KoJaK1990 wrote: I would like to know what temperature I need to set on the condensing furnace at an outside temperature of + 5C, the design temperature I want to have in the rooms is + 20C
There is no one simple answer to this, because you have to figure it out for yourself by trial and error.
Start at around 40 degrees. If you feel discomfort after the whole day, you raise the temperature.
The heating curve is based on the fact that by selecting the appropriate curve, the boiler automatically raises or lowers the heating water temperature depending on the outside temperature.
If you do not have a weatherman, you have to manually modify the temperature on the boiler depending on external conditions, so that your heaters give the right amount of heat.
If you hypothetically need approx. 500W of thermal power, this power will be provided by:
- type 22 radiator with dimensions of 600x1200 at a boiler water temperature of 40/35 (delta t = 5 degrees)
- type 22 radiator with dimensions of 600x1400 at a water temperature of 40/30 (delta t = 10 degrees)
- type 22 radiator with dimensions of 600x2000 at a water temperature of 40/25 (delta t = 15)
As you can see, for the same power and the same supply temperature but different return temperatures, different radiators are needed.
Generally, the smaller the radiator, the higher water temperature it needs, and the larger the heater, the lower the supply temperature can be to obtain the same heating power. The obtained delta t is also important, i.e. the difference between the boiler water supply and return, the smaller the temperature difference, the power increases a little, but also the required heating water flow rate in the system increases.
Summarizing the supply temperature or the heating curve is selected to the specificity of the premises we heat and the specificity of the installation, so there is no universal golden mean.
When selecting the temperature in the transition period, pay attention to how often the boiler will turn off, because if you give the boiler temperature too low, it may turn out that the boiler reaches it very quickly and the burner will turn off quickly. As a result, your boiler, instead of a few / a dozen burner shutdowns or continuous operation, will count, for example, several hundred during the day.