Best Gas Stove Brands & Models for 100m2 Apartment: Viessmann, Junkers, Bosch & More
kankox 24882 11
How do I choose a gas boiler model, power, and hot-water tank for a 100 m² house with mixed underfloor heating and radiators?
Choose the boiler by required power and local service availability, not by brand alone. For a 100 m² building, a maximum boiler output of about 14 kW is enough, while the most important parameter is low minimum modulation: about 2–3 kW for a 1-function boiler or 3–4 kW for a 2-function boiler [#18538197] The DHW tank should be sized to actual use; for two people with mostly showers, about 100 l was suggested, and a larger tank is only needed for a big bathtub or rain shower [#18535182] Boiler reliability depends heavily on water quality and installation, so use water treatment/softening and magnetic separators, because failures often come from pumps, valves, and scale rather than from the brand itself [#18549029] Because most of the house is underfloor heating, avoid a crude mixing-manifold solution; a proper setup needs hydraulic separation, a radiator pump, a mixing pump for the floor heating, and weather/boiler automation [#18559537] One specific model recommendation in the thread was the Vaillant VC 146/5-5 ecoTEC PLUS with a 120/150/200 l tank, weather regulator, and chimney set, while a cheaper alternative mentioned was Termet Silver 20 kW [#18559537][#18551904]
  • #1 18532975
    kankox
    Hello everyone. I have to install a gas stove, but I don't know anything about it. What company to install the stove: Viessmann, Junkers, Bosch or something else ?? Which model to choose to be trouble-free? What heating power ?? What water tray?
    Usable area of 100 m2
    The house is made of a 25cm ceramic brick + 15cm foam insulated with polystyrene. Floor heating (living room, kitchen, corridor, bathroom) 60m2. For this 3 rooms (each with a heater).
    Two people will live in the house.
    I am asking for specific answers what and how to choose. Thanks for any help.
  • #2 18535182
    TomekO1976
    Help: 11
    Rate: 60
    A gas boiler is best one that has a service as close as possible. It's good if it has a low minimum power. The tank is selected according to the actual consumption of hot water and the devices you will be using. If you have a large bathtub or rain shower, the consumption will be large and a larger tray will be needed. It is good for the tank to have an electric heater that, in the event of a gas boiler failure, heats up the water in emergency. Are there any solar panels planned in the future? Then a correspondingly larger tank with an additional coil.
  • #3 18535873
    ls_77
    Help: 500
    Rate: 947
    Nobody will tell you anything about the model. Of course you can, but each house is different and you have to put some effort into choosing a specific device.
    Go to the website Ciepłow gradwe.pl and fill in the selection of power for the building conscientiously - then you will know what device (power) you need.
    The second thing is, do you have access to the site in the area? Whether it's a big city or a small one, it will be hard to find someone.
    Has there been a cauldron so far? What? What installation: old, new, from what pipe diameters and what dimensions, what size and "material" radiators?
    How's the chimney? Is it possible to use an air-flue gas system for a condensing boiler, what diameters and lengths are available and here you should rather have a chimney sweep opinion.
  • #4 18538197
    BUCKS
    Help: 536
    Rate: 1087
    for 100m2 there is no problem, because boilers with a maximum capacity of 14kW will be sufficient and will have a reserve.
    14,000 W / 100 m2 = 140W / m2, and modern buildings require a constant power below 100W / m2 for frosts -20.
    Generally, the minimum power of the boiler is important.
    Generally, it can be said that the lower the minimum power, the better, because the boiler will be more flexible.
    For 2-function boilers, the lowest minimum power is 3-4kW.
    In turn, for 1-function boilers, the minimum power is 2-3kW.
    If it is a flat, a 2-function boiler is usually considered, i.e. a minimum of 3-4kW.
    If the house can be a 1-function boiler, that is minimum 2-3kW, and the maximum will usually be 14kW. As I wrote about what power with reserve and for domestic hot water, it is also OK, because you will have a tank, so you do not need more power, as is the case with instantaneous water heating.
    Then you can choose the brand and a specific model that will meet your other needs, but remember not to overdo it with minimum power.
    On the market, the range of available powers is large and if you can buy a 1-function boiler with a minimum power of e.g. 2.3kW, I don't see the point in buying a boiler with a minimum power of e.g. 6kW for such a small area, so look at the technical data of the specific model you are looking for. you will watch or someone will recommend you.
  • #5 18548453
    kankox
    Thank you very much for your answers. I thought it was easier with these boilers.
    This may give you a hint of which company to buy the stove. What are the low failure rates and if necessary they have cheap parts. The house is near Warsaw, so there will be no problem with the service.
  • #6 18548926
    -west
    Heating systems specialist
    Help: 143
    Rate: 523
    Everyone will break sometime. Each one requires an annual service.
    Boilers highly rated by the service include: Bosch. It does not criticize other brands. I only resist my own experiences
  • #7 18549029
    zales.vip
    Help: 191
    Rate: 589
    The failure rate of boilers largely depends on the working environment and the operation of the "pest".
    If your water is hard and you don't install a water softening / treatment station, breakdowns will come earlier. E.g. stuck switching valve, pump failure, heat exchanger over time. If you do not install good magnetic separators on the return from the central heating installation - there will also be breakdowns. Most often, pumps.
    There is - rather - no such thing that a given company's boilers are more or less emergency.
    On the other hand, some parts - subject to wear - such as seals, electrodes - may be more expensive or cheaper.
    The first thing - the proximity of the site.
    Second thing - minimum power
    Third thing - price - BUT
    fourth thing - what do you get for the price - and that's BUT it's all about.
    fifth point - the price of spare parts subject to wear. For example, a gasket under the burner. Junkers for the WB6 exchanger costs about PLN 55 and you will replace it every 2-3 inspections. For DeDietrich, for example Lumea MPX - it costs 20 PLN - the frequency of replacement - similar.
    Set of electrodes - for Junkers with WB6 - about 160 PLN, for DeDietrich - probably about 90-100, because you do not have to replace the set, but the ionization itself.
    BUT
    There may be a cheaper boiler with similar technical parameters (maximum and minimum power) but with a "poorer" motherboard - and you have to buy some control devices and the cheaper one will turn out to be more expensive.
    e.g. You have a boiler, e.g. a clutch and you want to give a second pump after the clutch, which is to switch on with the pump in the boiler when heating the central heating. In Junkers, for example Cerapur SMART - you have such a socket on the disc, and in some Dietrichs you don't. In the cheapest Vaillant EcoTec Pure - also probably not. So you have to buy an additional device, and this is a cost.
    Or a circulation pump. You connect to Junkers and select a circulation pump and the boiler will turn it on itself. A small thing, but in terms of "cheap / expensive" it can make a difference.
    I have given the above as an example. My point was that you should plan wisely what this boiler is to do and how many heating circuits are to be, as well as triggered ones, etc. Later, look - which of the boilers that meet your criteria with parameters already has built-in control options.
    You have a difficult choice ahead of you. Good luck
    Well, unless you want to recommend a specific device - then create a poll and we will vote, and you choose the number of votes ;) :D
  • #8 18550156
    kankox
    Honestly, I don't know anything about it. In my family house, there was a stove for wood, coal, etc. You lit the stove, turned on the pump and kept it in the stove. When the temperature on the stove was too high, the stove closed the air supply flap and that's it. No complications. And here? MAGIC. I read and read and it brightens on average.
    I did the calculation. I will be grateful if someone has a look.
    Your house needs warmth
    The average daily temperature at home throughout the heating season is 22.0 ° C.
    9.0kW - the maximum required heating power
    On the "coldest" day of winter, ie with a daily average of -20 ° C.
    4.4kW - average heating power
    This is what you will need on an average winter day, with a daily average of 1.3 ° C.
    75W / m2 power demand indicator
    This value can be found in the approximate boiler power selection table from its manufacturer. It's just that there it starts from 100W / m2 and above. Interesting, isn't it?
    18 680kWh = 67GJ total annual energy consumption for heating
    This is how much heat your home needs for the entire heating season. No energy gains are included here.
    This is a net amount - as much as the building will accept. Depending on what and with what efficiency you will heat, the amount of gross heat that you need to buy in the fuel will be correspondingly higher.
    157kWh / m2 per year energy demand ratio
    You will find this value on the building's energy certificate (newer ones have one). Based on this, your house is classified as energy class E
    Heating tap water (DHW)
    Requirements: for 2 people, Mostly showers, sometimes a bathtub.
    3kW additional power needed for domestic hot water heating
    It's enough. This is why a large container is placed so that it can be heated slowly, with little power. For a change, flow heating requires a power of over 30kW.
    ~ 100l boiler capacity appropriate to the needs
    What boiler power does the building need?
    13kW is the necessary total heating power (CH + DHW)
    As for the stove, I would like it not to have to be replaced in 2 years. If I have to buy a cheaper one, but after adding or changing (pump plates it) has a clear exit, as you say, it is better to buy a more expensive one right away and have peace of mind.
    The house is a one-story house with the possibility of arranging an attic, but I will not be doing this for now, maybe in 10 years. I will only insulate the ceiling with 20 cm polystyrene and that's it. 60 m of floor tiles in the house.
    It calculated for me that 13kW is needed. I found two stoves.
    Link
    Link
    The power should be enough.
    And is it possible to buy a stove with a higher output power ??? What is the meaning of the age ??
    Link
  • #9 18551904
    andrzej lukaszewicz
    Help: 626
    Rate: 2121
    If you don't have a gas connection, I would seriously consider a heat pump.
    And so I recommend a simple boiler termet silver 20kW, which is relatively cheap to buy and service.
    in 10-12 years, you will exchange for another one anyway, and this one costs less than PLN 3,000, and it heats the same way as boilers of famous brands, but the service and parts for them will be 50% or more higher than the termet.
    It is not a miracle of technology, but it does not aspire to it, especially the price, as some of the 2x more expensive "western" ones, and they break down just like all of them.
  • #10 18558924
    kankox
    I was offered such a set. What do you think about it ???
  • #11 18559537
    ls_77
    Help: 500
    Rate: 947
    Regarding the hydraulic system proposed by this plumber / installer. Like 90% of such plumbers / installers, he proposed to connect the heaters with the OP through an OP manifold with a pumping and mixing system based on a valve with a thermostatic head with a capillary. Firstly, such a system is not very suitable for condensing boilers operating at low temperatures, and secondly, such a system does not have OP weather control.
    You have ~ 60m2 of floor tiles and ~ 100m2 of the whole house, so most of the area is OP. Controlling it "constant temperature" with this mixing system, you will have either too hot or too cold. You will have to keep flying to the box and adjusting the setting on the head. Complete nonsense! Such systems are proposed by plumbers / installers when they do not want to scare the investor with the price of a correct hydraulic system, where there should be a hydraulic coupling, a pump for radiators and a pump with a mixer for the underfloor heating, and everything is controlled by the automation (additionally extended with appropriate modules) of the boiler.
    Either you have to take into account the increase in investment costs to adapt the entire system to the correct solution, or choose one type of heating throughout the building: either only radiators or only underfloor heating. And then the whole should be connected directly to the boiler without couplings, pumps and mixers.
    As for the boiler, I have heard opinions that like Viessman, they are worth recommending only from the Vitodens 200 model. I don't know Viessmann and its automation myself, so these are just opinions I heard from people who have and are considering buying a Viessmann.
    I know Vaillant boilers and I can recommend the VC 146 / 5-5 boiler from the ecoTEC PLUS series for such a building - the best price / quality ratio in Vaillant. The most cost-effective, of course, in packages with DHW tanks: 120/150/200 l. And a weather regulator and a basic chimney set included.
  • #12 18560147
    kankox
    The case is as I wrote before that I don't know anything about it. The first quote was sent to me here and of course I can ask you what you think. Tomorrow I will be calling other specialists so I will know what others are proposing.
The discussion revolves around selecting a gas stove for a 100m2 apartment, focusing on brands like Viessmann, Junkers, and Bosch. Key considerations include the heating power required, which is estimated at a maximum of 14kW for the space, and the importance of a low minimum power for flexibility. Users emphasize the need for reliable service and low failure rates, with Bosch being highly rated. The conversation also touches on the necessity of proper installation, including the hydraulic system for underfloor heating and the importance of water treatment to prevent breakdowns. Recommendations include considering a simple boiler like the Termet Silver 20kW for cost-effectiveness.
TL;DR: For ~100 m2, a 14 kW max boiler is enough; “the lower the minimum power, the better.” Choose low minimum output, match DHW with a tank, and avoid oversizing. This FAQ guides homeowners picking a condensing gas boiler and controls. [Elektroda, BUCKS, post #18538197]
Why it matters: Right‑sizing and correct controls improve comfort, cut costs, and prevent avoidable failures in mixed UFH+radiator systems.
Which gas boiler brand is best for a ~100 m2 home?
No brand is failure‑proof, and every boiler needs annual service. Service technicians rate Bosch highly. Choose accordingly and plan regular maintenance to keep reliability high. [Elektroda, -west, post #18548926]
What boiler power do I need for ~100 m2?
For ~100 m2, about 14 kW maximum is sufficient with reserve. The minimum power matters more. Target 2–3 kW minimum for single‑function, or 3–4 kW for combi. “The lower the minimum power, the better.” [Elektroda, BUCKS, post #18538197]
Should I pick a combi or a 1‑function boiler with a tank?
Flats often use combi boilers. Houses suit a single‑function boiler paired with a hot‑water tank. With a tank, you do not need high peak power for DHW. Pick a unit with low minimum power for heating flexibility. [Elektroda, BUCKS, post #18538197]
How big should the DHW cylinder be for two people?
About 100 liters matches two people who mostly shower, with occasional bathtub use. Plan roughly 3 kW extra power to heat the tank slowly. Instantaneous DHW typically needs over 30 kW, which drives boiler sizing. Upsize if your fixtures demand more. [Elektroda, kankox, post #18550156]
How do I size and plan the boiler quickly?
  1. Use the recommended online calculator to determine building power needs.
  2. Check whether qualified service is available in your area.
  3. Confirm chimney feasibility: air‑flue system, available diameters, lengths, and get a chimney sweep’s opinion. [Elektroda, ls_77, post #18535873]
Is a higher maximum‑power boiler better?
No. Oversizing maximum power is unnecessary here. Focus on low minimum power for steady operation and comfort. A 14 kW class unit is enough for ~100 m2 with reserve. Higher minimum power reduces flexibility. [Elektroda, BUCKS, post #18538197]
How should I connect underfloor heating with radiators?
Do not rely on a simple capillary thermostatic mixing head. It mismatches condensing boilers and lacks weather control. Use a hydraulic coupling, a radiator pump, and a UFH pump with mixer. Control them via boiler automation, or choose one emitter type direct. [Elektroda, ls_77, post #18559537]
Do I need weather compensation for underfloor heating?
Yes. UFH over most of the area needs weather control for stable comfort. Fixed‑temperature mixing causes rooms to swing too hot or too cold. Use boiler automation with the right modules and an outdoor sensor. [Elektroda, ls_77, post #18559537]
What maintenance and protections reduce failures?
Treat hard water to avoid stuck diverter valves, pump failures, and scaled heat exchangers. Fit a water softener or treatment station. Add a magnetic separator on the CH return to protect pumps from debris. These steps cut failure rates materially. [Elektroda, zales.vip, post #18549029]
Should my DHW cylinder include an electric element or solar coil?
Size the tank to actual use and fixtures. A large bathtub or rain shower needs a larger tank. An electric heater in the cylinder provides emergency hot water if the gas boiler fails. If planning solar, choose a larger tank with an extra coil. [Elektroda, TomekO1976, post #18535182]
Do I need extra controllers for secondary pumps or DHW recirculation?
Some boilers include sockets for a second pump or DHW recirculation, like Junkers Cerapur SMART. Budget models may lack this and need additional modules. Plan control needs early to avoid hidden add‑on costs later. [Elektroda, zales.vip, post #18549029]
No gas connection—should I consider a heat pump or a budget gas boiler?
If you lack a gas connection, consider a heat pump seriously. For gas on a budget, Termet Silver 20 kW is inexpensive to buy and service. Expect replacement after 10–12 years. Parts and service for “western” brands can cost 50%+ more. [Elektroda, andrzej lukaszewicz, post #18551904]
How often should I service a gas boiler?
Annually. Every boiler requires yearly service to maintain reliability and safety. Plan and budget for this maintenance interval. [Elektroda, -west, post #18548926]
Do I need a specific flue or chimney for a condensing boiler?
Confirm you can use an air‑flue gas system suitable for condensing boilers. Verify allowed diameters and lengths. Get a chimney sweep’s opinion before purchase and installation. [Elektroda, ls_77, post #18535873]
Any specific model recommended for ~100 m2 with UFH and radiators?
Consider Vaillant ecoTEC PLUS VC 146/5‑5. It offers a strong price‑to‑quality ratio for this size. Packages with 120–200 L DHW tanks are cost‑effective. They include a weather controller and a basic chimney set. [Elektroda, ls_77, post #18559537]