Painkiller1 wrote: Has anyone had a similar problem? What is the cause and what will need to be fixed?
The reasons are, as he described:
ls_77 wrote: The reason for its operation was very high temperature. You need to check what caused the overheating - dirty exchanger in the combustion chamber or stony on the water side or system with high air circulation and was not receiving heat.
It is often damaged by the user himself, namely the air in the exchanger after draining the water, e.g. when checking the pressure of the diaphragm vessel and sudden, incompetent filling of the installation, and then quick boiler start - the fuse overheats.
(see # 2:
https://www.elektroda.pl/rtvforum/topic3770267.html#19201475) Basically not a sensor, but a thermal fuse, so if it is good it should be NC, the resistance should be close to zero "0" ?.
Otherwise this thermal fuse inside irreversibly becomes NO, or its resistance is much higher than "0" ?, and the furnace electronics see it as damage to the exchanger.
For the main plastic exchanger, I do not recommend bridging this fuse for safety reasons!
Therefore, it is not commercially available as a separate new part (although it is removable), but when purchased it is a complete set with an exchanger, nearly 2,000 PLN.