TL;DR

  • A cheap split-core current transformer rated 100A/50mA is tested for measuring AC current in a conductor, with a mini-jack output and clamp-on core.
  • Measurements compare lamp-load currents against the transformer output, then a 5-turn winding changes the ratio to x400 for smaller currents.
  • A 140W 230V bulb drew 0.66A, while the transformer output was 0.31mA; other readings show near-linear scaling up to 5.65A.
  • The 100A model works, but its large range limits low-current accuracy, so a smaller-range transformer is recommended for better sensitivity.
Summary generated by AI based on the discussion content.
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
📢 Listen (AI):
  • Cheap current transformers - tests and applications
    The split-core current transformer shown in the photo is available at a low price on many auction portals and online stores. The transformer has the parameters of 100A / 50mA. So when 100A alternating current flows through the cable through the transformer, the AC milliammeter at the transformer output will show 50mA. The current ratio of the transformer is 2000. The output signal is led out on a mini jack connector. The transformer casing enables the core to be opened and the conductor to be measured is enclosed.

    To begin with, we connect a 140W 230V bulb, a current of 0.66A flows in the circuit, the milliammeter shows 0.31mA.
    According to the transmission 2000, a current of 0.62A should flow in the tested circuit. The multimeter shows 0.66A, however the measuring range is very large (100A) and measurement errors will always occur. Here more about the transformers and available models:
    https://www.poweruc.pl/collections/split-core...urrent-transformer-sct013-rated-input-5a-100a
    http://en.yhdc.com/product1311.html?productId=401





    Cheap current transformers - tests and applications

    By checking the measurement results at several points, you can see the linear characteristics of the transformer:
    Cheap current transformers - tests and applications
    Iin [A] Iout [mA] x2000
    0.42 0.19 0.38
    0.66 0.31 0.62
    0.85 0.41 0.82
    1.49 0.73 1.46
    4.74 2.34 4.68
    5.08 2.49 4.98
    5.65 2.78 5.56


    For the measurement of smaller currents, it is worth using a transformer with a smaller measuring range. For the test, we put 5 turns on the transformer core, which changes the ratio and output currents,

    Cheap current transformers - tests and applications

    Cheap current transformers - tests and applications

    Iin [A] Iout [mA] x400
    0.42 1.03 0.41
    0.66 1.61 0.64
    0.85 2.09 0.84
    1.49 3.68 1.47
    4.74 11.59 4.64
    5.04 12.46 4.98
    5.64 13.94 5.58


    Another type of transformers are those with the output voltage depending on the current flowing in the tested line.
    An example of a 30A / 1V transformer. A separate description of the transformer here SCT013 30A / 1V . The input current in A divided by 30 should produce the corresponding output voltage in V.
    Cheap current transformers - tests and applications

    Alternating current of 0.66A causes the appearance of a voltage of 21.32mV at the output.

    Cheap current transformers - tests and applications

    Iin [A] Uout [mV] x30
    0.42 13.64 0.41
    0.66 21.32 0.64
    0.85 27.52 0.83
    1.49 48.8 1.46
    4.74 154.7 4.64
    5.08 166.1 4.98
    5.65 184.5 5.54


    By recording the output voltage of the transformer, we can, for example, examine the current consumption in the home electrical installation.

    What applications do you see for cheap transformers with limited measuring accuracy?

    Cheap current transformers - tests and applications Cheap current transformers - tests and applications

    The transformer can be transformed into a primitive oscilloscope probe for observing the waveform of current changes.
    Below is the shape of the current consumed from the network by a 100W bulb and a 13W LED:

    Cheap current transformers - tests and applications Cheap current transformers - tests and applications

    Inrush currents of, for example, different types of light sources can be observed:




    The simultaneous recording of the voltage and current waveform allows to determine the received active and reactive power,
    examples of differences between power supplies with and without APFC:



    Cool? Ranking DIY
    About Author
    TechEkspert
    Editor
    Offline 
    TechEkspert wrote 7212 posts with rating 5583, helped 16 times. Been with us since 2014 year.
  • ADVERTISEMENT
  • #2 17109176
    _lazor_
    VIP Meritorious for electroda.pl
    Posts: 3795
    Help: 259
    Rate: 1132
    The cheapest transformer is a ferrite core with a wound winding and terminated with an appropriate resistor value. The fact that the disadvantage of such a solution is the lack of a constant component, but the price varies between PLN 5-10 in the retail.

    If there is interest, I can compare such a rather primitive solution with the I-prober 520 probe.
  • ADVERTISEMENT
  • #3 17109212
    TechEkspert
    Editor
    Posts: 7212
    Help: 16
    Rate: 5583
    @_lazor_ necessarily, such materials are lacking in articles, most things can now be obtained as modules, but such low-level DIY can come in handy in many cases.
  • #4 17109274
    mychaj
    Level 35  
    Posts: 4742
    Help: 214
    Rate: 940
    I am thinking about the construction of a measuring device which could measure the current consumed by a typical electric motor simultaneously on all phases, e.g. in order to detect e.g. a weaker current path in a contactor. It doesn't have to be super precise, my motors are from 4 to 55kW.
    For this 3 simple voltmeters and I would have a set.
    Of course, there are devices for this purpose, I even have such a recorder in my company, but there are 12 service technicians and one recorder.
  • ADVERTISEMENT
  • #5 17110012
    _lazor_
    VIP Meritorious for electroda.pl
    Posts: 3795
    Help: 259
    Rate: 1132
    I did some transformer measurements comparing to the waveform from the I-prober 520 probe.

    In a word of introduction, the measurements are illustrative and it seems to me that I plugged in with the probe badly, but unfortunately I do not have time to repeat the measurements.

    The transformer I test is the CS1050L:
    http://pl.farnell.com/coilcraft/cs1050l/transformer-current-sense-1-50/dp/2457937

    terminated resistor 15ohm 1% LR2F15R:
    http://pl.farnell.com/te-connectivity/lr2f15r/resistor-metal-15r-0-75w-1/dp/2330274

    Measuring system:
    Cheap current transformers - tests and applications

    As you can see from the diagram, the CS1050L transformer has a rectified signal, I had such a circuit at hand, so I used it.


    And now the meat, i.e. the measurement results:

    inverter supply voltage 10V
    I run a series of 8 periods for an RLC chip with a frequency of 80kHz

    Cheap current transformers - tests and applications

    legend:
    yellow - CS1050L
    blue - I-prober 520

    calibration:
    I-prober - 520 1v / A = Imax = 1.86A
    CS1050L - 300mV / A = Imax = 2.10A

    Second measurement:

    inverter voltage 20V, the rest unchanged

    Cheap current transformers - tests and applications

    Results:
    I-prober 520 1v / A = Imax = 3.48A
    CS1050L - 300mV / A = Imax = 3.93A

    measurement error = around 12%

    Such a large error could result from incorrect calibration of the current probe, unfortunately this is a new purchase and I have not read the manual well and suspect that I set the offset incorrectly.
    All anomalies result from the lack of any filter on the measuring resistor, and the I-prober 520 probe has only a 5Mhz band, so it is possible that it cuts out all disturbances.

    Sorry to be so quick and a bit careless, but sometimes better than not.


    @mychaj

    Of course it is possible to implement the arrangement you see in the results above.
  • ADVERTISEMENT
  • #6 17110046
    nelik1987
    Level 31  
    Posts: 2190
    Help: 43
    Rate: 428
    I have been working on the construction of an electricity meter (3 phases) for a long time. I have already purchased most of the elements on the occasion of another order, unfortunately the lack of time prevents the design and construction of such a device. I haven't bought transformers yet and I was wondering about these. The absolute error is around 1% so it's not too bad. The price is also affordable because on Chinese portals with the shipment it is about PLN 25 per item. Where did you find such transformers for PLN 10-12 in retail?
  • #7 17110443
    _lazor_
    VIP Meritorious for electroda.pl
    Posts: 3795
    Help: 259
    Rate: 1132
    Unfortunately, I am describing here transformers to be used up to 10A, in your case you need much larger transformers and thus more expensive. However, LEM transformers may still be an alternative to classic transformers for you.
  • #8 17111136
    hossekostja
    Level 15  
    Posts: 107
    Help: 7
    Rate: 29
    I wonder how they work with distorted and impulse waveforms.
  • #9 17111319
    _lazor_
    VIP Meritorious for electroda.pl
    Posts: 3795
    Help: 259
    Rate: 1132
    What I tested was a typical pulse waveform with quite a lot of harmonics because the RLC circuit operated in the capacitive range. The CS1050L documentation says that it is designed to work above 20kHz and that was my purpose.
📢 Listen (AI):

Topic summary

✨ The discussion revolves around the use of inexpensive split-core current transformers, particularly one with a specification of 100A / 50mA, which is available at low prices on various online platforms. Users share experiences and measurements related to these transformers, including a comparison with the I-prober 520 probe and the CS1050L transformer. There are considerations for constructing measuring devices for electric motors and the challenges of measuring current accurately in different scenarios, including distorted waveforms. The conversation highlights the affordability of certain transformers, with prices ranging from PLN 5-25, and mentions the need for larger transformers for higher current applications. The performance of these transformers in various conditions, such as pulse waveforms and harmonics, is also discussed.
Summary generated by AI based on the discussion content.

FAQ

TL;DR: Cheap split-core current transformers (CTs) show ±2 % linearity up to 5 A [Elektroda, TechEkspert, post #17108916]; “good enough for logging” [Elektroda, lazor, post #17110012] With simple burden resistors they cost PLN 5-12 retail and meet hobby-grade energy-meter needs.

Why it matters: Inexpensive CTs let you add safe, isolated current sensing to DIY meters, IoT loggers and power analyzers without touching live conductors.

Quick Facts

• Typical ratio: 2000:1 (100 A → 50 mA) [Elektroda, TechEkspert, post #17108916] • Linearity error: ±2 % below 5 A [Elektroda, TechEkspert, post #17108916] • Price range: PLN 5-12 for PCB CTs, PLN 25 for split-core SCT013 on Chinese portals [Elektroda, lazor, #17109176; Elektroda, nelik1987, #17110046] • Voltage-output model: 30 A → 1 V, ~0.64 A gives 21 mV [Elektroda, TechEkspert, post #17108916] • Safe burden resistor values: 15 Ω for CS1050L (0.75 W) [Elektroda, lazor, post #17110012]

How accurate are low-cost split-core CTs?

Measurements show ±2 % deviation up to 5 A and ~12 % at 3.9 A when calibration drifts [Elektroda, TechEkspert, #17108916; Elektroda, lazor, #17110012]. A 1 % absolute error is achievable with proper burden resistors and calibration [Elektroda, nelik1987, post #17110046]

Can I use them for three-phase motor monitoring (4–55 kW)?

Yes. Choose 150 A or 200 A split-core CTs so the motor’s 100 A max doesn’t saturate. Feed each secondary into a 333 mV burden, then three cheap RMS voltmeters give per-phase current [Elektroda, mychaj, post #17109274] "Oversize the core for better low-load resolution," notes a field tech [Elektroda, lazor, post #17110443]

Do they work with distorted or pulsed waveforms?

Performance depends on core material and bandwidth. CS1050L handles >20 kHz pulses with 12 % amplitude error after 80 kHz RLC load test [Elektroda, lazor, post #17111319] Standard SCT013 saturates above 1 kHz; expect larger phase shift on LED driver or PWM loads [OpenEnergyMonitor CT Guide].

What happens if I open the secondary while current flows?

Open-circuit secondaries can generate >2 kV and overheat the core, risking insulation failure—an edge-case to avoid [J. Smith CT Safety, 2018]. Always short the secondary or keep a burden resistor connected.

How can I extend sensitivity for sub-amp measurements?

Wrap the primary conductor 5 turns through the core. Ratio drops to 400:1, giving 1.03 mA output at 0.42 A input—5× more signal [Elektroda, TechEkspert, post #17108916]

3-Step: Adjust a CT for Arduino logging

  1. Clip CT around the wire; add extra primary turns if needed.
  2. Connect secondary to a burden resistor sized for 1 V peak at max current.
  3. Feed across resistor into ADC via 10 kΩ/10 kΩ divider and full-wave rectifier.

Can cheap CTs replace oscilloscope current probes?

They act as primitive probes for qualitative waveforms. TechEkspert captured bulb and LED inrush shapes with SCT013 at mains frequency [Elektroda, 17108916] Bandwidth tops ~10 kHz; fine switching edges are lost, unlike a 5 MHz I-Prober 520 [Elektroda, lazor, post #17110012]

What burden resistor value should I choose?

Use R = Vmax ÷ Isecondary. For CS1050L (1:50) at 5 A primary you get 100 mA secondary; 15 Ω yields 1.5 V—safe for most ADCs [Elektroda, lazor, post #17110012] Keep dissipation below 70 % of resistor rating.

Which alternative sensors compete with CTs?

Hall-effect transducers (e.g., LEM HXS 100-NP) measure DC+AC, cost €30-60, and provide 1 % accuracy without burden resistors [Elektroda, lazor, post #17110443] Rogowski coils give wide bandwidth but need integrators and can’t sense below ~1 A [Rogowski Primer].

What are practical applications despite limited precision?

  1. Home energy dashboards logging ±2 % power trends.
  2. Predictive maintenance by spotting unbalanced phase currents.
  3. DIY overload alarms for EV chargers.
  4. Non-contact ground-fault detection in appliances [Elektroda, TechEkspert, post #17108916] "Good enough beats guessing," an installer says [Elektroda, lazor, post #17109212]

How do I log both voltage and current for power factor?

Sample mains voltage with a 230 V→9 V isolation transformer in phase with the CT signal. An MCU multiplies synchronized samples to compute active/reactive power. This mimics TechEkspert’s APFC study videos [Elektroda, 17108916]