    I have a problem with Super Power Jack cylinders. For the gate to close or open I have to keep pressing the button on the remote control. I am asking for advice. What should I do to make the gate open and close smoothly?
  • #2
    kamo502
    Level 20  
    What driver do you have for this?
    Chinese on two relays?
  • #3
    tami272
    Level 10  
    yes chinese on two relays. What advice do you do?

    Added after 11 [minutes]:

    I have the same problem . What to do with this ?
  • #4
    kotbury
    Gantry automation specialist
    If you bought something with an antenna rolled up in a pigtail sold for a ... o by e ...... them and others then you can set jumpers in 3 modes (monostable, bistable, change of state) - you have probably set monostable mode you have to switch to the mode called "status change" by sellers. In this mode, after successive presses of one remote control button, one of the relays closes permanently, the other opens - and so on.
    And if you bought one that has no status change option and only has mono and bistable mode, buy one that has this status change.
  • #6
    kotbury
    Gantry automation specialist
    READ THE MANUAL and put the jumper on properly.
  • #7
    tami272
    Level 10  
    There is nothing about this in the instructions
  • #8
    kotbury
    Gantry automation specialist
    Such?
    If not, scan and give the instruction because it is more interesting invention than the above ....
  • #10
    kotbury
    Gantry automation specialist
    In fact - there are no configuration options (by the way, I see something like this for the first time but enterprising Poles are still working and will soon import the entire cross-section of Chinese technical thought ...).
    It remains to molest the seller - remote sales = unconditional exchange or return of goods within 2 weeks, the guest should also recognize the warranty claim ...
  • #11
    kortyleski
    Level 43  
    It should be added that when setting the change of state, the limit switches in the motors should be set correctly
  • #12
    kotbury
    Gantry automation specialist
    In this case, with the wrong setting of the limit switches, the servomotors would not work at all (the limit switches in these servomotors permanently cut off the engine power supply and only the change of polarity brings the motor back to life) - that is the fault on the "central" side.
  • #13
    tami272
    Level 10  
    In short, ask the seller to replace the driver or advertise all equipment.
    Thank you for your help . greetings
  • #14
    kortyleski
    Level 43  
    kotbury wrote:
    In this case, the actuators would not work at the wrong limit settings

    Unless they are set to a range larger than the gate has a swing. Then something will break ...
  • #15
    tami272
    Level 10  
    Kródko. Will this driver what I got in the set will work correctly or not ?????
  • #16
    kotbury
    Gantry automation specialist
    There will be but some patience:
    Now one more thing occurred to me - try to reduce the sensitivity of the amperometric protection with this famous "small knob" from the manual. It may be - that the sensitivity of the protection is too high from the very beginning (after all, one output pulls two servomotors) - turns off normal operation and by constantly pressing the remote control, you force the controller to operate in an emergency.
    If maneuvers adjusting the security sensitivity do not work (for starters try extreme positions and the potentiometer looks multi-turn i.e. you need to wind up) - consider contacting the seller and replacing the equipment.

    And what the previous speaker stubbornly mentions - that is, the correct setting of the limit switches on each actuator - is the next and final stage of adjustment.
  • #17
    tami272
    Level 10  
    It is true that I already did as you write but I did not try it in the extreme positions of the overload sensor. I will do it tomorrow and let you know.

    Added after 9 [hours] 14 [minutes]:

    Hello. I did as you wrote. Unfortunately no reaction.
  • #18
    tami272
    Level 10  
    Hello all. I installed a new driver and the gate works ok. I have only a question I want to install the second antenna because what is too weak. I want to buy one placed only on the pole where to connect it. Can I cut the antenna that is in the controller (spiral) and solder in series what I buy. Is it possible and will it work?
  • #19
    kotbury
    Gantry automation specialist
    Quote:
    Hello. I did as you wrote. Unfortunately no reaction


    Well - such a risk from the PRC

    Quote:
    I have only a question I want to set up a second antenna because the one that is too weak


    In general, desolder the spiral (or cut it close to the board and leave as short a piece of wire as a pin) - and solder instead (or to this pin) the middle coaxial cable. Leave the screen unconnected or, if there is a wide, obvious mass field nearby - solder the screen to it.
    Or another way - straighten this spiral, set it as "vertically" and if it has a different length - cut to exactly 16.5 cm - it should improve the range a lot.