Understanding Insulation Voltage Markings: 300/300V, 300/500V, 450/750V, 600/1000V - U0/U Explained

golec2604 28620 28
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 16700922
    golec2604
    Level 16  
    Quote:

    Marking on the cable 300 / 300V, 300 / 500V, 450 / 750V, 600 / 1000V
    indicates the rated voltage (effective value) of the cable insulation
    was executed where (U0 / U)
    U0 - RMS voltage between any conductor and the "earth" or the cable shield
    U - RMS voltage between any two phase conductors (phase-to-phase voltage)
    For wires and cables up to 1kV we meet the following markings:

    - 01 - 100 / 100V

    - 03 - 300 / 300V

    - 05 - 300 / 500V

    - 07 - 450/750 V.

    - 11 - 600 / 1000V


    As I wrote above, in this way U0 / U are marked with insulation wires.
    I don't understand one thing about these markings. For example, take the 450 / 750V insulation marking, it says that the wire insulation is made for a single-phase voltage of 450V and a phase-to-phase voltage of 750V.
    If the wire insulation can withstand 750V phase-to-phase voltage, why should this insulation not withstand 750V single-phase voltage?
    After all, voltage is the difference in potential between two points, what's the difference if these points are "phase to neutral" and "phase to phase"? Can someone explain it ??
  • ADVERTISEMENT
  • Helpful post
    #2 16701069
    Anonymous
    Level 1  
  • #3 16708548
    golec2604
    Level 16  
    There is something wrong with your translation. First of all, the "neutral / zero" wire also has insulation. Secondly, as you say, 2 x 450V for one wire gives 900V for two wires, not 750V. Can someone explain how is it ??
  • #4 16708570
    Anonymous
    Level 1  
  • #5 16708587
    golec2604
    Level 16  
    1. Let's say that we have a 5-core cable and we have a three-phase voltage "so-called force", the insulation of each single wire (out of these 5 wires) between it and the external element is 450V, and between the two wires is 750V. I understand well ??

    2. I am very curious how it is that a single conductor insulation is 450V and when we consider two conductors where theoretically the insulation should be doubled, but it is much less, i.e. 750V?

    3. I am interested in 300 / 300V insulation, since single insulation can withstand 300V, why the increased insulation does not give increased strength, but 300V is further?

    =======
    I am asking for answers in points 1,2,3 and some human explanation.
  • #6 16708601
    Anonymous
    Level 1  
  • #7 16708647
    golec2604
    Level 16  
    Could you please answer the individual questions separately?
    Second, expand your "bad naming" thinking
    I looked at this link, but there are only cable markings. I do not know what you mean.
  • Helpful post
    #8 16708710
    Anonymous
    Level 1  
  • ADVERTISEMENT
  • #9 16708719
    elpapiotr
    Electrician specialist
    Kraniec_Internetów wrote:
    More precisely, it is 230 * the root of 3. The same in the wire - 450V is the phase insulation voltage, and the wire (i.e. phase-to-phase) voltage is 450V * square root of 3, which is exactly 750V .

    Really ?
  • #10 16708758
    Anonymous
    Level 1  
  • #11 16711191
    golec2604
    Level 16  
    Thanks to Kraniec_Internetów for a great explanation. I searched the Internet for such an answer for a long time before I asked the question here, but I did not find it.

    ========================
    I do not really understand the answer to the 3rd question because if the maximum interfacial voltage is 300V, where can you find such voltage?

    One more question has now arisen for me. Having a 5-core cable / wire, we can use it to release 3 phases, so the marking 450/750 is correct. But why use such a marking in a cable / 3-wire conductor where we can only release one phase, so the marking should be only 450V.
  • #12 16711202
    Anonymous
    Level 1  
  • #13 16711238
    golec2604
    Level 16  
    Quote:
    One more question has now arisen for me. Having a 5-core cable / wire, we can use it to release 3 phases, so the marking 450/750 is correct. But why use such a marking in a cable / 3-wire conductor where we can only release one phase, so the marking should be only 450V.

    I would like to ask you more.
  • #14 16711753
    .Jack
    Electrician specialist
    Quote:
    I would like to ask you more.

    Rather, it was written before:
    So one value relates to the insulation resistance to voltage between any conductor and the external insulation
    The second value relates to the insulation resistance to voltage between the two inner insulations and not the outer insulation.

    During normal operation of the electrical system, the voltage in the 1-f system does not exceed 250V. But please take into account the possibility of switching overvoltages or short-circuit conditions. The rated insulation of cables is also selected taking into account the external conditions occurring in a given location, and often in special locations and installations where the 700 series standards recommend the installation of cables with reinforced insulation. And then there is no discussion here anymore.
  • #15 16711883
    czesiu
    Level 37  
    And how to understand the two voltages in the marking of single-core cables, e.g. YKY 1x120 0.6 / 1kV?
    1kV applies to two cables lying next to each other? :)
  • ADVERTISEMENT
  • #16 16713143
    golec2604
    Level 16  
    I was thinking today and I still don't understand a certain thing. Having a multi-core cable / wire, e.g. with a rated insulation voltage of 450/750 V, informs us that the insulation of a single core was made for a phase voltage of 450 V. And the second value of the phase-to-phase voltage was calculated by multiplying 450 x sqrt (3) = 780 - manufacturers they take a value less than 750. Ok, almost clear about the markings. But there is one thing that I don't understand.
    Since each single wire has an insulation that can withstand the phase voltage of 450V, if we wanted to determine the strength of the phase-to-phase voltage between two wires in this cable, every logical person would say that it is 900V (because it consists of two identical insulations withstanding 450V)

    Calculating the inter-phase voltage based on the knowledge of the phase voltage and vice versa is not difficult because we will use the sqrt (3) converter. But here it is not about calculating the voltages, but about calculating the insulation resistance to the given voltage. So it is logical that by having two identical insulations and adding their values we will get a total.

    I don't understand why the producers mean 450/750 and not 450/900 ??
  • #17 16714431
    Wirnick
    Level 30  
    Or maybe on the other hand - what is the rated value? 450 - can be used in a 230V 1F installation with a safety factor of about two times, and 750 - 3F - also about two times. The manufacturer offers the product for use in domestic installations with a guarantee of resistance to voltage breakdown of the insulation. I'm just thinking.
  • #18 16714755
    Anonymous
    Level 1  
  • #19 16714783
    golec2604
    Level 16  
    Please reply to what I asked.
  • #20 16715027
    Krzysztof Reszka
    Moderator of Electrical engineering
    golec2604 wrote:
    I don't understand why the producers mean 450/750 and not 450/900 ??

    golec2604 wrote:
    tells you what rated voltage (effective value) wire insulation was made where (U0 / U)

    In the underlining, you have the answer why the producers write two voltages.
    Now read what is the RMS voltage.
  • ADVERTISEMENT
  • #21 16715093
    Darom
    Electrician specialist
    Krzysztof Reszka wrote:

    In the underlining, you have the answer why the producers write two voltages.
    Now read what is the RMS voltage.

    I must admit that as always I understand Col. Reszka, now what is he talking about with this effective value?
    I guess I'm sleepy ... :bye:
  • #22 16716210
    Krzysztof Reszka
    Moderator of Electrical engineering
    Darom wrote:
    I must admit that as always I understand Col. Reszka, now what is he talking about with this effective value?

    And what not to understand, an example.
    The maximum value of the residential voltage equals; rms voltage / square root of 2, i.e. 325 V.
    Manufacturers, writing 350 V on the cable, then meet the minimum requirements for a given cable, which was 325V.
  • #23 16716216
    Anonymous
    Level 1  
  • #24 16716277
    Krzysztof Reszka
    Moderator of Electrical engineering
    Kraniec_Internetów wrote:
    However, according to the PN-88 E-02000 standard:
    "In the international standard, it is recommended that the voltages at the point of energy supply during normal operation of the 50Hz alternating current network above 110 to 1000V should not differ by more than +/- 10%"

    The standard about supplied energy is for consumers and has nothing to do with the insulation parameters used by manufacturers.
  • #25 16716794
    Wirnick
    Level 30  
    golec2604 wrote:
    Please reply to what I asked.

    The 450/750 (rated values) information does not have to be satisfactory for you - use 0.6 / 1kV - "for exaggeration and swelling".
    In the final stage of production, multi-core cables usually undergo an insulation test with a voltage of 4kV (I am talking about their use in municipal installations). European regulations also apply to those conductors where the protective conductor is without insulation.
    Now another note - In any type of 3x400V network and installation, the phase voltage is not greater than 230V + -15% with respect to the protection voltage. So much for analysis for now.
  • #26 16750550
    golec2604
    Level 16  
    No offense, but when you read your statements, you write nonsense, you probably do not know what it is about.
    Mr. Krzysztof Reszka, I see that you are confusing. See the definitions:
    Quote:

    The marking on the cable 300 / 300V, 300 / 500V, 450 / 750V, 600 / 1000V indicates the rated voltage (effective value) of the cable insulation where (U0 / U)
    U0 - RMS voltage between any conductor and the "earth" or cable shield
    U - RMS voltage between any two phase conductors (phase-to-phase voltage)

    You see in the definition it says "rated voltage (RMS)". If you don't know, I'll explain what they mean:
    Rated voltage - Voltage rated value (nominal, normal, typical) - the value at which the device operates in accordance with the standards or manufacturer's recommendations. Exceeding this value causes incorrect operation of the device, changes in parameters or its damage.
    RMS value - it is the rms value of a periodically changing signal, examples of such value are typical voltage in an apartment / house 230 V for one phase and 400 V phase-to-phase.
    What you gave was the conversion of the effective (i.e. average) value into the maximum value. In the definition of insulation, he writes about the effective value (and not the maximum value) that the insulation must withstand.


    So taking the example of a wire with an insulation strength of 450/750 V - it tells us that it will withstand a voltage of 450 V single-phase effective voltage (and not the maximum one) between the conductor and the earth or screen, and that it will withstand an effective inter-phase voltage of 750V between any two phase cores.

    ================================================== ===========

    My question is still valid. Let us take into account the case of a wire with insulation at 450/750 V. Since the insulation of one core will withstand 450 V of effective voltage, then when we take into account two identical wires, i.e. a double increase in insulation, then there is also no double value of the insulation strength, i.e. 900 V, and there is 750V ??
    It is logical that 2 x 450 gives 900V, so where does the lower value come from, i.e. 750V ??
  • #27 16750754
    retrofood
    VIP Meritorious for electroda.pl
    golec2604 wrote:
    My question is still valid.

    Similar questions have already been asked on the forum many times. Each phase to N has 230 volts, and there is only 400 volts in between. Quackery! Producers of wires and cables cannot count, I do not even mention measuring. That's what! :D :D :D
  • #28 16750905
    Anonymous
    Level 1  
  • #29 16750934
    Krzysztof Reszka
    Moderator of Electrical engineering
    golec2604 wrote:
    It is logical that 2 x 450 gives 900V, so where does the lower value come from, i.e. 750V ??

    It is not logical, because it is the material used by the manufacturer that determines its use. Why does he write in the DTR to what voltage and what application it is intended for.
    And adding tensions to each other by keeping the veins together appears to be lacking in knowledge.
    An example of a cable that looks identical from the outside.
    Telefonica;
    Cables for industrial and agricultural workshop equipment, boilers, electric heaters,
    portable lamps, electric tools such as drills, circular saws, household electric tools, and also
    portable motors or machines on construction sites or on farms etc., also for permanent installation
    in temporary buildings and barracks for power. They are suitable for wiring components
    in lifting equipment, machines, etc. For use in dry, damp and wet rooms.
    Also for use at low temperatures in the open air for caravans, for heaters
    cars and camping. Use with voltages up to 1000V AC is allowed
    in fixed secured installations (in conduit or devices), as well as for motor connections
    cranes or the like
    H07BN4-F - cable made according to the harmonized standard (H), voltage 450 / 750V (07), on isolation from
    heat-resistant EPR rubber (B) and a heat-resistant EPR rubber coating (B
    ), with flexible veins (F)



    Cables intended for common use in households, kitchens, offices and households
    powering devices where the cables are exposed to small mechanical stress (e.g. kitchen appliances, flasks
    soldering irons, toasters) also for use at low temperatures. They are not suitable for continuous use on
    in the open air, in agricultural or industrial workshops and for powering portable tools except
    domestic
    H05BN4-F - cable made according to the harmonized standard (H), voltage 300 / 500V (05), on isolation from
    heat-resistant EPR rubber (B) and a coating of heat-resistant oil-resistant and flame retardant rubber (N4),

    with flexible conductors (F)

    We close the topic, it has been exhausted.

Topic summary

The discussion revolves around the understanding of insulation voltage markings for electrical wires, specifically the meanings of U0/U values such as 300/300V, 300/500V, 450/750V, and 600/1000V. Participants clarify that the first number (U0) indicates the maximum voltage between a single conductor and ground, while the second number (U) represents the maximum phase-to-phase voltage. The confusion arises from the assumption that if a wire can withstand 750V phase-to-phase, it should also handle 750V single-phase, which is not the case due to different insulation requirements. The conversation highlights the importance of insulation thickness and the standards that dictate these ratings, emphasizing that the rated voltages are based on specific testing conditions and safety factors. Additionally, the discussion touches on the implications of using these cables in various electrical systems, including single-phase and three-phase networks.