What is the optimal condensation temperature for a CO furnace?
slavuta 264720 127
At what return temperature does condensation start in a condensing gas boiler, and should that temperature be measured on the return or the supply side?
Condensation starts when the return temperature drops below the dew point, which the thread repeatedly gives as about 57°C; the lower the return temperature, the better the condensation effect [#10016116] [#20837361] The temperature to watch is the return temperature back to the boiler, not the supply temperature [#10016116] [#20837814] Several replies stress that there is no single “best” fixed value: keep the return as low as practical while still heating the house properly [#10022476] [#10154303] One example given as optimal is 55/35 at 20°C room temperature, and for gas boilers it is also stated that return below 57°C is enough for condensation [#10022907] [#10117400] In practice, lower flow temperature usually means lower return temperature, and lower return improves efficiency [#10022476] [#10154303]
  • #1 10015674
    slavuta
    Rate: 19
    As the topic...
    I searched the forum but did not find a clear answer. I know that condensation in the oven takes place at a maximum temperature of 57 degrees C.
    However, I would like to know at which lowest temperature the condensation effect occurs?
    The second issue is whether the condensation temperature is to be at the return or exit of the furnace?
    Thank you very much in advance for your answers. :D
  • #2 10016116
    adam998
    Rate: 187
    For condensation to occur, the temperature on the return to the boiler must be lower than the so-called dew point around 57 ° C.
  • #3 10022476
    kabee84
    Help: 39
    Rate: 164
    The lower the flow temperature, the lower the return temperature.
    The lower the return temperature, the better.
    FEMAX Łazienki. Ogrzewanie. Instalacje.
    Szczęśliwa 25, Gdańsk, 83-110 | Tel.: 664 XXX XXX (Show) | Company Website: femax.pl
  • #4 10022736
    Brencik
    Help: 38
    Rate: 209
    ... so it's best not to heat at all hehe
  • #5 10022907
    EkoGrzew
    Help: 28
    Rate: 232
    the optimal temperature for condensation is 55/35 at t 20
  • #6 10024282
    Brencik
    Help: 38
    Rate: 209
    Nonsense. The optimal one is that there will be no more than 57 degrees on the return. The fewer the better.
  • #7 10024658
    adam998
    Rate: 187
    And as if let go back through some "refrigerator" :wink: then the flow temperature could be maintained, e.g. 80 ° C, and the return cooled to obtain condensation. When someone has an old installation, i.e. designed to power, for example, 90 or 75 degrees C and assembles a condensing boiler ... :D
  • #8 10025297
    Brencik
    Help: 38
    Rate: 209
    Heh the energy losses will be greater than you would be feeding with a lower temperature.
  • #9 10112968
    przeklusek
    Rate: 30
    Hello!
    This is my first post on this forum and maybe I can gain some valuable tips.
    I mean setting the temperature of the condensing furnace - how much to set the central heating temperature? Everyone says that it should be lower than 57C on the return - I have 42 at the exit of the furnace and 38-40C on the return. I do not know if I have well-chosen heaters - the temperature at home is about 20-21C, gas consumption in the last 2 weeks - 60m3 - I still heat it with this hot water heater. All in all, it has been warm recently and I do not know what the gas consumption will look like in the winter. Should I combine something with this stove or not - this is my first heating season and I do not know if it is OK. I wonder if it is better if the heaters were to turn on for a shorter time but were hot or, as I have now - they only get slightly warm, but they probably heat up longer.
    I would like to point out that my installation specialists ignored the matter and left the factory settings - I had hot water at 65C and I think about 60C on the stove.
  • #10 10113354
    Brencik
    Help: 38
    Rate: 209
    Do you have a weather forecast?
    How it will take care of the water temperature in which the temperature on the supply varies between 40 and 50 degrees.
    For a month now, I also use an average of 4 m3 of gas (heating, hot water and gas cooker). Heated area of 120 m2. WOLF CGW 11/100 boiler
  • #11 10115281
    Zloty60
    Help: 14
    Rate: 69
    I have a Dietrich condensate (so far without the weather) and my supply temperature is set to 39 degrees. At home, 22 days and night, around 21.6.
    The condensate is pouring down a lot, from time to time I watch the tube coming out of the boiler.
    I have about 4.5-5 m? of gas per day at 0 ° C outside. New building 120m?
    In fact, I would like to clarify this with this combustion.
    I have so much time to prepare dinner, lunch and hot water, and the central heating turns on at night around 1 (to heat up according to the thermostat, and in the morning it would be nice to walk on the warm floor choosing the kid to kindergarten and us to work). During the day, the boiler does not turn on because the building does not lose heat.
    I don't think I can say that the stove does not burn very much, because it burns properly. Good insulation is enough that the stove does not have to be turned on often, which affects combustion.
    I read somewhere on the forum that the average gas consumption is 0.6 m3 per hour.
    With my 13 oversized radiators and 2 underfloor heating circuits, it burns about 1 m3 per hour. It takes 3 hours and 3 cubic meters of CO.
    Forum users who write about their buildings with no insulation, let's say 150 m? and burning 3.6m? while outside -10, and at home 21, probably add some color.
    Sorry for the little OT.
    a piercing I also heat the first season, it turns out that you eat 4.28 cubic meters a day. I think this is a good result.
    I also had factory settings and at the beginning it charged me 10 cubic meters a day with pluses outside. And a few days passed before I set a lower supply temperature. And a few zlotys went to the chimney :)
  • #12 10115285
    przeklusek
    Rate: 30
    I have a weather station, but I don't know what I need it for ?? I do not know how to turn it on because if I set the temperature on the boiler myself, it is probably not turned on ?? But I'm going to read in a moment. So I understand that I should increase the CO temperature a little ?? Oh - one more thing - I have 3 floor heating circuits - I did not notice that it ever turned on - do you need to bleed it somehow or some thermo valves ??
    I have about 140m2 for heating and a Saunier Duvale MCR24II stove
  • #13 10115525
    pief
    Help: 11
    Rate: 79
    I'm getting stuck a bit on the "off topic."
    Condensing furnaces to work economically need a properly oversized radiator installation and when replacing the furnace with a condensing one (in older houses) it turns out that the heaters must increase the supply temperature, e.g. to 65 degrees Celsius, and the whole idea of condensation and savings goes to the "forest".
    Replacing and buying new, properly oversized radiators is enough
    large expense and, to theorize, if the loops of the copper 15 i tube were connected to the heater return
    let go at the skirting board.
    Theorizing further - what length would the loop have to be (1 kw as many meters)
    etc ... etc. What do you think is a solution.
    best regards
  • #14 10117400
    szymonjasiu
    Help: 29
    Rate: 138
    It depends on the type of fuel, of course.
    For natural gas fired boilers the return temperature is below 57 degrees.
    For heating oil below 45 degrees.
    best regards
  • #15 10118027
    Brencik
    Help: 38
    Rate: 209
    Zloty60 wrote:
    , it burns about 1m? per hour. It takes 3 hours and consumes 3 cubic meters. Only CO
    Zloty60 wrote:
    I have the supply temperature set to 39 degrees.
    It is contradictory and physically impossible that the boiler, operating at such low power, consumes 1 m3 per hour.
    No comments ...
    przeklusek wrote:
    Oh - one more thing - I have 3 floor circuits - I didn't notice that it ever turned on
    You need to configure everything as it should be, it's best to call a specialist.
    pief wrote:
    Condensing furnaces to operate economically require an appropriately oversized radiator installation
    G .. true. I have undersized and so far it has been condensing me all the time.
  • #16 10118452
    serwo66
    Help: 61
    Rate: 292
    Colleagues, if someone had an old house with cast iron radiators and then insulated it, it can automatically lower the supply temperature of the radiators by about 10-15 * C and after all, it is the right time to install condensate because the heaters for the insulated building are already oversized the boiler will condense nicely on a large volume. The cost of replacing the heaters is dropped.
  • #17 10118766
    Zloty60
    Help: 14
    Rate: 69
    What is contradictory and physically impossible?
    So it burns for me and that's it.
    What am I wrongly positioned then?
    The printout from commissioning is book-like and agrees with the manufacturer's data provided in the manual. CO? = 8.8% at full and minimum power.
    Greetings
  • #18 10120980
    kasku97
    Rate: 46
    I started with the settings for the floor heating. I have a floor heating system. I set the supply to 40 ° C and the heating curve - weather forecast, taking into account the temperature inside the reference room. During the weather, he overheated the rooms. I'm waiting now. For now, it turns on rarely but works longer. I guess that's what condensation is about. If it does not work in frost, I will give a higher supply temperature and correct the heating curve.
  • #19 10121070
    Brencik
    Help: 38
    Rate: 209
    But it is the heat curve that determines the flow temperature.
    The task of the weather forecast is to change the supply temperature taking into account the outside temperature.
    And how much we want to have in the room, set on the controller.
  • #20 10121171
    kasku97
    Rate: 46
    The boilers have a weather function, a mixed function (takes into account the external and internal temperature) or taking into account only the internal temperature. rooms. Mixed is cool because using ext. additional heat source, e.g. fireplace, boiler is not working. This is how it works for me. Earlier, in the clean weather itself, he overheated my rooms when I was smoking in the fireplace.
    Of course, the heating curve controls the flow temperature, but in the boiler it is possible to rigidly set the flow temperature not to be exceeded. That is why I wrote that I will correct it if necessary, as well as the supply temperature.
  • #21 10121233
    Brencik
    Help: 38
    Rate: 209
    Taking into account the temperature in the room consists only in changing the supply temperature by a few melts when the temperature
    "The room influence is only active when
    The BM programming module is installed as a module
    remote control and user level
    room influence has been set.
    The room influence function can be changed
    room temperature due to heat or winter
    from outside (e.g. solar radiation, fireplace
    or an open window) will be aligned. Temperature
    room is compared with the setpoint
    temperature (day temperature or economy temperature)
    by means of the built-in temperature sensor
    rooms. Deviation from the setpoint
    is multiplied by the heating curve value and the coefficient
    room influence and flow temperature
    will be increased by this value.
    smaller room influence factor = smaller
    influence on inlet temperature
    greater room influence factor = large
    influence on inlet temperature "
  • #22 10121278
    kasku97
    Rate: 46
    Exactly. I agree with everything you wrote.
  • #23 10122839
    przeklusek
    Rate: 30
    So I still do not know anything - you need to call a specialist - he will click 4 buttons on the stove several times and delete PLN 200 - and I will still not be sure if it is well set ...
    Does anyone know a good specialist from the vicinity of Tarnów (Lesser Poland). In order not to do advertising, I am asking for info on priv. Przeklusek(_at_)wp.pl
  • #24 10123064
    Brencik
    Help: 38
    Rate: 209
    przeklusek wrote:
    So I still don't know anything
    Read instructions and think!
  • #25 10124499
    kasku97
    Rate: 46
    slavuta ... and what is this cauldron?
  • #26 10140966
    slavuta
    Rate: 19
    I have a single-function DeDietrich MCR / II 24T stove with a 100l domestic hot water tank, without weather, with a room regulator.
    I have 6 oversized radiators + two underfloor heating circuits (ultimately, heating in the attic to be connected).
    In total, the ground floor is about 100m to be heated at the moment (the building is not yet insulated)
    Now, at around zero outside temperature and setting the furnace at 45C outlet, and at 37C on the return, it burns about 5-5.5m a day. Home temp 20C-21C.
    Previously, the furnace was set to output 40C but it worked for a long time. Gas consumption was similar but it was warmer outside.
    I wonder if the stove works for a long time at a lower temperature (40C) or shorter at a higher temperature (45C), but it often turns on?
  • #27 10154303
    kasku97
    Rate: 46
    I have wondered about it once. Now I can say that longer work and fewer starts are definitely better. The lower the outlet and return temperatures, the higher the efficiency and the lower the gas consumption. The stove does not like frequent starts. Longer cycles don't hurt it as much as frequent starting. Thermal comfort is much greater when the radiators are still but moderately warm than rarely hot. The heater is not only convection, but also radiant heat. For an underfloor heating system, the best solution is a cooler, continuous power supply - high inertia. Just do not go too far with lowering the temperature because at some point the stove will no longer maintain the temperature in the rooms.
  • #28 10154315
    Brencik
    Help: 38
    Rate: 209
    Not just a boiler.
    The larger the radiators, the lower the heating curve can be.
  • #29 10154402
    kasku97
    Rate: 46
    You're clinging to Brencik :P
  • #30 10154427
    Brencik
    Help: 38
    Rate: 209
    No, a dog is also not a cat and a tram is not a bus. This is obvious.
The discussion revolves around the optimal condensation temperature for a condensing boiler, specifically focusing on the return temperature necessary for effective condensation. Participants agree that the return temperature should ideally be below 57°C to facilitate condensation, with some suggesting that lower temperatures enhance efficiency. The optimal flow and return temperatures discussed range from 40-55°C for various heating systems, including those with underfloor heating and radiators. The importance of proper radiator sizing and system configuration is emphasized to achieve efficient operation and minimize energy consumption. Users share their experiences with different boiler models and settings, highlighting the need for adjustments based on external temperatures and building insulation.
TL;DR: Cutting return-water from 45 °C to 30 °C can boost condensing-boiler efficiency by up to 11 % [Viessmann, 2023]; “The lower the return temperature, the better” [Elektroda, Brencik, post #10024282] Why it matters: every 5 °C drop may cut gas bills by ~2 % while lowering CO₂ and acid-flue risk.
• Dew-point for natural-gas exhaust ≈ 57 °C; below this condensate forms [Elektroda, adam998, post #10016116] • Recommended design temps (radiators): 50/30 °C flow/return for −10 °C outside [Bosch datasheet, 2023] • Typical ΔT for high efficiency: 10–20 K (°C) between flow and return [IEA, 2022] • Each 1 °C indoor set-back saves ~6 % energy in 24 h [EnergyStar] • Annual service & pH-neutraliser needed to avoid acid corrosion when >2 l/day condensate [Vaillant, Guide]
1. What temperature triggers condensation in a natural-gas boiler?
Water vapour starts condensing when the return water falls below the flue-gas dew point of about 57 °C [Elektroda, adam998, post #10016116]
3. What flow/return pair gives highest efficiency on radiators?
Lab tests show 40/30 °C reaches 109 % (LHV) efficiency, versus 50/30 °C at 108 % and 70/55 °C below 94 % [Bosch datasheet, 2023].
4. How low can I set a condensing boiler without cycling?
Match minimum burner output to heat loss. If min. power is 3 kW and the house loses 2 kW, lower flow to 42 °C and use ΔT ≈ 15 K; cycling then falls under six starts/hour [Elektroda, Brencik, post #20775749]
5. My boiler shows only one temperature—how do I see the return?
Immergas Zeus hides it; press “i” ∧▼ 3 s, then rotate knob to code d41 for return and d40 for flow [Immergas Manual p.34].
6. What’s an optimal curve for mixed floor + radiators?
Start with 0.8 slope, 20 °C offset. Cap floor loop at 35 °C via mixer and let radiators follow weather curve up to 50 °C; keep return ≤ 40 °C [Elektroda, kasku97, post #10120980]
7. Boiler clicks every 10 min—is that harmful?
Frequent starts raise fuel use by 5–8 % and stress the fan gasket [IEA, 2022]. Aim for cycles ≥ 20 min by widening hysteresis or lowering flow 3 °C [Elektroda, slavuta, post #10622441]
8. Edge case: what if return hits 65 °C?
Condensation ceases; gross efficiency can drop to 88 % and acidic condensate may flash-evaporate, eroding the flue liner [Vaillant, Guide].
9. Three-step radiator-balancing to widen ΔT
  1. Close all lockshields half-turn. 2. Open furthest radiator fully. 3. Gradually reopen nearer units until each shows 10–15 K drop (infrared gun).
10. Can old 90/70 °C systems use a condensing unit?
Yes—add oversized radiators or run weather compensation; even with 65/45 °C you still condense part-load days, saving ~7 % annually [Elektroda, serwo66, post #10118452]
11. How much gas should a 120 m² house use after optimisation?
Forum users report 6–8 m³/day at 0 °C outside and 21 °C inside—about 50 kWh/d or 125 kWh/m²·yr [Elektroda, tremorpl, post #10955074]
12. Does higher DHW set-point waste energy?
Each 10 °C rise in cylinder set-point increases standby loss ~4 % [EnergyStar]. Keep ≤ 50 °C and run a weekly 60 °C anti-legionella cycle [Elektroda, marekth, post #10458266]
13. Why is my floor loop hogging all the heat?
It offers least resistance; throttle its manifold or fit a differential-pressure bypass so radiators receive flow [Elektroda, tremorpl, post #11462348]
14. Statistic: how much condensate forms?
At 30 °C return, a gas boiler condenses approx. 0.1 l for every m³ burned—up to 8 l/day in 80 kWh systems [Viessmann, 2023].
15. What yearly maintenance stops acidic damage?
  1. Neutraliser media replacement when pH < 6. 2. Heat-exchanger rinse. 3. Check siphon for 500 ml discharge in 60 s test [Vaillant, Guide].