Faac 740 Sliding Gate Actuator Issue: Gate Only Opens, Wiring and FSW CL Diode Problems

Boku1 15921 18
Best answers

Why does my Faac 740 sliding gate only open and not close, with the FSW CL LED off after installing the photocells and wiring the control board?

Your gate only opens because the closing safety input FSW CL is open; it must see a normally closed (NC) photocell contact on COM, not NO, or the controller will block closing [#16846300][#16851941] Check that the photocell transmitter and receiver are powered, aimed at each other, and that the receiver relay clicks / its LED changes when the beam is interrupted [#16845501][#16846300] To isolate the fault, temporarily bypass the photocells on the control board with the jumper/test bridge described in the thread (for example 3-4-11 or terminal 4 to 7/8, depending on the wiring) [#16845501][#20049655] If the gate then closes, the problem is in the photocell wiring, a bad cable, or a faulty photocell [#16845501][#16851941]
Generated by the language model.
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 16845371
    Boku1
    Level 2  
    Posts: 4
    Rate: 4
    Hello
    At the beginning, I am not a specialist. Yesterday I completed the installation of the sliding gate with the faac 740 actuator. I connected the photo on the closing and bridged 5 out of 7 on the control panel. Unfortunately, the gate only opens. The pilot also programmed somehow strangely. The fsw cl diode is not on at all. I already read so much on the forum that my head hurts but I do not know how to solve this problem. I have a photo of xp20d and magnetic terminals. I also had an additional button in the garage connected to the open button and I disconnected the stop on the control panel for now, I thought that there was a problem here, but it's not that. Can anyone help.
  • ADVERTISEMENT
  • #2 16845501
    zybex
    Helpful for users
    Posts: 15888
    Help: 2093
    Rate: 2916
    You probably have a problem with the photocells. They detect an obstacle and therefore cannot close. Either you have NO turned on instead of NC, or the photos do not see each other (incorrectly aimed), or the sending photo has no power. As for the pilot, try without him for now. Short-circuit terminal 1 with 7 (open A), i.e. take out two cables and make a short circuit. Hope you bridged between 6 and 8 too.
    You can also always bypass the photocells by shorting 3 and 4 out of 11. Then the gate must close when you give the command.
  • #3 16846290
    Boku1
    Level 2  
    Posts: 4
    Rate: 4
    Hello
    1st bridge between 6 and 8 is
    2. What is it: Well, Nc
    3. I did as you said, I closed 1 of 7 and the gate opened like a remote control, but after another short circuit, no reaction, only the open A LED flashed, the gate did not move, the same effect as after clicking the remote control. I don't know what's going on, in the dark I already messed up something with cables that it didn't even open for me, but it can be recreated I think
    I have not taken 4 photos anymore. Too dark
    Attachments:
    • Faac 740 Sliding Gate Actuator Issue: Gate Only Opens, Wiring and FSW CL Diode Problems IMG_20171124_153252.jpg (3.71 MB) You must be logged in to download this attachment.
  • ADVERTISEMENT
  • #4 16846300
    zybex
    Helpful for users
    Posts: 15888
    Help: 2093
    Rate: 2916
    Boku1 wrote:

    2. What is it: Well, Nc

    NO - Normal Open (normally open)
    NC - Normal Close (normally closed)
    It concerns the state of the relay contacts. The relay contacts have three leads, COM, NO, and NC. It's such a switch. COM is in the middle and NO and NC are on the sides. So, depending on the needs, we use the contacts about which the instruction says.

    Faac 740 Sliding Gate Actuator Issue: Gate Only Opens, Wiring and FSW CL Diode Problems

    For you, FSW CL is off, which means that the protection has worked. You are to have a normally closed contact connected, as shown in the diagram. In addition, it's worth checking if the photos can be seen. After the optical barrier is broken, we need to hear the relay in the receiving photo.
  • ADVERTISEMENT
  • #5 16849371
    Boku1
    Level 2  
    Posts: 4
    Rate: 4
    You are to have a normally closed contact connected, as shown in the diagram. In addition, it's worth checking if the photos can be seen. After the optical barrier is broken, we need to hear the relay in the receiving photo.
    My wife passed the transmitter and something snapped. I checked the pics for the cables, cut them and then nothing. I got pissed off with the cables from the photos and I did according to fig. 5. And the gate works, although I won't say no, I have photos to hang on the posts, so that I will annoy this topic.
    Question from another fairy tale, I read on the forums that in order to have, for example, a switch to open in the garage, it is enough to have a simple bell and some write to connect open 1 with stop, others write open 1 with -. For me neither one nor the other works? I also set the E logic, but something with slowdowns is wrong.
    How, how can I check myself without taking photos, are they functional?
    Thanks for your help. Greetings
  • #6 16849439
    zybex
    Helpful for users
    Posts: 15888
    Help: 2093
    Rate: 2916
    Boku1 wrote:

    My wife passed the transmitter and something snapped. I checked the pics for the cables, cut them and then nothing.

    Between the transmitter and the receiver in standby mode there is a beam of invisible light (infrared). The receiver has a relay that turns on and off when the beam is interrupted. A characteristic "beep" can be heard in the receiver.
    In addition, the receiver has an additional diode, which optically signals the proper operation of this barrier. The relay has three contacts COM, NO and NC as standard. We always connect COM and the appropriate one as needed, in this case NC.
    You can see for yourself that omitting the photos and bridging everything according to Figure 5 gives the correct operation of the gate (there is also closing). So I don't see a big problem here, because when you properly connect these pics, it will work. If you are not sure about their work, use COM and NO, because there is no other option. Perhaps this is the "catch" here. You can understand the NC state in various ways, because I do not know when the relay is holding and when it is released? I don't have these pics (you have them) and you can easily check them as described above. You only have two choices, COM and NC or COM and NO.
    Boku1 wrote:

    Question from another fairy tale, I read on the forums that to have, for example, a switch in the garage to open, an ordinary bell is enough

    As for the wired opening button (bell), you connect it under 1 and 7 (i.e. Open A and minus). You can put several such buttons in different places to make your life easier. Most often I installed miniature ones, because the currents flow there very little. Of course, the cable is also thin, eg telephone 2x0.5mm2. Someone requested in three places. Of course, if we want, we install an ordinary bell.
    Faac 740 Sliding Gate Actuator Issue: Gate Only Opens, Wiring and FSW CL Diode Problems Faac 740 Sliding Gate Actuator Issue: Gate Only Opens, Wiring and FSW CL Diode Problems
    I installed the visible ones in existing intercoms in a single-family house.
  • #7 16849465
    kotbury
    Gantry automation specialist
    Posts: 9488
    Help: 2080
    Rate: 3575
    Quote:
    I do not have photos to hang on the posts, so that I will annoy this topic.

    What pics do you have? if Faacowskie, there are 2 LEDs on the receiver - one indicates power and the other - poorly visible and a little to the side - goes out after covering (and the relay in the receiving photo is clicked). If so, look for a problem in the cables or bad connection to the control panel.
    The previous speaker has already written about the button.
    Quote:
    I also set the E logic, but something with slowdowns is wrong.

    Specifically what?
    You can have a version with slows down before the limit switches (on time), i.e. rP in the menu - do not use this (set to zero) because it is unstable.
    The basic releases (the distance of which is set in the menu under the rA item) are the releases after the switch is activated (i.e. the limit switch will work and the gate continues to drive slowly through the distance in cm corresponding roughly to the rA value). This release is very short - max 7 cm - but sufficient - and you have to take it into account when setting the limit switches (i.e. set them a bit earlier).
  • #8 16849720
    Marek J.
    VIP Meritorious for electroda.pl
    Posts: 2368
    Help: 526
    Rate: 945
    zybex wrote:
    For you, FSW CL is off, which means that the protection has worked.

    Here I would only add that they can be damaged, badly connected, damaged cable etc ...
    It results from the photo, where you can see that fsw cl is off (and it should make the automatic start the closing cycle), and in the "light" of the photocells between the posts there is no obstacle.
  • #9 16849721
    kotbury
    Gantry automation specialist
    Posts: 9488
    Help: 2080
    Rate: 3575
    Quote:
    I do not have photos to hang on the posts, so that I will annoy this topic.

    What pics do you have? if Faacowskie, there are 2 LEDs on the receiver - one indicates power and the other - poorly visible and a little to the side - goes out after covering (and the relay in the receiving photo is clicked). If so, look for a problem in the cables or bad connection to the control panel. The FSW_CL diode should also go out (on uncovered photos).
    The previous speaker has already written about the button.
    Quote:
    I also set the E logic, but something with slowdowns is wrong.

    Specifically what?
    You can have a version of the drive with decelerations before the limit switches (on time), i.e. rP in the menu - do not use this (set to zero) because it is unstable.
    The basic releases in each 740/41 (the distance of which is set in the menu under the rA item) are the releases after a limit switch is activated (i.e. the limit switch will work and the gate will still drive slowly through the distance in cm corresponding roughly to the rA value). This release is very short - max 7 cm - but sufficient - and you have to take it into account when setting the limit switches (i.e. set them a bit earlier).
  • ADVERTISEMENT
  • #10 16851146
    Boku1
    Level 2  
    Posts: 4
    Rate: 4
    Thank you all for helpful advice. I have set the slowdown and before and after the krancowka. Tomorrow I will. The rest of the things are probably only from the next Friday I will have fun, unfortunately, but the end of free time and late with work I will return and in the dark it is not a job.
    I understand that it is about connecting with a cable either COM with NO or with NC.
    Damaged cables are not 100 percent of the time. Thanks again and let me know how to tinker with it
  • #11 16851941
    zybex
    Helpful for users
    Posts: 15888
    Help: 2093
    Rate: 2916
    Boku1 wrote:

    I understand that it is about connecting with a cable either COM with NO or with NC.

    You connect two cables. One to COM and the other to NO or NC. Besides, two cables for power supply (one can be common, according to the diagram).

    On a similar topic Kotbury He wrote about photocells such as yours, quotation: "As for the LED - TX should be on all the time (power), RX - one should be on all the time (power) and the other should be on as the photos can be seen and fade out when obscuring. the FSW CL LED on the control unit should behave. "

    Since you have this FSW CL off, you have a broken light beam or (more likely) a break to COM-NO (NC), i.e. replace one wire from NC to ON or vice versa. Simply in standby mode (photos can be seen) there should be a short circuit between COM and the second terminal (as in diagram 9).
    I do not know if the instruction from the photos tells exactly about this detail, i.e. when is NC and when NO. If you find it out, give me your answer here, because a similar assembly is coming soon.
  • #12 19650033
    fantomek
    Level 10  
    Posts: 468
    Help: 1
    Rate: 154
    I will connect to the topic yesterday I changed the bulb in the siren. Faac 740 drive. Upon completion, the Gate operated both ways. The only thing is I didn't screw the antenna on because I forgot. Today the Gate only opens but does not close. What happened? What was reprogramming?
  • #13 19650130
    zybex
    Helpful for users
    Posts: 15888
    Help: 2093
    Rate: 2916
    Is it not possible to close the door with the button in the garage (direct control)?
    Probably something wrong with the photocells. The lack of an antenna has nothing to do with it.
    Check the photocells for contamination both from the outside and from the inside, if necessary. You can do the test by ignoring the photocells.
  • #14 19650197
    fantomek
    Level 10  
    Posts: 468
    Help: 1
    Rate: 154
    Zybex, I do not have to close the entrance gate to the property in the garage, only via remote controls. I checked on two different remote controls and the same. I wrote about the lamp in this context that maybe some moisture got to it through the inlet where the antenna enters.
  • #15 19650286
    kotbury
    Gantry automation specialist
    Posts: 9488
    Help: 2080
    Rate: 3575
    As the previous speakers wrote - the lamp has nothing to do with it
    Are the FSW CL and FSW OP LEDs on? If you do not - you probably nudged the photo with your foot and the corroded wire released. Make working jumpers 3-4-11 in the control panel. If the gate regains closing - laborious searching for a break on the cables ...
  • #16 20049502
    gabi126
    Level 10  
    Posts: 5
    Rate: 1
    I have a similar problem, the gate worked with photocells, suddenly it can only be opened and not closed. Off FSW CL transmitting photocells on receiving photocells are on, two LEDs are on when there is a break, the beam one goes out and you hear the contactor, but nothing changes on the control unit.
    Where exactly are NC and NO in the photocell? or on the switchboard.
  • #17 20049655
    sisko
    Level 33  
    Posts: 1406
    Help: 296
    Rate: 521
    @ gabi126 in this topic Link you have a sample photo of a photocell.
    If the FSW CL is off, there is an open circuit somewhere or the relay in the photocell is not working properly.

    For the test, connect the terminal No. 4 to the terminal No. 7 or 8. The FSW CL LED should light up.

    The second test can be performed at the photocell, short-circuiting the wires going to the COM and NC or NO terminals, depending on how the given photocell performs this function.
    If the FSW CL LED is on, there is no interruption in the installation and the photocell is damaged.
  • #18 20049710
    gabi126
    Level 10  
    Posts: 5
    Rate: 1
    Thanks for the info. As soon as I get home, I'll do some tests. only my photocell has 4 connections
    Attachments:
    • Faac 740 Sliding Gate Actuator Issue: Gate Only Opens, Wiring and FSW CL Diode Problems 20220605_185054.jpg (375.45 KB) You must be logged in to download this attachment.
  • #19 20050374
    gabi126
    Level 10  
    Posts: 5
    Rate: 1
    4 out of 7 lit up

    Added after 1 [hour] 2 [minutes]:

    The cable for 2 photos to 4 in the switchboard was bad. Works Thanks for your help

Topic summary

✨ The discussion revolves around issues with a FAAC 740 sliding gate actuator, specifically that the gate only opens and does not close. The user has connected photocells incorrectly, leading to the FSW CL diode being off, indicating a problem with the photocell circuit. Various troubleshooting steps are suggested, including checking the wiring, ensuring the photocells are properly aligned, and verifying the relay connections (COM, NO, NC). Users recommend bypassing the photocells to test the gate's functionality and suggest that damaged cables or incorrect connections may be the root cause of the issue. The conversation also touches on the proper configuration of limit switches and the importance of ensuring that the photocells are operational.
Generated by the language model.

FAQ

TL;DR: Most FAAC 740 “opens-only” faults trace to the photocell safety loop; set rP=0 and note the release is max 7 cm. “This release is very short.” [Elektroda, kotbury, post #16849721] Why it matters: This FAQ helps DIY installers quickly restore closing, verify FSW CL/OP LEDs, and wire push-buttons safely on FAAC 740 systems.

Quick Facts

Why does my FAAC 740 open but not close?

Your closing safety input is open. When FSW CL is OFF, the control blocks closing to protect users. Check photocell alignment, power, and the COM–NC contact wiring. If needed, bypass with a temporary 3–4–11 jumper to confirm the loop is the fault path before repairing cables or terminals. [Elektroda, zybex, post #16846300]

How do I test if the photocells are the problem?

Do two checks. First, add a temporary jumper across 3–4–11 on the board; if the gate closes, the photocell loop is open. Second, inspect for disturbed or corroded wires and reseat terminals. Restore normal wiring after testing; the jumper is only for diagnostics. [Elektroda, kotbury, post #19650286]

What do FSW CL and FSW OP LEDs mean on the FAAC board?

FSW CL indicates the closing photocell chain. When it’s OFF with a clear path, the board sees an open circuit and blocks closing. FSW OP serves the opening side. Restore the correct COM–NC contact at the receiver to re‑enable closing. [Elektroda, zybex, post #16846300]

How should I wire the wall push-button (bell) for manual control?

Connect the button across terminals 1 (Open A) and 7 (–). You can parallel multiple buttons. Low current allows small cable, such as 2×0.5 mm². This provides open/step control independent of the radio receiver. [Elektroda, zybex, post #16849439]

NO vs NC on photocells—what’s the difference and which do I use?

Photocell receivers have a relay with COM, NO, and NC. For closing safety, the board expects a closed loop at rest, so wire COM–NC unless your photocell specifies otherwise. If FSW CL stays OFF, swap to the other contact and retest. [Elektroda, zybex, post #16851941]

Where are NC and NO located—on the photocell or the control board?

They are relay outputs on the receiving photocell. The control board only senses that contact across its safety terminals. For diagnosis, you can short the two wires that go to COM and NC (or NO) at the photocell to see if FSW CL lights. [Elektroda, sisko, post #20049655]

How do I align and verify my FAAC photocells work?

Power TX and RX, aim them until the RX LED indicates alignment, and listen for the relay click when you block the beam. The receiver typically shows two LEDs: power and alignment/beam. Realign until the LED behavior and click are consistent. [Elektroda, kotbury, post #16849465]

Does a missing antenna or lamp issue stop the gate from closing?

No. Radio range may drop without the antenna, but closing faults point to the safety circuit. As one expert notes, the antenna “has nothing to do with it.” Focus on cleaning, powering, and testing the photocells first. [Elektroda, zybex, post #19650130]

I changed a lamp and now it won’t close—what’s the edge case?

You likely nudged a corroded or weak photocell wire, opening the safety loop. Add a 3–4–11 jumper to confirm, then trace for a broken cable, loose terminal, or water ingress. Fix the cabling and remove the jumper to restore protection. [Elektroda, kotbury, post #19650286]

How do I temporarily bypass the photocells to diagnose?

  1. Power off and add jumpers across 3–4–11 on the board.
  2. Power on and issue a close command; observe normal closing.
  3. Power off, remove jumpers, and repair the photocell wiring before regular use. [Elektroda, kotbury, post #19650286]

How do I set deceleration correctly on a FAAC 740?

Use rA for the release after the limit switch. Expect about 0–7 cm extra travel, so set limits slightly early. Disable rP (time-based deceleration) by setting it to zero for stability. This improves repeatability after stops. [Elektroda, kotbury, post #16849721]

What is a limit switch and how does it affect slowdown?

A limit switch signals fully open or closed. After it activates, rA applies a short slow run, about a few centimeters, to finish smoothly. Set mechanical limits a bit early to account for this release distance. [Elektroda, kotbury, post #16849465]

Why did FSW CL light after I linked 4 to 7/8?

That link simulates a closed safety contact. If FSW CL lights, the control board and cabling back to the panel are intact. Faults then point to the photocell receiver, its relay, or the run between receiver and board. [Elektroda, sisko, post #20049655]

I only have remotes—how can I test closing without reprogramming?

Short terminals 1 and 7 to simulate the Open A command. If the gate closes after you’ve bypassed the photocells, the radio is fine. Restore normal wiring and consider adding a simple wall button for future tests. [Elektroda, zybex, post #16845501]

My receiver shows two LEDs—what do they indicate?

On many FAAC receivers, one LED shows power and a second shows beam alignment. When you block the beam, the alignment LED changes and you hear a relay click. If LEDs act right but FSW CL stays OFF, inspect wiring to the board. [Elektroda, kotbury, post #16849465]

What cable should I use for a push-button run?

Use small low-voltage cable; 2×0.5 mm² telephone cable works well for short indoor/outdoor runs. Keep joints dry and strain-relieved to avoid intermittent opens that mimic photocell faults. [Elektroda, zybex, post #16849439]
Generated by the language model.