    Hello,
    I have installed the tension of the FAAC 740 sliding gate,
    After moving the gate manually, the drive enters some strange mode in which it opens very slowly and closes.
    This is the case every time you manually move it.
    What to change in the options? What parameter is responsible for this?

    The second thing I noticed is the slow operation of the remote control, i.e. the gate closes only after the second press of the button.
    Can it be changed so that it closes when the button is pressed? Something wrong is connected NO, NC?

    Thank you
    Andrew
  • ADVERTISEMENT
  • Helpful post
    #2 16865096
    kotbury
    Gantry automation specialist
    Posts: 9540
    Help: 2094
    Rate: 3612
    What radio? If plugged in - there is no possibility of making a mistake, if on the cables - connecting the NC contact instead of NO (it should be NO, i.e. open at rest) may result in all the above symptoms ...
    As for free action - is the return to normal after some concrete action or after reaching the extreme gate? And are there any disturbing noises from the gear after activating the gate after locking the lock?

    Ps. The slow operation of the gate may be caused by a wrong gate time setting (parameter t - set a few seconds more than the actual gate stroke time) together with decelerations before the limit switches (rP parameter - if there is any - turn it off and replace with the slowdown after the limit switches - parameter rA)
  • ADVERTISEMENT
  • #3 16865324
    AndrzejF
    Level 13  
    Posts: 239
    Rate: 50
    FAAC 740 Operator: Slow Opening Post-Manual Movement & Remote Control Delay Issues FAAC 740 Operator: Slow Opening Post-Manual Movement & Remote Control Delay Issues FAAC 740 Operator: Slow Opening Post-Manual Movement & Remote Control Delay Issues FAAC 740 Operator: Slow Opening Post-Manual Movement & Remote Control Delay Issues FAAC 740 Operator: Slow Opening Post-Manual Movement & Remote Control Delay Issues
    kotbury wrote:
    What radio? If plugged in - there is no possibility of making a mistake, if on the cables - connecting the NC contact instead of NO (it should be NO, i.e. open at rest) may result in all the above symptoms ...
    As for free action - is the return to normal after some concrete action or after reaching the extreme gate? And are there any disturbing noises from the gear after activating the gate after locking the lock?

    Ps. The slow operation of the gate may be caused by a wrong gate time setting (parameter t - set a few seconds more than the actual gate stroke time) together with decelerations before the limit switches (rP parameter - if there is any - turn it off and replace with the slowdown after the limit switches - parameter rA)


    Plug-in radio. Just like in the pictures.
    Back to normal as the gate moves to the end - the extreme. Interestingly, if I stop the gate with the remote control in this "free" mode and press the closing / opening on the remote control again (depending on the state), the drive seems to have remembered where it was already normal and from there it works normally. It will go from extreme to extreme and it's OK.

    The drive is new. What noises do you mean?
    Because when it moves slowly, it looks as if the engine has no strength.
  • ADVERTISEMENT
  • #4 16865433
    suworow
    VIP Meritorious for electroda.pl
    Posts: 8802
    Help: 650
    Rate: 1276
    AndrzejF wrote:
    What to change in the options? What parameter is responsible for this?


    kotbury wrote:
    Ps. The slow operation of the gate may be caused by a wrong gate time setting (parameter t - set a few seconds more than the actual gate stroke time) together with decelerations before the limit switches (rP parameter - if there is any - turn it off and replace with the slowdown after the limit switches - parameter rA)

    And what?
  • ADVERTISEMENT
  • #5 16866221
    kotbury
    Gantry automation specialist
    Posts: 9540
    Help: 2094
    Rate: 3612
    For the sake of peace, disconnect the radio at all and test the gate by starting it with a short short circuit OPEN A (terminal 1) with negative (terminal 7). If the situation repeats, it means that the failure is in the switchboard itself, and since it is new, burying the electronics is not really an option ... So warranty or replacement ...
  • #6 16871362
    AndrzejF
    Level 13  
    Posts: 239
    Rate: 50
    Hello,
    after changing the parameters t, rP, rA as he took away with his hand, the gate moves as it should.
    Does anything else change in the parameters below?

    Basic
    - LO - AP
    - PA - 1,2 (this is how long the gate waits to close)
    - FO - 23 (do you set the force to the maximum here, a light gate is about 100 kg)
    - dl - E- (opens to the left)
    - ST - 00

    Advanced
    - because - no
    - br - 00
    - FS - no
    - SA - no
    - PF - no
    - SP - 00
    - Ph - no
    - oP - no
    - EC - 00
    - rP - 00
    - rA - 03
    - AFTER - 05
    - t - 22
    - AS - no
    - nc - 00


    Thank you very much for your help.