logo elektroda
logo elektroda
X
logo elektroda

Galmet Boiler Connection Issues: Double Coil Type U, Radiator Valves & Reverse Orientation

pawelek00708 29718 12
Best answers

How should a Galmet double-coil U-type boiler be connected when it is installed upside down and the hot water runs out too quickly?

Connect the tank with the coil feed on the top connector and throttle the return/bottom valve rather than leaving it fully open; if it is mounted upside down, the anti-mixing shutter ends up in the wrong place and cold water mixes with hot water faster [#17263655] [#17265807] [#17293677] On a gravity-only installation this is especially important, and the installation may need to be reworked if the flow is not correct [#17263801] Do not rely on the nipple colors; the top connector should be open fully and the lower one partially closed to keep heat in the CWU tank [#17265807] [#17293677]
AI summary based on the discussion. May contain errors.
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 17263622
    pawelek00708
    Level 9  
    Posts: 12
    Rate: 5
    Good morning
    Boiler galmet connection
    coil double coil type U in the boiler is hot at the top and bottom heat (summer) boiler connected in reverse (upside down) quickly water cools in the boiler

    valves for radiators out of screw heat the boiler itself



    Galmet Boiler Connection Issues: Double Coil Type U, Radiator Valves & Reverse Orientation Galmet Boiler Connection Issues: Double Coil Type U, Radiator Valves & Reverse Orientation
  • ADVERTISEMENT
  • Helpful post
    #2 17263655
    Wawrzyniec
    Level 38  
    Posts: 4006
    Help: 392
    Rate: 1075
    On the cold (utility) water supply, as the boiler is properly connected, there is a shutter that reduces the mixing of hot and cold water. As you have connected the other way, this shutter is at the top, and from the bottom, cold water flowing in at each water intake mixes with hot water and you have fast cold water.
  • #3 17263680
    pawelek00708
    Level 9  
    Posts: 12
    Rate: 5
    Wawrzyniec wrote:
    On the cold (utility) water supply, as the boiler is properly connected, there is a shutter that reduces the mixing of hot and cold water. As you have connected the other way, this shutter is at the top, and from the bottom, cold water flowing in at each water intake mixes with hot water and you have fast cold water.


    I asked the plumber, he told me that it does not matter, but I also do not fit with the reverse is connected
    and the tube from the spark plug at the top is hot and the heat at the bottom
  • Helpful post
    #4 17263801
    W0jtek92
    Level 39  
    Posts: 3852
    Help: 469
    Rate: 1257
    Hello, it is not important whether the supply is at the bottom or the top (although for gravity it is very important) and at the same time a single or double horizontal coil pipe is always the right RETURN of the installation must be bent valve for even more than half a whistle to keep the coil of the CWU container holding heat flowing in and slowly returning it from the second connector. If you have an installation with 100% gravity, you have to convert it.
    Greetings.
  • ADVERTISEMENT
  • #5 17263851
    pawelek00708
    Level 9  
    Posts: 12
    Rate: 5
    W0jtek92 wrote:
    Hello, it is not important whether the supply is at the bottom or the top (although for gravity it is very important) and at the same time a single or double horizontal coil pipe is always the right RETURN of the installation must be bent valve for even more than half a whistle to keep the coil of the CWU container holding heat flowing in and slowly returning it from the second connector. If you have an installation with 100% gravity, you have to convert it.
    Greetings.



    Gravitational installation without any pumps and so on (boiler Double coil "U" type SGW (L) x2
    If I understand correctly what you wrote, then the boiler should be connected in the reverse way, as it should be and additionally the valve on the coils of this blue color now red should I screw?

    I also thought that the coil would somehow aerate, the back of the boiler is running a bit (in the old boiler it was even higher and it worked about 10 or 15 years)
    You could explain it to me a little brighter
  • ADVERTISEMENT
  • Helpful post
    #6 17265807
    W0jtek92
    Level 39  
    Posts: 3852
    Help: 469
    Rate: 1257
    Hello. You have an upside down reservoir, do not be suggested with colors on the nozzles, the one at the top has to be open to the max and the one at the bottom is half-bitten, aleeee. if the plumber connected the tray to the color of the chapel. You have to replace it, the coil feed must be on the top coil connector.
    Greetings.
  • #7 17278029
    pawelek00708
    Level 9  
    Posts: 12
    Rate: 5
    I screwed the valve on the bottom. The plumber did not connect the tray to the colors, only the boiler turned away because nothing had to be changed. The power supply is on the upper coil connector (hot water from the stove is flown in the upper tube). The problem is that 2 people will wash and 3 already have summer water (not to wash but still warm) as if the coil has been blocked or had a poor flow of water? The old boiler had a simple coil, it has a little different, the gravity installation on the old boiler worked very well and on the new one there is something wrong
  • #8 17278061
    arturdip
    Level 31  
    Posts: 1176
    Help: 170
    Rate: 324
    The producer probably gave such a sign without "kozery". Can you ask for the exact symbol of this boiler?
  • #9 17278269
    pawelek00708
    Level 9  
    Posts: 12
    Rate: 5
    Galmet boiler Double coil "U" type SGW (L) x2 120 polyur.
  • #10 17278685
    W0jtek92
    Level 39  
    Posts: 3852
    Help: 469
    Rate: 1257
    Hello, say something about the old tray, what producer? if it was homemade, say something about it, did your plumber change only the hot water tank or did you bury something during the installation from the boiler to the tray? Stupid question but still ... Did the plumber sometimes make a mistake when connecting cold and hot water on the tank?
    Greetings.
  • ADVERTISEMENT
  • #11 17278856
    pawelek00708
    Level 9  
    Posts: 12
    Rate: 5
    Old homemade tray (but as he is inside, I do not know about 16 years he held the assumption, he has a simple coil) plumber connected a new boiler in place of the old without altering the installation only the new turned upside down because nothing needs to be processed, i.e. screwed coil for the valve with only valves, the inlet and outlet of the hot water from the boiler.
    "The plumber sometimes did not make a mistake when connecting cold and hot water on the tank?" He did not make a mistake, he only made a special mention because you did not have to change anything

    Galmet Boiler Connection Issues: Double Coil Type U, Radiator Valves & Reverse Orientation Galmet Boiler Connection Issues: Double Coil Type U, Radiator Valves & Reverse Orientation
  • Helpful post
    #12 17293677
    W0jtek92
    Level 39  
    Posts: 3852
    Help: 469
    Rate: 1257
    Hello. The connection is correct but bite the coil by closing the valve in the tank returning halfway.
    Greetings.
  • #13 17303770
    pawelek00708
    Level 9  
    Posts: 12
    Rate: 5
    thanks for helping everyone

Topic summary

✨ The discussion revolves around connection issues with a Galmet double coil type U boiler, specifically regarding its reverse orientation and radiator valve settings. Users report that the boiler cools quickly when connected upside down, leading to inadequate hot water supply. Responses suggest that the cold water supply connection may be incorrectly positioned, causing mixing of hot and cold water. It is emphasized that the top coil connector should be used for hot water input, and adjustments to the radiator valves may be necessary to optimize performance. The importance of proper installation, especially in gravity-fed systems, is highlighted, with suggestions for ensuring correct valve settings to maintain heat retention in the coil.
AI summary based on the discussion. May contain errors.

FAQ

TL;DR: Close the coil return ≥50% and, "for gravity it is very important" to orient ports correctly; this curbs rapid DHW cooling on Galmet SGW(L)x2 double U‑coil setups. [Elektroda, W0jtek92, post #17263801]

Why it matters: Helps homeowners with gravity-fed systems fix lukewarm water after retrofits or upside‑down connections.

Quick Facts

How do I stop my Galmet SGW(L)x2 from losing heat so fast on gravity?

Throttle the coil return valve more than halfway to slow natural circulation. Keep the supply and return correctly oriented for gravity. This preserves stratification and reduces mixing during draws. If the system is fully gravity, consider partial conversion or balancing. This change usually fixes rapid cooling complaints. [Elektroda, W0jtek92, post #17263801]

Which coil port is the supply on a double U‑coil Galmet?

Use the upper coil connector for the hot supply from the stove or boiler. Connect the return to the lower coil connector. Open the upper valve fully, and balance the return downstream. As the expert said, "coil feed must be on the top coil connector." [Elektroda, W0jtek92, post #17265807]

Why does reversing the DHW cold and hot connections cool the tank quickly?

Cold water normally enters through a diffuser that limits mixing inside the tank. If you swap the connections, that anti‑mixing feature sits at the top. Cold water then mixes from the bottom during every draw and chills the tank. "There is a shutter that reduces the mixing of hot and cold water." [Elektroda, Wawrzyniec, post #17263655]

Do I need to convert a 100% gravity installation for this tank?

Edge case: 100% gravity circuits can self‑circulate and strip heat from the coil. Throttle the return hard, or add measures that limit unwanted flow. As the installer noted, "If you have an installation with 100% gravity, you have to convert it." This advice helps retain stored heat between draws. [Elektroda, W0jtek92, post #17263801]

What valve positions should I use after correcting the connections?

Fully open the valve on the upper coil connector (100%). Set the lower return valve around halfway (≈50%) to limit thermosiphon. Verify hot supply flows into the upper coil, and the cooler water returns below. This preserves stratification and stabilizes outlet temperature during draws. [Elektroda, W0jtek92, post #17265807]

Could misconnecting the tank’s DHW cold and hot cause lukewarm water at taps?

Yes. If cold and hot are reversed, the cold inlet diffuser cannot do its job. Cold inflow will mix with hot water and reduce outlet temperature quickly. You will notice fast cooling during consecutive showers. Correct the inlet and outlet to restore stratification. [Elektroda, Wawrzyniec, post #17263655]

Is it acceptable to mount the cylinder upside down to reuse existing pipes?

No. An upside‑down cylinder misplaces key internals and ports. Reinstall it upright and route the hot supply to the top coil connector. Then balance the lower return as needed. Avoid trusting paint colors on nozzles during reconnection. Follow the marked functions instead. [Elektroda, W0jtek92, post #17265807]

My 120 L SGW(L)x2 gives only two hot showers; is that normal?

One user reported two hot showers and a lukewarm third on a 120 L tank. That suggests stratification loss during draws. Check the orientation and return throttling as in this FAQ. [Elektroda, pawelek00708, post #17278029]

How can I verify my coil feed is on the correct connector?

Confirm the stove or boiler supply connects to the upper coil connector, as required. If it does not, reconnect so the upper coil is the feed. Then set the lower return as advised for gravity systems. [Elektroda, W0jtek92, post #17265807]

Do color caps on the ports matter when connecting?

Ignore paint colors on the nozzles. Follow functional markings and connect the hot supply to the upper coil connector. As the expert noted, "do not be suggested with colors on the nozzles." [Elektroda, W0jtek92, post #17265807]

What’s a simple 3‑step way to connect the SGW(L)x2 correctly in a gravity setup?

  1. Mount the cylinder upright so its top ports are at the top.
  2. Connect the hot supply to the upper coil; connect the return to the lower coil.
  3. Open the upper valve fully; set the lower return about halfway to limit thermosiphon. [Elektroda, W0jtek92, post #17265807]

I fixed the coil piping, but the tank still cools fast during draws—why?

If DHW in/out are reversed, the anti‑mixing baffle sits wrong. Cold water then enters low and mixes the tank during draws. Correct the DHW connections to restore the diffuser’s effect and preserve stratification. [Elektroda, Wawrzyniec, post #17263655]
AI summary based on the discussion. May contain errors.
ADVERTISEMENT