[Solved] Vaillant Ecotec 186/3-5 Plus Condensing Boiler Hums During Operation - Solutions & Experiences

ptak01 9582 12
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 17054137
    ptak01
    Level 10  
    Has anyone encountered a boiler hum during boiler operation. I have a Vaillant Ecotec 186 / 3-5 Plus boiler and the boiler "hums" from time to time.

    During the service technician's visit, the problem did not occur, and the service technician stated that everything was fine, and the boiler hums from time to time (when the heating is turned on).
    After turning the boiler off and on again, in most cases the boiler does not hum, but after some time the problem returns.

    anyone have any ideas what it might be?

    Attached is a video with the sound of the boiler.


    [movie: 1ffc772742] https://filmy.elektroda.pl/32_1519239491.mp4 [/ movie: 1ffc772742]
  • ADVERTISEMENT
  • #3 17054864
    ls_77
    Level 37  
    You can remove the casing and put your hand on the pump. It will probably vibrate slightly. Either it is over or the debris has accumulated in it.
  • ADVERTISEMENT
  • #4 17055598
    Darek A.
    Level 20  
    Exactly, because in the gas boiler, apart from the pump, there are no mechanics that would emit a constant hum.
  • #5 17055629
    ls_77
    Level 37  
    Alternatively, the fan may also cause a hum, or more precisely, a muffler which draws air in.
  • #6 17056506
    ptak01
    Level 10  
    Darek A. wrote:
    Pump - bows.



    I was also thinking about the pump, but whether the pump should not make noise, regardless of whether hot water is being prepared or heating is working. Meanwhile (maybe it's a coincidence and a lack of careful observation), the hum only occurs when there is "active heating".
  • #7 17056568
    Darek A.
    Level 20  
    The pump circulates a closed circuit of water in the radiators so that they all heat up, hot tap water flows into the boiler fresh, which simply pushes it with pressure without the need for a pump :)
  • ADVERTISEMENT
  • #8 17057034
    mauri_b
    Heating systems specialist
    Darek A. wrote:
    The pump circulates a closed circuit of water in the radiators so that they all heat up, hot tap water flows into the boiler fresh, which simply pushes it with pressure without the need for a pump :)

    Go film man, don't spam.

    bird01, open the front cover and listen, for now it's reading coffee grounds.
  • #9 17057041
    ls_77
    Level 37  
    Darek A. wrote:
    hot tap water flows into the boiler with fresh water, which simply pushes it under pressure without the need for a pump :)

    With hot water, it is like you write, but to heat this water, the water circulating in the boiler in the so-called short circuit, i.e. the pump pushes the boiler water to the main exchanger where it receives heat from the burner and flue gas, and then pushes it to the secondary exchanger where it gives the heat to the incoming cold water (it can be a plate exchanger in a combi boiler or a coil in a DHW tank).
    Perhaps there are greater resistance in the central heating installation here and the pump is more difficult to push the water than in this short circuit to heat the hot utility water.
  • #10 17058407
    kz61
    Level 27  
    When there was a service technician, he probably removed the casing and nothing strange happened then. So the analyzer and checking what it sucks is one time, and the gas tightness check in the boiler (on the move) is two.
  • ADVERTISEMENT
  • #11 17060778
    ptak01
    Level 10  
    at the moment there is silence, I am waiting for symptoms to appear
  • #12 17583152
    nickiel
    Level 12  
    Buddy bird01 what came out with your boiler because mine started to rumble exactly the same ...
  • #13 17583846
    ptak01
    Level 10  
    nickiel wrote:
    Buddy bird01 what came out with your boiler because mine started to rumble exactly the same ...


    service diagnosis: pump to be replaced, but after replacing the pump, a symptom appeared after some time - and here the reason turned out to be clogged with stone "elbow 90 ° below the boiler.- and the pump had problems with pushing the water through.

    there was silence after cleaning the elbow,

    An interesting fact is that the filter on the boiler was clean ...

Topic summary

The discussion revolves around a humming noise experienced during the operation of a Vaillant Ecotec 186/3-5 Plus condensing boiler. Users suggest that the hum may originate from the pump, which can vibrate and cause noise, especially when the heating is active. Some responses indicate that debris accumulation in the pump or increased resistance in the central heating system could exacerbate the issue. Additionally, the fan or muffler may also contribute to the humming sound. A follow-up from the original poster reveals that after a service diagnosis, the pump was replaced, but the humming returned due to a clogged elbow fitting below the boiler. Cleaning the elbow resolved the noise issue temporarily.
Summary generated by the language model.