Can a 230V delta-connected motor be powered from a 400V network through an inverter, and what output voltage does the inverter generate?

No, a normal 400V-supplied inverter does not simply produce a 230V line-to-line output for a 230V delta motor. An inverter rectifies the supply to DC and then synthesizes AC again, so its motor output voltage is determined by the inverter settings and the U/f (V/f) curve, not by directly using the mains interphase voltage [#16788896] [#16786821] The replies say that the inverter input voltage must match the inverter design: many units are made either for 3x230V motors or for 3x400V motors, and you can enter the motor’s rated voltage in the menu [#16812518] For a 230V delta motor, the forum answer says it works only when the inverter is powered from 230 VAC; with a 400 VAC supply, you should not expect a safe 230V delta setup [#16790795] Lowering frequency lowers speed, and the inverter changes voltage together with frequency to keep the motor flux/current in range [#16786557] [#16786821]
AI summary based on the discussion. May contain errors.
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 16786486
    platinet64
    Level 5  
    Posts: 28
    Rate: 1
    Hello

    A 230V delta-connected motor powered by an inverter, I wonder what it is like because our network has 400V interphase, a little bit not for such a motor. What output voltages do inverters have ??? Will there be a phase voltage of 130V behind the inverter and 230V between the phases so that such a motor can work in a delta configuration ??? How does the inverter transform the voltages ??? I was looking for information on the Internet, but I can't find any information, please explain, thank you
  • ADVERTISEMENT
  • #2 16786557
    kosmos99
    Level 38  
    Posts: 4188
    Help: 338
    Rate: 820
    platinet64 wrote:
    delta-connected motor for 230V powered by an inverter, I wonder how it is because our network has 400V interphase, a bit not very suitable for such a motor.


    The inverter is reliably powered from one phase, i.e. 230V.

    platinet64 wrote:
    What output voltages do inverters have ??? Will there be a phase voltage of 130V behind the inverter and 230V between the phases so that such a motor can work in a delta configuration ???


    The inverter output voltage depends on the set frequency.
  • ADVERTISEMENT
  • #3 16786603
    Anonymous
    Level 1  
  • #4 16786821
    Darom
    Electrician specialist
    Posts: 2779
    Help: 231
    Rate: 588
    Hello
    The fact that inverters have a U / f strategy is obvious - it results from maintaining the correct flux.
    It seems to me that the author wants to answer the question about the rated supply voltage of the inverter and the rated voltage of the motor. My guess is that the device will be connected to a 3x400V installation (standard in Poland) and the motor itself has 230V windings.
    The author did not provide any data about the inverter. The inverter supply voltage (input voltage) must match the system voltage. As for the motor - most inverters (at least with which I have come across) have the option of entering the motor parameters, including the rated voltage.

    kisses
    - GIFT-
  • ADVERTISEMENT
  • #5 16786866
    Anonymous
    Level 1  
  • #6 16786881
    djlukas
    Level 27  
    Posts: 1606
    Help: 94
    Rate: 266
    Or maybe the 87Hz technique is used here?
  • #7 16787129
    platinet64
    Level 5  
    Posts: 28
    Rate: 1
    Lord Darom understood me more or less what was going on. Gentlemen, this is a topic as well as a more theoretical question, I want to understand the principle of operation of inverters. At 50Hz, could my motor work in a delta configuration like a 230V motor Triangle and our 400V interphase network, I have not read the answer if the inverter's (output) phase voltage would be, say, 130V, so that there was 230V between the phases so that this motor could the triangle work ??? is it as i understood my colleagues well about frequency regulation? well, what if I turn it up to 50 Hz will the voltage increase and I will not burn the engine ??? and even if I reduce the frequency, it will spin slower? Please explain the topic further ...
  • #8 16787194
    djlukas
    Level 27  
    Posts: 1606
    Help: 94
    Rate: 266
    If you set 230V 50Hz on the inverter in the motor parameters, the inverter will generate this much for this frequency.
  • Inverter input voltage is decoupled from motor supply

    #9 16788896
    Darom
    Electrician specialist
    Posts: 2779
    Help: 231
    Rate: 588
    Hello
    Although I started and programmed a couple of inverters, I do not feel like a specialist in this field. There are a few professionals on the forum who have proved that they know very well about inverters and drives, but as you can see, they are not always available. There are many pages that cover this topic in depth.
    In short, it looks like this:
    Understanding Inverter Output Voltages for 230V Delta-Connected Motor in a 400V Network

    You can see that the input (power) voltage of the inverter has little to do with the motor's supply voltage. Along the way, it is converted into direct current (DC) and back into alternating current (AC). The parameters of this alternating current result from the inverter settings and the signal controlling the rotation of the drive.
    You can learn more on the website:
    Link Building inverters

    kisses
    - GIFT-
  • #10 16790792
    platinet64
    Level 5  
    Posts: 28
    Rate: 1
    Thank you gentlemen.
  • ADVERTISEMENT
  • #11 16790795
    Krzysztof Kamienski
    Level 43  
    Posts: 21895
    Help: 2033
    Rate: 5167
    platinet64 wrote:
    Will there be a phase voltage of 130V behind the inverter and 230V between the phases so that such a motor can work in a delta configuration ???
    No. Only when the inverter is powered with 230 VAC, one or three-phase.
    kosmos99 wrote:
    The inverter output voltage depends on the set frequency.
    Yes, but not enough to make a delta connection of the motor.
    Kraniec_Internetów wrote:
    Which can be understood as the motor rated voltage is 230/400, so a delta connection would be dangerous.
    It is correct
    .
    djlukas wrote:
    If you set 230V 50Hz on the inverter in the motor parameters, the inverter will generate this much for this frequency.
    At 400 VAC power supply? Congratulations :D .
  • #12 16791757
    djlukas
    Level 27  
    Posts: 1606
    Help: 94
    Rate: 266
    Krzysztof Kamienski wrote:
    djlukas wrote:
    If you set 230V 50Hz on the inverter in the motor parameters, the inverter will generate this much for this frequency.
    At 400 VAC power supply? Congratulations

    Did your colleague hear about 87Hz?
  • #13 16802675
    jaro33
    Level 15  
    Posts: 100
    Help: 7
    Rate: 33
    And there are even inverters that do not have the correct voltage on the DC bus to get 400V for the motor.

    The 1-phase inverter with 230V voltage controls a 400V star-connected motor (400V) and has almost four hundred
    and it is true that such a situation should not be long-lasting because the motor and the inverter suffer.

    This is the reverse of your case.
  • #14 16802868
    Krzysztof Kamienski
    Level 43  
    Posts: 21895
    Help: 2033
    Rate: 5167
    @ jaro33 Have a colleague heard about inverters with voltage doublers? Very popular in the USA. Powered by 120 VAC, they drive the 3x 220VAC motor. So who is suffering here? :D
  • #15 16804738
    jaro33
    Level 15  
    Posts: 100
    Help: 7
    Rate: 33
    Krzysztof Kamienski wrote:
    @ jaro33 Have a colleague heard about inverters with voltage doublers? Very popular in the USA. Powered by 120 VAC, they drive the 3x 220VAC motor. So who is suffering here? :D


    I do not entirely agree.
    This is how the inverter has a system that allows you to power the motor with higher voltage.
    And I wrote that there are such solutions, but at the cost ... .. I can not even mention because I did not analyze this issue.
    But nothing is free in nature, and prices must be calculated. Only my opinion - maybe wrong.

    And besides, why inverters for 1-phase motors are much more expensive ???

    Quote:
    And there are even inverters that do not have the correct voltage on the DC bus to get 400V for the motor.

    Haven't read that anymore?

    Understanding Inverter Output Voltages for 230V Delta-Connected Motor in a 400V Network
    to compare

    Understanding Inverter Output Voltages for 230V Delta-Connected Motor in a 400V Network

    865 and 346 is a big difference
    https://www.sklepfaliczki.pl/faliczki-do-silnikow-1f.html
    Anything you can do is just another thing like economics.
  • Inverter motor voltage range can span 230V to 660V

    #16 16812518
    Darom
    Electrician specialist
    Posts: 2779
    Help: 231
    Rate: 588
    Hello
    Today I had the opportunity to correct the settings of inverters that were installed a year ago. Due to the amount of space, the designer assumed an increase in the efficiency of small fans by increasing the rotational speed.
    Understanding Inverter Output Voltages for 230V Delta-Connected Motor in a 400V Network
    For example - this inverter can be ordered as single-phase 230V or three-phase 3x400V.
    In the menu, I can choose a powered motor: 3 x 230V or 3 x 400V.
    I have come across inverters that have a much wider motor rated voltage, for example from 3x230V to 3x660V.

    kisses
    - GIFT-

Topic summary

LABEL_AI_GENERATED
The discussion revolves around the operation of a 230V delta-connected motor powered by an inverter in a 400V network. Participants clarify that the inverter's output voltage is adjustable based on the motor parameters set within the inverter, adhering to the U/f (voltage/frequency) principle to maintain proper motor flux. The inverter converts the input AC voltage to DC and then back to AC, allowing for the generation of the required output voltage for the motor. Concerns are raised about the compatibility of the motor's voltage ratings with the inverter's output, particularly regarding the phase voltage and the potential risks of connecting a 230V motor to a 400V supply. The conversation also touches on the use of inverters with voltage doublers and the implications of operating motors at different frequencies.
AI summary based on the discussion. May contain errors.

FAQ LABEL_AI_GENERATED

TL;DR: 3×400 V is standard in PL networks, and inverters follow "U/f = const" to keep motor flux right. Many drives let you enter a motor’s rated 230 V even on a 400 V input, but model limits apply. [Elektroda, Darom, post #16786821]

Why it matters: This FAQ helps electricians and hobbyists wire 230 V delta motors safely to 400 V systems using the right inverter settings and vocabulary.

Quick Facts

How does an inverter’s input relate to its motor output voltage?

The drive first rectifies the input to DC, then inverts it to variable AC. Because of this DC link, input voltage and motor voltage are not one-to-one. The motor’s voltage and frequency come from drive settings and the speed command, not directly from the mains. [Elektroda, Darom, post #16788896]

Can I run a 230 V delta motor from a 3×400 V supply using a VFD?

Often yes, if the VFD supports entering a 230 V rated motor and limits its output accordingly. Many drives allow selecting a 3×230 V motor profile even when the input is 3×400 V. Check the model’s motor voltage range before wiring. [Elektroda, Darom, post #16812518]

Is it safe to set 230 V, 50 Hz on a VFD that’s fed with 400 VAC?

Not always. Some drives cannot deliver a reduced 230 V line-to-line with a 400 VAC input. Treat a simple "set 230 V" on a 400 V–fed drive with caution unless the model explicitly supports it. [Elektroda, Krzysztof Kamienski, post #16790795]

What does U/f control mean in practice?

U/f control keeps the voltage-to-frequency ratio constant to maintain magnetic flux. As frequency rises, the drive raises voltage proportionally; as frequency falls, it reduces voltage to avoid overfluxing and excess current. "U/f = const." [Elektroda, Anonymous, post #16786603]

Will lowering frequency simply slow the motor?

Yes. The inverter’s frequency setpoint dictates motor speed, while voltage follows per settings. The drive synthesizes an AC waveform from the DC bus to match the requested speed and torque. [Elektroda, Darom, post #16788896]

What is the 87 Hz technique on VFDs?

It’s a setup where a motor intended for 400 V star is connected delta and driven up to about 87 Hz so the winding sees correct voltage per U/f. It extends the constant-power range when the drive supports it. [Elektroda, djlukas, post #16791757]

Can a 230/400 V nameplate motor be wired delta on 400 V directly?

No. A 230/400 V motor in delta expects 230 V line-to-line. Applying 400 V delta overvolts the windings and risks damage. Use a suitable VFD profile or change connection to star as appropriate. [Elektroda, Anonymous, post #16786866]

Do some single‑phase 230 V drives output near 400 V three‑phase?

Yes, there are cases where a 1‑phase 230 V–fed inverter runs a 400 V star motor, but it stresses the system if the DC bus is marginal. Treat this as a constraint case rather than normal operation. [Elektroda, jaro33, post #16802675]

What are voltage‑doubler VFDs and where are they used?

Some drives include voltage doublers that boost low mains (e.g., 120 VAC) to run 3×220 VAC motors. They are common in the USA and avoid external transformers. "Very popular in the USA." [Elektroda, Krzysztof Kamienski, post #16802868]

How do I configure a VFD for a 230 V motor on a 400 V system?

  1. In motor parameters, select a 3×230 V motor profile and enter nameplate data.
  2. Set base frequency to 50 Hz and confirm U/f curve matches the motor.
  3. Test no‑load, then tune ramps and protections. Many drives provide both 3×230 V and 3×400 V options. [Elektroda, Darom, post #16812518]

Does U/f control also help limit current at low frequency?

Yes. Reducing frequency lowers winding impedance; keeping U/f constant prevents overfluxing and excessive current. This is a key reason drives tie voltage to frequency in scalar control modes. [Elektroda, Anonymous, post #16786866]

What is the DC bus (link) inside a VFD?

It’s the internal DC stage after rectification. The inverter section chops this DC to create variable‑frequency, variable‑voltage AC for the motor. Because of this, the motor sees what the drive commands, not raw mains. [Elektroda, Darom, post #16788896]

Any real‑world example of selectable motor voltage in a VFD menu?

Yes. One cited drive can be ordered for 230 V or 3×400 V input, and its menu lets you choose a 3×230 V or 3×400 V motor. Enter the motor’s rated data during commissioning. [Elektroda, Darom, post #16812518]

What failure should I watch for with higher motor voltages?

Some inverters lack enough DC‑bus voltage to reach a true 400 V output. In that edge case, both motor and drive can run hot if pushed. Plan for the drive’s bus capability. [Elektroda, jaro33, post #16802675]

Is 3×400 V really the standard in Poland?

Yes. The thread explicitly states a 3×400 V installation is standard, which informs how users size and set their VFDs and motor connections. [Elektroda, Darom, post #16786821]
AI summary based on the discussion. May contain errors.
ADVERTISEMENT