Nie, dziękuję Przekieruj mnie tamCez166 wrote:1. The set will be about 8-10m from the wall of the house with the inverter (~ 10-12m of cable, ground). I wonder how to connect the DC box on the structure with the inverter at home, or with 4mm2 or 6mm2 PVC cables in an additional sheath in arot or a cable dedicated to the ground (max current ~ 9A)?
Cez166 wrote:2. Is it necessary to provide a second DC lightning protection at the inverter with such a DC cable length?
Cez166 wrote:3. 3-phase inverter max. Current ~ 6A / phase distance ~ 8m from the main switching station in the house to which I will connect. In the inverter manual they write that at such a distance, a 5x2.5mm2 cable can be used, but I wonder if 5x4 mm2 will not be better.
Cez166 wrote:4. Request for opinions: should we give pv fuses in the DC box (what they protect in practice, or are they just a disconnector between the PV and the rest for some service work) and when do we use a 100mA 3-phase differential behind the inverter?
StaruchPl wrote:In my opinion, this is an obvious induction loop. I had a similar dilemma to you and as a consequence I applied the solution as shown in my drawing (Version II). It is true that with my solution more solar cable comes out, but for safety, I think that it is better to add a few zlotys. In my installation, all the cables shown in the diagram were run next to each other and fastened together with UV-resistant cable ties.
sz.lukas wrote:will the 25-year guarantee be respected by him?
Maybe someone from the forum who works with it will comment on a daily basis.
greetings
MichałS wrote:sz.lukas wrote:will the 25-year guarantee be respected by him?
Maybe someone from the forum who works with it will comment on a daily basis.
greetings
Forget that in 25 years any of the current producers will exist. Just see how they are changing today. In addition, the panels do not withstand that much. 10-year-olds brought from southern Europe simply fall apart (and 10 years ago everything was more solid).
TL;DR: A 12-15 m DC run without extra surge protection violates EN 50539-11, “add a limiter at the panels” [Elektroda, Spajder_PL, post #18356639] Experts warn: “keep wires short” [Elektroda, Spajder_PL, post #18371751] Fix loops, add SPDs, and separate AC/DC to stay safe.
Why it matters: Correct routing and protection prevent lightning-induced surges, fires and warranty disputes.
• EN 50539-11 requires an extra DC SPD when array-inverter distance > 10 m [Elektroda, Spajder_PL, post #18356639] • EN 62305 limits SPD lead length to ≤ 0.5 m to curb inductive voltage [Elektroda, Spajder_PL, post #18371751] • Typical 4 kW ground-mount string current: ~9 A; use 4–6 mm² Cu cable [Elektroda, Cez166, post #19629719] • Type 1+2 AC SPD plus C-curve 20 A breaker meets Polish practice [Elektroda, theo33, post #18356954] • DC connector faults cause 29 % of PV fires [Fraunhofer ISE, 2020]