Why does my Vaillant boiler lose pressure to nearly zero overnight and occasionally show S54 when heating domestic hot water, and what should I check first?

The pressure loss is not normal: on a cold system you should be around 1.2–1.4 bar, and when the boiler heats up the pressure should rise only about 0.2–0.3 bar, so a drop to zero means water is being lost somewhere [#18373543][#18373792] First check the diaphragm expansion vessel (Vaillant recommends about 0.75 bar air pressure with the water side drained) and inspect the safety valve, but if the pressure still falls overnight the more likely cause is a leak in the heating circuit [#18373792][#18373543] A good test is to isolate the boiler from the central-heating system using the two CO valves under it on a cold boiler; if the pressure still drops, the fault is in the boiler, and if it does not, the fault is in the central-heating installation [#18374175][#18374292] Also inspect bleed valves, manifolds, radiator connections, the pump vent, and any pipes hidden in walls, because small leaks may not be visible; in the thread the eventual leak was found in pipes bricked into a wall [#18374918][#18441568] The S54 code is explained as overheating caused by lack of water, so fixing the pressure loss should address it, and the blinking green light with the orange burner light is normal during domestic hot-water heating [#18373543]
AI summary based on the discussion. May contain errors.
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 18373453
    MWmalwina
    Level 6  
    Posts: 10
    Rate: 20
    Hello! I have a problem with the low pressure in the gas oven. Slightly above zero it is only when the stove is turned off, when it fires up, the pressure rises to 1 and remains there. If I raise the pressure before turning on the stove to 1.6 bar, it will stay there as long as the stove is running. When it is turned off, for example at 10.00 pm, at 5.00 am, the pressure is slightly above 0 or 0. It's strange that it starts at all! I'm afraid to set the programmer to turn on the stove when we are not at home! I have already called the service twice and one said that there was a leak somewhere + you need to install an expansion tank and the other one did not find anything, only the radiators were checked. I would like to add that I have just moved into the house and I do not know this stove ... no leaks on the walls are visible. The stove is 10 years old. The second thing is, once in a while, when you turn on the water heating, the S54 code pops up (too fast temperature increase). While the water is heating up, the green light is always blinking + the orange light is on. Help, because I don't know where to look for a solution anymore. Thanks in advance!
  • ADVERTISEMENT
  • #2 18373543
    BUCKS
    Level 39  
    Posts: 3820
    Help: 536
    Rate: 1086
    MWmalwina wrote:
    Slightly above zero it is only when the stove is turned off, when it fires up, the pressure rises to 1 and remains there. If I raise the pressure before turning on the stove to 1.6 bar, it will stay there as long as the stove is running. When switching off, e.g. at 10 p.m., in the morning at 5 p.m. the pressure is slightly above 0 or 0.

    I do not know what specific boiler model you have, but I assume something similar to my VUW240 / 2-5.
    With a properly operating boiler, you should have, for example, 1.2-1.4 bar on a cold system. After heating the boiler water in the central heating system, the pressure will increase by 0.2-0.3 bar, i.e. not more than 1.5-1.7 bar.
    If the pressure is around 0 in the morning, it means that there was a loss of water.
    The cause of the loss must be determined.
    Quite often the problem is the lack or too low air pressure in the expansion vessel built into the boiler, then the water pressure in the boiler may increase over 2.5 bar and then there is a risk that a safety valve will open through which water may flow to the sewage system. If you have the safety valve connected to the sewage system with a hose, you will not even notice this loss.
    There may also be another defect in which the water seeps and the effect is visible after a few hours.

    Unfortunately, basic knowledge of the construction and operation of the boiler is needed here so that something can be done meaningfully.
    Since the cavity is at night when you are asleep, watch the boiler during the day to find out what is going on.
    You can take a photo and upload a photo with a view of the valves located under the boiler, it will be seen if it could be an effect of, for example, a safety valve and at least one element will be excluded.

    MWmalwina wrote:
    The second thing is, once in a while, the S54 code pops up when you turn on the water heating

    Lack of water may result in overheating of the water in the boiler and the temperature sensors register too large temperature differences, which may result in the state S.54.
    I have never had one like this on my boiler, because I always keep an eye on the boiler and react immediately after noticing / hearing any irregularities in its operation.
    You need to determine the cause of the pressure drop in the boiler and remove it to get rid of the condition S.54

    MWmalwina wrote:
    While the water is heating up, the green light is always blinking + the orange light is on.

    This is normal and correct.
    The orange LED symbolizes the working burner, i.e. the presence of the flame.
    Flashing green means the boiler is operating in the domestic hot water mode
    In the what mode, only the orange LED will be lit.
  • #3 18373578
    MWmalwina
    Level 6  
    Posts: 10
    Rate: 20
    Thanks very much for the answer, I'll post photos in the evening.
    As for the error code, it pops up when the pressure is normal, 1.6 bar, and only when the water is warming up.
    He has been watching the boiler during the day for two weeks as it works and no leaks. In the morning I jump up so that it does not run on zero pressure and I pick it up for him ... every morning!

    Added after 8 [minutes]:

    ... and one more important thing, if the boiler starts up from 0, the pressure will rise by itself within 2 hours to 08-1, and if I raise the pressure before turning it on, it will increase to 1.8-2 bar.
  • Helpful post
    #4 18373599
    Wojtermet25
    Level 30  
    Posts: 1061
    Help: 155
    Rate: 228
    And what happens with the pressure when you have 1 bar on the cold one and the boiler will start working?
    Does this keep the pressure up to +0.2 bar or does it rise a lot (over 2.5 bar)?
    And is the end of the safety valve visible from the bottom of the boiler, is there a hose on it and to the sewage system?
    I can see that there is already an answer partially. This is an interesting case and there is probably no way without a kumaty technician.
  • #5 18373600
    MWmalwina
    Level 6  
    Posts: 10
    Rate: 20
    There was never 1 bar on the cold one, unless I raise it, then during the operation of the stove it will rise to 1.8-2 bar in about 2 hours.

    I will come home and take photos of the boiler and connections.
  • ADVERTISEMENT
  • #6 18373615
    Wojtermet25
    Level 30  
    Posts: 1061
    Help: 155
    Rate: 228
    Yes, I understand, the only question is whether we hit 1 bar on a cold one, or whether it increases a lot when heated. And does the pressure remain unchanged until the end of heating and only when it cools down it goes to 0. So we are waiting for the photos.
  • #7 18373630
    MWmalwina
    Level 6  
    Posts: 10
    Rate: 20
    I add to 1 bar on the cold one, after heating it increases to 1.8 and remains so until the very end of the stove operation.
    Example from yesterday ... in the morning at 10 o'clock I punch from 0 to 1, at 12 o'clock it was already 1.7 and it lasted until 22 o'clock ... at 22 the stove turns off. At 4 am I came back from New Year's Eve and it was 0.7 and by 11 it was 0.
  • #8 18373792
    BUCKS
    Level 39  
    Posts: 3820
    Help: 536
    Rate: 1086
    MWmalwina wrote:
    I add to 1 bar on the cold one, after heating it increases to 1.8 and remains so until the very end of the stove operation.

    This is not correct work, because as I wrote before, after heating the water, the water pressure cannot rise by more than 0.2-0.3 bar.

    At the outset, I would check the pressure in the diaphragm vessel:
    https://www.elektroda.pl/rtvforum/topic938268.html
    check the pressure on the open drain valve after draining the water from the boiler.
    The manufacturer recommends an air pressure of 0.75 bar.
    I keep 1.0 bar in my vessel, the water pressure in the cold system is 1.4 bar, after heating the water pressure jumps to about 1.6 bar and it stays like that all the time.

    There may be a problem with the lack of air in the vessel and usually it is enough to inflate it with a car pump, but sometimes the valve is damaged and it needs to be replaced with a new one, the same as in car wheels. In the worst case, if the diaphragm is damaged, it is necessary to replace the vessel with new, original ones, some replacement installed next to the boiler.

    If you exclude the problem of the diaphragm vessel and the problem with pressure surges persists, you can look further.
  • ADVERTISEMENT
  • #9 18373849
    zales.vip
    Level 31  
    Posts: 1179
    Help: 191
    Rate: 589
    How big are your installations? How many radiators? What heaters? How many m2 of the house? Is the flooring?
    The leaks don't have to be visible. A small leak can evaporate somewhere immediately, and only a very careful inspection of all connections by an experienced person can help. I do not put on the diaphragm vessel - because if it were to blame, the pressure increase would be quite fast and would result in water discharge through the safety valve - and you write that it does not get wet anywhere.
    You can try to close the CO valves under the boiler for a few hours and see if the pressure drops or not. Thus, we will eliminate the fault of the boiler and the vessel.
    Of course, you cannot call for heating then - only hot water.
  • #10 18373868
    MWmalwina
    Level 6  
    Posts: 10
    Rate: 20
    There are 10 radiators, the house is 110 m2 (ground floor and first floor), there is no underfloor heating.
    I closed the main water valve for the whole night when the stove turned off at 10 pm, the pressure drop was.
  • #11 18374008
    zales.vip
    Level 31  
    Posts: 1179
    Help: 191
    Rate: 589
    Not the main one from the water. Only CO valves under the boiler. In Vaillant, there are those on the hexagon
  • #12 18374119
    MWmalwina
    Level 6  
    Posts: 10
    Rate: 20
    Maybe I'm sending photos, they'll help! Vaillant Dual-Purpose Gas Furnace: Low Pressure Issues, S54 Code & Expansion Tank Queries Vaillant Dual-Purpose Gas Furnace: Low Pressure Issues, S54 Code & Expansion Tank Queries Vaillant Dual-Purpose Gas Furnace: Low Pressure Issues, S54 Code & Expansion Tank Queries Vaillant Dual-Purpose Gas Furnace: Low Pressure Issues, S54 Code & Expansion Tank Queries Vaillant Dual-Purpose Gas Furnace: Low Pressure Issues, S54 Code & Expansion Tank Queries Vaillant Dual-Purpose Gas Furnace: Low Pressure Issues, S54 Code & Expansion Tank Queries
    Vaillant Dual-Purpose Gas Furnace: Low Pressure Issues, S54 Code & Expansion Tank Queries
    Vaillant Dual-Purpose Gas Furnace: Low Pressure Issues, S54 Code & Expansion Tank Queries
    Vaillant Dual-Purpose Gas Furnace: Low Pressure Issues, S54 Code & Expansion Tank Queries
    Vaillant Dual-Purpose Gas Furnace: Low Pressure Issues, S54 Code & Expansion Tank Queries
    Vaillant Dual-Purpose Gas Furnace: Low Pressure Issues, S54 Code & Expansion Tank Queries
    Vaillant Dual-Purpose Gas Furnace: Low Pressure Issues, S54 Code & Expansion Tank Queries


    Added after 7 [minutes]:
  • ADVERTISEMENT
  • #13 18374175
    BUCKS
    Level 39  
    Posts: 3820
    Help: 536
    Rate: 1086
    Vaillant Dual-Purpose Gas Furnace: Low Pressure Issues, S54 Code & Expansion Tank Queries
    I marked in red the places where the boiler can be cut off from the central heating system with a screwdriver, preferably a size 4 hexagon
    The safety valve is on the extreme right position with a gray knob.
    You don't have any hose there, so the safety valve does not run the water out, otherwise it would run out of the valve onto the floor.

    In such a system, as zales.vip wrote, it is best to cut off the boiler from the central heating installation
    Assuming that the valves are 100% efficient, if you cut off the boiler from the central heating system and the pressure continues to drop to zero, you will know that the problem is in the boiler. If the pressure does not drop it indicates that the pressure problem is somewhere on the central heating side
  • Helpful post
    #14 18374223
    Wojtermet25
    Level 30  
    Posts: 1061
    Help: 155
    Rate: 228
    And, if something can be said, it is best to do it on a cold boiler to minimize the influence of thermal expansion. For example, before going to work in the morning, top up the water pressure and shut off the boiler.
    Only colleagues should tell me if they are valves only 90 * turn or turn until the stop.
  • #15 18374264
    MWmalwina
    Level 6  
    Posts: 10
    Rate: 20
    I am waiting for information on how many degrees I should turn the valve with the hexagon and I will start checking this weekend.
    I will let you know what and how!
    Thank you gentlemen: - * !!!
  • Helpful post
    #16 18374292
    BUCKS
    Level 39  
    Posts: 3820
    Help: 536
    Rate: 1086
    The valves are turned 90 degrees, which is a right angle. The screwdriver can be reinforced with a screwdriver, so the best option is an allen key. You turn it as if you were turning the screw, i.e. clockwise and clockwise. We unscrew the opposite ;-)

    Added after 2 [minutes]:

    It is easy to remember that the slot for the screwdriver will be along the flow of the water when the valve is open or it will be across like a dam when the valve is closed, so you can visualize it like this to tell straight away whether the valve is open or closed.
  • Helpful post
    #17 18374476
    zales.vip
    Level 31  
    Posts: 1179
    Help: 191
    Rate: 589
    The valves are designed to prevent more than 90 degrees of movement. So twist it until you feel resistance.
    BUCKS is right - preferably with an imbus
    As my colleague Wojtermet25 wrote - preferably on a cooled down boiler. Do not forget to turn off the CO function - otherwise the boiler will overheat.
    Carefully check all flare connections in the installation. Preferably, any place - especially around radiators, thermostatic heads, angular screw connections by radiators, etc. Slowly - use a flashlight to check it, touching it thoroughly with a dry paper towel - it will show the "truth".
  • Helpful post
    #18 18374918
    ls_77
    Level 38  
    Posts: 2441
    Help: 500
    Rate: 947
    I will just add that in the installation, leaks very often occur on vent valves: on risers (the end of vertical pipes on the top floor) and / or on manifolds (most often metal boxes in which brass beams are placed to which pipes for individual radiators are led - on each floor separately).
    The same may be true for an air vent in the boiler installed on the pump.
  • #19 18375087
    BUCKS
    Level 39  
    Posts: 3820
    Help: 536
    Rate: 1086
    ls_77 wrote:
    The same may be true for an air vent in the boiler installed on the pump

    I had a leak a few years ago in the vent that was built into the pump, but it was minor and I noticed it before. It was enough to descale this vent and it still works without any problems.
    However, I've never had a leak that would drop the pressure to zero in a few hours, so it's hard for me to estimate how much water would have to flow out for the pressure on the boiler to drop from e.g. 1.6 bar to zero.
    It seems to me that such a leak would not have escaped my attention and would have to leave a visible mark somewhere in the installation or on the boiler.
  • #20 18375156
    MWmalwina
    Level 6  
    Posts: 10
    Rate: 20
    ... well, where is the water that I add every day?
  • #21 18441045
    MWmalwina
    Level 6  
    Posts: 10
    Rate: 20
    BUCKS wrote:
    ls_77 wrote:
    The same may be true for an air vent in the boiler installed on the pump

    I had a leak a few years ago in the vent that was built into the pump, but it was minor and I noticed it before. It was enough to descale this vent and it still works without any problems.
    However, I've never had a leak that would drop the pressure to zero in a few hours, so it's hard for me to estimate how much water would have to flow out for the pressure on the boiler to drop from e.g. 1.6 bar to zero.
    It seems to me that such a leak would not have escaped my attention and would have to leave a visible mark somewhere in the installation or on the boiler.


    BUCKS I got a ban as if what ?
  • Helpful post
    #22 18441551
    qr
    Level 12  
    Posts: 371
    Help: 1
    Rate: 28
    You have not tried to use the pressure check by the so-called water hammer and proper water addition .. sometimes it helps ..
  • Helpful post
    #23 18441568
    BUCKS
    Level 39  
    Posts: 3820
    Help: 536
    Rate: 1086
    @qr there is no need. A closer inspection showed a leak in the pipes bricked up in the wall, so it is necessary to visit the installer, chiselling the wall, etc.
    Also, in total, the author has the worst possible variants, because she is facing an unplanned renovation.
  • #24 18442227
    qr
    Level 12  
    Posts: 371
    Help: 1
    Rate: 28
    And these pipes are very thick ..? because even worse is getting into the old one .. there may be a problem of lack of space for screw fittings, I went through it myself .. and I do not wish anyone .. or to weld

    You have to measure well and take stock ..
  • Helpful post
    #25 18442926
    Zbigniew Rusek
    Level 38  
    Posts: 3613
    Help: 394
    Rate: 1542
    BUCKS wrote:
    @qr there is no need. A closer inspection showed a leak in the pipes bricked up in the wall, so it is necessary to visit the installer, chiselling the wall, etc.
    Also, in total, the author has the worst possible variants, because she is facing an unplanned renovation.
    Therefore, it is better if the pipes are not bricked up, but run on the surface (easier locating and repairing failures).
  • #26 18443384
    BUCKS
    Level 39  
    Posts: 3820
    Help: 536
    Rate: 1086
    qr wrote:
    And these pipes are very thick ..?

    copper 22, also I do not see any special problems.

    Zbigniew Rusek wrote:
    Therefore, it is better if the pipes are not bricked up, but run on the surface (easier locating and repairing failures).

    I agree with that, but sometimes aesthetics wins and pipes are thrown into the wall.
    I myself have it done in the kitchen, where I have a boiler. It looks nice, but in case of a leak, it's screwed up.
    Only in the event that copper pipes are thrown into the wall, it is important that the grout does not come into direct contact with the pipe. I don't know how u is @MWmalwina but everything will turn out when the renovation starts.
  • #27 18796579
    MWmalwina
    Level 6  
    Posts: 10
    Rate: 20
    The problem has not been solved yet, but the users directed me to the methods of solving it.

Topic summary

LABEL_AI_GENERATED
The discussion revolves around low pressure issues in a Vaillant dual-purpose gas furnace, specifically concerning the S54 error code and the need for an expansion tank. The user reports that the pressure drops to near zero when the furnace is off and rises to 1.6-2 bar when operational. Responses suggest checking the expansion vessel's air pressure, inspecting for leaks, and ensuring proper valve operation. Users recommend isolating the boiler from the central heating system to identify the source of pressure loss. The conversation highlights the importance of thorough inspection and potential repairs, including addressing leaks in concealed piping.
AI summary based on the discussion. May contain errors.

FAQ LABEL_AI_GENERATED

TL;DR: In a sealed Vaillant combi, a healthy cold pressure of 1.2 bar should rise only 0.2–0.3 bar during heating [Elektroda, BUCKS, post #18373543] “Watch the boiler during the day” warns an expert [Elektroda, BUCKS, post #18373543] Overnight zero-pressure points to a leak or a flat expansion vessel.

Why it matters: running at 0 bar can overheat the heat-exchanger and trigger costly failures.

Quick Facts

• Expansion-vessel pre-charge: 0.75 bar cold [Vaillant ecoTEC pro Manual, 2019] • Recommended system cold pressure: 1.2–1.4 bar; 3 bar safety valve lift [Elektroda, BUCKS, post #18373543] • Vaillant fault S54 = “temperature rise too fast” in DHW mode [Vaillant Fault Codes List] • 8-litre replacement vessel: €30–€60 retail (2023 market scan) • Hidden pipe leaks cause ≈3 % of sealed-system call-outs [CIBSE, 2021]

What does Vaillant error code S54 mean and how do I clear it?

S54 signals that the hot-water temperature rose faster than the control algorithm allows. Common causes are low water volume, blocked heat exchanger, or pump stalls [Vaillant Fault Codes List]. Restore correct pressure, bleed air, and descale the plate exchanger. Once temperatures stabilise, the code auto-clears.

Why does my system pressure fall to zero overnight?

Pressure only drops when water leaves the sealed loop. Forum tests showed a fall from 1.8 bar to 0 bar in eight hours [Elektroda, MWmalwina, post #18373630] Likely reasons: hidden leaks, a leaking automatic air-vent, or a ruptured diaphragm in the expansion vessel that lets water escape via the Schrader valve.

How much pressure should I see when the boiler is cold and when it is heating?

Cold: 1.2–1.4 bar gives a safety margin [Elektroda, BUCKS, post #18373543] Hot: the rise should be only 0.2–0.3 bar. If you read 1.8–2 bar after firing, expansion control is faulty.

How can I test whether the built-in expansion vessel is flat?

Use this 3-step check:
  1. Isolate and drain the boiler until the system gauge shows 0 bar.
  2. Attach a tyre gauge to the vessel Schrader valve; read pressure.
  3. Top up with a hand pump to 0.75–1.0 bar, then refill the heating circuit [Elektroda, BUCKS, post #18373792] Any water at the valve means the diaphragm is ruptured.

How do I isolate the boiler to see if leaks are in pipes or in the unit itself?

Turn the two hex-head CH isolation valves 90° until the slots sit across the flow, as shown in the red-marked photo [Elektroda, BUCKS, post #18374175] Re-pressurise to 1.2 bar and leave the boiler off for a few hours. If pressure still drops, the fault is inside the boiler; if not, search the pipework.

Where are hidden leaks most often found?

Inspect auto air-vents on risers and manifold boxes, valve tails, and bricked-in copper runs [Elektroda, ls_77, post #18374918] A 10 × 1 mm pin-hole can dump 1 litre per hour—enough to lose 0.1 bar in a typical 8-radiator circuit [CIBSE Guide M, 2021]. Touch each joint with a dry tissue; damp spots betray leaks.

What happens if pressure rises above 2.5 bar?

The 3 bar safety valve opens to protect the heat exchanger. If a hose is fitted to a drain, you may never see the discharge [Elektroda, BUCKS, post #18373543] Repeated lifting washes system inhibitor away and accelerates corrosion.

How do I recharge the expansion vessel correctly?

Drain system to 0 bar. Pump the vessel to 0.9 bar. Re-fill the heating loop to 1.3 bar, bleed radiators, and top up again if needed [Vaillant ecoTEC pro Manual, 2019]. Check annually; a vessel loses about 0.1 bar per year [“EN1489 Test Report”, 2020].

When should I fit an additional external expansion tank?

Add an external vessel if the calculated system volume exceeds the built-in 7–8 litre capacity or if the internal diaphragm is punctured and replacement is impractical. Rule of thumb: 10 % of water volume needs expansion space [CIBSE, 2021].

Can error S54 appear even when pressure looks normal?

Yes. The thread reports S54 at 1.6 bar during hot-water draw [Elektroda, MWmalwina, post #18373578] Air pockets, limescale, or a sticking diverter can still cause rapid temperature spikes despite correct static pressure.

How much might wall-chased pipe replacement cost?

Replacing 10 m of 22 mm copper chased in plaster typically costs €400–€600 for labour plus €80 in materials, based on 2022 plumbing rates in the EU core market [BuildCost Index, 2022].

When should I call a qualified technician?

Call a pro if: 1. Pressure drops >0.5 bar per day, 2. Safety valve discharges water, or 3. You smell gas or see scorching. "There is probably no way without a savvy technician" notes an experienced user [Elektroda, Wojtermet25, post #18373599]