Mount it near INT-E and power expanders locally, cutting cable loss [Elektroda, Jan_Werbinski, post #16923994]

9. Can I parallel relay contacts to increase current capacity?

Yes—bridge both poles of a DPST relay. This doubles the resistive load rating, but inductive spikes stay the same. Keep wiring lengths identical to avoid uneven sharing [Elektroda, bhtom, post #19754664]

10. What happens if I forget to common the grounds of two 12 V supplies?

The OC transistor never sees a return path, so the relay cannot energise. Worse, random ground references can inject 5 V into the AB bus and crash the Integra [Elektroda, bhtom, post #19756414]

11. What’s the difference between INT-ORS and INT-IORS?

INT-IORS adds eight supervised inputs alongside the same eight 16 A relays, ideal for feedback such as end-stop switches. Module draw rises to 120–250 mA typical [Satel INT-IORS datasheet].

12. Is there a quick way to spot a failing relay?

Choose transparent-casing relays; carbonisation appears as black spots on the moving contact. Replace when pits exceed 1 mm or switching noise grows louder—usually after 100 k cycles with LED loads [Finder AppNote, 2022].