Redistributing 3 Phases for Multiple Appliances: 2 Refrigerators, Oven, Microwave, Radio
wilk2002 13470 25
Can I feed three single-phase sockets from three different phases using one shared neutral in a 5x2.5 mm cable, and what current would then flow in the neutral conductor?
The neutral current in a 3-phase setup is the vector sum of the phase currents, so it can be very small or even close to zero when the three phases are similarly loaded [#17661714][#17674692] However, the thread’s advice is not to build three separate socket circuits with one shared neutral: each circuit should have its own L+N+PE, and a shared neutral between phases is considered unsafe and impractical [#17664886][#17664924] The main risks mentioned are overload/overheating of the neutral, bad/loose neutral connections, and the possibility of putting phase-to-phase voltage onto appliances if the neutral opens [#17664110][#17664886] If you want to spread the load across phases, the recommended solution is to run separate properly protected circuits from the switchboard rather than tying multiple single-phase outlets to one neutral [#17661758][#17664241]
  • #1 17661687
    wilk2002
    Good morning,
    I need to redo the sockets in the apartment. Currently I have 3 sockets on one phase (3x2.5mm wire). Standard and typical installation as in new blocks (TN-S). I want to connect receivers to these three sockets: two refrigerators, an oven, a microwave and a radio. Of course, one phase can't handle it, so I have to modify it. I want to pull 3 phases from the switchgear and use them as follows: the first phase for refrigerators (ordinary household refrigerators), the second phase for the oven, the third phase for the microwave and radio. And now I come to the question part. Since there is little space in the switchgear, the cables are arranged tightly, can I replace the current 3x2.5mm cable with a 5x2.5mm cable and use one Neutral wire for all receivers? To clarify the question: what current can I expect on the neutral wire, unfortunately I cannot calculate it myself. Is such an installation a safety hazard or may it not function properly?
  • #2 17661714
    xury
    Automation specialist
    Help: 878
    Rate: 1498
    The current on the neutral is the geometric sum of the phase currents. It follows that the closer the load on each phase is to each other, the lower the total current on the neutral conductor. So if all three pradyys are equal then the geometric sum will be zero.
  • #3 17661758
    Plumpi
    Heating systems specialist
    Help: 874
    Rate: 2678
    Such a system will work, and theoretically the current flowing through the neutral conductor should never be greater than the highest current flowing in any of the phases.
    In the case of a 3-phase supply, if each of the phases is loaded with the same current, no current flows through the neutral conductor. Then the neutral wire is not needed.
    In practice, the value of the current in the N conductor may be higher if the connected devices introduce phase shifts and additional harmonics.
    Why just mix it up? Such a connection carries a number of problems, including damaging devices connected to 1-phase sockets, if the circuits are to be protected with a 3-phase differential. Unfortunately, such an installation cannot be secured with 1-phase differential circuits, and protection of this installation with one 3-phase differential circuit can damage devices powered by 230V.
  • #4 17661770
    mawerix123
    Help: 482
    Rate: 951
    wilk2002 wrote:
    Good morning,
    No combinations with 5x2.5 cable, separate single-phase circuits must be led out of the switchgear. Since the protection of a 3-phase cable will fit, it will also fit 3 1-phase protections.
  • #5 17661779
    xury
    Help: 878
    Rate: 1498
    I don't understand your way of thinking, how is connecting a three-phase RCD to damage devices? Damage to connected devices can only occur when there is a break in the main neutral. You just need to make sure that something like this can't happen and, of course, to choose the correct overcurrent protection.
  • #6 17661788
    Andrzej42
    Level 32  
    Help: 178
    Rate: 322
    As a colleague mawerix123 writes: if you have a renovation, you have a choice, so do it right.
    If the switchgear is too small, replace it - immediately with a larger one...
    Now you have a small problem, and if something goes wrong, then it will be a big problem.
  • #7 17661859
    wilk2002
    Thank you for such a quick response, I will add a few sentences to dispel doubts and clarify the situation:
    - the idea came from the fact that there are already so many wires from the switchgear that pushing the next two there is really problematic in practice. The laid wires would force them to be forged and repositioned to make room for new ones or, alternatively, to forge under the existing wires (in reinforced concrete :/) and pull the new wires crosswise under the existing ones. In short: it's dense.
    - the whole question refers only to these three specific sockets (for the mentioned receivers), the rest of the installation is made in a boxless system "in God's way", i.e. each L has its N in one cable (3x2.5mm)
    - in the switchgear at the input there is a three-phase differential with one N
    - Wires (3x2.5mm) from different phases are run on the flat and all their N's are gathered in the switchgear into one rail. "Run from different phases" means that the L's are derived from overcurrent protections connected with a three-phase bus, so every third overcurrent protection has the same phase and such an installation is distributed around the apartment.
    I hope this additional information clarifies the context, if I missed something please point it out to me.
  • #8 17662116
    Plumpi
    Help: 874
    Rate: 2678
    A 3-phase RCD also disconnects the N conductor. Dust, especially gypsum dust, bits of plaster often get inside. If such a particle gets between the N contacts, the "disco" begins. I don't think I need to write about the effects, because you probably know what's going on? I don't think I need to add that such a 3-phase differential does not even react to the lack of continuity of the N conductor, also on the contacts inside the differential.
    For typical 3-phase devices, this condition is not a problem, because for such devices the N conductor is not needed for proper operation.
    However, problems arise when 1-phase circuits are protected by 3-phase differentials.
    These are not theoretical considerations, but I have encountered such situations many times. The last one was earlier this month. As a result of such a failure of the RCD, the electronics of the gas boiler failed.
  • #9 17662764
    CYRUS2
    Help: 1241
    Rate: 3536
    Only the electronics of the stove - and the other receivers have not been damaged?
    The electronics of a gas oven can be damaged for an unspecified reason.
    These devices "have it".
  • #10 17662813
    Plumpi
    Help: 874
    Rate: 2678
    Just the whole house is powered from a different box and from a different differential. Unfortunately, also 3-phase.
    The differential that failed is in the boiler room and powers only the boiler room. If the whole house was powered from it, the losses would probably be higher.
    The differential tube was probably finished off with dust and coal and ash dust, because previously there was a fine coal boiler used there.
  • #11 17663072
    Brivido
    Help: 226
    Rate: 430
    Although I have not had contact with damage strictly by RCDs or 4-pole disconnectors, but once the connection from the differential circuit with the N outlet strip loosened after several years and there were losses in some equipment.
  • #12 17664085
    wilk2002
    Dear Gentlemen,
    thank you for your replies. Please help me understand them because I have doubts. Some of you wrote that I have to run 3 separate wires to the three sockets so that each socket has its own Neutral, but can you please tell me the reasons for this recommendation? If I don't do this, do you think I will damage the receivers now or in the future? Why, in your opinion, should I not pull 5x2.5mm and power three sockets from three phases, leading only one Neutral from them?
    Others of you have pointed out possible problems with the three-phase differential. Only that let me point out that it would be a separate problem in the apartment, because this is exactly the installation that was provided by the developer in the apartment. There is a three-phase differential at the input with one N. And all three phases have been "randomly" distributed around the apartment, the overcurrent rail simply distributes the phases 1, 2, 3 in a cycle after overcurrent protection and in this way the phases go to the installation, from which all their N's are collected on one neutral rail, so already without any modifications of mine, the developer has provided in the switchgear such a scheme that Neutral wires from different phases are collected on one rail and through the differential are connected to the Neutral "output" from the apartment. So, according to some of you, the installation from the developer can cause problems?
    If I missed something or misunderstood something, please correct me. May I ask for your comments, what do you think about the above summary? That is:
    1) Can I connect three outlets to three phases and use one Neutral for all three outlets? This is the original question of this thread
    2) Do you think the installation from the developer is "faulty" or could it be?
  • #13 17664110
    retrofood
    Help: 1140
    Rate: 4800
    So that you don't ever power the devices connected to these sockets with phase-to-phase voltage. Why don't you listen to your elders if they're giving you good advice?
    wilk2002 wrote:
    that Neutral conductors from different phases are collected on one busbar
    Exactly. All of them connect only on the bus. It's not like you're running one around the house.
  • #14 17664175
    wilk2002
    I listen as much as I can, I just want to understand and learn.
    So if I run the same phase in all three cores, but use one N core, will it be ok? I don't have to push 3 phases, I can choose one (I just thought it would be better because I will spread the load over the phases).
    It's really cramped in there... ;) ... I would have to redo the entire switchboard just to have these three sockets on separate Neutrals, demolition for 2-3 days instead of a 2-3h job.
  • #15 17664237
    mawerix123
    Help: 482
    Rate: 951
    wilk2002 wrote:
    but can you please give reasons for this recommendation?
    Example.... You are planning one socket for the oven and the regulations are clear, each device above 2kW must have a separate circuit ... (CIRCUIT i.e. L+N+PE) and not a phase wire.
    Another thing is the protection .... a 3P circuit breaker will be used, which will turn off everything when activated on one of the phases :?:
    And the dragons flew over the city.
  • #16 17664241
    retrofood
    Help: 1140
    Rate: 4800
    It will not! With each phase conductor, you are to run separate N and PE conductors! And don't try to wipe your face with glass, because it's not fun.
    Added after 52 [seconds]:
    wilk2002 wrote:
    ... I would have to redo the whole switchgear
    This is switchgear not a separation.
    You have perform well And if you don't like it, why are you asking?
  • #17 17664473
  • #18 17664493
    retrofood
    Help: 1140
    Rate: 4800
    plum1978 wrote:
    I do not support what you want to do, because it is certainly not a good solution, but on the other hand, demonizing a 3-phase RCD for 1-phase installations is funny to me.
    Please note that your friend wants to run a 3-phase 1 (in words: one) N wire from this RCD and branch it along the route. And this is the problem you deign not to notice. Might be less fun.
  • #19 17664710
  • #20 17664781
    retrofood
    Help: 1140
    Rate: 4800
    plum1978 wrote:
    I'm already blind from the monitor (next year I'll buy Eizo or Nec), but I'm not quite thinking. Of course, the idea of the author of the post is not the best / correct, but ask yourself if he / his wife will use these devices industrially like in the kitchen in the canteen, or maybe occasionally like each of us and whether, despite the asymmetric load, N will lead to the limit temperature destructive to insulation. In this case, I would be more worried about a good connection of 4 N wires, as well as damage to the RCD in the N track.
    I am not worried about the temperature, but about the break in the N wire in a 3-phase installation. Besides, there is no trace of PE in the author's statements. And the RCD is supposed to be...
    Are you serious now?
  • #21 17664872
    wilk2002
    Once again, thank you very much for the discussion and all the comments. I particularly appreciate the practical approach to my problem. It is clear to me that according to the art, three separate circuits based on three 3x2.5mm wires should be made. However, I am asking you to evaluate the implementation of such an installation on one Neutral conductor so that I can save a lot of work and obtain a safe and functioning effect in home conditions for the above-mentioned receivers. In order to dispel doubts about my intentions, I allowed myself to put together a diagram of the planned connection. In my intentions, PE will not die, all three circuits will be secured with overcurrent, and the "bridging" of N'ki and PE will take place in the first box to which I would lead 5x2.5mm.
    The "scheme" is located at https://prnt.sc/m1gfci
    PS: Of course, there was a typo in the diagram, instead of RDC it should be RCD. It's getting late and that's why :/
  • #22 17664886
    Plumpi
    Help: 874
    Rate: 2678
    What is the meaning of demolition 2-3 hours or 2-3 days if you do it for several dozen years?
    Running a common neutral for 3 phase wires (different phases) causes the problems I wrote about and is impractical, because you will have to make additional junction boxes and make sure that the connections are secure.
    If you lead a 5-wire cable from socket to socket to the next socket, connecting the wires to the terminals of the sockets, if the N cable loosens in one of the sockets, all appliances in the kitchen will burn.
    But running a common neutral wire and 3 wires connected to the same phase is extreme stupidity and playing with fate.
    You are probably surprised now - why?
    You see, with current, if you have a common neutral for 3 circuits powered from 3 different phases, the current returning through the neutral will never be greater than the highest current of any of the phases. If you start to load subsequent phases, the current in the N conductor decreases.
    For example, we have loads:
    1 phase conductor L1 - 10A
    2 phase wire L2 - 10A
    3 phase wire L3 - 10A
    N = 0A (zero)
    No current flows through the neutral wire.
    But let's now take an identical situation, but
    2 phase wire L1 - 10A
    3 phase conductor L1 - 10A
    N = 30A (sum of currents from all phase conductors)
    Overcurrent protections are not only used to protect the installation in the event of short circuits, but also limit the value of the current flowing in the wires, i.e. they also protect the wires against overload/overheating.
    Unfortunately, in such a situation as above, the neutral conductor may be overloaded and the contacts burnt, which in the case of standard sockets have a strength of 16A. This wire can burn up somewhere in the box or switchgear.
    A few years ago I was asked to repair the installation in a detached house built by a developer. It turned out that the whole house almost burned down. The distribution box was covered with a wardrobe, and clothes hung in the wardrobe.
    The electrician who performed the installation there did it exactly as you want it to be done, i.e. the entire installation was divided into lighting and socket circuits.
    It's just that several phase wires, each with a separate 20A protection, and one neutral wire were led to both the lighting and the sockets. Unfortunately, the house was powered by 1-phase, because it was cheaper. The developer was "riding" maximally at cost.
    As a result, the terminal block of the neutral conductor in the distribution box burned up. Puffs of smoke appeared. Thanks to the fact that it happened during the presence of the household members, they managed to throw all the clothes out of the wardrobe and disconnect the power supply in time before the fire broke out. But the wall remained sooty. There was a burning smell throughout the house.
    When I saw it, my hair stood on end. I called the electrician who did the installation. He explained that the developer told him to do so. Unfortunately, he built several houses there, and in each of them the same problem.
    I probably have pictures of that box somewhere. If I find it, I'll throw it.
  • #23 17664924
    CYRUS2
    Help: 1241
    Rate: 3536
    This is a "pure" operational recommendation.
    As in the circuit with a receiver above 2kW, you will turn on the additional ones
    receivers, it may inadvertently turn off the fuse - accidental overload. Just enough.
    There is no prohibition of connecting to any socket on a multi-socket circuit a receiver with a power of more than 2kW.
    If these are single-phase circuits, this cannot be done, because the N conductor must have the same cross-section as the N conductor.
    The 3+N circuit is a 3-phase WLZ.
    Dangerous situation. If the N comes loose in the box, you will damage the receivers.
    WLZ can be done, but it requires experience and the use of good quality elements.
    This poses a risk of failure also in the switchgear.
    In general, the N wires can be disconnected with impunity - this N from the WLZ just not.
  • #24 17674135
    wilk2002
    Thank you very much for all the answers. I didn't write back because of the New Year's Eve period :)
    I will take all your comments to heart.
    I have another question regarding the following:
    N = 0A (zero)
    This is probably elementary knowledge, but unfortunately I do not understand the above. It is logical for me to add up N'ki's load when I use one phase, but I don't know why the load will "cancel" when three different phases are fully loaded. What should I read to understand this? What should I look for to find out why this is happening? What do I need to learn to be able to calculate it myself or at least understand it?
  • #25 17674692
    Plumpi
    Help: 874
    Rate: 2678
    Because the three-phase network consists of three phases with sinusoidal waveforms, the voltages of which are shifted relative to each other by 120°
    This is what the graph of these waveforms looks like:
    https://www.wykop.pl/cdn/c3201142/comment_gfIDFnITNVbs7El3wtCrP6xUubtsnn8D.jpg
    If we take any time point on this graph and add up the voltages of all the phases, it will always be 0 (zero).
    Below the central axis, the graphs have a negative sign and above the positive sign.
    The same happens with currents if all phases are loaded with receivers of the same power.
  • #26 17674707
    Strumien swiadomosci swia
    Help: 1405
    Rate: 6430
    You don't have to learn anything, just do what you can and leave the electrics to the electricians.
    You too Plumpi.
The discussion revolves around the user's intention to modify the electrical sockets in their apartment to accommodate multiple appliances, including two refrigerators, an oven, a microwave, and a radio. The user seeks to redistribute the load across three phases due to the limitations of a single phase. Key concerns include the feasibility of using a 5x2.5mm cable with a single neutral wire for all appliances and the potential safety hazards associated with this setup. Responses highlight that while theoretically possible, using a common neutral for different phases can lead to issues such as overloads and damage to appliances if the neutral wire fails. Experts recommend running separate circuits for each appliance to ensure safety and compliance with electrical regulations, particularly for high-power devices like ovens. The importance of proper circuit protection and the risks associated with three-phase RCDs in single-phase circuits are also emphasized.
TL;DR: Up to 30 A can hit one 2.5 mm² neutral if three 10 A phase circuits share it, "It will not!" warns retrofood [Elektroda, retrofood, post #17664241] Break that neutral and 400 V phase-to-phase may toast appliances. Why it matters: Correctly separate neutrals avert overloads, fires, and costly kitchen downtime.
• Max safe current for 2.5 mm² Cu conductor: 20 A continuous (IEC 60364-5-52). • 4-pole RCDs disconnect N as well as 3 L poles (EN 61008). • Appliances >2 kW require dedicated circuit (Polish PN-HD 60364-7-702) [UKE, 2022]. • 23 % of residential electrical fires stem from wiring faults [NFPA, 2021]. • Typical 12-module consumer unit upgrade: €45–€80 hardware cost “ABB SZ2012”.
1. Why can’t I run three different phases on one shared neutral?
Because the neutral would carry the vector sum of three unbalanced currents. If any phase conductor loosens, the neutral can see the full phase current, overheat, or open—sending 400 V across 230 V devices [Elektroda, Plumpi, post #17664886] Separate N conductors keep fault currents within rated limits.
2. How much current flows in the neutral of a balanced three-phase load?
With equal, linear loads the instantaneous currents cancel and neutral current is theoretically 0 A [Elektroda, xury, post #17661714] Harmonics or unequal loads raise it, so designers still size the neutral equal to phase conductors.
3. What happens if the shared neutral breaks?
Phase voltages float; the most heavily loaded phase drags the star point, producing up to 400 V on lightly-loaded circuits. Users report burnt boiler electronics after N failure inside a dusty RCD [Elektroda, Plumpi, post #17662116]
4. Do I legally need separate circuits for a >2 kW oven?
Yes. National transposition of IEC 60364 states each fixed appliance exceeding 2 kW must have its own L+N+PE circuit and breaker [UKE, 2022]. This avoids nuisance trips and overheating of shared conductors.
5. Is a 4-pole (three-phase) RCD safe for single-phase sockets?
It can be, but clogging dust or gypsum between N contacts may stop neutral continuity while leaving phases energised, leading to overvoltage [Elektroda, Plumpi, post #17662116] Regular testing and clean enclosures mitigate the risk.
6. Can I keep one neutral if all three sockets use the same phase?
No. Wiring rules demand each line conductor in a final circuit be accompanied by its corresponding N and PE from origin to outlet to ensure equal impedance and fault-loop integrity [IEC 60364-5-54].
7. What cable size suits kitchen power circuits?
Use 3×2.5 mm² Cu for single-phase sockets up to 20 A. For a grouped run in insulation, derate by 0.8, giving 16 A usable load [IEC 60364-5-52].
8. How do I correctly redistribute loads over three phases?
  1. Install a larger consumer unit so three single-pole breakers align with L1, L2, L3.
  2. Run separate 3×2.5 mm² cables to each socket (oven, fridge pair, microwave).
  3. Label sockets with phase colour codes for service clarity. This maintains individual N and PE paths.
9. Is the developer’s one neutral busbar faulty?
Collecting neutrals on a single bar inside the board is normal; each circuit still has its own wire up to that point. The problem arises only when circuits share one conductor along the route [Elektroda, retrofood, post #17664110]
10. How often do wiring faults start fires?
Wiring or related equipment caused 23 % of U.S. home electrical fires in 2015-2019 [NFPA, 2021]. Neutral failures are a documented subset, underscoring strict segregation of conductors.
11. What’s the cost of upgrading the switchgear to fit more breakers?
A 12-module DIN consumer unit costs about €45–€80; add €5–€8 per single-pole breaker and €25 for a type-A RCD. Labour varies by region but averages €25/hour.
12. Must the PE (protective earth) follow every phase conductor?
Yes. PE must run in the same cable or conduit as associated live conductors to ensure low-impedance fault return and minimal inductive loop area [IEC 60364-5-54]. Skipping it violates safety codes.
13. Edge case: What if harmonic currents exist?
Switch-mode power supplies in fridges or ovens inject 3rd harmonics that add in the neutral, sometimes exceeding phase current by 30 % [Bernstein, 2019]. Oversize or separate neutrals prevent overheating.
14. “Can one neutral overheat before a breaker trips?”
Yes. Breakers monitor phase conductors only. A shared neutral can silently exceed 20 A while each phase stays below its 16 A breaker limit, leading to insulation failure [Elektroda, Plumpi, post #17664886] Quoting an expert: "Overcurrent protections ... limit the wires, not the shared neutral" [Elektroda, Plumpi, post #17664886]