wilk2002 wrote: retrofood wrote: wilk2002 wrote: Why, in your opinion, should I not pull 5x2.5mm and power three sockets from three phases, leading only one Neutral from them?
So that you don't ever power the devices connected to these sockets with phase-to-phase voltage. Why don't you listen to your elders if they're giving you good advice?
I listen as much as I can, I just want to understand and learn.
So if I run the same phase in all three cores, but use one N core, will it be ok? I don't have to push 3 phases, I can choose one (I just thought it would be better because I will spread the load over the phases).
It's really cramped in there...

... I would have to redo the entire switchboard just to have these three sockets on separate Neutrals, demolition for 2-3 days instead of a 2-3h job.
What is the meaning of demolition 2-3 hours or 2-3 days if you do it for several dozen years?
Running a common neutral for 3 phase wires (different phases) causes the problems I wrote about and is impractical, because you will have to make additional junction boxes and make sure that the connections are secure.
If you lead a 5-wire cable from socket to socket to the next socket, connecting the wires to the terminals of the sockets, if the N cable loosens in one of the sockets, all appliances in the kitchen will burn.
But running a common neutral wire and 3 wires connected to the same phase is extreme stupidity and playing with fate.
You are probably surprised now - why? You see, with current, if you have a common neutral for 3 circuits powered from 3 different phases, the current returning through the neutral will never be greater than the highest current of any of the phases. If you start to load subsequent phases, the current in the N conductor decreases.
For example, we have loads:
1 phase conductor L1 - 10A
2 phase wire L2 - 10A
3 phase wire L3 - 10A
N = 0A (zero)
No current flows through the neutral wire.
But let's now take an identical situation, but
1 phase conductor L1 - 10A
2 phase wire L1 - 10A
3 phase conductor L1 - 10A
N = 30A (sum of currents from all phase conductors)
Overcurrent protections are not only used to protect the installation in the event of short circuits, but also limit the value of the current flowing in the wires, i.e. they also protect the wires against overload/overheating.
Unfortunately, in such a situation as above, the neutral conductor may be overloaded and the contacts burnt, which in the case of standard sockets have a strength of 16A. This wire can burn up somewhere in the box or switchgear.
A few years ago I was asked to repair the installation in a detached house built by a developer. It turned out that the whole house almost burned down. The distribution box was covered with a wardrobe, and clothes hung in the wardrobe.
The electrician who performed the installation there did it exactly as you want it to be done, i.e. the entire installation was divided into lighting and socket circuits.
It's just that several phase wires, each with a separate 20A protection, and one neutral wire were led to both the lighting and the sockets. Unfortunately, the house was powered by 1-phase, because it was cheaper. The developer was "riding" maximally at cost.
As a result, the terminal block of the neutral conductor in the distribution box burned up. Puffs of smoke appeared. Thanks to the fact that it happened during the presence of the household members, they managed to throw all the clothes out of the wardrobe and disconnect the power supply in time before the fire broke out. But the wall remained sooty. There was a burning smell throughout the house.
When I saw it, my hair stood on end. I called the electrician who did the installation. He explained that the developer told him to do so. Unfortunately, he built several houses there, and in each of them the same problem.
I probably have pictures of that box somewhere. If I find it, I'll throw it.