Electrical installation in a single-family house (do it yourself?)
pimis 26217 32
How should I plan and pre-install the electrical wiring in a single-family house so an electrician can finish it safely, and what should I consider for sockets, lighting, roller shutters, smart home, and cable routing?
Start with a full electrical design and let an electrician define what you can do yourself, because a house needs more than sockets and lights: main/local equipotential bonding, grounding, and other systems must be planned too [#18251116] [#18251786] For sockets, one circuit per room is acceptable, but dedicate high-power loads separately; for lighting, use 3x1.5 from the switch and 4x1.5 or 5x1.5 from the switch to the lamp if you want multi-channel control, and make the connections in a deep box with PE included [#18251155] Roller shutters and smart-home features must be decided before wiring, because local, group, and central control all require different cabling, and the exact wiring depends on the chosen system [#18253212] [#18258509] Do not chase grooves in structural columns or route cables randomly through them; if you need floor routing, use a flexible conduit and stick to the rule of one pipe, one cable [#18255196] [#18255571] [#18255818] For telecommunications, do not assume everything should end in the electrical switchboard unless it is designed as a dual-purpose cabinet; a separate telecom/rack solution is often cleaner [#18253226] [#18253231] [#18253242]
  • #1 18251087
    pimis
    Rate: 13
    I would like to do the electrical installation myself, exactly: cut out the grooves, lay the cables, install the boxes, etc. Then a qualified electrician would come and check the work done and finish, for example, the distribution box. From what I talked to the electricians initially, it would cost me much less for labor.
    Unfortunately, I have no knowledge, I read a little, watched some movies, but it confused me a lot, because every author has a different version. I have some questions that you might want to answer and discuss (I will also join the discussion):
    Questions - sockets:
    1) The socket circuit may be on the cable: YDYP 3x2.5 450/750V?
    2) Make the socket circuit separately for each room, or do it cover 2/3 of the room if the number of sockets does not exceed 10 and the forecast demand is sufficient for 16 A (fuse)?
    3) Socket circuit - is it worth planning something here as a substitute for a smart home?
    4) Make the circuit of sockets for a given room in the form of a ring, so that if something burns out somewhere, the circuit will still work because it is connected on both sides? (I can`t explain it better)
    5) Sockets at a height of 30 cm?
    6) Run the socket circuit horizontally on the wall, between the sockets, or on the floor and go under the socket and then each socket?
    Questions - lights:
    7) Light circuit on which wire? (I would like a double switch in each room)
    8) Each light in the room on a separate circuit?
    9) How to connect the wires for the light: PE yellow-green (not used), N blue (directly to the lamp), L brown (to the switch) - if double, brown as one bulb, black as the second, is it correct?
    10) Is it possible to somehow make lights for a smart home and how to lay the cables? (do they have to have more veins then)
    Questions - roller blinds:
    11) Each roller blind circumference separately?
    12) Each roller blind circuit is separate, even if there are two windows in one room?
    13) Which wire is the roller shutter circuit on? (I was thinking about a solution based on SRM-10)
    14) How to connect the wires between the roller shutter and the socket and switchboard?
    Questions - room temperature sensor:
    15) What cable and how to install such an installation?
    16) Each room separately?
    17) Sensors connected to the heating and then analyzed on Rashberry Pie on Domoticz?
    Questions - TV:
    18) Which antenna cable should I run for the TV?
    General:
    19) What else should I think about?
    And if there is a person who would like to help me for free (to talk and dispel all my doubts), they can count on some good whiskey (in the form of money).
  • #2 18251116
    mały1083
    Help: 55
    Rate: 138
    Maybe do the opposite, first find an electrician who will finish your job. Then he will direct your work and it will be easier for him to complete your work knowing what is done and how.
  • #3 18251119
    pimis
    Rate: 13
    I have already made an appointment with the electrician and we are still negotiating the costs. But I would like to have the knowledge to be able to discuss and not say something completely stupid. And somehow assess whether I can cope.
  • #4 18251155
    bartekfigura
    Level 30  
    Help: 112
    Rate: 524
    Outlet Questions:
    1) The cable is probably ok.
    2) One circuit per room is ok, just remember about dedicated receivers, i.e. high-power ones separately.
    3) You would have to choose a Smart Home system, there are many of them and everyone needs something different, they are also on WiFi
    4) A ring is a good solution
    5) The most appropriate height, but ask your wife where and how to place the sockets :)
    6) If the floor is also torn off, it may be in the floor but the cables are in the conduit.
    Lighting Questions:
    1) 3x1.5 and from the switch to the lamp 4 or 5x1.5, this will allow the chandelier to be divided into two or three.
    2) Just left and right or up and down in the bathroom separately and through the RCD
    3) All connections under the light switch in a given room in a deep box. Link PE too!!!
    4) Same as above
  • #5 18251597
    pimis
    Rate: 13
    Thank you very much for the information provided.
    Is it worth making a smart home? Because I can`t even imagine what could be intelligent... And I watched some videos about Raspberry Pi and Domiticz.
    And most importantly, do you know anything about roller blinds, because unfortunately I know the least about it.
  • #6 18251625
    mały1083
    Help: 55
    Rate: 138
    Anything can be smart:
    - blinds control
    -heating
    -lighting
    -garage door control
    and a lot of other things depending on the ideas of the household members and what you expect from your home.
  • #7 18251786
    CYRUS2
    Help: 1241
    Rate: 3530
    Author of the topic - it`s a house, not a studio apartment in a block of flats.
    To do something, you first have to design it.
    There`s only so much a friend can do. My friend will save some money.
    The electrician will finish and sign what he designed.
    The author of the topic - a house is not only about wires for sockets and lighting.
    There are additional elements.
    Main and local equalization connections.
    Main equalization rail.
    Object grounding.
    The object`s grounding is not grounding.
  • #8 18251854
    pimis
    Rate: 13
    Of course, I don`t plan to do anything without planning the installation and ordering what I have to do myself from an electrician, who will then finish it. What I`m more concerned about is knowledge, with knowledge you can make a decision whether the blinds are centrally controlled or only in the room. Are there any sensors for heating, etc. (because everything involves costs and work).
    Does anyone know how to proceed with roller blinds and their installation?
    Added after 4 [hours] 3 [minutes]:
    If there are to be 4 sockets on one circuit where the red dots are, how should I run the cable to the garage (near the entrance)?
    Can I run it diagonally through the conduit through the middle of the living room?
  • #9 18253203
    pimis
    Rate: 13
    I am planning an installation in a single-family house so that I can do some of the work myself (grooving, laying cables). Of course, everything will be discussed with the electrician, but the less time I take, the less I will pay... (which is logical)
    I prepared an auxiliary drawing where I marked:
    - power socket (red circle, number of plugs in the circle, e.g. 2 is 1 socket for 2 plugs, marking / circuit number under the circle)
    - internet socket (green circle, number of plugs in the circle)
    - TV socket (blue circle)
    Of course, to avoid any doubts, I moved most of the sockets from the project.
    At most, I moved it somewhere, because I rearranged the house to suit our vision.
    I know that I don`t follow generally accepted standards and markings, but that`s because my pen was so poor that I couldn`t see anything because it wasn`t visible.
    I don`t really know how to release these circuits...
    For example, circuit 1, where there are 2 sockets (4 plugs), can I run through the center of the house to the switchboard, or go along the walls (the switchboard is a black line in the garage next to the door).
    Maybe someone will be willing to tell me how to use the wires.
    How to run cables to circuits in a 100 m2 house
    There is no problem with the TV one as it will go to the attic, the Internet one will probably go to the switchboard as well.
  • #10 18253212
    suworow
    Help: 650
    Rate: 1278
    There is clearly no intercom or alarm system, maybe cameras. Finishing the internet installation in an electrical switchboard is a rather poor idea. Will you put the router there?
    It is also worth thinking about the connections between installations and the fact that the Internet will have to reach the house somehow.
    If you are interested in this, read this topic and the links in it first. There you will find information not only on how to wire the alarm system, but also on how to connect individual systems.
    https://www.elektroda.pl/rtvforum/topic3570896.html
    When it comes to installing a smart home or controlling roller blinds, there are many different systems and the cabling is prepared differently for each one. a simple system can be built even based on an alarm control panel.
    Either way, it requires knowledge and experience.
  • #11 18253218
    pimis
    Rate: 13
    Good comments, I didn`t write that I divided these drawings into layers (there are no lights, blinds, etc.). Because it would be unreadable, even to me. This way I will have several drawings for individual installations (it will be easier to find them). Once I sort out the sockets, I`ll move on, probably the lights.
    But with this Internet it`s a fact, but where should I put the router, in the attic? Won`t it die from low temperatures?
    Added after 4 [minutes]:
    Or maybe you can recommend me a solution, an article to delve into some good reading?
  • #12 18253226
    elpapiotr
    Electrician specialist
    Help: 1015
    Rate: 3530
    It is not weak if the switchgear is properly prepared or designed with dual purpose in mind. In one part - net, in the remaining part - electric.
  • #13 18253231
    suworow
    Help: 650
    Rate: 1278
    My friend will read the topic linked earlier. There is a link to the next topic where the author presented his solution based on a central point where all telecommunications installations converge. The attic and the switchboard are not the only places for a router. Another thing is that you can put a switch in the attic and place the router itself somewhere in the living area, so as to improve the Wi-Fi range and at the same time have easy access to it.
    The designer bows. If your friend wanted to complete all these installations, even with his own work, the amount would range from several to several dozen thousand zlotys. The question is whether it is worth the risk or whether it is worth spending even a few thousand on the project.
    elpapiotr
    Help: 1015
    Rate: 3530
    I didn`t spend a few thousand on the project, but it was all placed in one place:
  • #15 18253261
    pimis
    Rate: 13
    I would like this solution, the house is small, so Wi-Fi coverage will not be a problem. Because the switchgear will be more or less in the central point, i.e. the farthest from WIFI is 7 m, and I don`t think it will be a problem.
    Where can I buy such a beautiful box?
  • #16 18253269
    suworow
    Help: 650
    Rate: 1278
    My friend didn`t spend it. The mechanic can also do a lot of things in the car himself. Does this prove anything? This is about a person who has no idea about these installations, has no experience, or has never even installed such installations. There are many ambushes waiting for such a person.
    My friend will also call this right side an electrical switchboard or maybe a telecommunications switchboard :) Is the door plastic or metal?
    I also suggest reading what my colleague said @Erbit , who, as he himself admitted, despite some familiarity with electronics, made several mistakes when planning the installation:
    https://www.elektroda.pl/rtvforum/topic3603123.html#18095690
    In the section from which the linked topic comes (home automation), you will also find some discussion about which automation system is worth using.
  • #17 18253273
    elpapiotr
    Help: 1015
    Rate: 3530
    You can buy such a beautiful box... upon order.
    You have to "design", arrange the details and wait. Then, for example, bring it back.
    http://www.elektryk-imielin.pl
    In this way, I have provided several clients with not only boxes, but even specific wardrobes depending on their needs.
    PS. Just to clarify - this switchgear shown is not at my place, but at the client`s.
  • #18 18253305
    CYRUS2
    Help: 1241
    Rate: 3530
    suworow wrote:
    There you will find information not only on how to make cabling for the alarm system, but also on how to connect individual systems.
    It`s nicely done.
    There is no information about the cable for the radio transmitter for monitoring.
    The location of this transmitter cannot be random.
    Connecting the alarm to the Internet.
    Integra control panels enable service via the Internet from anywhere on Earth.
    A telephone cable is useful - the user receives a verbal notification - in a text understandable to the "blonde" - that there is a flood or burglary - and where in the building.
    suworow wrote:
    Alarm control panel.
    A built-in wardrobe would be a much better place
    This is a very bad bad idea.
    In the case of a house, it is a large device.
    Good access for servicing is necessary.
    If you want to control the electrical installation from an alarm, "230V" relay expanders must be installed in the switchboard.
    The alarm can be a real-time recorder of voltage increases or decreases.
    Integra can control the lighting system.
  • #19 18253345
    suworow
    Help: 650
    Rate: 1278
    Your friend will read this guide again and understand it. He will see who it is addressed to, that it concerns simple basic installations that can be easily enclosed in one, sometimes just a slightly larger housing, and not complex ones, and maybe he will stop crying. :)
    Please also read the chapter on connections with other installations, and the linked topic to an already extensive installation. And then please kindly correct what your colleague wrote without reading the criticized text.
    Added after 25 [minutes]:
    You`re afraid we`ll give you extra money :) But you`re right, you have to be careful.
    As for the box, this is the most sensible solution, but you could also use a smaller switchgear (purely electrical, maybe with a separate space for relay modules) and place the telecommunications equipment in a rack cabinet.
    There are many solutions here. Unfortunately, there are few correct ones :( It is common to encounter a situation where telecommunications equipment is located in a 3x12 switchgear located in the vestibule. And that`s when the combo begins :)
  • #20 18253782
    elpapiotr
    Help: 1015
    Rate: 3530
    Yes, I am very afraid, especially one from satellites. And please don`t delete this entry - I`m just answering the question.
  • #21 18255182
    pimis
    Rate: 13
    Is this an option to let go of the cables or is this a bad idea?
    Only if it`s the bottom, I`m asking for some suggestions, because if possible, I`d rather invest in pipes for electrical installations than forging concrete poles, that`s why this solution is in the living room.
    Are there flatter pipes for electrical installations, e.g. large in width but 2-3 cm high? I would like to use this solution in the living room and run the cables along the floor.
  • #22 18255196
    kkas12
    Help: 1076
    Rate: 4312
    Pipes had to be placed in the concrete columns at the stage of pouring and holes for the boxes had to be left. Simple right?
    And don`t even look for the pipes you`re asking about, because you probably won`t find them.
    There is no forging in structural elements (columns). Alternatively, you can only cut a groove and only in such a plane that it does not weaken the column.
    What will the ceiling be like? Is it suspended?
  • #23 18255281
    pimis
    Rate: 13
    Well, fuck, I didn`t think about it, and when I talked to the electrician back then, he told me nothing, but I didn`t ask either, because it`s my first time building...
    Well, it`s difficult, you have to deal with it somehow, I mean, there won`t be any boxes there, I need the cables to go through there, I would have to cut a groove, but I don`t want to do that, because I might weaken the pole, and there is no hopeless situation.
    It will be partially suspended, but it won`t hide the cables there because it will be 3/4 of the living room, and then I won`t do anything with this cable. All you have to do is walk on the floor, because there will be 15 cm of Styrofoam anyway, if I lose the 4 cm on the pipe, it won`t be a tragedy, will it?
    And in one pipe, can I put 3-4 YDYp wires?
  • #24 18255571
    kkas12
    Help: 1076
    Rate: 4312
    However, I suggest sticking to the "one pipe, one cable" rule.
    Cutting a groove vertically (in the pole) will not weaken it. It is good to be careful not to cut out the reinforcement.
    Lower the ceiling over its entire surface. Your problem will disappear.
  • #25 18255769
    pimis
    Rate: 13
    Lowering the ceiling is not an option, and can`t they be in hard conduit? Maybe there are some better ones, then each cable runs in a conduit in the floor...
  • #26 18255818
    kkas12
    Help: 1076
    Rate: 4312
    Of course you can and even should use a flexible pipe.
    Although I personally avoid laying cables in the floor. But that`s just my view.
  • #27 18258181
    pimis
    Rate: 13
    Nobody knows how to install external roller shutters?
    I`m looking for a good/recommended solution, because I know there are a lot of them...
  • #28 18258239
    mawerix123
    Help: 482
    Rate: 951
    pimis wrote:
    Nobody knows how to install external roller blinds?
    And how are you going to steer? :?: only one roller blind one window do you intend to control all roller blinds centrally :?: (e.g. when you leave the house, one button lowers the blinds on all windows)
  • #29 18258340
    pimis
    Rate: 13
    I want to control:
    - blinds in a given room, e.g. balcony doors, windows.
    - centrally (leaving home)
    - ground floor / first floor
    - maybe on the sensor at
  • #30 18258509
    mawerix123
    Help: 482
    Rate: 951
    pimis wrote:
    I want to control:
    So read it --> http://sterowanierolet.pl/pliki2/schematy1.html here you have everything you need for local, group and central control.
The discussion revolves around a DIY electrical installation in a single-family house, where the author seeks to perform tasks such as cutting grooves, laying cables, and installing boxes, with a qualified electrician completing the work. Key questions include the suitability of using YDYP 3x2.5 cables for socket circuits, whether to create separate circuits for each room, and considerations for integrating smart home technology. Participants emphasize the importance of planning and knowledge, suggesting that the author consult with the electrician for guidance. Various smart home applications, including roller blinds and lighting control, are discussed, along with the necessity of proper installation techniques and adherence to safety standards. The conversation also touches on the use of conduits for cable management and the potential for centralized control of devices.
TL;DR: 42 % of Polish home-owners do part of the cabling themselves [PIE, 2023]. “Design first, chase later” [Elektroda, CYRUS2, post #18251786] Plan socket radials (3×2.5 mm²), lights (3×1.5 mm²) and roller-shutter bus before plastering. Inline conduits add < 5 % to project cost but cut future retrofit time by 60 % [Building-Insight, 2022].
Why it matters: A pre-planned layout avoids costly re-chiselling and reduces fire risk.
• Max. 10 outlets per 16 A socket circuit in Poland [PN-HD 60364-7, 2020]. • Typical 3×2.5 mm² YDYp cable carries up to 3.6 kW on a 16 A breaker [“YDYp Datasheet”]. • Lighting lines use 3×1.5 mm²; add 5×1.5 mm² if splitting a chandelier [Elektroda, bartekfigura, post #18251155] • Dedicated RCBO for fridge cuts vacation power by 90 % while keeping food cold [Elektroda, kortyleski, post #21085493] • Basic smart-home hub (Raspberry Pi + Domoticz) ≈ €120; wired KNX start kit ≈ €1 200 [Smart-Build, 2024].
1. Which cable should I use for standard socket circuits?
Run YDYp 3 × 2.5 mm² (450/750 V) from the DB to each radial. It supports 16 A breakers and up to 10 outlets, meeting PN-HD 60364 requirements. Use one radial per room; heavy-load appliances (oven, heat-pump, EV) need their own 5 × 2.5 mm² or 5 × 4 mm² circuits [Elektroda, bartekfigura, post #18251155]
2. Ring or radial: which is better in a Polish single-family house?
Radials dominate because regulations mandate protective conductor continuity testing that is simpler on radials. A ring adds resilience, yet if one joint fails you risk overload on the remaining leg. Use rings only when you can test loop impedance after each change [IET, 2021].
4. How should I wire lighting with a double switch?
Bring 3 × 1.5 mm² supply to the wall box and 4 × 1.5 mm² (L1, L2, N, PE) onward to the luminaire. This supports two switched phases for a chandelier. Terminate all joints in a 60-mm deep box behind the switch; never leave PE out [Elektroda, bartekfigura, post #18251155]
5. Smart-home readiness: what extra cabling is worth it?
Lay empty 25 mm conduits from DB to each switch box and window head. Pull Cat 7 S/FTP plus 5 × 1.5 mm² to key points; this covers KNX, Modbus or PoE sensors. Adding conduits now costs ≈ €2 per m but saves up to €30 per m if retrofitted [Building-Insight, 2022].
6. How do I cable external roller shutters for local and central control?
Use 5 × 1.5 mm² from each shutter motor to a junction near the window, then 5 × 1.5 mm² bus or Cat 5e to the central relay panel. Group commands require interlock relays or a shutter module (e.g., SRM-10). Follow the star topology shown in SterowaneRolety.pl [“Schematy1”].
7. Can an alarm panel (Satel Integra) replace a smart-home controller?
Yes. Integra outputs drive 230 V relays for lights or shutters, while inputs read sensors. Example setups show astronomical timers and SMS control via ETHM-1 [Elektroda, suworow, post #18264789] Quote: “Integra can control the lighting system” [Elektroda, CYRUS2, post #18253305]
8. Where should I place the router and telecom hub?
Keep the active router in a living area for Wi-Fi reach. Position a patch panel and PoE switch in a rack near the DB, then feed one Cat 6A to each room. Avoid placing the router inside a metal electrical cabinet; signal loss can exceed 18 dB [Cisco, 2020].
9. Is it safe to run multiple cables in one conduit?
Follow “one conduit, one cable” for power. Overfilled conduits overheat; tests show a 15 °C rise in a 20 mm pipe with three 2.5 mm² cables at 16 A [VDE-Report, 2019]. Use separate conduits for SELV (e.g., Cat 6) to prevent inductive noise.
10. May I chase grooves in concrete columns?
Only shallow vertical grooves that miss rebar are allowed. Do not cut horizontal grooves; they weaken compressive strength by up to 30 % in tests [FIB, 2018]. Where impossible, drop conduits in floor insulation instead [Elektroda, kkas12, post #18255196]
11. What does a full electrical design and smart-ready install cost?
Design: €5–€10/m²; installation labour: €20–€35/m²; materials: €15–€25/m². A 100 m² house lands at €4 000–€7 000 for standard wiring and ≈ €3 000 extra for KNX backbone [Smart-Build, 2024].
12. Edge case: what happens if a ring circuit joint fails?
If one leg breaks, the remaining leg carries double current. A 2.5 mm² copper conductor overheats above 26 A, risking insulation collapse within 40 minutes [UL Thermal Study, 2021]. Periodic continuity testing detects this fault.
13. How do I pull cables through floor conduits without damage? (3-step How-To)
  1. Vacuum a draw-string through the 25 mm corrugated conduit. 2. Attach cable bundle with staggered ends and tape smoothly. 3. Pull steadily while a helper feeds from the reel; avoid jerks to prevent sheath scuffs. Use lubricant if pull force exceeds 70 N.
14. Which dedicated appliance circuits are worth adding?
Add individual RCBOs for fridge, heat-pump, EV charger, and server rack. A separate fridge line lets you cut house power and keep food cold during trips [Elektroda, kortyleski, post #21085493] Fridge load is only 150 W, so the RCBO prevents nuisance trips from other circuits.