Hello. I am modifying the home installation a bit and hence the question. While I can handle the measurement and can handle it, I need to measure the earth resistance. I don't have any specialized equipment at the moment. Any advice?
Czy wolisz polską wersję strony elektroda?
Nie, dziękuję Przekieruj mnie tamkj1 wrote:Do you have an ipz meter?
Darom wrote:You can measure the static value of the earth resistance using the technical method.
kortyleski wrote:What type of distribution network - connection conditions.At the moment, I have ONE copper circuit of 1.5 mm square on which hangs a kettle, washing machine, dishwasher and thermal bath. sometimes the oven. Happy what? It used to be like this ...
CYRUS2 wrote:What type of distribution network - connection conditions.
kortyleski wrote:So when I do a pen separation (TN-C)
zdzisiek1979 wrote:I once read about a patent somewhere in radio broadcasters to check the earth electrode, you need to connect a 100W bulb. Earth electrode - light bulb - phase how much truth is I do not know. Have any of you heard about such a patent?
zdzisiek1979 wrote:I once read about a patent somewhere in radio broadcasters to check the earth electrode, you need to connect a 100W bulb. Earth electrode - light bulb - phase how much truth is I do not know. Have any of you heard about such a patent? Heard, read?
Quote:The total resistance of the transformer windings, wires, tested earthing and the neutral point earthing of the supply network are measured then. If the earth resistance, measured in this way, does not exceed the permissible value, then the tested earth resistance is acceptable. "
elvis13 wrote:A short-circuit loop in a properly made TN-CS is completely metallic (L-PE and PE, after all, "comes out of" the PEN in TN-C).
elvis13 wrote:What specific condition does the colleague want to check?
elvis13 wrote:It's best to draw a diagram of the installation with cameras and think how the electricity will flow.
elvis13 wrote:
And I propose to find out what influence the TN earth electrode has on the SWZ![]()
elvis13 wrote:It's best to draw a diagram of the installation with cameras and think how the electricity will flow.
kortyleski wrote:Use the advice of your friend Elvis13.I have it in my head for a long time.
kortyleski wrote:Only one - which one is a random option.What devices will work and in what order when there is a direct short-circuit L to PE (housing) in the device - let it be a washing machine.
kortyleski wrote:No leakage currents in the TN installation are dangerous to the user.What cameras will work when there is a slight insulation damage, or turn off the power warning me about the problem? We are talking about leakage currents that can be dangerous and will not trip the B16 circuit breaker.
kortyleski wrote:You have installed some PEN break protection - no.What cameras will work when the PEN on the pole is scorched or the neighbor's spruce breaks and this PEN breaks off?
kortyleski wrote:I will implement the basic protection through the SWZ.
kortyleski wrote:1) What apparatuses will work and in what order when there is a direct short-circuit L to PE (housing) in the device - let it be a washing machine.
CYRUS2 wrote:kortyleski wrote:
What cameras will work when there is a slight insulation damage, or turn off the power warning me about the problem? We are talking about leakage currents that can be dangerous and will not trip the B16 circuit breaker.
No leakage currents in the TN installation are dangerous to the user.
Even those of the order of 5A.
The grounding has nothing to do with it
kortyleski wrote:Not true. It will also work in the absence of an earth electrode.But in the case of 30 mA leakage to the housing, and therefore also the PE conductor, the RCD will be activated. Same as PEN burnout, but only with efficient grounding.
CYRUS2 wrote:kortyleski wrote:Not true. It will also work in the absence of an earth electrode.But in the case of 30 mA leakage to the housing, and therefore also the PE conductor, the RCD will be activated. Same as PEN burnout, but only with efficient grounding.
In both cases.
kortyleski wrote:Will work without an earth electrode.However, in the case of a break in the pen and leakage, it will only work if the grounding is in working order.
CYRUS2 wrote:Will work without an earth electrode.
kortyleski wrote:Single-phase installation - you are writing only now.The installation is single-phase so I won't lose it.
kortyleski wrote:This is a completely pointless coincidence.In the event of a pen interruption with the rest of the installation in working order, the leakage current will close in the L-RCD - device - PE - distribution point - ground circuit. The RCD will work.
slim24 wrote:What should be the resistance value to meet the standards?