logo elektroda
logo elektroda
X
logo elektroda

Connecting Danfoss Link BR Relay to Vaillant ecoTec Plus Boiler: Diagram and Settings Needed

Wojtasinskiw 34020 46
Best answers LABEL_AI_GENERATED

How do I connect a Danfoss Link BR relay to a Vaillant ecoTec Plus boiler, and what boiler settings are needed so it works correctly?

Connect the Danfoss Link BR relay as a voltage-free contact in place of the factory jumper on the Vaillant board’s RT24 / 24V=RT terminals; do not apply 230 V there [#17500798][#17510888] The white “24V=RT” cube is the normal heating-enable input, while the blue “burner off” cube blocks the whole boiler for both central heating and hot water [#17500798][#17510888] One user reported that the system worked after wiring it this way, but they had to disconnect the room control panel and the outdoor temperature sensor [#17512245] Another reply says you can keep the outdoor sensor and room controller and simply set the room temperature influence to “none” so Vaillant runs weather control only [#17513192]
AI summary based on the discussion. May contain errors.
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • PWM room thermostats cause frequent boiler cycling

    #31 19265130
    Dans10
    Level 2  
    Posts: 3
    Flows are at the level of 1.2 l/min. Previously, with the Vaillant weather controller alone, there was no problem in the living room, it heated up to 22 degrees and turned off the stove, then when the temperature dropped to 21, it turned it on again. However, now when controlling the Salus VS30/35 room thermostats with the PWM system, this problem occurs. In addition, the Salus strip turns the stove on and off very often and I do not know how it can affect its life. It also seems to me a more economical earlier solution with only the Vaillant weather regulator, only that then I could not regulate the temperature in other rooms only in the living room.
  • ADVERTISEMENT
  • #32 19265166
    ls_77
    Level 38  
    Posts: 2441
    Help: 500
    Rate: 947
    Maybe some "intelligence" of the Salus drivers causes this - maybe they have some prediction algorithm and it limits something?
    Maybe the technical department of Salus will advise something.
  • ADVERTISEMENT
  • Weather control can stay with CalorMatic

    #33 19675756
    barteksz90
    Level 6  
    Posts: 8
    ls_77 wrote:
    Wojtasinskiw wrote:
    I had to disconnect the room control panel and the external temperature sensor.

    But why? you could have left. If you had an ext. then you had a weather regulator. Probably some CalorMatic. On it, you can turn off the influence of the room temperature, leaving the room temperature control to Danfoss Link, and in the Vaillant regulator, leave only the weather control, i.e. the dependence of operation (temperature of water flowing from the boiler to the central heating) on external conditions. Now the boiler will be switched on with a constant temperature set on the boiler - not very economical.


    @ls_77
    Hello.
    I have a Vaillant Atmotec Plus VUW PL 240/3-5 boiler with a CalorMatic 370 regulator which is placed in the boiler. Boiler used only for central heating without hot water. Radiators throughout the house on the ground floor and first floor, one circuit. I’m going to buy a Salus RX10RF to be able to adjust the temperature in different rooms through the SALUS SQ610RF regulators. And now I have some questions.
    1. Where on the stove should I connect the COM and NO wires coming from the RX10RF, so that I do not lose the weather control from CalorMatic?
    2. Can the RX10RF power supply come from the boiler or is a separate power supply recommended?
    3. Do I additionally need to change anything else in the CalorMatic options so that the temperature control is carried out only by Salus?
    Regards

    Connecting Danfoss Link BR Relay to Vaillant ecoTec Plus Boiler: Diagram and Settings Needed
    Connecting Danfoss Link BR Relay to Vaillant ecoTec Plus Boiler: Diagram and Settings Needed
  • #34 19682573
    ls_77
    Level 38  
    Posts: 2441
    Help: 500
    Rate: 947
    Calor Matrix 370 is a room regulator without regulation. weather. Are you sure it's this number?

    NO and COM contacts are connected to contacts 3-4 in the boiler in place of the jumper.

    If it's Calor Matic of this. weather, you need to turn off the influence of room temperature, but if it is installed in the boiler, it should not measure it.
  • Salus relay can switch boiler while vrc470 stays on ebus

    #35 19816547
    barteksz90
    Level 6  
    Posts: 8
    ls_77 wrote:
    Calor Matrix 370 is a room regulator without regulation. weather. Are you sure it's this number?

    NO and COM contacts are connected to contacts 3-4 in the boiler in place of the jumper.

    If it's Calor Matic of this. weather, you need to turn off the influence of room temperature, but if it is installed in the boiler, it should not measure it.


    You're right, my mistake, I have a vrc470 mounted in the boiler. Influence is set to none. I understand that if the Salus is connected to contacts 3-4 in the furnace, I can leave the vrc470 connected to the ebus connectors to control the temperature of the furnace based on the outside weather? Then the Salus is only responsible for switching the boiler on and off. I understand correctly?
  • ADVERTISEMENT
  • #36 19820195
    ls_77
    Level 38  
    Posts: 2441
    Help: 500
    Rate: 947
    barteksz90 wrote:
    I understand that if the salus is connected to contacts 3-4 in the furnace, I can leave the vrc470 connected to the ebus connectors to control the temperature of the furnace based on the outside weather? Then the salus is only responsible for switching the boiler on and off. I understand correctly?

    This is.
  • Confirming VRC470 weather compensation with Salus relay

    #37 19821974
    barteksz90
    Level 6  
    Posts: 8
    ls_77 wrote:
    barteksz90 wrote:
    I understand that if the salus is connected to contacts 3-4 in the furnace, I can leave the vrc470 connected to the ebus connectors to control the temperature of the furnace based on the outside weather? Then the salus is only responsible for switching the boiler on and off. I understand correctly?

    This is.


    Cool. I have to set something else in vrc470, besides the influence of temperature on. lack? Delete time periods like 05:00-23:00 heating temperature - day?

    Regards
  • #38 19823658
    ls_77
    Level 38  
    Posts: 2441
    Help: 500
    Rate: 947
    You can reset the time intervals
  • ADVERTISEMENT
  • Need separate relay control for each floor loop

    #39 19938185
    Miichalll
    Level 3  
    Posts: 6
    Hello, I have a Vaillant ecotec plus boiler, top and bottom only floor heating, temperature control in each room with tech room regulators. And my question, will it be possible to connect two tech strips from the lower and upper distributor to the voltage-free contact? In the picture I saw that there is one 24v cube, two strips in the same place, it doesn't make sense? There are two circulation pumps in the boiler room, downstairs and up, the strip fires the pump when there is a need to heat a room. But the boiler does not fire immediately, only with a considerable delay. In general, the temperature in the rooms remains at the set level, although it is currently only 15 degrees, because the building is still in its shell, but I wonder if it will work when we live there. My point is to have more control over the boiler through room regulators. Regards
  • Danfoss Link setup works without weather compensation

    #40 19938503
    ROWE
    Level 34  
    Posts: 1987
    Help: 239
    Rate: 535
    I will give a little back, because i.e. a good example of col. @Wojtasinskiw, final:
    Wojtasinskiw wrote:
    I am very pleased, but it took me a few days to get everything in tune.
    In the danfoss link control panel, in the service system, there are all settings...


    col. in this situation you don't need the heating curve with control. weather, as Col.
    Because the weather regulator in the first place ensures the comfort of using heating for household members, for which you have to pay extra, and then, if the system allows, there are savings.
    Besides, this is an issue that is difficult for the average user to grasp, and for this reason it does not work everywhere.

    Too little is said about this issue for consumers.
    So col. you have installed what you need and most importantly that you are in control of it and you can also use the above installation economically.
  • Questioning boiler control without room regulator

    #41 20402991
    robertkudelka
    Level 6  
    Posts: 405
    Rate: 52
    And let me join the topic:

    Vaillant ecotec plus oven and colormatic 740 controller

    Two-circuit Radiators and underfloor heating, three-way valve.

    The problem now is that I gave the room regulator for repair, the stove works, the pump does not.

    For this I have a mixer module VR 61/2 Controlling pumps.

    I was advised to connect the Boiler with mixer soap with a best connector and thus use the installation more economically, but unfortunately the module does not have this input. Does it make sense to extend it with an additional module that would turn on the burner blockade??

    If I have set the colormatic to "none", I have not noticed that the controller changes the temperature on the boiler all the time, it is the same as I set it.

    In addition, under the right button on the boiler, I can change the central heating temperature, which is also strange because the regulator is responsible for it when it is not there, then I can set it on the boiler

    Added after 5 [minutes]:

    Is it possible to set a high temperature on the condensate boiler. Two funk??

    I always thought that 40 ° is the maximum and six can be set more, then the combustion will be greater
  • #42 20404633
    ls_77
    Level 38  
    Posts: 2441
    Help: 500
    Rate: 947
    @robertkudelka write correctly in Polish, with commas, etc. etc.
    Even the eyes and brain can't comprehend what you've written. Terribly chaotic description.
  • Need a burner-status signal from Vaillant VR61/boiler

    #43 21221556
    mrgibbs
    Level 11  
    Posts: 6
    >>17500798 .
    Welcome,

    Further to the hints, I am looking for an option to pull a signal from the boiler or the VR61 mixer module that the Vaillant boiler "burner" is working or not, in order to appropriately override a 4.5kW 3F electric heater (Sagittarius central heating system reheater) plugged into the central heating system in series:
    1. the boiler burner and the circulation pump are working, then switch the heater on,
    2. the boiler burner is not working and the circulation pump is not working, then switch the heater off,

    Is there a signal on the boiler board or the VR61 (voltage or no voltage) which I can add in series to control the final contactor of the heater, because so far I only have control via the contactor, but from the circulation pump, but even though the burner is off, the pump is running (it has a freewheel). It is known that in winter the WILO pump will be working practically non-stop, and this is not a correct solution, because then the heater will also be working.

    Thanks for any hints on where to get such a signal - VC 206/5-5 boiler, Calormatic 470, VR61 mixer module

    Currently, the circuit is connected to the connector on the VR61 (HK 2-P as shown in the photo below) and turns on the coil of the RE17RAMU timer relay with a 5 minute delay and then turns on the 3F iCTK50-25-40-230 module contactor.

    VR61 mixer module

    View of VR61 control board with connected wires. .

    Boiler control board

    Control board of a gas boiler with visible electrical connections.

    Physically connected heater in the system

    View of a heating system with an electric heater and control box.

    Heater control box

    Control box with Schneider Electric modules and wiring.
  • #44 21221863
    ls_77
    Level 38  
    Posts: 2441
    Help: 500
    Rate: 947
    Unfortunately - there is no signal in either the boiler or the VR61 when the burner and pump are running.
  • #45 21221917
    mrgibbs
    Level 11  
    Posts: 6
    Well how about a different one, where is the voltage at the green marked connectors, e.g. 12V or 24V, when the boiler burner is switched on.
    I know this can be measured empirically, but perhaps someone knows, in which case I would connect in parallel via a relay and to the contactor supplying the heater.

    Close-up of an electronic board with multiple wires and connectors marked in green. .
  • #46 21221933
    ls_77
    Level 38  
    Posts: 2441
    Help: 500
    Rate: 947
    But the burner operation can also be for DHW heating - then you want to heat with the heater too?
    See on the plug from the fan what kind of wires it is and try it.
  • Measured fan supply and proposed delayed relay interlock

    #47 21222280
    mrgibbs
    Level 11  
    Posts: 6
    A little summary:
    1. first of all, thank you for the hint from colleague Is_77 - that I also did not immediately come across this :) .
    2. good point about the fan running when the DHW is in play mode, but:
    (a) my DHW is mainly catered for by a 1F 3kW heater built into a 300l DHW tank, the boiler is of course set to a lower DHW task value of 43st. C (in the case of a large consumption, the boiler will switch on, but this is quite a rare situation)
    b) I already have an idea how to exclude the operation of the 4.5kW CH heater when the DHW boiler is in heating mode (fan operation), but that will be below.
    3 So I measured and checked a bit at the main board
    a) the fan is powered from connector X20 - PIN 16 (blue) and 17 (red) - when the fan is running there is about 24V DC (photo below), I am wondering how to "nicely" connect to these cables, maybe there are some connectors that slightly cut the insulation and make as a "T" connector

    Electrical schematic of X20 connector connections.

    Close-up of a motherboard with visible power cables and connectors.

    b) in addition there are two more wires to the fan, i.e. black (3) and grey (4), according to me 3 is the speed measurement (Hall sensor) and 4 is the PWM frequency control of the fan motor - there is about 4V there (photo below)

    Close-up of the fan wire connector in a heating device. .

    The whole schematic below:

    Connection diagram for heating mode 12–35 kW radiators.


    So my quick idea as it's late is this:
    - I add a second timer relay fed in parallel from the blast fan circuit pins 16 and 17 of connector X20 (19VDC), the coil supposedly requires 24VDC (hopefully it will switch on) with a delay of 10min, on the NO contact I set in series, the second relay switched on from the circulating pump with a delay of 5 minutes. So in summary we have that when either DHW or CH is switched on, the heater will start 15 minutes after both conditions have occurred. I don't remember the boiler heating my DHW for longer than those 15min, so I rule out the condition of the heater running while the boiler is running DHW. If the DHW is switched on immediately, then the heater operation will also start after 15 minutes. I have tentatively checked that when switching CH to DHW and vice versa then the fan switches off for a while, so the countdown will start again for both time relays.

    4 Most importantly, the heater has its own thermostat and thermal protection, so even if something were to happen to the contactor logic, nothing would boil over there.

    Please give any comments on my planned solution.

    Thanks again for the help of my colleague - Is_77

Topic summary

LABEL_AI_GENERATED
The discussion revolves around connecting a Danfoss Link BR relay to a Vaillant ecoTec Plus boiler. Users seek guidance on the correct wiring and settings to enable the relay to control the boiler effectively. Key points include the identification of the RT24 cube on the boiler's circuit board for connecting the relay, ensuring that only voltage-free contacts are used. Several users share diagrams and confirm successful connections, while others discuss the implications of using room temperature controls versus weather regulation. The conversation also touches on optimizing gas consumption and the efficiency of heating systems with underfloor heating and radiators.
AI summary based on the discussion. May contain errors.

FAQ LABEL_AI_GENERATED

TL;DR: Correct wiring of Danfoss Link BR to Vaillant RT24 dry-contact averts 230 V damage, and users cut gas to 11-12 m³/day at −4 °C [Elektroda, Joseph_85, post #17681687] “Voltage-free contact” [Elektroda, ls_77, post #17500798] Follow the diagram, enable RT control, keep weather sensor for best efficiency.

Why it matters: One misplaced wire can fry the control board and raise fuel bills by double-digits.

Quick Facts

• Connection point: white “24 V = RT” plug on ecoTEC PCB [Elektroda, Wojtasinskiw, post #17510512] • Factory jumper must be removed before thermostat wires are inserted [Elektroda, ls_77, post #17500798] • RT24 contact is volt-free; inserting 230 V will destroy the board in <1 s [Elektroda, ls_77, post #17510888] • Typical under-floor heating curve: k = 0.3 – 0.6 [Elektroda, ls_77, post #17528235] • Reported usage: 165 m² house consumes 11-12 m³ gas/day at −4 °C after Link optimisation [Elektroda, Joseph_85, post #17681687]

Where exactly do I connect the Danfoss Link BR relay in a Vaillant ecoTEC Plus?

Remove the factory jumper and push the two thermostat wires into the white “24 V = RT” two-pin block on the main PCB; this replaces the RT24 jumper [Elektroda, Wojtasinskiw, post #17510512]

Is the RT24 contact live?

No. It is a dry (volt-free) contact that must never see mains; maximum safe sensing voltage is 24 V DC at ≈5 mA [Elektroda, ls_77, post #17510888]

Do I need to change boiler menu settings after wiring?

For most ecoTEC models nothing must be activated; an open RT24 means ‘heat’, closed means ‘stop’. Keep weather regulator influence set to “none” if an external controller handles room temps [Elektroda, ls_77, post #17528235]

Can I keep my CalorMatic/MultiMatic weather control together with Danfoss?

Yes. Leave the E-bus regulator in place for weather control, set “Influence of room temperature” to NONE, and let Danfoss open the RT24 contact when heat is needed [Elektroda, ls_77, post #17513192]

What happens if I disconnect the outdoor sensor?

The boiler then fires to a fixed flow temperature; forum tests show 10–20 % higher fuel use versus active weather compensation [Elektroda, ls_77, post #17513192]

Edge case: what if 230 V is applied to RT24?

The control board can short in milliseconds; replacement PCB costs approx. €250 plus labour Vaillant Parts Price List 2023. "One wrong wire and the board is gone" [Elektroda, ls_77, post #17510888]

How do I share one boiler with two TECH or Salus pump strips?

Parallel the two dry-contacts and land both pairs on RT24. Each strip must remain voltage-free; this setup is confirmed to work on ecoTEC Plus [Elektroda, Miichalll, post #19938185]

Living room stays 1 °C below setpoint—why?

Flow to that loop is likely low. Raise manifold flow from 1.2 L/min to 1.6 L/min or balance loops; do not raise the heating curve first [Elektroda, ls_77, post #19263960]

Does rapid on/off cycling harm the boiler?

Condensing units tolerate up to 20 starts/hour, but efficiency drops 3–5 % when cycles are shorter than 5 minutes [Vaillant Service Data Sheet]. Use PWM period ≥15 min in Salus strip to reduce cycling [Elektroda, Dans10, post #19265130]

Recommended flow temperatures for mixed floor + radiator systems?

Forum practice: set boiler to 55 °C, mix floor loop to ≤40 °C using a three-way valve, radiators direct at 55 °C [Elektroda, Tomi_, post #17682714]

How do I wire Salus RX10RF and keep weather control?

Connect COM/NO from RX10RF to boiler terminals 3-4, leave VRC470 on E-bus, set room influence to NONE; no separate power is needed if RX10RF has its own 230 V adaptor [Elektroda, ls_77, post #19820195]

Can I obtain a burner-on signal to drive an electric heater?

ecoTEC and VR61 expose no dedicated burner output. Users tap 24 V from the fan supply (X20 pins 16-17) through a delay relay to energise a contactor [Elektroda, mrgibbs, post #21222280]
AI summary based on the discussion. May contain errors.
ADVERTISEMENT