Bosch PIE631FB1E 7.4kW Induction Hob: Protection Assignment - B16 2p Overcurrent Fuse Suitability
wsmpw 49278 12
Can I protect a Bosch PIE631FB1E induction hob powered from two phases with a B16 breaker, and should the neutral also be disconnected?
Yes—use overcurrent protection on the two phase conductors only, and do not disconnect the neutral [#18336011] For the Bosch PIE631FB1E, the thread says it requires two phases, the third phase is unused, and the factory cable is 2.5 mm² [#19571903] The model-specific reply states that each side is 3600 W, the maximum continuous current per phase is about 15 A, and the booster current of about 24.6 A is only brief, so a 16 A breaker per phase should be acceptable in normal use [#19571903] One reply suggested 20 A and even 4 mm² for longer full-load operation, but that was a more general recommendation rather than a model-specific calculation [#18328227][#19571903]
  • B16 2p breaker likely suitable for 7.4 kW hob
    #1 18328183
    wsmpw
    Rate: 30
    I bought an induction hob and now the question arises what protection to assign to it? The hob has a maximum power specified in the manual 7400W. I want to power it with two phases. Will a B16 2p overcurrent fuse be good for this type of connection? Can it give normally 3P where the 3rd N line will also be disconnected in case of overload?
    The cable from the switchgear is 5x2.5mm2
    I am asking for advice and suggestions.
    Thank you and best regards.
  • Recommend 20A breaker and 4 mm² cable
    #2 18328227
    Tumiwisizm
    Help: 125
    Rate: 196
    Once you do, give it 20A, because there will be about 18.5A on the phase-to-phase (the same current) plus longer work, at least these 20A. And god forbid neutral on the fuse. As for the cross-section of the wire
    a little. Four (4mm2) would be useful.
  • #3 18330322
    Barthezz1976
    Level 19  
    Help: 24
    Rate: 164
    Rarely will you exceed 2 kW of constant load on induction.
    I only use the booster for the kettle, so it's 2-3 kW literally for 2 minutes or less depending on how much water is in the kettle.
    1 phase and 2.5mm is enough.
    When you run a gastronomy, it's like a friend with a cable above 4mm
  • #4 18330397
    wsmpw
    Rate: 30
    So what kind of protection should you give? B16A 3 lines ?
  • #5 18336011
    Tumiwisizm
    Help: 125
    Rate: 196
    @wsmpw do not disconnect the neutral. If you want to power the hob with two phases, put a circuit breaker on the phases only. I do not know what connection the plate has inside, but if you power it from phase to phase, a 16A switch (per phase) for these 3kW is enough.
  • #6 18336267
    wsmpw
    Rate: 30
    It seems to me that inside it is so that 2 coils are powered from 2 generators, i.e. 2 generators for 2 pairs of burner coils.
    and the connection is for 2 phases, i.e. as if each "power board" has 2 coils (burners) to be operated from one phase.
    I'm just still wondering how the overcurrent 3-pole dam will be unused.
    It can be like that?
  • #7 18336306
    Brivido
    Help: 226
    Rate: 430
    Yes it can be.
  • #8 18336477
    zhudomel
    Home appliances specialist
    Help: 1280
    Rate: 3373
    Have you checked the warranty card whether an electrician's entry is required to make the connection?
  • #9 18336498
    wsmpw
    Rate: 30
    @zhudomel that's the information there.
    I think SEP licenses up to 1kV will suffice.
  • #10 18337108
    Tumiwisizm
    Help: 125
    Rate: 196
    They're enough. If only the electrician entered the date of connection and the number of his licenses (if he does not run a business in this area, if it is carried out by a stamp with the number of licenses).
  • #11 18337170
    ^ToM^
    Help: 495
    Rate: 2939
    zhudomel wrote:
    Have you checked in the warranty card whether an entry of a licensed electrician about making the connection is required?
    However, this is only needed if you want to take advantage of the manufacturer's warranty. If the warranty will not be used (for some reason), of course, you do not need to fill it out.
  • #12 18337198
    jerry1960
    Level 37  
    Help: 285
    Rate: 1560
    What board is it, name the manufacturer and model. The board is probably powered by 2 x 230 V.
  • Two-phase wiring limits hob current to 25A
    #13 19571903
    lstela
    PIE631FB1E is a Bosch board, not Amica.
    Requires two phases. The third phase is not connected or used. The factory cable attached to the board has a cross-section 2.5mm sq .
    According to the manual, the unused phase wire is used as the second neutral, which suggests that it is a "star" connection (a bit lame), and the system is powered by 240V and not 400V. I guess the left fields ("burners") draw current from one phase, and the right ones from the other.
    Left and field power is 3600W (6200 in booster mode)
    The power of the right fields is 3600W (5900 booster)
    This means the maximum continuous current on one phase 15A (24.6A in booster mode) .
    It is not possible to activate the booster mode for all burners at once.
    The booster mode is time-limited, so a 24.6A instantaneous current will not blow a 16A fuse.
    The maximum continuous current for a 2.5mm cable is 25A, so it's also normal here.
The discussion revolves around the appropriate protection assignment for the Bosch PIE631FB1E induction hob, which has a maximum power of 7400W and is intended to be powered using two phases. Users suggest that a B16 2p overcurrent fuse may be suitable, with recommendations for a 20A rating due to potential current draw during operation. It is noted that the hob operates on a star connection, utilizing two phases and a neutral, with a maximum continuous current of 15A per phase and a booster mode that can draw up to 24.6A momentarily. The importance of ensuring proper electrical connections and compliance with warranty requirements is also highlighted, emphasizing the need for a qualified electrician for installation.
TL;DR: PIE631FB1E draws about 15 A per phase (24.6 A boost); "Requires two phases." Size phase protection accordingly and note booster is time‑limited. [Elektroda, lstela, post #19571903]
Why it matters: For Bosch PIE631FB1E owners and installers, this FAQ clarifies breaker sizing, wiring, and warranty steps to avoid trips and claims issues.
What breaker size should I use for Bosch PIE631FB1E on two phases?
Use a 20 A breaker per phase when supplying phase‑to‑phase loads near 18.5 A. Do not place protection on the neutral. “And god forbid neutral on the fuse.” [Elektroda, Tumiwisizm, post #18328227]
Is a B16 2‑pole MCB enough for this hob?
A 16 A device can work because booster current is time‑limited. Continuous per‑phase load is ~15 A, and boosts near 24.6 A are brief. The factory 2.5 mm² lead supports about 25 A continuous. If nuisance trips occur, consider upsizing protection as allowed. [Elektroda, lstela, post #19571903]
Should the neutral conductor be protected or switched?
No. Protect only the phases and keep the neutral unswitched. “And god forbid neutral on the fuse.” [Elektroda, Tumiwisizm, post #18328227]
Can I use a 3‑pole breaker and leave one pole unused?
Yes. You can use a 3‑pole device and leave one pole unused for a two‑phase hob. “Yes it can be.” [Elektroda, Brivido, post #18336306]
Is a 5×2.5 mm² feeder cable adequate for the PIE631FB1E?
Yes. The hob’s factory cable is 2.5 mm², per‑phase current is 15 A continuous, and 2.5 mm² supports ~25 A. Short 24.6 A boosts are time‑limited. A 5×2.5 mm² feeder is adequate when installed correctly. [Elektroda, lstela, post #19571903]
How are the cooking zones split across phases?
Left zones share one phase at 3600 W (6200 W booster). Right zones share the second phase at 3600 W (5900 W booster). Expect ~15 A continuous per phase. The third phase is unused. [Elektroda, lstela, post #19571903]
Can I enable the booster on all burners at once?
No. The controller prevents enabling booster on all zones simultaneously. Left can reach 6200 W and right 5900 W in boost, not concurrently. [Elektroda, lstela, post #19571903]
How do I wire and protect this hob on two phases?
Follow the manual.
  1. Confirm two‑phase configuration; the third phase is unused. The spare conductor may serve as a second neutral.
  2. Connect L1 to Phase 1 and L2 to Phase 2; supply is 230 V per phase.
  3. Size protection to ~15 A continuous and time‑limited 24.6 A boosts; a 16 A device often holds. [Elektroda, lstela, post #19571903]
Do I need a licensed electrician’s entry to keep the warranty valid?
Yes, if you intend to use the warranty. “This is only needed if you want to take advantage of the manufacturer’s warranty.” Record the installer’s details per the warranty card. [Elektroda, ^ToM^, post #18337170]
What qualifications satisfy the installer entry?
SEP authorization up to 1 kV is sufficient. The electrician should note the connection date and their license number or stamp in the warranty record. [Elektroda, Tumiwisizm, post #18337108]
What’s a realistic everyday power draw for home cooking?
About 2 kW continuous is typical. A kettle on booster draws roughly 2–3 kW for around two minutes. This intermittent load profile reduces continuous stress on breakers and cabling during normal use. [Elektroda, Barthezz1976, post #18330322]
Is the PIE631FB1E a 400 V three‑phase appliance?
No. It operates at 230 V per phase with a star‑like internal link, and the third phase is unused. The spare phase conductor may serve as a second neutral per the manual. [Elektroda, lstela, post #19571903]
Can I run the PIE631FB1E from a single phase?
No. This model requires two phases, and the third phase is not used. Single‑phase operation is not described in the referenced configuration. [Elektroda, lstela, post #19571903]