Homemade method of measuring earth resistance
kortyleski 109839 46
How can I measure earth electrode resistance at home without specialized test equipment?
You can do a rough home measurement with a small transformer, a voltmeter and an ammeter, or with an ammeter + voltmeter and a known load such as about 2 kW, then calculate resistance from Ohm’s law using the no-load and loaded values [#16179887][#16179901] A simple lamp method was also mentioned: connect a 100 W bulb between phase and the earth electrode, but that only gives an indicative result because you are really measuring the whole loop, including transformer windings, wires and the supply network’s neutral-point earthing, not just the electrode itself [#16180403] For protection purposes, the required value depends on the system: in TN the earth electrode resistance is not what determines shock protection, while for lightning protection it is typically expected to be below 10 ohms [#19039429][#19039760] In TT systems, the acceptable value depends on the protective device; with a 30 mA RCD the theoretical limit is much higher, but the real target is still to keep the resistance as low as possible [#19039429]
  • #1 16179548
    kortyleski
    Help: 957
    Rate: 3860
    Hello. I am modifying the home installation a bit and hence the question. While I can handle the measurement and can handle it, I need to measure the earth resistance. I don't have any specialized equipment at the moment. Any advice?
  • #2 16179560
    kj1
    Electrician specialist
    Help: 278
    Rate: 850
    Do you have an ipz meter?
  • #3 16179594
    Darom
    Help: 231
    Rate: 588
    You can measure the static value of the earth resistance using the technical method.
    kisses
    - GIFT-
  • #4 16179887
    kortyleski
    Help: 957
    Rate: 3860
    Ammeter + voltmeter + 2 kW load. Measurement of voltage without load, then voltage and current with load. then it's Mr. Ohm's law and calculations.
    Can I have a description, please?
    Maybe I'll explain the topic.
    At the moment, I have ONE copper circuit of 1.5 mm square on which hangs a kettle, washing machine, dishwasher and thermal bath. sometimes the oven. Happy what? It used to be like this ...
    From the seat post to the meter I have 2x10mm square meters of copper. I leave the circuit that I described only for lighting, I run new three socket circuits. Of course, 3x2.5. Would use EP. I have an old pipe from a filled well. It is not connected to anything, just a piece of galvanization sticking out in the basement, the rest of which (about 10 m) sits in the ground. There will be expansion in the spring, there will be a border. for now I have to rely on what I have. So when I do the pen (TN-C) separation, I will go down from the gsu section in the basement, taking into account the measuring connector along the way. I will connect the GSU with this pipe. All connections LGY 10. After completing the work, I would like to measure this EP. I have several ammeters and AC voltmeters. I would like some advice.
  • #5 16179901
    kozi966
    Help: 599
    Rate: 1288
    You will need a small transformer, voltmeter and ammeter for your work.
  • #6 16180205
    CYRUS2
    Help: 1241
    Rate: 3530
    What type of distribution network - connection conditions.
    Tell me what you are up to.
  • #7 16180211
    zdzisiek1979
    Help: 561
    Rate: 1254
    I once read about a patent somewhere in radio broadcasters to check the earth electrode, you need to connect a 100W bulb. Earth electrode - light bulb - phase how much truth is I do not know. Have any of you heard about such a patent? Heard, read?
  • #8 16180391
    kortyleski
    Help: 957
    Rate: 3860
    kortyleski wrote:
    So when I do a pen separation (TN-C)
    i think to measure the voltage between L and PE and then the same at light load. it should give me an indicative RPE. With resistances of the order of ohms, ipz should not be of great importance
  • #9 16180403
    Darom
    Help: 231
    Rate: 588
    This is the easiest method. But strictly speaking, it is not a measurement of the earth resistance, because
    The total resistance of the transformer windings, wires, tested earthing and the neutral point earthing of the supply network are measured then. If the earth resistance, measured in this way, does not exceed the permissible value, then the tested earth resistance is acceptable. "
    quote from page 7 Link to Principles of earthing measurements and evaluation of measurement results - Arrow
    kisses
    - GIFT-
  • #10 16180417
    kkas12
    Help: 1076
    Rate: 4312
    What is the grounding resistance to the short-circuit loop impedance in the TN system ???
  • #11 16181102
    CYRUS2
    Help: 1241
    Rate: 3530
    Measuring is checking.
    A question to my friend Kortyleska.
    The question is which results (?) will be bad and which will be good.
  • #12 16182014
    kortyleski
    Help: 957
    Rate: 3860
    In principle, PE needs only an additional protection such as RCD. So if it meets this condition with a tenfold margin, it will still be enough. And it is known that the less the better.
    However, I still have a technical question. Can the rim and gsu joint located outside the building be treated as a measurement joint or should it be introduced separately from gsu?
  • #13 16182164
    elvis13
    Help: 18
    Rate: 77
    A short-circuit loop in a properly made TN-CS is completely metallic (L-PE and PE, after all, "comes out of" the PEN in TN-C).
    What specific condition does the colleague want to check?
    And I propose to find out what influence the TN earth electrode has on the SWZ ;)
    It's best to draw a diagram of the installation with cameras and think how the electricity will flow.
    We can subject this pattern to a constructive analysis ;)
  • Can external ring-to-GSU bonding serve as measurement joint?
    #14 16183183
    kortyleski
    Help: 957
    Rate: 3860
    Supposedly true, but it would aim at treating PE as a working conductor and it is not ... But thanks for paying attention, the IPZ will be extended with connectors at the PEN distribution in the switchgear.
    What current will flow with a direct connection of L and my improvised PE.
    To the point
    I will implement the basic protection through the SWZ. After the measurement of the IPZ, I will decide which apparatus to choose so that the condition is met. AT DIRECT JOINT L with any conductor that ends in the switchgear and is not L. because I have PE and N connected, it will work. But PE is not a work conductor.
    I have it in my head for a long time.
    For thought, let's assume RPE = 200 ohms, IPZ at B16 meets the conditions of SWZ.
    Let us consider three cases. Of course there is a 30mA RCD.
    1) What apparatuses will work and in what order when there is a direct short-circuit L to PE (housing) in the device - let it be a washing machine.
    2) What devices will work when there is a slight damage to the insulation, or turn off the power warning me about the problem? We are talking about leakage currents that can be dangerous and will not trip the B16 circuit breaker.
    3) What devices will work when the PEN on the pole is burned or the neighbor's spruce breaks and this PEN breaks?
    no ...
  • PEN conductor break defeats other protective devices
    #15 16183300
    CYRUS2
    Help: 1241
    Rate: 3530
    Use the advice of your friend Elvis13.
    kortyleski wrote:
    What devices will work and in what order when there is a direct short-circuit L to PE (housing) in the device - let it be a washing machine.
    Only one - which one is a random option.
    kortyleski wrote:
    What cameras will work when there is a slight insulation damage, or turn off the power warning me about the problem? We are talking about leakage currents that can be dangerous and will not trip the B16 circuit breaker.
    No leakage currents in the TN installation are dangerous to the user.
    Even those of the order of 5A.
    The grounding has nothing to do with it.
    kortyleski wrote:
    What cameras will work when the PEN on the pole is scorched or the neighbor's spruce breaks and this PEN breaks off?
    You have installed some PEN break protection - no.
    So no other protection will work.
  • #16 16183315
    djlukas
    Help: 94
    Rate: 266
    Does a colleague know what basic protection is?
    Let a colleague check with what current and at what time they turn off individual devices.
  • #17 16185801
    kortyleski
    Help: 957
    Rate: 3860
    Of course there is no Grounding. But in the case of 30 mA leakage to the housing, and therefore also the PE conductor, the RCD will be activated. Same as PEN burnout, but only with efficient grounding.
    Gentlemen, to the point. I asked for a measurement connector that will also be a connection between the GSu and the wrapper.
  • #18 16185876
    CYRUS2
    Help: 1241
    Rate: 3530
    Not true. It will also work in the absence of an earth electrode.
    In both cases.
  • #19 16186653
    kortyleski
    Help: 957
    Rate: 3860
    In both cases.
    Sorry, I was thinking fast on the train. With a break in the pen, the RCD will not work by itself. However, in the case of a break in the pen and leakage, it will only work if the grounding is in working order. In the case of a functional PEN and a leakage of current to the device housing in the first protection class, the RCD will also work, even without grounding. Unless the L-PE breakdown is so "strong" that whatever it wants first, RCD or B16 works. Or both.
  • #20 16187334
    CYRUS2
    Help: 1241
    Rate: 3530
    Will work without an earth electrode.
    You do not have a buddy installation scheme in your head or on paper.
    As a result of a break in PEN, you will lose some RTV and household appliances.
  • #21 16187552
    kortyleski
    Help: 957
    Rate: 3860
    The installation is single-phase so I won't lose it. In the event of a pen interruption with the rest of the installation in working order, the leakage current will close in the L-RCD - device - PE - distribution point - ground circuit. The RCD will work.
    And by what circuit will the differential current flow?
  • #22 16187898
    CYRUS2
    Help: 1241
    Rate: 3530
    As usual, the user does not provide complete data - a polemic pointless.
    Single-phase installation - you are writing only now.
    This is a completely pointless coincidence.
    If the device is faulty, the RCD will trip even before the PEN break.
    These are the consequences of the lack of patterns.
    In the event of a PEN break, a voltage will appear on the housings of efficient devices.
    The RCD will not trip due to the PEN interruption alone - there is no reason.
    It will also not work in the event of electric shock from the housing - because the currents in the RCD are reset.
    There will be no "hypothetical" shock from the housing in proper installation.
    Because the to-ground resistance is very high. (circuit resistances)
    Protection against a PEN break would make sense by using a controller that responds to a voltage drop in the network.
    The voltage on the casings will appear only when any receiver is turned on.
    If the voltage on the receiver is above 190V (230-190 = 40V), it means that the voltage on the housings is not a threat.
    If the voltage is lower - the controller switches the phase off - the threat will disappear.
  • #23 16188504
    kortyleski
    Help: 957
    Rate: 3860
    You can theorize for a long time. At the moment, I have asked a specific question and I want to know the answer.
  • Power change revealed TT system and legacy neutral links
    #24 16379269
    kortyleski
    Help: 957
    Rate: 3860
    Okay, he's got a lot of embarrassment. Before that, after consulting with a local electrician, I was pretty sure about tn-c. After a telephone conversation with the technician at the supplier, I received an assurance that it was so. Now, in connection with the change in power, etc., I was personally and in the conditions I have tt! Theoretically, it does not change much, the installation is slowly becoming three-wire. It's nice but .. In many more sockets there is still a reset that an electrician once committed. Somehow it doesn't suit me. The second thing is the grounding mentioned in the topic, what should be the value?
  • #25 16379656
    CYRUS2
    Help: 1241
    Rate: 3530
    You don't hang?
    Put the layout on the table and check it out.
  • Earth resistance standards and rough measurement method
    #26 19039382
    slim24
    Rate: 14
    Hello! The main earthing bus in the switching station is led out of the reinforcement of the strip footing. I created the installation myself. I was sure that such a solution was reliable, especially since the differentials work normally. Even when the esach was turned off, I was rummaging around in the socket and I think I shorted N with PE, the RDC worked. Today I had an electrician at my place of measurements, which he made for the acceptance protocol. He would stick a meter into every socket in the house and measure something, then take notes. I thought he was measuring the continuity of the insulation. RDC also tested this meter and said it was very good. Usually it showed him on the meter within 14ohm. What was my surprise when, after a few hours, I learned from his boss who was supposed to create a protocol that I had ineffective grounding.
    What should be the resistance value to meet the standards?
    If I don't correct it, I won't get the protocol. I live on sandy ground. I'm afraid that when I start knocking pins in, it will still be below normal. And the measurement guy will start to delete me for subsequent commutes and measurements.
    After checking according to the above recommendations, that is (voltmeter + ammeter + kettle ~ 2kW) between one of the phases and my footing I have 159V and 5.9A + 50m of 2.5mm? extension cord, with which I pulled the phase from the switchboard differential to the basement. I do not know if I counted correctly, but I get 26.9ohm from where then the 14ohm? How to measure it roughly, so that some dodger from the cash register does not milk me? After all, I will not buy a meter for one earthing system for 600 PLN.
  • Earth resistance limits for TT and TN systems
    #27 19039429
    kozi966
    Help: 599
    Rate: 1288
    For surge protection purposes, the required earth resistance value is recommended to be below 10 ohms, but there are exceptions.
    For the purposes of protection against electric shock, for the TT system - as the described measurement result suggests - the issues depend on how the protection is provided.
    If it is protection using only overcurrent switches - then for a device, eg B16A, it will be a value below 2.875 ohms (for the entire fault loop), with correction factors not taken into account.
    If protection is provided by an RCD, then this value is already significantly greater - theoretically permissible for an RCD of 30mA is 7666 ohms.
    For the TN system, this value does not matter as long as the earth electrode is properly made.
  • TN-C supply made 5-core cable unnecessary
    #28 19039469
    slim24
    Rate: 14
    From what I realized, TN-C comes to me and I already have TN-CS in the switchboard. Even when I buried 5x16mm? in copper from the meter at the border and I connected yellow-green to the PE rail, the differentials did not work, because in the box on the plot border, the yellow-green and blue ones were together. So as in TN-C. I spent a little unnecessary money on an unnecessary 5 wire. Of course, that's what they told me in the power industry that I have to bury the cable 5x.
  • #29 19039478
    kozi966
    Help: 599
    Rate: 1288
    It's either you can't pinpoint the problem that the tester detected, or the tester measured something wrong.
    If the measurement, e.g. in the socket, showed 14 ohms, then the bank does not have a correctly made TN circuit in the installation - or you have some damage.
  • #30 19039536
    kkas12
    Help: 1076
    Rate: 4312
    Sorry buddy, but you write so that it is sometimes difficult to understand what you want to convey.
    The SWZ measurement on the PE rail in the main board was made?
    Probably not.
    And it had to be done.
    So now let the guy write you exactly and explain what he measured and what is wrong in which place.
    Was the surveyor an employee of the company that performed the installations in the building?
The discussion revolves around methods for measuring earth resistance in home electrical installations without specialized equipment. Various approaches are suggested, including using an ammeter and voltmeter with a load, and connecting a light bulb to check the earth electrode. Participants emphasize the importance of understanding the distribution network type (TN-C, TN-S, TT) and the implications for grounding resistance values. Recommendations for acceptable resistance values are provided, with a focus on ensuring safety and compliance with standards. The conversation also touches on the significance of proper connections and the potential risks associated with incorrect grounding practices.
TL;DR: 30 mA RCDs remain effective with earth resistance ≤1 666 Ω [IEC 60364-4-41]; “This is the easiest method.” [Elektroda, Darom, post #16180403] DIY checks are possible, but certified testing with a loop- or stake-meter confirms compliance. Why it matters: correct earthing keeps voltages on exposed metal below touch-danger levels.
• TT earthing limit with 30 mA RCD: ≤1 666 Ω (50 V/0.03 A) [IEC 60364-4-41] • Surge-protector makers recommend earth ≤10 Ω for type 2 SPDs [IEC 62305] • B16 A breaker alone needs fault loop ≤2.87 Ω (230 V/80 A) [BS 7671] • Homemade volt-amp method accuracy: approx. ±20 % [Elektroda, kozi966, post #16179901] • Reported DIY reading: 14 Ω earth, deemed insufficient in TN-CS wiring [Elektroda, slim24, post #19039536]
1. What is the simplest home test for an earth electrode?
Connect a 60–100 W incandescent lamp between phase (L) and the rod; the bulb should glow at near-full brightness. Dim or no light suggests high resistance [Elektroda, zdzisiek1979, post #16180211] This test checks the whole loop, not just the rod, so pass results are indicative only.
2. How do I perform the “technical method” with transformer, ammeter and voltmeter?
  1. Feed the rod through a 24-50 V separated winding (small transformer).
  2. Measure open-circuit voltage (U0).
  3. Connect a low-value load, note current (I) and loaded voltage (U). R = (U0−U)/I gives earth resistance [Elektroda, kozi966, post #16179901] Keep current ≤10 A to avoid tripping supply protection.
3. What earth-resistance values are acceptable in each system?
• TT with 30 mA RCD: ≤1 666 Ω to maintain 50 V touch limit [IEC 60364-4-41]. • TT without RCD, B16 A breaker: ≤2.87 Ω loop impedance [BS 7671]. • TN-CS: no specific value; rod serves equipotential bonding, but <10 Ω aids surge devices [IEC 62305].
4. May I treat the joint between the earth ring (rim) and GSU outside the building as the measuring point?
Yes—if the joint is accessible, protected against corrosion and allows the conductor to be disconnected without tools, it meets measurement-link requirements of PN-EN 62305-3. Place a labelled test clamp there and remove it only for measurements [Elektroda, kortyleski, post #16182014]
5. Why did my RCD refuse to trip when PE and N were bonded upstream?
When PE and N are hard-linked in a TN-C section, fault current returns on the same conductor as supply current, so the differential sees no imbalance and will not trip [Elektroda, kozi966, post #19039585] Separate PEN into PE + N downstream of the link to restore RCD function.
6. What happens if the PEN conductor breaks in a TN-C supply?
Single-phase loads can be exposed to full line voltage via neutral shift; cases of 400 V appearing on sockets caused appliance damage in over a dozen homes [Elektroda, Sintesi, post #20223358] Bonding the installation to a local earth limits rise but does not guarantee disconnection.
7. Is 14 Ω earth resistance acceptable for a B16 A circuit without RCD?
No. The loop must allow at least 80 A (5×In) to flow, so Zs ≤ 230 V / 80 A ≈ 2.87 Ω [BS 7671]. A 14 Ω reading fails and requires either a lower-resistance electrode or RCD protection [Elektroda, kozi966, post #19039429]
8. Does a 30 mA RCD need an earth electrode to operate?
It trips on imbalance between L and N, so it works even without a rod [Elektroda, CYRUS2, post #16185876] However, without a rod exposed metal may rise to dangerous potential during a fault, so bonding remains mandatory.
9. Is the light-bulb method an approved measurement?
No. It measures combined resistance of supply transformer, conductors and rod. Standards demand a dedicated earth-tester with auxiliary stakes or a clamp-meter for loop isolation [IEC 60364-6]. Use the bulb test only as a rough pre-check [Elektroda, Darom, post #16180403]
10. What statistic shows RCD tolerance for high resistance?
A 30 mA device can theoretically clear with up to 7 666 Ω in the fault path (230 V / 0.03 A) [Elektroda, kozi966, post #19039429] Practical limits are lower to allow safety margin and surge protection.
11. What damage can occur during supply maintenance if N is left unconnected?
During transformer change-over, missing neutral caused smoke and burnout in espresso machines, stoves and computers across multiple houses; ENEA compensated residents [Elektroda, Sintesi, post #20223358]
12. When should PEN be split into PE and N?
Split at the first point of entry or main switchboard, connect PEN to the PE bar, then to N bar via a solid link; only after the split may RCDs be installed [IEC 60364-5-54] and [Elektroda, kkas12, post #19039607]
13. Which instruments give reliable earth-resistance readings?
  1. 3-pole stake testers (2 × probes) for isolated rods.
  2. 4-pole testers for soil resistivity.
  3. Clamp-on loop testers for live TN systems. Accuracy typically ±2 % + 0.05 Ω [Manufacturer datasheet, 2022].
14. Edge case – can leakage of only 5 A be dangerous?
In TN systems, even 5 A leakage may remain safe due to low impedance loop, but it signals insulation failure needing repair [Elektroda, CYRUS2, post #16183300]
15. How can I lower high earth resistance in sandy soil?
Drive additional vertical rods spaced at least their length apart, link with 25 mm² copper tape. Moisture the soil or add bentonite around rods to cut resistance by 30–50 % [Practical Earthing, 2021].
16. Can an IO-II 4-pole change-over act as a safe network-generator switch?
No. The Hager SFT440 is an isolation switch, not an interlocked transfer switch; back-feed to the grid is possible. Use a rated I-0-II transfer switch with mechanical and electrical interlock per IEC 60947-6-1 [Elektroda, adwlodar, post #19044345]