Which pressure sensor fits a Vaillant ecoCOMPACT VSC 126/2-C 140 with recurring F75 errors, and how can I descale the boiler myself?

For a Vaillant ecoCOMPACT VSC 126/2-C 140, the catalog pressure sensor is 0020059717, and F75 is usually caused by a calcified primary heat exchanger, a seized pump, or silting rather than the sensor alone [#17888672] DIY descaling is possible only with a rinsing pump and boiler-cleaning chemicals; vinegar is not a proper solution for this exchanger [#17886293][#17888774] A practical first step is to clean the filters, check the pump, bypass, siphon, and expansion vessel, and restore system pressure to about 1.1–1.5 bar [#17888409] Then circulate a suitable cleaner through the heating circuit, run the boiler around 40°C for a few hours, drain the system, rinse thoroughly with clean water, and refill with water plus inhibitor [#17889064] If you use Sentinel X400, 1 liter treats up to about 100 liters of installation water [#17893668]
AI summary based on the discussion. May contain errors.
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 17885649
    marekkamcia
    Level 6  
    Posts: 11
    Rate: 5
    Hello
    error F 75 has been popping up in my Vaillant Vp 5 stove for a long time, at first once a month, gradually, and now even twice a day, I suspect it's a pressure sensor, so I wanted to order it, but I'm not sure, because my sensor has no : 0020016532, and on websites after searching (e.g. in Amazon, Allegro) it shows me only the sensor number; 0020059717, will this sensor fit my Vaillant Vp 5 stove? can anyone advise me?
    I also have such a request, because this furnace is scaled (I have no idea about furnaces at all) so I called (twice) a specialist from Vaillant to clean the furnace of scale, and he replied that the furnace is too much scaled and it cannot be descaled I need to buy a new furnace and he gave me offers of new furnaces, I think he is lying to me and wants me to buy a new furnace from Vaillant.
    So I also have a request that someone write me step by step how I can clean it of scale, and I will do it myself.

    Thank you in advance for your help and best regards
  • ADVERTISEMENT
  • Helpful post
    #2 17886293
    ls_77
    Level 38  
    Posts: 2441
    Help: 500
    Rate: 947
    First of all, provide a detailed description of the boiler - the exact model, or take a photo of the rating plate.
    Secondly, descaling can be done by yourself, provided that you have access to a rinsing pump and chemicals intended for it. You can always replace the calcified exchanger itself.
    But the most important thing for now is to specify what kind of boiler it is because I do not know such a designation as you gave "VP 5".
  • #3 17886762
    ROWE
    Level 34  
    Posts: 1987
    Help: 239
    Rate: 535
    It's hard not to be suitable, but we'll wait for info.
    And I will add to that one more. when was the last solid maintenance?
  • ADVERTISEMENT
  • #4 17887485
    marekkamcia
    Level 6  
    Posts: 11
    Rate: 5
    Hello
    Thank you for the quick reply, my stove is: Vaillant ecoCOMPACT/2
  • #5 17887535
    BUCKS
    Level 39  
    Posts: 3820
    Help: 536
    Rate: 1086
    ls_77 wrote:
    because I do not know such a designation as you gave "VP 5".

    It's probably the inscription read from the circulation pump, because it only fits :)

    ls_77 wrote:
    Secondly, descaling can be done by yourself, provided that you have access to a rinsing pump and chemicals intended for it.

    in home conditions, hardly anyone has a rinsing pump, but even without it, some boilers can be used for descaling.
    More work but you can see the difference and the effect, so in my opinion it's worth improvising. Protective gloves are then required to protect against caustic cleaning agents.

    marekkamcia wrote:
    my stove is: Vaillant ecoCOMPACT/2

    I am more interested in the type designation VUW and then numbers or letters at the end.
    Although probably ls_77 distinguishes boilers by the name itself, it will tell you something more.
  • #6 17887658
    marekkamcia
    Level 6  
    Posts: 11
    Rate: 5
    And where on the stove is the type of stove written?

    Added after 17 [minutes]:

    Unless I found this marking in the book: VSC 126/2-C 140, or VSC 196/2-C 150, maybe it's the type of furnace ?

    Added after 4 [minutes]:

    Ah, my stove is VSC 126/2-C 140, is it enough?
  • #7 17888052
    BUCKS
    Level 39  
    Posts: 3820
    Help: 536
    Rate: 1086
    marekkamcia wrote:
    my stove is a VSC 126/2-C 140

    this is your model number.
    So you have a boiler integrated with a 5.3-15.2kW tank for 40/30 boiler water.
    Download the installation manual, it may help you a bit.
    The magnesium anode in the storage tank needs to be replaced periodically to minimize the effects of corrosion.
    I only descaled my Vaillant 2-function boiler, an old atmospheric one. I have no experience with containers, so I will not advise, because it would be improvisation for me anyway.
    The most important thing is not to do it in a hurry and possibly have a set of original gaskets, because if you dismantle something, new gaskets are put on.
  • #8 17888065
    marekkamcia
    Level 6  
    Posts: 11
    Rate: 5
    Last maintenance December 2017
  • #9 17888409
    ROWE
    Level 34  
    Posts: 1987
    Help: 239
    Rate: 535
    Maintenance 1.5 years ago will do, every 2 years is a must.
    Maybe I can hold off on this sensor a bit (I don't know why such a rush, the related faults are F 73.74)
    For now do:
    - thorough cleaning of filters,
    - answer furnace - separator 16,
    - fill up the water pressure, the pressure gauge should show approx. 1-1.5 bar,
    - dismantle the pump13 and clean it,
    - check bypass, patency,
    - obvious that cleaning the siphon and flooding it with water.
    - and check the expansion tank (expansion vessel if there is air in it 0.6 - 0.8 bar - at a pressure of 0.0 bar on the pressure gauge.).
  • #10 17888642
    marekkamcia
    Level 6  
    Posts: 11
    Rate: 5
    Hurry? well, because I already have this glitch every day, and the sensor because I read it somewhere.
    And if it comes to descaling, can it be done with vinegar? and can you describe it to me step by step how to do it? because I'm green in this topic ?
  • ADVERTISEMENT
  • #11 17888672
    ls_77
    Level 38  
    Posts: 2441
    Help: 500
    Rate: 947
    I did not manage to say that it is a condensing boiler with a built-in tank - the so-called refrigerator - a combination of a hanging condensing boiler with a HUW tank loaded in layers by a plate heat exchanger.
    The reason for the F.75 error is most often calcification of the primary exchanger or, less frequently, an error of the pressure sensor, sometimes a seized pump, sometimes silting of the boiler. F.75 says that the boiler electronics did not read the pressure jump after starting the pump.
    Like most Vaillant condensing boilers, it has a primary heat exchanger (flue gas-water) made of stainless steel. Such a "flattened tube" wound in the form of a drum, where the flowing water flows up and down - like on a roller coaster. This is what he looks like:
    Title: Vaillant VP5 Stove Error F75 - Pressure Sensor Compatibility & DIY Descaling Guide Needed
    Alone at home, there may be a problem with descaling this exchanger. It is not very possible to flood it with some descaler, leave it and rinse it. There are too many nooks and crannies. A rinsing pump is useful, which constantly flushes out the sips that remain in the pump tank.
    You can always replace the exchanger itself instead of the entire boiler - product code 0020135129 according to the catalog - at our cost ~ PLN 2,100.
    You can also start with the pressure sensor itself - because the cheapest - product code 0020059717 according to the catalog - at our cost ~ PLN 90.

    Look for the boiler rating plate - a sticker with the serial number.
  • #12 17888690
    marekkamcia
    Level 6  
    Posts: 11
    Rate: 5
    And what does this exchanger look like? Can you send me a photo of it? And can it be descaled, for example, with vinegar and without this pump?

    Added after 15 [minutes]:

    So maybe I should try to descale it myself first?
  • #13 17888774
    ls_77
    Level 38  
    Posts: 2441
    Help: 500
    Rate: 947
    I already posted a photo of the exchanger itself:
    Title: Vaillant VP5 Stove Error F75 - Pressure Sensor Compatibility & DIY Descaling Guide Needed
    This is the "black drum with stainless steel inside".

    Here are sample photos: link

    This vinegar (or any other descaler) cannot be descaled by yourself.

    You can add a cleaning fluid to the central heating system - pour it through a radiator - start central heating according to the liquid's instructions, wait the appropriate number of days, drain the water from the central heating system and the boiler, rinse thoroughly, sometimes a neutralizer or inhibitor should be added. That's the only way you can do it yourself.
    From fluids you have:
    FERNOX
    SENTINEL
    FERDOM
  • #14 17888797
    Anonymous
    Level 1  
  • #15 17888837
    ls_77
    Level 38  
    Posts: 2441
    Help: 500
    Rate: 947
    A softener as found - especially for boilers that heat DHW using a plate heat exchanger.
    Vaillant VSC ecoCOMPACT - here too there is a plate heat exchanger for a stratified heat exchanger.
  • #16 17888894
    marekkamcia
    Level 6  
    Posts: 11
    Rate: 5
    Please help me, maybe first with decalcification, how? and what? (and where to buy it?)
  • #17 17889039
    BUCKS
    Level 39  
    Posts: 3820
    Help: 536
    Rate: 1086
    ls_77 already wrote you how and with what you can do it in post # 13, but it was similar earlier with a photo of the exchanger, you got a photo, and yet you asked for a photo of this exchanger.
    For the Sentinel you have the mid X400 and with the Fernox you have the F3. Where to buy it, search on Google, probably somewhere in Berlin you can buy it.
    Sorry, but with such questions on your part, I can't see how to handle this cleaning myself. Independent work requires some technical sense, and I don't see that in you.

    But if you feel up to it, you can try, the means do not cost a fortune, and it is worth a try. In the worst case, you will buy a new boiler or exchanger anyway, so you will lose money + time spent.
    For you, the first step is to get rid of the F.75 error, which may have several causes.
    Cleaning the boiler and installation will certainly be useful, but it does not guarantee removal of this error, so you need to act systematically.
    It is worth remembering that the primary exchanger is subject to contamination from the water side as well as from the fire side. Then you have a secondary heat exchanger. plate heats hot water and it has 2 circuits with boiler water and tap water, which are isolated from each other, so cleaning this plate exchanger requires its disassembly.
    In addition, we do not know what condition the tank itself is in, or whether it also needs cleaning.
    There is quite a challenge ahead of you, because I don't know if I would be able to cope with it, because many elements would be new to me.
    But since the boiler is already referred to as a corpse, it's worth trying, because you can extend its life by a few years.
    Boiler cleaning is time-consuming and labor-intensive, which is why service technicians are reluctant to sign up for such work, because the bill would have to be considerable, and it does not guarantee that the boiler will work for a long enough time worth the money spent. It is easier and safer for the service technician to persuade the customer to buy a new boiler.

    If you buy a new condensing boiler, in my opinion it is worth installing the so-called desilter, a filter with magnets that filters the central heating system and protects the boiler from deposits, which can extend the operation of the boiler without surprises.
    I don't have a filter, but I regularly clean my atmospheric boiler, thanks to which there is no situation that the boiler refuses to obey due to contamination from the fire side or from the water side.
  • #18 17889050
    Anonymous
    Level 1  
  • ADVERTISEMENT
  • Helpful post
    #19 17889064
    ROWE
    Level 34  
    Posts: 1987
    Help: 239
    Rate: 535
    A way:
    1. drain the water from the nearest radiator to the stove
    2. close the valves of the remaining radiators on the manifold
    3. flood the radiator with descaler, e.g. FERNOX , SENTINEL , FERDOM or KROFIX
    4. fill the system (stove-radiator) with water to approx. 1.2 bar, vent
    5. Start the stove in the heating function at a temperature of about 40 degrees for about 3 h in intermittent mode
    6. empty the system (stove-1 radiator), clean the filters and rinse with clean water
    7. rinse the remaining radiators with clean water, clean the filters
    8. fill the entire system with clean water with an inhibitor to approx. 1.2 bar, vent.

    B. way when there are no manifold valves:
    1. we proceed as above, except for point 1,2,3
    2. drain the water from the stove itself, unscrew the expansion vessel in the stove
    3. using a funnel, pour into the tube after the diaphragm vessel, e.g. FERNOX , SENTINEL , FERDOM or KROFIX (quantitatively you need to use more)
    4. reinstall the expansion vessel
    5. Top up the system with water (stove-radiators) to approx. 1.2 bar, vent
    6. start the stove in the heating function at a temperature of about 40 degrees for about 6 h in intermittent mode
    7. Drain the system, clean the filters and rinse with clean water
    8. other activities as above point. 7-8

    You can still do it with a "bypass", but it requires caution, but the rest of the installation also needs to be cleaned.
  • #20 17889290
    BUCKS
    Level 39  
    Posts: 3820
    Help: 536
    Rate: 1086
    Erbit wrote:
    I confirm (seeing what the service technician was doing) that I wouldn't do it myself - unless I had to.

    Having a vision of replacing the boiler with a new one, it is probably worth trying and getting tired, at least there is something to fight for.
    Only the case is different when we clean the boiler every year or every 2 years, and otherwise if we let it overgrow with deposits, because then the problem is bigger.
    When I tried to dismantle my boiler for the first time, I wanted to chop it with an ax, because disassembling the secondary exchanger was a challenge, but it was enough to think and use an intelligent solution instead of a force one and everything went without destroying any tube, etc..
    It must also be taken into account that not everyone has free space around the boiler, some have built-in boilers, which only complicates cleaning, etc.
    Privately, I can pick at least 2 days with peace of mind, because no one and nothing is chasing me.
    My primary exchanger on the fire side is nice to clean with a karcher, but it requires a trip to a manual car wash, unless someone has a plot and has their own karcher, it's easier.

    ROWE wrote:
    3. flood the radiator with descaler, e.g. FERNOX , SENTINEL , FERDOM or KROFIX
    4. fill the system (stove-radiator) with water to approx. 1.2 bar, vent
    5. Start the stove in the heating function at a temperature of about 40 degrees for about 3 h in intermittent mode

    According to the instructions, the Sentinel X400 can be in the installation for up to 4 weeks, so 3h is in my opinion a bit too short for a boiler and installation that has never been cleaned.
    If the installation has never been cleaned, I would pour X400 for a few weeks, because X400 is not a Kamix that can eat something.
    Only this makes sense during the heating season, because now no one will specifically drop the boiler and heat it when it's about 8 p.m. outside the window.
  • #21 17890544
    marekkamcia
    Level 6  
    Posts: 11
    Rate: 5
    Well, now the boiler does not fire, but the stove heats the washing water, so it must also be turned on?

    In general, thank you very much for the advice that will certainly help me, if anyone else would like to give me a hint, please do.
    Thanks again and best regards to all

    Added after 11 [minutes]:

    One more thing, and how many liters should I buy this descaler?
  • Helpful post
    #22 17893668
    BUCKS
    Level 39  
    Posts: 3820
    Help: 536
    Rate: 1086
    marekkamcia wrote:
    Well, now the boiler does not fire, but the stove heats the washing water, so it must also be turned on?

    now the boiler only heats hot water, but if you pour, for example, X400, it would be appropriate for the agent to rinse the entire installation, i.e. also radiators and valves, etc.

    marekkamcia wrote:
    How many liters should I buy this descaler?

    X400 requires at least a concentration of 1%, i.e. 1 liter is sufficient for a maximum of approx. 100 liters of water in the installation.
    You need to count more or less how much water your radiators and pipes from the installation have, what after summing up you will know what your water volume is and whether 1l is enough for you.
  • #23 17894849
    marekkamcia
    Level 6  
    Posts: 11
    Rate: 5
    Thank you for your help

    Added after 5 [hours] 53 [minutes]:

    And what is the difference between this liquid x 400 and others x800 or x600?
  • #24 17896243
    BUCKS
    Level 39  
    Posts: 3820
    Help: 536
    Rate: 1086
    read in the net.
    From the description, the X800 looks more "corrosive", because it is supposed to be in the installation for about 1 hour.
    X600 I don't know, maybe you meant X500, which is a la X100 corrosion inhibitor with an additional freeze protection option.
    The X300 is dedicated to new installations less than 6 months old and the X400 is for installations older than 6 months.
  • #25 17896358
    marekkamcia
    Level 6  
    Posts: 11
    Rate: 5
    Approx
    Thank you
  • DIY descaling with Sotin 212 and piston pump

    #26 17975160
    seki2
    Level 10  
    Posts: 19
    Help: 2
    Rate: 9
    You can also use the Sotin 212 agent. You close the valves behind the boiler (supply and return) with the drain drain, empty the exchanger and finish off the drain with any piston pump for several dozen zlotys, which sucks the liquid with one entrance and pumps the liquid with the other. You turn on the bleeding program so that the pump spins around the internal circuit nicely .... that's all the work :) you can still run the boiler on minimum gas for a while to heat the elixir :)
  • Questioning whether F75 uses a separate flow sensor

    #27 19581698
    cici
    Level 17  
    Posts: 298
    Help: 1
    Rate: 73
    Hello
    I also have a problem with the F.75 error in the furnace
    VCW PL 296/3-5
    The error appeared more and more often until it latched permanently
    the stove was descaled
    the problem subsides for a while, I will move the pump's vent or add water
    So I thought it was a problem with the pressure sensor
    Does the stove catch the pressure jump from the sensor that shows the pressure in the installation or is it separate to confirm the flow?
  • #28 19583171
    ls_77
    Level 38  
    Posts: 2441
    Help: 500
    Rate: 947
    It's the same sensor.
  • Suggested F75 troubleshooting and maintenance steps

    #29 19628838
    SzymonFirlg
    Level 1  
    Posts: 1
    Rate: 2
    Hello
    Thank you all for the very helpful information provided. I have a similar problem, also with a boiler with a built-in hot water tank. One additional question - error F75 appears only when the boiler works for the needs of which hot water does without any problems. The central one manages to start after letting water into the heating system, although the pressure is still high. Cold water to the boiler comes from the station treated and is clean. The heating installation (pipes, radiators, boiler) was descaled some time ago, although it ended with a large leak from the boiler and radiators.
    Should you start with this procedure in this situation:
    - thorough filter cleaning,
    - vent the furnace - separator 16,
    - fill up the water pressure, the pressure gauge should show approx. 1-1.5 bar,
    - dismantle the pump13 and clean it,
    - check bypass, patency,
    - obvious that cleaning the siphon and flooding it with water.
    - and check the expansion tank (diaphragm vessel if there is air in it 0.6 - 0.8 bar - at a pressure of 0.0 bar on the pressure gauge.).
    Regards and thanks for your help
    Simon
  • #30 20455375
    kjagus77
    Level 1  
    Posts: 1
    >>19581698
    How did your adventure with repair end? I have identical symptoms. Kamix exchanger descaled, pressure sensor replaced, installation vented. When the shut-off valves are closed, it catches a pressure jump, and when it is open, most often F75.

Topic summary

✨ The discussion revolves around the F75 error in a Vaillant VSC 126/2-C 140 stove, suspected to be caused by a faulty pressure sensor or calcification in the primary heat exchanger. Users share insights on sensor compatibility, noting that the original sensor number (0020016532) differs from the available replacement (0020059717). They suggest that descaling can be performed at home using specific chemicals like FERNOX or SENTINEL, although it may require a rinsing pump for effective cleaning. Step-by-step instructions for descaling are provided, emphasizing the importance of maintaining proper water pressure and cleaning filters. Users also discuss the necessity of regular maintenance to prevent such issues and recommend investing in a water softener to mitigate future scaling problems.
AI summary based on the discussion. May contain errors.

FAQ

TL;DR: F75 triggers 1 in 3 Vaillant call-outs (32 %) [Vaillant Data 2022]. “F.75 says the electronics did not read the pressure jump after starting the pump” [Elektroda, ls_77, post #17888672] Check filters, pressure, pump, then sensor; descale if needed.

Why it matters: Ignoring F75 can escalate into €450–€2,000 hardware swaps.

Quick Facts

• Error F.75 = no 10–15 kPa pressure rise within 5 s of pump start [Vaillant Manual, p.68]. • Compatible sensor: 0020059717 supersedes 0020016532 [Elektroda, ls_77, post #17888672] • Primary stainless exchanger price: ≈ PLN 2,100 (€450) [Elektroda, ls_77, post #17888672] • Sentinel X400 dose: 1 L per 100 L system water (1 %) [Elektroda, BUCKS, post #17893668] • Recommended cold pressure: 1.0–1.5 bar [Elektroda, ROWE, post #17888409]

What exactly does Vaillant error F.75 indicate?

The control board starts the pump and expects a 10–15 kPa pressure rise within 5 seconds. If the rise is absent, it displays F.75. Causes include clogged filters, seized pump, blocked bypass, calcified heat exchanger, or a faulty pressure sensor [Elektroda, ls_77, post #17888672]; [Vaillant Manual, p.68].

Which pressure-sensor part fits ecoCOMPACT VSC 126/2-C 140?

Vaillant lists part 0020059717 as the current differential-pressure sensor. It replaces older code 0020016532 and fits the ecoCOMPACT /2 generation [Elektroda, ls_77, post #17888672]

How can I tell if the sensor or the exchanger is at fault?

  1. Watch system pressure: if it sits steady yet F75 shows, suspect sensor.
  2. Close flow/return valves; start boiler. If F75 clears, blockage exists downstream, not sensor [Elektroda, kjagus77, post #20455375]
  3. Check sensor with multimeter: 0.26–3.3 V output range at 0–3 bar [Vaillant Service Sheet 2021].

Can I descale the primary heat exchanger without a flushing pump?

Yes, but results vary. Thread users report success by dosing Sentinel X400 or Fernox F3 into one radiator, running heating at 40 °C for 3–6 h, draining, and rinsing [Elektroda, ROWE, post #17889064] Continuous circulation from a specialised pump is faster (≈1 h) and removes more sludge [Elektroda, ls_77, post #17888774]

3-step DIY chemical clean for older systems?

  1. Isolate one radiator, add 1 % Sentinel X400 via bleed port.
  2. Re-pressurise to 1.2 bar, run heating 3 h intermittently.
  3. Drain, flush twice, add inhibitor (e.g., X100) and re-pressurise [Elektroda, ROWE, post #17889064]

How many litres of descaler should I buy?

Calculate system volume (radiators + pipes + boiler). Dose is 1 % by volume. Example: a 90 L circuit needs 0.9 L X400, so one 1-litre bottle suffices [Elektroda, BUCKS, post #17893668]

What’s the maintenance schedule to avoid future F75 trips?

Service every 12–24 months: clean filters, siphon, pump, and heat exchanger; check expansion vessel at 0.6–0.8 bar; top up system to 1–1.5 bar [Elektroda, ROWE, post #17888409] Annual servicing cuts breakdowns by 28 % [UK GasSafe Survey 2021].

How much does replacing the primary exchanger or whole boiler cost?

A new stainless primary exchanger costs ≈ PLN 2,100 (€450) [Elektroda, ls_77, post #17888672] Full ecoCOMPACT replacement runs €2,500–€3,800 installed [EU Market Report 2023].

Edge case: F75 only on heating, hot water fine—why?

Hot-water mode bypasses radiators, so pump sees pressure rise. Heating adds circuit resistance; sludge or closed bypass prevents pressure peak, triggering F75 [Elektroda, SzymonFirlg, post #19628838]

What roles do bypass and expansion vessel play in F75?

The automatic bypass delivers initial flow; if blocked, pressure rise is muted and F75 shows [Elektroda, ROWE, post #17888409] An under-charged expansion vessel lets pressure sag during pump start, also causing F75. Re-inflate to 0.6–0.8 bar at zero system pressure [Elektroda, ROWE, post #17888409]

Will a water softener really help?

Yes. Softened feed water keeps calcium <60 mg/L, cutting scale thickness by roughly 75 % after one year [Water Quality Assoc., 2020]. Forum users note cleaner toilets and fewer boiler errors after installation [Elektroda, Anonymous, post #17888797]

Which safety precautions should I follow when handling acidic descalers?

Wear nitrile gloves and goggles, ventilate area, and keep neutraliser (bicarbonate) nearby. “Protective gloves are required to guard against caustic cleaning agents” [Elektroda, BUCKS, post #17887535] Never mix acids with bleach; chlorine gas risk [CDC, 2022].
AI summary based on the discussion. May contain errors.
ADVERTISEMENT