logo elektroda
logo elektroda
X
logo elektroda

Norax 3 Photovoltaics: Is 3kW Installation & Energy Meter Suitable for Donated Energy?

klexus 71970 51
Best answers LABEL_AI_GENERATED

Does a Norax 3 meter measure energy fed back to the grid from my 3 kW photovoltaic installation?

Yes—if the Norax 3 is configured as a two-way meter, it measures exported energy as well, and the export register is 2.8.0 while 1.8.0 is imported energy [#17170751] [#18584945] [#21043653] In some cases the meter can be programmed as one-way, so exported PV energy may then be counted as consumption instead of being shown separately [#17170751] [#21043712] [#21046022] The practical check is to compare the OBIS registers: 1.8.0 for import, 2.8.0 for export, and 15.8.0 for total energy counted in both directions [#18584945] [#21043712] So the answer depends on how your particular meter was programmed and what the operator reads for settlement [#21043541] [#21046022]
AI summary based on the discussion. May contain errors.
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #31 18634570
    rsv6
    Level 13  
    Posts: 1713
    Rate: 284
    Rather, you will pay a fine when they see that you give energy without permission and you will not feel like whole panels .. The more that everything is visible in this meter.
  • ADVERTISEMENT
  • #32 18634595
    czaczus22
    Level 12  
    Posts: 61
    Rate: 25
    shrek565 wrote:
    czaczus22 wrote:
    At the G11 tariff
    1.8.0 the amount you have downloaded from the PGE network
    2.8.0 amount of energy transferred to PGE

    From the count of 2.8.0 you subtract 20% for PGE.
    Then it comes out how much energy you have clean.
    From the production of energy, you subtract the consumption of 1.8.0 and you get how much energy you have to collect in the winter.
    Until puk you do not have a contract for prosumers, you pay according to the old contract. Only after signing a new contract, for example, the overpayment is returned.


    Well, it is obvious to me.
    So if I do not have a contract, I can use the FV and what I give to the network will be lost at most, but I will be a plus from what I will produce and use during the day for my own use until I sign the contract?


    You will not lose the kilowatts you produce.

    Because later you can pick them up in the winter, but 20 less.
    I currently have an old contract, I do not have a new contract because of the virus, everything is sluggish.
    Although I have a new meter, I have to pay forecast invoices for the disassembled meter.
    I called PGE, asked what and how.
    I have to wait for the new contract, then I will get the settlement of the old meter ..
    Until a new contract is signed, the old one is valid.

    Added after 8 [minutes]:

    If photovoltaic installation is reported to PGE,
    and there is a 2-way meter, you can easily produce electricity.
  • #33 18634627
    shrek565
    Level 9  
    Posts: 9
    Rate: 11
    I have an energe at the moment
    I'm already crazy myself and I don't know what to do

    Installation reported from two weeks ago.
    And from the very beginning as I live the counter in the box outside is the same bidirectional object.
    I don't know whether to wait for them to come and replace them or what to do ....
  • #34 18634681
    czaczus22
    Level 12  
    Posts: 61
    Rate: 25
    [quote = "shrek565"] I have one at energe
    I'm already crazy myself and I don't know what to do

    Installation reported from two weeks ago.
    And from the very beginning as I live the counter in the box outside is the same bidirectional object.
    I don't know whether to wait for them to come and replace them or what to do .... [/ quote

    You may have 2-way, but it's probably only programmed for 1-way
    and then your inverter will count as receiver and not manufacturer.

    In my case, when I called asking when the new meter will be, PGE has a month to change or reprogram the meter.
  • #35 18634706
    shrek565
    Level 9  
    Posts: 9
    Rate: 11
    Well just no. The counter counts in both directions. Does not add 1.8.0 to obis
    I explained everything earlier in the post


    shrek565 wrote:
    I have the same problem and I don't know what to do.
    When starting the installation, the counter at position 1.8.0. if 1.8.1 (3866.3) stops punching despite running washing machine, heat pump and dishwasher.
    At position 2.8.0 or 2.8.1, he starts punching the kilowatts supplied to the net (11.5).
    And in item 1.5.8.0 it sums up the energy taken from the grid plus the energy given to the grid (3,877.8).
    With Energi there is still no message that the received instance, although everything works as if the meter was already reprogrammed to receive energy. I'm in despair too, and I don't know whether to run or not .......
    I have real settlements turned on and I always enter the status on the page from 1.8.0, which means that it would not reach this status ...
    below photos

    Norax 3 Photovoltaics: Is 3kW Installation & Energy Meter Suitable for Donated Energy? Norax 3 Photovoltaics: Is 3kW Installation & Energy Meter Suitable for Donated Energy? Norax 3 Photovoltaics: Is 3kW Installation & Energy Meter Suitable for Donated Energy?




    piwalek77 wrote:
    Hello,
    Today the installation of PV on my roof has been completed. The application to the ZE will be next week, and they are supposed to have a month to respond ... In addition, with the current development of the coronavirus, it may be even longer! Therefore, I feel sorry for the installation, which has to wait so long for it to start working on itself ...

    And here I have a question about the meter and its settings - it turns out that I already have a two-way meter (Norax3) installed, so theoretically I could return energy to the ZE right away. Of course, I will not be able to settle any surpluses until the contract is signed, but maybe at least I can use the generated energy on an ongoing basis? On the other hand, I am worried if the switched on installation will have the opposite effect - and it will not start to "punch" the meter ...

    So I did a little test and checked the OBIS codes:
    1.8.0 Imported active energy A +, sum => 21536
    2.8.0 Exported active energy A-, sum => 4
    15.8.0 Imported active energy | A |, sum => 21540

    So it looks like everything is working fine, but now I don't know if:
    - 2.8.0 shows the surplus itself or the total energy given away (everything I produced)?
    - what is the absolute reading 15.8.0 used for? - i.e.
    - what is the risk of leaving the installation on?

    My question boils down to the following example:
    If I use 5kW at a given moment and at the same time give away (produce) 2kW - will the reading of the consumed energy (1.8.0) be 5kWh or 3kWh?

    Best regards!
  • #36 18634774
    czaczus22
    Level 12  
    Posts: 61
    Rate: 25
    Norax 3 Photovoltaics: Is 3kW Installation & Energy Meter Suitable for Donated Energy? Norax 3 Photovoltaics: Is 3kW Installation & Energy Meter Suitable for Donated Energy? From what I see, it is a 1-way counter and it must be replaced.

    These photos, what I put in, is a 2-way counter.
  • ADVERTISEMENT
  • #37 18635141
    janekk77
    Level 9  
    Posts: 29
    Help: 1
    Rate: 3
    czaczus22 wrote:
    These photos, what I put in, is a 2-way counter.

    I have the one from the first photo and unfortunately it is unidirectional. In total, it shows the direction of energy (transferred-consumed), but still counts to the input. So it probably all depends on how they program it.
  • ADVERTISEMENT
  • #38 18635204
    derekk
    Level 12  
    Posts: 17
    Rate: 5
    Unfortunately, the Corax 3, despite being bidirectional, is not suitable for PV. This is the position of PGE (I talked about) now they assume a new one with the module. As for this super-intelligent meter that counts direct consumption, I had a conversation with Apator's service (producer) and they said that it counts "absolute value" or something like that and the meter will not stand still when the panels are working. Maybe it's programmed that. Starting PV installations is pointless because I gain nothing and the energy company earns. All that's left is to wait for the favor of PGE.
  • #39 18640268
    shrek565
    Level 9  
    Posts: 9
    Rate: 11
    Somehow it worked after acquaintance and after 5 days they set up a counter. In fact, they dismantled it and it's new. Do I have to arrange any papers now with the operator? Norax 3 Photovoltaics: Is 3kW Installation & Energy Meter Suitable for Donated Energy?
  • #40 18640306
    3301
    Level 34  
    Posts: 2100
    Help: 224
    Rate: 869
    If it is OSD Tauron, it is nothing to use, only ask for a certificate of assembly, needed for the application "my current"
  • #41 18640333
    slaslo
    Level 18  
    Posts: 185
    Help: 24
    Rate: 56
    After all, you can see the Energa Operator sticker in the photo.
  • #42 18663800
    Wbm
    Level 12  
    Posts: 34
    Rate: 7
    czaczus22 wrote:
    derekk wrote:
    Hello.
    At PGE, I have a Corax 3 meter and I am waiting for a replacement due to the installation of PV panels. They should replace 04/04/2020 but the meter is in the room so they won't come and I can jump them. I wanted to use the installation without overproducing energy only for direct consumption, this is allowed by the Fronius inverter. Unfortunately, this meter is super intelligent and, despite the lack of overproduction, it counts direct consumption as if I were downloading from the network. How is it possible ??



    The panels must not be operated without a bidirectional counter
    Normal PGE meter It treats the solar inverter as a load and not as an electricity producer.


    Well, see, and my three-phase C52z from PAFAL before the replacement did not want to treat the inverter as a receiver if you know what I mean ;-)
    But that's right, it's not worth putting your PV plant in operation before replacing the meter.


    greeting
    -
    Wbm.
  • #43 18769942
    and_you
    Level 12  
    Posts: 40
    Rate: 7
    Hello
    I have NORAX 3 and I'm not complaining, it measures in both directions rather correctly. [G12 tariff]
    It was replaced a year before the PV, but after the installation was installed, they came and reprogrammed it. [I stayed at the G12]
    These meters count internally and record data in both directions, but may possibly add up the energy input as consumed before being reprogrammed. I heard that some of them had reprogrammed values on the energy abacus.
    It seems to me that the counter is ok - maybe there is still a question of what operator will program it.

    Codes
    Downloaded: SUM- 1.8.0, WT- 1.8.1, NT- 1.8.2
    Given: SUM- 2.8.0, WT- 2.8.1, NT- 2.8.2
    Instantaneous charged 1.7.0
    Instantaneous delivery 2.7.0
    Max absorbed power 1.6.0
    Max output power 2.6.0
    It shows the voltages and amps on each phase.

    For me, there is interfacial - vector balancing, so what to pick on. The only thing that may not be counted so precisely (but apparently all of them do) - rather to the disadvantage of the consumer ... yes from my observations - but probably within the error - only always in their favor hehe. (e.g. with 5kW output, it can lose about 100W - either I have losses somewhere, or the inverter shows the 100W more)
    [that is, the inverter shows 5000W and the meter shows ~~ 4900W - a questionable matter or a measurement error] - these are my observations.

    What is the new OTUS3 - hmmmm - I have mixed feelings - remote reading is not everything ... because it has, for example:
    - Built-in contactor that allows remote disconnection / switching current circuits
    - Power limiter with local control or DSM / DSR signals
    - Remote replacement of non-measurement software

    What can they use it for? - I think they have some plan for it.
    I do not mind the collector every six months - only that they probably want to take readings and control very often - how much do you do when, how much do you use, what power you take at given moments. It's ok for now, but who knows what will happen in some time, if everything will be under control.

    I can be wrong on some things - but these are just my feelings.
    I greet everyone
  • Terminal box cover open alarm on Norax 3 meter

    #44 19390024
    bartekfigura
    Level 30  
    Posts: 1294
    Help: 112
    Rate: 523
    czaczus22 wrote:
    Hello. I have an exclamation mark in a triangle, in the Norax 3 bidirectional counter, what? He marks. Nowhere to find this marking, what kind of error it is.

    This is the terminal box cover open alarm. This means that the cover was opened since the last deletion or it does not fit well and jumped off itself (there is a pin that should fit well when it stretches somewhere, then it is like that later). In fact, the installer should check it before closing the replacement order.

    Added after 3 [minutes]:

    and_you wrote:
    What is the new OTUS3 - hmmmm - I have mixed feelings - remote reading is not everything ... because it has, for example:
    - Built-in contactor allowing for remote disconnection / connection of current paths
    - Power limiter with local control or DSM / DSR signals
    - Remote replacement of non-measurement software

    The built-in contactor is for remote disconnection if you do not pay the invoice.
    The power limiter is to block you from getting more power than contractual
    Remote software replacement is simply an update of the OTUS 3 meter software, it is such a small computer that has great possibilities.
  • Norax 3 meter shows 32 kWh exported

    #45 20714827
    lampowiec
    Level 14  
    Posts: 185
    Help: 4
    Rate: 221
    Good morning!
    Well, now I think I'm going to bend everyone's mind...
    Hybrid photovoltaic installation, power source switches, 100% inverter output not connected to the grid.

    The Apator Norax 3 - 2.8.0. meter indicates 32 kWh of energy given up - unfortunately I don't know if this has changed since the installation was installed, I just checked it now.

    Is everything according to you correct?

    Greetings,
    Damian
  • #46 21038444
    bakupl
    Level 12  
    Posts: 43
    Rate: 3

    Most of the information and posts are from the times of net-metering.

    The question is as follows - how can I most assuredly check whether the Norax 3 counter has been programmed correctly for bidirectionality?
    I.e. - what is the best way to check (switching off power receivers is not an option) whether the power output from photovoltaics is not counted as consumption?
  • #47 21043541
    bartekfigura
    Level 30  
    Posts: 1294
    Help: 112
    Rate: 523
    This counter is not programmed for bi-directionality - by default, it is manufactured in such a way that it can count supply and consumption. It all depends on which registers are read by the collector and settled by the DSO.
  • Norax 3 lacks 2.8.0 export reading support

    #48 21043653
    michalPV
    Level 31  
    Posts: 2311
    Help: 96
    Rate: 723
    bakupl wrote:
    I.e. - what is the best way to check (switching off power receivers is not an option) whether the power output from photovoltaics is not counted as consumption?

    1.8.0 active energy consumed
    2.8.0 active energy released

    If you don`t have 2.8.0, it means that donating counts as conscription.

    I had NORAX 3 and a test run on-grid: the transfer was counted as a consumption. I did not have the 2.8.0 code on the display

    After reporting the micro-installation to Tauron, I had the meter replaced with one with a SIM card.
    Norax 3 doesn`t seem to have remote reading capabilities.
  • Check Norax 3 bidirectional registers 1.8.0, 2.8.0, 15.8.0

    #49 21043712
    k_pec
    Level 34  
    Posts: 1772
    Help: 271
    Rate: 562
    bakupl wrote:
    The question is as follows - how can I most definitely check the correct programming of the Norax 3 meter for bidirectionality? That is, what is the best way to check (switching off power consumers is not an option) whether the power output from photovoltaics is not charged as a consumption?

    Check and compare registers:
    • 15.8.0 - total power counted by the counter (in both directions)
      1.8.0
      2.8.0
  • #50 21046022
    bakupl
    Level 12  
    Posts: 43
    Rate: 3

    There are registers 2.8.0 and they are counted.
    Production is not included until 1.8.0

    15.8.0 - is the sum - and that's how it should be, but the clue is here: It depends on which registers are read.
    I think someone knows that it is supposed to read 1.8.0.

    Despite this, the installation is disabled for fear of being penalized.

    That's right - Norax 3 does not have a remote reading option
  • Use net metering and register the installation

    #51 21062501
    cdtdsilva
    Level 11  
    Posts: 173
    Help: 4
    Rate: 15
    Most meters have the capability of measuring power on both directions. But unless specifically programmed for that purpose, they will measure everything as consumption.

    You can measure that. Run your solar for one hour with everything off and see what register on the meter change. That simple.

    Also, unless you have a solar array capable of feeding your loads 100% of the time, you probably want to take advantage of netmetering. Under netmetering the supplier calculates how much was exported and imported and bills the difference. In Poland a period of one hour is used. The meter is still measuring consumption and export - These calculations are conducted by tauron and they require a suitable meter that provides remote readings with time stamps. The supplier will then make an adjustmet, which is on your favour.

    In Summary, unless you want to go off-grid get someone to sign the papers and register the instalation. The network operator will then change your meter and you'll have everything registered and legal.
  • ADVERTISEMENT
  • #52 21062634
    studniarz
    Level 20  
    Posts: 338
    Help: 23
    Rate: 179
    bakupl wrote:
    That's right - Norax 3 doesn't have a remote read option

    Is a colleague sure about this word -.-- " agrees "?
    I have had this meter since 2020 and never in 4 years has there been a collector or anyone from PGE.... AND I can download from the PGE website my data every 5 minutes...
    Interesting....

    Electricity meter with a display showing 1086.5 kWh consumption. .

Topic summary

LABEL_AI_GENERATED
The discussion revolves around the suitability of the Norax 3 energy meter for measuring energy produced by a 3kW photovoltaic installation, particularly in the context of energy donation to the grid. Users confirm that the Norax 3 is a bidirectional meter capable of measuring both energy consumption and energy exported to the grid. However, concerns are raised regarding its programming, as some users report that the meter may not accurately reflect energy exported if not properly configured. The importance of notifying the grid operator about the photovoltaic installation is emphasized, as it may affect the meter's functionality and the user's ability to benefit from net metering. Additionally, users share experiences with different energy companies and the challenges of accessing remote readings and data from the meter.
AI summary based on the discussion. May contain errors.

FAQ LABEL_AI_GENERATED

TL;DR: A correctly-programmed Norax 3 shows export on register 2.8.0; values above 0.5 kWh h⁻¹ confirm bidirectionality. “If you don’t see 2.8.x, the meter adds export to import” [Elektroda, michalPV, post #21043653] Why it matters: mis-programming can inflate your bill by up to 20 % every billing cycle.

Quick Facts

• Accuracy class: 1 % (active energy) [Apator Norax 3 Datasheet]. • Max current: 5–100 A, 3-phase, 4-wire [Apator Norax 3 Datasheet]. • Key registers: 1.8.x import, 2.8.x export, 15.8.0 absolute sum [Elektroda, 3301, post #17916012] • Typical prosumer write-off: 20 % of exported kWh in net-metering ≤10 kW [Energy Act, Art.4g]. • Remote reading only in GSM/GPRS variant OTUS 3; base Norax 3 lacks this module [Elektroda, michalPV, post #21043653]

How do I confirm my Norax 3 is counting export separately?

Compare 1.8.0 and 2.8.0 over one sunny hour. A rise only in 2.8.0 means proper bidirectionality; a rise in 1.8.0 means mis-programming [Elektroda, bakupl, post #21046022]

Which OBIS codes matter for a G11/G12 prosumer?

1.8.0 (total import), 1.8.1/1.8.2 (WT/NT import), 2.8.0 (total export), 2.8.1/2.8.2 (WT/NT export), and 15.8.0 (absolute energy) [Elektroda, Viszna, post #18457049]

What if only 1.8.x is visible and 2.8.x is missing?

Exported energy will add to 1.8.0, inflating consumption. Request re-programming or meter swap; one user saw this on an un-reprogrammed unit [Elektroda, janekk77, post #18635141]

Can Norax 3 balance energy between phases?

Yes, vector (inter-phase) balancing is supported; 5 kW export on L1 can offset 5 kW import on L2 within the meter’s algorithm [Elektroda, and_you, post #18769942]

Is Internet monitoring possible with Norax 3?

Only the GPRS-equipped OTUS/Norax variant supports remote reading; the standard Norax 3 lacks that modem, so operators send collectors or manual uploads [Elektroda, marcinbbb, post #18265303]

Will turning on PV before signing the prosumer contract cause penalties?

Yes. Feeding the grid without an annex can trigger fines; operators see uncontracted export in 2.8.0 [Elektroda, rsv6, post #18634570]

How does the 20 % write-off work in Polish net-metering?

For ≤10 kW systems, you receive 0.8 kWh credit per 1 kWh exported; larger systems get 0.7 kWh. That deduction appears on your settlement, not on the meter itself [Energy Act, Art.4g].

What is 15.8.0 and why is it higher than 1.8.0?

15.8.0 records absolute energy flow (|import|+|export|). It will always exceed or equal 1.8.0 because it adds both directions [Elektroda, piwalek77, post #18584945]

Edge case: Can the meter count PV generation as consumption even with 2.8.0 present?

If programmed for “absolute” billing, the DSO may read 15.8.0 instead of 1.8.0, charging you for both flows; one user reported this mis-billing risk [Elektroda, theo33, post #18634346]

How do I run a quick three-step test of meter direction?

  1. Write down 1.8.0, 2.8.0. 2. Disconnect house loads (leave inverter on). 3. After 10 minutes, only 2.8.0 should rise. If 1.8.0 rises, call your DSO for re-programming [Elektroda, cdtdsilva, post #21062501]

What is the maximum current Norax 3 can handle?

The meter is rated for 5–100 A per phase, class 1 accuracy [Apator Norax 3 Datasheet].

Does Norax 3 support remote disconnection?

Only OTUS 3 carries a built-in contactor for remote cut-off; base Norax 3 models lack this feature [Elektroda, and_you, post #18769942]

Statistic: How much export did users log in the first month?

One ENERGA prosumer recorded 90.8 kWh export against 139.6 kWh produced—65 % self-consumed [Elektroda, Viszna, post #18457049]

Failure fact: What happens if you run PV on a unidirectional Corax/Norax?

The meter adds export to import, so every kWh you generate is billed; Apator support calls this “absolute value” mode [Elektroda, derekk, post #18635204]
AI summary based on the discussion. May contain errors.
ADVERTISEMENT